Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

PV wiring size

  • 29-04-2018 9:23am
    #1
    Registered Users Posts: 28


    Hi all,
    I have a sunnyboy 4000tl and have bought 15 axitech AC-260P/156-60S. The SMA design tool calculated wiring of 1.5 mm diameter, i have bought 4mm solar cable, but wanted to double check, its the right size, the panels are 30 mtres from garage where inverter is, looked at online calculator, the VDC for the system is 15 panels so 360vdc? , so the calculator is saying wire diameter of 1.5 mm. I intend to wire the panels in a single string, as the tool states that the max voltage is below the max the inverter can handle. All help appreciated


Comments

  • Registered Users, Registered Users 2 Posts: 1,111 ✭✭✭freddyuk


    AC-260P/156-60S VOC is 38v so string voc = 38 * 15 ?? You also need to take into account the temperature coefficient.... which will increase the VOC in colder temperatures. Inverter limit is 750v so you are within the acceptable range.
    4mm cable would be the standard acceptable size so this is correct.
    The inverter will unlikely be at best efficiency as it is oversized for the system. Normally 80% of the total installed wattage is more efficient so a 3600tl would be a closer match but I have not run the designer.


  • Registered Users, Registered Users 2 Posts: 1,627 ✭✭✭quentingargan


    If you are burying the cables in walls, solar cable might not be ideal. Under UK MCS standards, solar cable can only be used where it is visible. Otherwise it should be in separate steel trunks or SWA. See attached. This is because you cannot fuse a single string so there is no protection.


  • Registered Users Posts: 28 Pauldub


    Thank you for the replies, much appreciated. I am not burying the cable in the fabric of the garage. It will run up outside wall through flexible conduit, then in through DC Disconnect isolator, into conduit into garage, both cable into single conduit, then to inverter. Great PDF, very informative,

    I was just double checking cable size, as its very important. Thanks again


  • Posts: 5,238 ✭✭✭ [Deleted User]


    so there is no protection.

    The protection is the cable is rated to handle peak fault current.