    Hi lads,

    So i got a renovation and asked the electrician to wire a supply to the shed in ductingfor an eventual few sockets and lights as I was going to turn it into a gym. I asked him what breaker would go in the main board and sub board and he said a 32amp breaker on each end feeding a 20amp and 10amp for sockets and lights.

    Does that sound right? Looks like a 4sq nym-j cable running from board to shed.


Comments

  • Registered Users, Registered Users 2 Posts: 10,934 ✭✭✭✭Stoner


    I'm sure he had an 32 amp rated isolater at one end and the 32 amp breaker at the other

    Or a 32 amp breaker feeding a 25 amp breaker wouldn't really have the same size breaker at either end.

    Most sub boards under 100 amps are fed by an disconnection device with a breaker at the sub board side


  • Registered Users, Registered Users 2 Posts: 1,856 ✭✭✭Phil.x


    GSPfan wrote: »
    Hi lads,

    So i got a renovation and asked the electrician to wire a supply to the shed in ductingfor an eventual few sockets and lights as I was going to turn it into a gym. I asked him what breaker would go in the main board and sub board and he said a 32amp breaker on each end feeding a 20amp and 10amp for sockets and lights.

    Does that sound right? Looks like a 4sq nym-j cable running from board to shed.

    Ive a 6 square swa with a 25amp rcbo at the house and a single row board in the shed.

    A 32amp rcbo is ok with that square cable, cables outdoor have a higher current rating.
    It has to be a mcb + elcb or rcbo for protection.


  • Registered Users, Registered Users 2 Posts: 7,843 ✭✭✭GSPfan


    Just checked the supply cable and it’s actually 6sq mm.