Gas Boiler Integral By Pass

Comments

  • Registered Users, Registered Users 2 Posts: 1,019 ✭✭✭anthonyos


    There is no plate heat exchanger in an intergas afaik


  • Registered Users, Registered Users 2 Posts: 3,916 ✭✭✭John.G


    anthonyos wrote: »
    There is no plate heat exchanger in an intergas afaik

    That,s right (or no diverter valve) but I'm talking about a conventional combi boiler like the one (Baxi) above that states it has this integral by pass?


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Hi John, its a small bore pipe between flow/return with a spring loaded bypass valve (so would only open when the pump is running but the system flow is blocked (by a closed motorised valve) and is designed to accommodate pump over-run.

    It is however always recommended to install a system bypass and auto-bypass valve external to the appliance.