  • Registered Users, Registered Users 2 Posts: 113 ✭✭lausp


    deezell wrote: »
    The Allen relay seems to actuated by a 24v volt supply, from the UFH controller? Your sonoff relays gangs can be wired independent of the mains, I think they are volt free. Simply wiring one of these in series with either the relay actuating voltage, or the connection to the boiler would do.

    I think I understand.

    I was hoping to use the cable already in the home control box marked "brown to gas boiler", (the one I have the phase tester on in the picture) as it already seems to be connected to the Allen but I understand what you are saying.

    Basically I could re route the 24 volt line currently feeding the Allen relay and run it via the sonoff, and leave the timer on constantly and instead use the sonoff as my "timer". I understand and it would work.

    You are 100% correct about the sonoff, it's basically just a 4 gang switch, the gangs are not powered from mains.

    I will have another look in the morning and see if I can figure this out some more. That boiler cable and a few "spare line to home control" cables are bugging me in that box and I would love to get them put to use and tidied up :)


  • Closed Accounts Posts: 844 ✭✭✭CrazyFather1


    I have been hanging around for a few weeks on different websites and I think I got myself a bit of a bargain
    First off I got offer to load 80 pound into Amazon and they give me £85 so that was £5 extra
    Then I checked the Drayton Wiser kits, I always keep an eye on used as I buy loads of stuff which is perfect but just returned
    New set, small imperfections etc etc
    Its the set below with 2 radiator thermostats
    £112 that is including VAT

    https://www.amazon.co.uk/gp/product/B075GSQDZF/ref=ppx_yo_dt_b_asin_title_o00_s00?ie=UTF8&psc=1

    Another one on Amazon if you want to grab a potential bargain
    Now I guess this is the right kit for me with a boiler and heating/hot water zone?


  • Registered Users, Registered Users 2 Posts: 7,711 ✭✭✭deezell


    lausp wrote: »
    I think I understand.

    I was hoping to use the cable already in the home control box marked "brown to gas boiler", (the one I have the phase tester on in the picture) as it already seems to be connected to the Allen but I understand what you are saying.

    Basically I could re route the 24 volt line currently feeding the Allen relay and run it via the sonoff, and leave the timer on constantly and instead use the sonoff as my "timer". I understand and it would work.

    You are 100% correct about the sonoff, it's basically just a 4 gang switch, the gangs are not powered from mains.

    I will have another look in the morning and see if I can figure this out some more. That boiler cable and a few "spare line to home control" cables are bugging me in that box and I would love to get them put to use and tidied up :)

    Yes, that will do. Just keep mains away from any sonoff relay terminals you use. While live mains is habitually used to signal boilers to fire, your boiler requires a volt free closure on 3 and 4 (though it could be internal mains that is being switched). Hence, the original install used an isolating Allen relay. Its also less usual that the boiler call signalling from the UFH unit is 24v, not volt free or mains, again, you don't want to accidentally get mains across this signal if you choose to interrupt it, as it would fry your UFH controller if that is the source, though I do see another transformer on the rack. Anyway, you have it sussed. It will be satisfying to get this function working, set up a heating schedule, if you want use IFTTT or other to create away mode etc.


  • Registered Users, Registered Users 2 Posts: 113 ✭✭lausp


    deezell wrote: »
    Yes, that will do. Just keep mains away from any sonoff relay terminals you use. While live mains is habitually used to signal boilers to fire, your boiler requires a volt free closure on 3 and 4 (though it could be internal mains that is being switched). Hence, the original install used an isolating Allen relay. Its also less usual that the boiler call signalling from the UFH unit is 24v, not volt free or mains, again, you don't want to accidentally get mains across this signal if you choose to interrupt it, as it would fry your UFH controller if that is the source, though I do see another transformer on the rack. Anyway, you have it sussed. It will be satisfying to get this function working, set up a heating schedule, if you want use IFTTT or other to create away mode etc.

    I got in there again this morning and I actually think that the home control box cable is running to the boiler, as well as one from the Allen relay.

