Soot build up in oil boiler

  • 17-03-2025 02:00PM
    #1
    Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭


    Hi,

    I'm having ongoing issues with the oil burner not burning clean. This then means the photocell is getting blocked and it's not firing up.

    I've kept it servided since we moved in and the boiler service guy has called a couple of times to check the gas comosition and clean it out. THis time he modified the baffles a litte and was confident this would sort it.

    I'm wondering if the fact that I've put a new door and new window in the shed so there's now no draught would impact things. When he's checking the flu gas the door could be open or was open recently so the air is fresh. What I don't know is how to check if I have a balanced flu or a standard one. If it is a balanced one my theory would probably carry little weight!

    The boiler was serviced last March, it then wasn't used until mid November and a month later the photocell issue arose. I have to clean it every couple of days so the incomplete burning is quite bad.

    The boiler is a Firebird Enviromax Popular 26kW installed 19 April 2010. That's a photo of the flu.

    I did email firebird and the asked for some info but I'm waiting on them to get back to me.

    IMG_20250125_203007.jpg


Comments

  • Moderators, Home & Garden Moderators Posts: 6,514 Mod ✭✭✭✭Wearb


    It's most likely a balanced flue, but possibly not being used like that. Sometimes the flue seal breaks down and the tech might pull the snorkel pipe off.

    Take off the front cover and take a few pics, also of both ends of the flexible air pipe.



  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    you need to stop cleaning the photocell this is only making the problem worse and stop using boiler

    these boilers can be a bitch to set up properly do you have a print out of the flugas analysis post pic if you have

    they are also suspect to wind direction because of the burner been on top



  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    is this discharging in to a confined area looks like it is in pic you posted

    also post pic of very bottom of boiler where the plastic hose is connected



  • Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭mp3ireland2


    Hi thanks for the interest. It's discharing out the back of a garden, it's not very sheltered. The photo may have been misleading.

    I don't have a print out unfortunately.

    When you say take off the cover fix you mean the wire guard or is there another cover? I didn't get a chance to do either but I did get some photos. I'll take off cover tomorrow.

    The holes in the second photo are underneath the flue

    IMG_20250317_185110.jpg IMG_20250317_185012.jpg IMG_20250317_184930.jpg IMG_20250317_184925.jpg IMG_20250317_184917.jpg

    Hopefully some of the photos are useful. Maybe it is just coincidence that this issue occurred after I replaced the door and window in the shed but it was just a thought I had.



  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    on the last pic can you post a photo of the front where there is a little dial showing numbers

    door and window not the issue as the air is been taken from the outside with the balance flu hose



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭mp3ireland2


    IMG_20250317_210448.jpg

    Here's the numbers.



  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    theres your issue boiler is way under aired you need a new service person that knows what their at

    these boilers are usually around 3.5 to 4 on that dial

    VERY IMPORTANT you do not adjust this yourself as its done in conjunction with a nozzle change and pressure gauge to check boiler is running at manf recommended pressure

    to go adjusting this yourself could lead to a boiler producing dangerously high carbon monoxide levels

    this applies to any boiler not just yours

    its an easy fix for somebody with experience



  • Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭mp3ireland2


    Thanks, it's disappointing that the original servicer didn't pick up on this.

    With no knowledge on the subject, I would have assumed a flue gas analysis would have indicated it was underaired so it's strange that he didn't pick it up.

    Thanks for your advice.



  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    the thing with this boiler it needs more air than the manf paperwork recommend

    its a long story but but but



  • Registered Users, Registered Users 2 Posts: 2,011 ✭✭✭Lenar3556


    The core issue is more rooted in the boiler design, than the service person. Firebird had some great boilers in the past but really let themselves down when they released this one. There has been various improvements since, but they have struggled to regain market share.

    The solution to your issue is to have your service person use the following settings;

    0.6 80ES Nozzle

    Oil Pump pressure: 9.5 bar.

    CO2 - 11.2% max

    Remove flap from snorkel on balanced flue.

    Replace condensate trap with stainless steel variant and renew condensate hose.

    Clean the whole thing out and it should be ok.

