Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Cable size from inverter

Options
  • 13-10-2019 9:34pm
    #1
    Registered Users Posts: 297 ✭✭


    Just checking what size cable you would recommend going from the inverter to the board for a 4.7kw solar setup covering a distance of about 30m


Comments

  • Registered Users Posts: 2,822 ✭✭✭air


    spose wrote: »
    Just checking what size cable you would recommend going from the inverter to the board for a 4.7kw solar setup covering a distance of about 30m

    Go 10sq minimum to limit the voltage rise, worth it for the small increase in marginal cost.
    Your electrician will have the final say anyway.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    Link

    Max operational current +20% overhead.
    Panels to inverter < 3% voltage drop.
    Inverter to CU < 3% voltage drop.
    Charger to battery ~1% voltage drop depending on nominal battery voltage.


Advertisement