  • Registered Users, Registered Users 2, Paid Member Posts: 1,731 ✭✭✭rx8


    BopperSnr wrote: »
    I received the following quote, What do you folks think?

    I am more inclined to go for the 16 panels with the bigger inverter. I also have an EV in case that impacts anyone's advice.

    16 PANELS 340 WATT 5.44KW JA SOLAR 25 YEAR GUARANTEE.
    5.0 KW SOLIS INVERTER
    4.8 PYLON TEC. BATTERY.
    I BOAST WATER DIVERTER.
    WI FI DONGLE
    10500 EUROS INC. VAT. Minus 3000 euro Grant = 7500 Euros

    Or

    12 PANELS 340 WATT 4.08KW JA SOLAR 25 YEAR GUARANTEE
    3.6 KWSOLIS INVERTER
    4.8 PYLON TEC.BATTERY.
    IBOAST WATER DIVERTER.
    WIFI DONGLE
    9500 EUROS INC. VAT. Minus 3000 euro Grant = 6500 Euros

    Looks good to me but interested in what the group think?

    Get him to price the first one again, without the diverter and with only 1 battery (2.4kwh),that should knock about 1500-2k off it. You don't need 2 batteries and the water diverter is only a gimic most of the time. Add as many panels as you can fit on the "Sunny" side. If you can get that for around 6k nett you'll be getting a good deal.


  • Registered Users, Registered Users 2 Posts: 12,178 ✭✭✭✭DrPhilG


    rx8 wrote: »
    Get him to price the first one again, without the diverter and with only 1 battery (2.4kwh),that should knock about 1500-2k off it.

    Not sure it'll drop it by quite that much. The diverter that this installer uses (and I suspect its the same one you and I used) I believe is about €200 fitted. Losing the second battery will likely drop it by around €1k at most since he'll already be fitting 1 and the second is a 5 minute job to add so only really the value of the battery itself to come off.


  • Registered Users, Registered Users 2 Posts: 157 ✭✭BopperSnr


    championc wrote: »
    Your initial post confirmed a high slant / pitch, so that will be a non-runner realistically. You could look now and see if your NE facing roof surface ever even gets any sunshine ?

    And is your SW facing flat surface butwern any dormer bits coming out from the flat surface, which can throw shading on any part of where you propose to install panels ? You want a clear, unobstructed, view of the southern sun, for as much of the day as possible
    Unfortunately there is a high chimney and a velux window on the SW face which will reduce the number of panels (due to shade and space). I will start looking at the NE roof over the next few days and see if it gets any sun. I also have a brick flat roof shed that I wonder could take panels. But it’s about 20 feet away from the house so would need cables running. I have another installer coming to do a survey next week, so will ask him too what he thinks about the panel situation.


  • Registered Users, Registered Users 2 Posts: 2,683 ✭✭✭SD_DRACULA


    Got a quote of 9k after grant for 6kw, 18*340w qcells, 5kw battery, 6kw solis inverter, still seems quite high to me when you consider the parts are around 6.5k doesn't it?


  • Registered Users, Registered Users 2 Posts: 118 ✭✭Cyloncity


    SD_DRACULA wrote: »
    Got a quote of 9k after grant for 6kw, 18*340w qcells, 5kw battery, 6kw solis inverter, still seems quite high to me when you consider the parts are around 6.5k doesn't it?

    Still better than I was doing and if you think installer is most likely getting it better than 6.5k then that's 6k-ish for a day's work.
    Maybe things might actually be better value when the grant goes!


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 118 ✭✭Cyloncity


    BopperSnr wrote: »
    Unfortunately there is a high chimney and a velux window on the SW face which will reduce the number of panels (due to shade and space). I will start looking at the NE roof over the next few days and see if it gets any sun. I also have a brick flat roof shed that I wonder could take panels. But it’s about 20 feet away from the house so would need cables running. I have another installer coming to do a survey next week, so will ask him too what he thinks about the panel situation.

    If you are dropping down from 8 panels on the SW side. I might question if it's worth it?
    How many would you get on shed roof? If it's flat could you point them at any angle you want?
    Definitely something I'd consider....