    Fit a grant vortex the next time.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    agree 100% but if the service person doesnt know the fix and goes by the book



  • Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭mp3ireland2


    Thanks all, I contaced my service guy and he wasn't aware of the updated settings, he was going by the book. I told him I was in touch with Damien in firebird and I got some information about updated setttings to get around the design flaw…I then shared the info provided above. I was in touch with Damien but he didn't get back to me lately. The service guy was going by the orignal settings: .65 80 es nozzle and 11.5 on co2 8 bar oil pressure



  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    in theory its an upside down boiler

    the design is trying to force heat down when it naturally wants to rise good idea to hold as much heat in the chamber for as long as possible

    but the flue way up the back of the boiler was too narrow and restricted the gasses from getting away cleanly

    firebird cant for obvious reasons are not going to admit this

    lenars post above explains the fix perfectly

    the little bit of efficiency lost is not even 1% and a lot better than a sooty boiler once a month

    as stated earlier cleaning the photocell to keep the boiler running is only making the problem worse as you are sooting it up more

    you are fixing the problem not the cause



  • Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭mp3ireland2


    Adjusted boiler to new settings, and upgraded/replaced parts as per guidance above but still getting the build up.

    Could something have failed that would cause this?

    The boiler was working ok on the manufactuing settings for a couple of years, i would only need to clean the sensor once per year (not ideal I know), so I don't know what changed that it was then a weekly or even more frequent failure. WE were keeping the same settings and getting it serviced once a year.

    The boiler isn't kicking in as much now with the warmer weather so it's hard to tell if things did improved as I'd expect it to take longer to clog up when running less.

    Maybe i should get a second boiler repair person but I'd like to find somebody who already knows about the Firebird settings ideally and familiar with it. Suppose I'll just need to contact some people and ask



  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    what area are you in maybe somebody on here may be able to help and cover your area



  • Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭mp3ireland2


    I'm in Gorey in Wexford, one of the lads on here did give me the name of a guy in county Wexford that he rated highly, but unfortunately he didn't come up at far as Gorey he said.

    Its a frustrating one, and I'm guessing a new boiler would be about 3.5k installed so worth getting a second look.

    It's 16 years old, wood you typically get more than that?



  • Moderators, Home & Garden Moderators Posts: 6,514 Mod ✭✭✭✭Wearb


    You should keep it going until it leaks water. 16 years is about 2/3rd lifespan for a well installed and maintained one. They do benefit from an automatic bypass.



  • Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭mp3ireland2


    Thanks, hopefully I can get to the bottom of this issue!



  • Moderators, Home & Garden Moderators Posts: 6,514 Mod ✭✭✭✭Wearb


    What's the condition of the baffles. Did you ever take a pic when the service guy had them out?

    Are the electrodes property set? Is the head burned?



  • Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭mp3ireland2


    I'm afraid I've always been at work when he was here so I've never had a chance to check anything.

    I would hope that he'd be aware of the things you mention as they sound like standard things you'd check during a service, especially if he knows there's an issue….however I've no way to know.

    He did mention that the baffles can be a factor and he cut the corners off them, I'm not sure if that sounds like the right thing to do?



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,514 Mod ✭✭✭✭Wearb


    I've never done that (though i wouldn't be too critical of it) to the baffles. Some of the experienced lads on here have bent the corners a little. I've never done it. I've found that setting to lowest allowed output and about 0.2% lower co2 than recommended by manual (always allowing for air inlet temperature) works for me. AND of course a properly done annual service.

    You might need to replace a couple of baffles after about a decade. Badly warped baffles can make them difficult to setup properly and shorten the period needed between service.

    Those boilers do have the weakness mentioned, but can be OK with proper annual service. Otherwise they can have a snowball effect of escalating problems and shortened lifespan.

    Oil boilers are worth looking after as they have a depreciation of about €200 per year, so every year extra is worth €200.



  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    just had a look back there at all the photos you posted

    post 5 shows the flue discharge but it doesnt seem to have a diverter for the flue gasses

    in other words the air intake can be contaminated by the discharging gasses

    especially if the wind is blowing in the wrong direction and into the flue

    a 1mtr plume kit to take the discharge higher would certainly be a help

    have you noticed the photocell issue worse with windy conditions



  • Registered Users, Registered Users 2 Posts: 4,005 ✭✭✭jimf


    to test for contaminated air intake you need a flugas analyser

    to do above a small hole is made in the air intake hose and the probe of the analyser is inserted

    air intake should be reading 20.9 % if fluctuating its a problem



  • Registered Users, Registered Users 2 Posts: 1,891 ✭✭✭mp3ireland2


    I haven't noticed any wind related issues but I suppose it's not an instant thing, it's more of a gradual build up so it's hard to know .

    I suppose the thing that could rule this out a bit, would be for the first two years after we moved in, it wasn't a very bad issue .. Clean it once a year but something changed the past year

    I assume the service guy would have noticed the flu gas composition being off.

    I had seen mention of those kits in other forums. Appreciate you taking the time to look into it