Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Air to Water Heat Pump Defrosting

  • 19-08-2018 5:23pm
    #1
    Registered Users, Registered Users 2 Posts: 3,562 ✭✭✭


    Re the above: I understand that in Reverse Cycle Defrosting (RCD) that the outside unit (Evaporator) fan is stopped, the reversing valve changes over, the hot gas from the compressor discharge is directed to the evaporator (to melt the accumulated ice) and the liquid refrigerant is then expanded through another? expansion valve into the condenser? and returns to the compressor suction.
    My question is: Where does the heat come from that is required to evaporate that liquid refrigerant?, is it from the residual heat in the heat exchanger and is the circulating pump left running to the UFH (or rads) and is a auxiliary heating device like a electric heating element switched in while the defrost cycle is on.?. Thanks.


Comments

  • Registered Users, Registered Users 2 Posts: 239 ✭✭ShanE90


    The heat source for defrost comes from the heating circuit as there wouldn’t be enough heat in the indoor heat exchanger alone to perform a successful defrost of the outdoor coil. The circulating pump is left running to prevent the heat exchanger from freezing and to supply the needed heat for defrost. There is a minimum water volume that is Always required be in circuit to be available to “defrost into”. Systems with low water volume may require a volume tank for defrost and short cycling purposes. The immersion heater isn’t normally used for defrost it’s purpose it to provide backup heat for DHW and to bring the DHW tank past 60degC for sanitization.


  • Registered Users, Registered Users 2 Posts: 3,562 ✭✭✭John.G


    ShanE90 wrote: »
    The heat source for defrost comes from the heating circuit as there wouldn’t be enough heat in the indoor heat exchanger alone to perform a successful defrost of the outdoor coil. The circulating pump is left running to prevent the heat exchanger from freezing and to supply the needed heat for defrost. There is a minimum water volume that is Always required be in circuit to be available to “defrost into”. Systems with low water volume may require a volume tank for defrost and short cycling purposes. The immersion heater isn’t normally used for defrost it’s purpose it to provide backup heat for DHW and to bring the DHW tank past 60degC for sanitization.

    Thanks, what kind of temperature drop might you expect to see in a circulating system at the end of a defrost cycle from say heating mode conditions of 35C/30C flow/return.


Advertisement