    So I suspect that it may be possible to switch the boiler off on its existing main fused switch and use the sonoff to provide power. I have a friend who is an electrician so I might have him have a look at it to be sure.

    Thanks for your help!


  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    Back with more issues...

    My 28-30mm adaptors finally arrived, and I fitted them last night.

    I put a general climate setting on the 3 rooms in question, they're spare rooms, office/gym rooms etc that don't need much heat, but at the same time I don't want them sub zero. So I set a 24 hour minimum of 15 degrees.

    Came in from work today and one was at 17, one at 19 and one at 24!

    So they're not behaving as they should. They're set up correctly and assigned to the rooms, but the one in the 24 degree room in particular was pretty hot.

    Does this suggest that the TRVs are not getting on well with the adaptors? I don't see any other reason why the heat wouldn't go off.

    See attached. And don't laugh, "posh living room" was what I grew up calling a second living room in other people's houses. Now I have one, so it's the posh living room.

    543494.jpg


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    Also not sure if it's relevant, but the rad in the posh living room is now only luke warm at the bottom, but toasty at the top.

    I've turned the heating to "away mode" so that all heat is now off. Also opened the windows in that room to see how it reacts when the temp drops. But the battery thermostat I have in the room reads 19 now. But the TRV stat still says 23.5?


  • Registered Users, Registered Users 2 Posts: 41 steve584


    DrPhilG wrote: »
    Back with more issues...

    My 28-30mm adaptors finally arrived, and I fitted them last night.

    I put a general climate setting on the 3 rooms in question, they're spare rooms, office/gym rooms etc that don't need much heat, but at the same time I don't want them sub zero. So I set a 24 hour minimum of 15 degrees.

    Came in from work today and one was at 17, one at 19 and one at 24!

    So they're not behaving as they should. They're set up correctly and assigned to the rooms, but the one in the 24 degree room in particular was pretty hot.

    Does this suggest that the TRVs are not getting on well with the adaptors? I don't see any other reason why the heat wouldn't go off.

    See attached. And don't laugh, "posh living room" was what I grew up calling a second living room in other people's houses. Now I have one, so it's the posh living room.

    543494.jpg

    Probably a stupid question but I have to ask....you did calibrate them?


  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    steve584 wrote: »
    Probably a stupid question but I have to ask....you did calibrate them?

    That's possibly part of the problem.

    I did calibrate them when adding them. But that living room one that's going haywire didn't calibrate.

    Today I removed it and added it again, and again when I turned the stat to the minus side, it didn't calibrate.

    It also now says that the room is 25 degrees...

    The gym is now also increasing to 20.5 degrees even though the rad is cool.


  • Registered Users, Registered Users 2 Posts: 41 steve584


    DrPhilG wrote: »
    That's possibly part of the problem.

    I did calibrate them when adding them. But that living room one that's going haywire didn't calibrate.

    Today I removed it and added it again, and again when I turned the stat to the minus side, it didn't calibrate.

    It also now says that the room is 25 degrees...

    The gym is now also increasing to 20.5 degrees even though the rad is cool.

    When calibrating did you twist and hold on the plus position until the lights flashed? Then the minus when fitted?

    Another question regarding the adapters, when screwing them on did you feel the adapter pushing in the pin on the valve? I had this problem with one of my adapters which meant though the trv wasn't calling for heat if another room was that rad would heat up. Sorry if that's a bit confusing.


  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    I'll unscrew them all and screw in again.

    I did follow the pairing process correctly. Turn + and hold til green flash, then after pairing turn - and hold til calibration.

    Both stats in the living room are fine, those were a 30mm fitting from the start so no adaptor.

    But the 3 that are using the adaptor are all playing up. All seemed to heat too high, and all are now showing a higher than normal temp despite the heat being off.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    Ps just got home after being out for an hour.

    Rads in all 3 of those rooms are warm.

    The valve definitely isn't closing the pin properly and they're still heating. Since all 3 are doing it to varying levels, I think it's most likely that the adaptors are not fit for purpose.