  • Posts: 8,756 ✭✭✭ [Deleted User]


    I'm being asked for €9,900 for the below...


    4.08 KW 340 WATT 12 Panels JA Solar

    5.0 Solis Inverter
    4.8 Pylon TEC Battery

    Eddie Water Diverter.


  • Registered Users, Registered Users 2 Posts: 12,178 ✭✭✭✭DrPhilG


    I'm being asked for €9,900 for the below...


    4.08 KW 340 WATT 12 Panels JA Solar

    5.0 Solis Inverter
    4.8 Pylon TEC Battery

    Eddie Water Diverter.
    Pre/post grant?


  • Registered Users, Registered Users 2 Posts: 2,683 ✭✭✭SD_DRACULA


    Cyloncity wrote: »
    Still better than I was doing and if you think installer is most likely getting it better than 6.5k then that's 6k-ish for a day's work.
    Maybe things might actually be better value when the grant goes!

    So even after paying roofer & spark & profit cut, 12k (pre-grant )seems a bit on the high side to me but I think we're in the worst situation now.
    Everyone rushing to install PV before grant goes out, installers are busy AF can turn down jobs if you don't like their high quotes
    Can't see a lot of 12k installs once the grants are out.


  • Registered Users, Registered Users 2 Posts: 6,547 ✭✭✭championc


    BopperSnr wrote: »
    I also have a brick flat roof shed that I wonder could take panels. But it’s about 20 feet away from the house so would need cables running.

    Could be a great option. No reason why it cannot take them. You could put the inverter in the shed and just run an armoured electric cable to your board.

    I have run DC cables from my house roof out the my inverters located in the shed, so there's no issue running AC or DC cables a decent distance


  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 1,731 ✭✭✭rx8


    I'm being asked for €9,900 for the below...


    4.08 KW 340 WATT 12 Panels JA Solar

    5.0 Solis Inverter
    4.8 Pylon TEC Battery

    Eddie Water Diverter.

    That's mad money if it's before the grant and probably still high if it's after it.
    Why do you want 2 batteries with FIT coming in.? You would do better if you got rid of the diverter and put up more panels with the saving.
    Sending you a pm.


  • Posts: 8,756 ✭✭✭ [Deleted User]


    DrPhilG wrote: »
    Pre/post grant?




    PreGrant


  • Posts: 8,756 ✭✭✭ [Deleted User]


    rx8 wrote: »
    That's mad money if it's before the grant and probably still high if it's after it.
    Why do you want 2 batteries with FIT coming in.? You would do better if you got rid of the diverter and put up more panels with the saving.
    Sending you a pm.




    That was the initial quote before even a survey/phone call, just on the email I sent.


    It's before the grant.


    I currently can only heat water from the oil boiler and have to fire that up just to get some hot water. Also have constant queue for showers (parents training each night and 2 active kids). Is it still advisable to shy away from the diverter?


  • Registered Users, Registered Users 2, Paid Member Posts: 1,731 ✭✭✭rx8


    That seems like a lot of hot water there. The diverter will only start working when there is excess energy generated. So the 1st thing to charge will be batteries and then the diverter will kick in. Maybe don't bother with the batteries at all, the difference in the grant is only small. Your excess will then all go into the water heating and to the FIT, once it comes in.


  • Moderators, Home & Garden Moderators Posts: 7,243 Mod ✭✭✭✭graememk




    I currently can only heat water from the oil boiler and have to fire that up just to get some hot water. Also have constant queue for showers (parents training each night and 2 active kids). Is it still advisable to shy away from the diverter?

    When you use the oil to heat hot water, can you only heat the tank?

    You'll not save money with a diverter, but there could be a convenience factor. Also depends on how deep/position of the immersion is, how much of the tank it will heat.

    If you go into this knowing that it's hard for the diverter to pay for itself, and your getting it for convenience, it's up to you to judge if it's worth it.

    Eg my parents. Have a hot water diverter, got it for the summer, so they don't have to keep a fire ticking over for them to have hot water.


