Back boiler issue

  • 21-12-2020 11:51AM
    #1
    Registered Users, Registered Users 2 Posts: 2,648 ✭✭✭


    Hi,


    So my house has oil central heating and a back boiler to my stove in the kitchen.


    Issue I have at the moment - Oil seems to heat the radiators fine.
    If I put the stove on the pipes make a number of noises the radiators do not seem to be that hot but the hot water is being spat out into the hot water over flow tank in the attic.


    I have seen this issue before but only because the thermostat is set too high so I was thinking the thermostat might be gone anyone know how I would check that?


Comments

  • Registered Users, Registered Users 2 Posts: 3,916 ✭✭✭John.G


    What is its setting now?
    Keep turning it down until the pump starts, you should also hear a click from the stat, if not, turn the stat up until you hear a click on the way up, if "clicking" OK problem is with wiring or the pump.


  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    those pump stats are nearly bomb proof as john says id guess pump