  • Registered Users, Registered Users 2 Posts: 41 steve584


    DrPhilG wrote: »
    I'll unscrew them all and screw in again.

    I did follow the pairing process correctly. Turn + and hold til green flash, then after pairing turn - and hold til calibration.

    Both stats in the living room are fine, those were a 30mm fitting from the start so no adaptor.

    But the 3 that are using the adaptor are all playing up. All seemed to heat too high, and all are now showing a higher than normal temp despite the heat being off.

    What I did is I put on the adapter and left the trv off. I put on the heating and found the rad heating up so I just unscrewed the adapter a little. I was lucky as this was installed in a rad cover so nobody would be touching it.


  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    Just reset everything in the room again. Took the TRV off and screwed on the adaptor. Made sure that there was resistance but I could push the pin in manually.

    Then reset the TRV again, and added it. This time it did seem to calibrate, blue light came on and the groaning/grinding noise for about 5-10 seconds.

    I'll see how it goes now.


  • Registered Users, Registered Users 2 Posts: 7,711 ✭✭✭deezell


    Adapters are a bit of a minefield. Was looking through some info from Drayton, they linked a company for adapters, they had adapters for the same thread, say 28 to 30, but for differing brands of valve, so even valves with a similar thread might have a different pin depth and travel. I'll try find that link. Can you read the brand name off those 28mm valves?


  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    deezell wrote: »
    Adapters are a bit of a minefield. Was looking through some info from Drayton, they linked a company for adapters, they had adapters for the same thread, say 28 to 30, but for differing brands of valve, so even valves with a similar thread might have a different pin depth and travel. I'll try find that link. Can you read the brand name off those 28mm valves?
    Don't see a brand on them.

    They cost £8 or so each. Plumber says he can replace the joint with a standard 30mm for about a tenner.

    More work as he'll have to drain the system etc but given that the rad in the living room is staying hot at the top but cool at the bottom, he might need to remove and flush it anyway.


  • Registered Users, Registered Users 2 Posts: 41 steve584


    https://www.google.com/url?sa=t&source=web&rct=j&url=https://wiser.draytoncontrols.co.uk/sites/default/files/documents/lm07-019_schneider_wiser_adapter_guide_2020.pdf&ved=2ahUKEwjctZfsw-fuAhUIahUIHQCFDoEQFjAAegQIARAB&usg=AOvVaw1-xTBtqBkL3b7-ihB8UlUq

    This was the guide they sent me when I asked. None of them were any good for me as my valves were 28 x 1.0 thread.

    I've read about guy's getting a dremmel to shave a bit off the valve pin to stop the adapter from pushing the pin in.

    I eventually moved the trv from my troublesome valve as I felt a priority elsewhere. However if I needed it tight I'd have tried finding a washer to sit into the adapter to offset the adapter pushing in the pin.


  • Registered Users, Registered Users 2 Posts: 7,711 ✭✭✭deezell


    DrPhilG wrote: »
    Don't see a brand on them.

    They cost £8 or so each. Plumber says he can replace the joint with a standard 30mm for about a tenner.

    More work as he'll have to drain the system etc but given that the rad in the living room is staying hot at the top but cool at the bottom, he might need to remove and flush it anyway.
    Defo change the valve is the best option, have them all standard 30mm. If its not breaking the bank, go for it.


  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    deezell wrote: »
    Defo change the valve is the best option, have them all standard 30mm. If its not breaking the bank, go for it.

    Yeah for the sale of a few quid extra each it's the better option.

    1 I could excuse as a faulty TRV or faulty adaptor, but all 3 is definitely suspect.

    Although I'm pondering if that TRV in the posh living room is faulty anyway. Just popped in there. Rad is warm but far from scorching. Battery stat says 21 degrees. Rad stat still says 23.5.


  • Registered Users, Registered Users 2 Posts: 7,711 ✭✭✭deezell


    Have you placed the battery stat in the same location as the TRV, say sitting on top if it. It might read a bit higher so close to the radiant heat of the rad.


