Amperage into house

  • 30-03-2025 11:44PM
    #1
    Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭


    was reading somewhere recently that there should be a minimum of 100amps going into a house, I looked into the box at the side of the house and there’s a picture attached

    we do get quite a few cut outs where the main switch in the consumer unit trips, switch it back up and all is ok again 🤷🏼‍♂️

    Wonder what is, if any, the issues with having a 60/80amps vs. a 100amp unit into the house??


    any help/advice would be appreciated, TIA


    maybe it doesn’t matter and the cut outs are just one of those things🤷🏼‍♂️

    6486234C-6DBE-4721-967B-D83DFEB99F8B.png


Comments

  • Registered Users, Registered Users 2 Posts: 13,341 ✭✭✭✭Calahonda52


    Where did u read that: I dont believe it is correct to say 100

    You should never think this

    maybe it doesn’t matter and the cut outs are just one of those things

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    i can’t actually remember but I did google it and it states new homes are Min 100amp



  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    Yeh that’s why I created a post to get some advice from the experts



  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    thanks, and would there be any benefit to have a sparks change that to a 100/200 or more amps?

    Or would that be an ESBN job?



  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    any tangible benefit to having it increased to at least 100amps? It’s a 5 bed detached house



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 13,341 ✭✭✭✭Calahonda52


    OP you need to deal with this

    we do get quite a few cut outs where the main switch in the consumer unit trips, switch it back up and all is ok again 🤷🏼‍♂️

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    Well there’s nothing specific, maybe when the shower is on but in the main no specific reason


    in not enquiring into why it trips though



  • Registered Users, Registered Users 2 Posts: 13,341 ✭✭✭✭Calahonda52


    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    Well it says that there is a bigger family hence more use of power



  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    nice language, it tells you that there’s 4 showers and 7 people in the house so one could gather draw from the amount of people in the house no, given the number of bedrooms? Maybe not

    All of the above are used, except a welder



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    a bit humpy aren’t you

    thanks for your contribution



  • Registered Users, Registered Users 2 Posts: 251 ✭✭JL spark


    another thing to factor is ,

    Upgrading your esb supply ,

    New mains cable

    New 16kva rated fuseboard

    Testing of whole house

    All above if done properly,adds a lot to the cost 1000s



  • Registered Users, Registered Users 2 Posts: 24,280 ✭✭✭✭ted1


    You need to look at the issue. There is obviously an issue somewhere.

    Was the shower installed after the house was built. If you are tripping for over current a priority switch should have been fitted


    there may be an easy fix, it might just be faulty breaker



  • Registered Users, Registered Users 2 Posts: 24,280 ✭✭✭✭ted1


    Tells us nothing. The 4 showers could be gas heated..



  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    Thanks will get an electrician in, there is a new electric shower in place of an original one, Triton t90 for new version but not sure if the “cut outs” are only since that was installed. I’d have to check with the boss 😜, the cut outs aren’t regular and not specific to the shower being on though, I watched to see if it happened when a shower, washing machine and dishwasher was on together but no, nothing happened. Hard to pin down



  • Registered Users, Registered Users 2 Posts: 1,062 ✭✭✭geographica


    1 electric (Triton where water heater at the unit)

    3 pumped electric (where water used is from hot water cylinder)


    max only two used at once