What's the difference here?

Comments

  • Registered Users, Registered Users 2 Posts: 8,560 ✭✭✭K.Flyer


    There is no difference, both radiators are the same.
    If you look at the specifications for the Stelrad radiator on Stelrad's website you will see that they state the btu/hr output for that radiator as 8273 btu at Delta T.50. When you look at the specification info on the best heating site for the radiator at Delta T.50 its the same, but they also quote the higher btu output at Delta T.60.


  • Registered Users, Registered Users 2 Posts: 369 ✭✭teflon


    K.Flyer wrote: »
    There is no difference, both radiators are the same.
    If you look at the specifications for the Stelrad radiator on Stelrad's website you will see that they state the btu/hr output for that radiator as 8273 btu at Delta T.50. When you look at the specification info on the best heating site for the radiator at Delta T.50 its the same, but they also quote the higher btu output at Delta T.60.

    Thanks for that. Is it possible so to achieve the higher btu?


  • Registered Users, Registered Users 2 Posts: 3,916 ✭✭✭John.G


    It is, just about, the specified deltaT is the mean radiator temperature minus the required room temp (generally accepted as 20C).
    So the normal DeltaT.50 would require flow/return temps of 75/65C, mean of 70C, minus 20C = 50C.
    DeltaT.60 would require flow/return temps of 85/75C, mean of 80C, minus 20C = 60C.