  • Registered Users, Registered Users 2 Posts: 6,467 ✭✭✭championc


    I have to say that the Tado solution is fantastic the way they include an adapter pack which appears to cater for 100's it potential TRV's


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    deezell wrote: »
    Have you placed the battery stat in the same location as the TRV, say sitting on top if it. It might read a bit higher so close to the radiant heat of the rad.

    I've disconnected the 3 stats now and put the old ones back.

    Left the Wiser stats sitting side by side with the battery ones to check.


  • Registered Users, Registered Users 2 Posts: 12,975 ✭✭✭✭DrPhilG


    DrPhilG wrote: »
    I've disconnected the 3 stats now and put the old ones back.

    Left the Wiser stats sitting side by side with the battery ones to check.

    And interestingly, all 3 TRVs and digital stats are now accurate to within half a degree of each other (because the little digital ones round up.


  • Closed Accounts Posts: 844 ✭✭✭CrazyFather1


    Just bought the Wiser and hope it arrives tomorrow. Should I be concerned the rad stats won't work? or do I need to buy something now.

    Was going Tado but I decided against because of the recurring charge.


  • Registered Users, Registered Users 2 Posts: 6,467 ✭✭✭championc


    Was going Tado but I decided against because of the recurring charge.

    That only applies to the Open Window detection and Geofencing options. And by buying a v3 bridge second hand, you can then have those options for free.

    I certainly was never aware of the Drayton TRV's not being supplied with all possible combos of adapters. The Tado comes with a bag full.


  • Registered Users, Registered Users 2 Posts: 41 steve584


    Just bought the Wiser and hope it arrives tomorrow. Should I be concerned the rad stats won't work? or do I need to buy something now.

    Was going Tado but I decided against because of the recurring charge.

    The only issue I've had is I needed to get adapters for the rad valves as mine were 28mm diameter with a 1.0 thread. The Wiser only comes with 1 adapter however if your valves are 30 x 1.5 you should be fine.


  • Closed Accounts Posts: 844 ✭✭✭CrazyFather1


    Thanks for all the help, I currently have a climote. Which was supposed to be taken out but the electrician hasn't come with covid. I took it off and had a look at the back plane.

    Am I correct the wiring on the climote is the same as a standard? e.g. the 1234 on the climote will be the same as the standard back place?


  • Registered Users, Registered Users 2 Posts: 7,711 ✭✭✭deezell


    Thanks for all the help, I currently have a climote. Which was supposed to be taken out but the electrician hasn't come with covid. I took it off and had a look at the back plane.

    Am I correct the wiring on the climote is the same as a standard? e.g. the 1234 on the climote will be the same as the standard back place?

    Yes, the base for the 2 zone wiser hubr is the same as your second image, which is an eziprog. N, L, then HW on 3 and CH on 4. Discard the links to 1 and 2, COM is wired internally. Note that the Climote is the reverse on 3 and 4, CH on 3 and HW on 4, so reverse black and grey wires.

    543648.jpg


  • Closed Accounts Posts: 844 ✭✭✭CrazyFather1


    Thanks, the eziprog was supposed to be installed a few weeks back The Climote is going into a holiday home. Looks like I might be trying to do myself

    So from the image

    I will have 1 & 2 not connected
    3 will be black wire and 4 will be grey?


  • Registered Users, Registered Users 2 Posts: 7,711 ✭✭✭deezell


    Thanks, the eziprog was supposed to be installed a few weeks back The Climote is going into a holiday home. Looks like I might be trying to do myself

    So from the image

    I will have 1 & 2 not connected
    3 will be black wire and 4 will be grey?

    Yes, for either the eziprog or the Wiser you're expecting.


  • Advertisement
  • Closed Accounts Posts: 844 ✭✭✭CrazyFather1


    deezell wrote: »
    Yes, for either the eziprog or the Wiser you're expecting.

    Installed there eziprog this morning and up and running with no issues. Then of course the electrician rings and says he is on way over. Has to come for other jobs so will let him have a look

    The new Drayton system arriving today as well, have to love Amazon Prime, order on Saturday and arrive on Monday, even with Brexit