Garage wiring 16amp circuit

  • 11-03-2018 11:36PM
    #1
    Registered Users, Registered Users 2, Paid Member Posts: 3,456 ✭✭✭


    Hi all,

    I recently bought a table saw that requires a 16amp circuit. Can I run this from a 20amp mcb at the CU via 2.5 or even 4 T&E into a blue socket? Some people say T&E should not be used. Surely it would be ok if I install steel conduit ?


Comments

  • Registered Users, Registered Users 2 Posts: 24 davemc1987


    Hi,

    2.5 or 4 T&E should be fine if you use the conduit to protect it.

    If no conduit then the correct option would be SWA (Steel Wire Armoured) Cable.

    /Dave