  • Posts: 8,756 ✭✭✭ [Deleted User]


    graememk wrote: »
    When you use the oil to heat hot water, can you only heat the tank?

    You'll not save money with a diverter, but there could be a convenience factor. Also depends on how deep/position of the immersion is, how much of the tank it will heat.

    If you go into this knowing that it's hard for the diverter to pay for itself, and your getting it for convenience, it's up to you to judge if it's worth it.

    Eg my parents. Have a hot water diverter, got it for the summer, so they don't have to keep a fire ticking over for them to have hot water.


    Theoretically we should be able to heat just the water tank, in reality, it heats the rads on the way to the tank too.
    2 bedrooms, bathroom, and walk-in


  • Moderators, Home & Garden Moderators Posts: 7,243 Mod ✭✭✭✭graememk


    Theoretically we should be able to heat just the water tank, in reality, it heats the rads on the way to the tank too.
    2 bedrooms, bathroom, and walk-in

    That then could skew things a bit in your favour, in summer.

    I'd look into getting a smart heating control with smart TRVs too


  • Moderators, Sports Moderators Posts: 18,470 Mod ✭✭✭✭slave1


    Family of 4 here, myself, wife and two teenage daughters with long hair so high hot water demand with minimum 5 showers a day.
    So far in April I've let a lot of PV go to the water i.e. 78kWh and as it's all done automatically, there's no flapping around with switches etc.
    Also it is better to consume your PV before letting it go to battery/grid etc.

    Hot Water Diverter is probably financially flat over it's lifetime (as depends on install cost and how long it lasts) but it is very convenient and a lot better that burning fossil fuel.

    All week we've had plenty of hot water, all from the sun

    My stuff on Adverts, mostly Tesla Pre Highland Model 3

    Public Profile active ads for slave1



  • Registered Users, Registered Users 2 Posts: 217 ✭✭Caspero


    SD_DRACULA wrote: »
    Everyone rushing to install PV before grant goes out

    A quick FYI on this point. The SEAI now has an online application where the homeowner just has to submit MPRN, house location and select their solar installer from the drop-down list of SEAI approved installers. The confirmation comes straight away and then you have 8 months to get the installation completed and BER cert.

    So best to get that done as soon as you've picked your installer.

    The site to register your solar grant claim is here: https://mgen.seai.ie/


  • Moderators, Sports Moderators Posts: 18,470 Mod ✭✭✭✭slave1


    I actually thought it was 6 months, 8 months much nicer.

    Solar installers are busy because this is the season for it, lead time much less Oct-Feb

    My stuff on Adverts, mostly Tesla Pre Highland Model 3

    Public Profile active ads for slave1



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,178 ✭✭✭✭DrPhilG


    I confirmed my order in early July. Installer had me live before the end of the month.


  • Registered Users, Registered Users 2 Posts: 680 ✭✭✭Alfagtamini


    Hi all

    Is this a descent quote for 12 panels ?

    https://imgur.com/gallery/CrQumQt

    Thanks


  • Registered Users, Registered Users 2 Posts: 1,469 ✭✭✭MAULBROOK


    Hi all

    Is this a descent quote for 12 panels ?

    https://imgur.com/gallery/CrQumQt

    Thanks

    Not bad but the inverter is too small, reprice with a 6kw Solis invertor. The price difference is very small.Better to be looking at it than looking for it.


  • Registered Users, Registered Users 2 Posts: 680 ✭✭✭Alfagtamini


    MAULBROOK wrote: »
    Not bad but the inverter is too small, reprice with a 6kw Solis invertor. The price difference is very small.Better to be looking at it than looking for it.

    Very true, thank you. I'll get back onto them and see how much extra that wil be.


  • Registered Users, Registered Users 2 Posts: 2,683 ✭✭✭SD_DRACULA


    Yeah it's a good quote before grant for sure, I got quoted 5k after grant for similar, so 8k


  • Registered Users, Registered Users 2 Posts: 521 ✭✭✭WayneEnterprise


    Hi all

    Is this a descent quote for 12 panels ?

    https://imgur.com/gallery/CrQumQt

    Thanks

    Hi there - would you mind sharing who gave that quote?


  • Moderators, Sports Moderators Posts: 18,470 Mod ✭✭✭✭slave1


    Hi all

    Is this a descent quote for 12 panels ?

    https://imgur.com/gallery/CrQumQt

    Thanks

    Not bad, you have a Harvi included, see is it possible to run some Ethernet cable instead, hard wired will always be preferable and is also permanent.
    The cables need to run from PV and Grid feeds back to wherever your are putting your EDDI hot water diverter.

    My stuff on Adverts, mostly Tesla Pre Highland Model 3

    Public Profile active ads for slave1



  • Registered Users, Registered Users 2 Posts: 680 ✭✭✭Alfagtamini


    slave1 wrote: »
    Not bad, you have a Harvi included, see is it possible to run some Ethernet cable instead, hard wired will always be preferable and is also permanent.
    The cables need to run from PV and Grid feeds back to wherever your are putting your EDDI hot water diverter.

    Thanks for that, I'll mention that to the installer. I have ethernet pulled into most rooms and empty ducting so no hassle in using them over wireless


  • Posts: 8,756 ✭✭✭ [Deleted User]


    slave1 wrote: »
    Not bad, you have a Harvi included, see is it possible to run some Ethernet cable instead, hard wired will always be preferable and is also permanent.
    The cables need to run from PV and Grid feeds back to wherever your are putting your EDDI hot water diverter.




    If no ducting then a TPLink EoP be suitable?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 60 ✭✭Lush


    Hi all, hope you can cast your expert eyes over these 2 quotes I've received this week for a single string 8 panel with an Eddi hot water diverter (I currently have a Zappi for my EV). I'm not sold on a battery system as yet as they're so expensive as far as I can make out anyway, happy to be redirected here! Any here are the 2 quotes in question, no names just their quotes:

    QUOTE NUMBER 1
    Equipment costs
    8x LONGI 365W SOLAR PANEL solar panel
    Solis Mini 2000 4G with DC inverter
    Eastron SDM120A Single Phase Energy Meter
    Set of PV warning labels / stickers
    Eddi Immersion Controller
    Harvi Wireless CT Clamp
    Projoy 4 Pole Fire Safety Switch PEFS-EL16-4
    2x KN Newbury 20A 4-pole AC isolator
    KG20-4 DC isolator
    2x Pair of MC4 connectors
    100m reel of 4mm2 solar cable
    8x Renusol end clamp (black)
    12x Renusol mid clamp (black)
    8x Renusol end cap (black)
    20x genius retrofit
    20x Renusol portrait flat tile roof hook
    4x Renusol rail splice
    6x Renusol rail 3.2m silver
    AC Equipment
    misc
    DELIVERY
    Total equipment cost €3,148.75
    Labour costs
    Installation of PV Panels Installation of AC-DC equipment On Site Support
    Total labour and overheads
    €1,300.00
    Total before tax €4,448.75
    VAT at 13.5% €600.58
    Total including tax €5,049.33


    QUOTE NUMBER 2

    8 of 375 Watt Mono Trina PV Module
    Trannergy Inverter model: PVI 2800TL
    Power diverter to divert excess generation to immersion heater eddi
    Fireman switch as per regulation
    AC and DC cabling and isolators.
    Suitable 25 amp type 'B' RCBO protection
    Full label kit to identify all components
    All associated necessary plant and equipment
    Notification to ESB Networks by NC6 form as set out by the 'Conditions Governing the Connection and Operation of Micro- generation', document.
    Full installation of 3 kWp roof mounted PV system.
    All performance testing and commissioning of PV system.
    Full explanation with client of every aspect of the installation and expectations.
    To complete all of our works professionally and efficiently with Safe Systems of Work Practices adhered to with and as little disturbance to clients property as possible.
    As set out by SEAI in grant guidelines to fulfil all of the documentary requirements to enable the successful grant allocation to the client.
    Parts Subtotal
    Amount
    €6,318.00


    Many thanks in advance!