Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

My DIY installed Vaillant AroTherm Plus is now LIVE

  • 01-10-2024 12:49pm
    #1
    Registered Users Posts: 6,202 ✭✭✭


    Live link to my system data - https://emoncms.org/app/view?name=championc&readkey=5e5a2bd11d69740be46a55e1793e551d

    Well, after months of planning, research (between blogs, FB posts and YT videos), my Vaillant AroTherm + is now Live and up and running. While there is no Irish support, Vaillant Technical Dept in the UK have been very helpful with queries, and the UK FB group is very active, with several of the prominent YouTuber installers and users on there too. And of course, the Vaillant is always up there at the top of the www.heatpumpmonitor.org charts. The potential for running the AroTherm at higher temperatures, given that it’s R290 Propane based, meant that I could, in theory, run at gas boiler temperatures, if push comes to shove.

    Overall, it has been a fairly painless experience.

    We have a 3 bed Semi-D in Sth Dublin. We currently have a Vaillant Combi non-condensing non-modulating Gas boiler (so only around 60 – 65% efficient). I figured that evening running the AroTherm + at high temperatures, I would still have better efficiency. We also have a 30 Tube Kingspan Solarmax solar tubes installation since 2012. The tank has no spare coils and with the Kingspan working very well, it made sense to leave well enough alone.

    Last November, I started using the MyEnergi Eddi to heat water to 60 deg overnight (on 5c/kWh Pinergy was a no-brainer). The tubes did an additional topup during the day on good days. If necessary, I could boost with the MyEnergi app in the evening if required. This meant I could stop using Gas and the Combi for DHW, and that worked very successfully over last winter. I had also lowered the CH Max flow temp as a way of understanding how a lower rads temperature might work out.

    Therefore, the DHW requirement (and associated potential pipework) was removed completely from the plan. We currently use the Tado system with electronic TRV’s on all rads. We don’t heat all rads all of the time currently, but I am open to including more usage of ones which are currently less used. While efficiency is important, I want to run economically (even at the expense of efficiency). With no UFH, it made sense not to install a buffer tank. With sufficient capacity in the rads for defrosting too, there was no need to have to consider adding a volumizer either.

    So the AroTherm flow and return would simply be T’d into the existing rads circuits.

    I started with doing a heatloss calculation using https://heatpunk.co.uk and concluded I needed a 5kW unit, especially since I knew I still wouldn’t be heating the whole house constantly. Mind you, I was pretty certain of this size, based on blogs and YT videos for similar properties.

    The first decision was the outdoor unit location. I had considered locating it in the side passageway, backing straight onto the wall of the combi. But it would have been blowing straight onto the neighbours house side wall, and would have narrowed the access considerably, since I will likely wrap the house next year, and so that would reduce the gap by a further 100mm. Airflow between both houses wouldn’t have been great either. So I went with the back garden, backing onto the boundary wall. I used M10 bolts screwed into zebedee’s for mounting and levelling. It is very important for the unit to be perfectly horizontal and vertical is all directions

    The next decision was the arrangements of the pipework accessories. I got an Inta 1 ¼” to 1” valve for the flow, and an Impel 1” Filter & Mag valve on the return after a 1 ¼” to 1” reducer, with 1” Flexi hoses. I also got a 1” Anti-Freeze valve and a 1” Fill & Flush valve ( https://www.heiz24.de/Flushing-and-filling-unit-DN-25-1-internal-thread-2xKFE-12-NEW - a fantasic buy). I ended up putting the Filter, Anti-Freeze and Fill & Flush in series, after the Flexi hose.

    Threaded joints are an absolute nightmare. However, when in Chadwicks, a Polish customer recommended Sellador thread locker. It was absolutely brilliant. So no tape anywhere – used this on ALL threaded joints.

    From there, it was 1” copper all the way into the house. The pipes are lagged with Primary Pro insulation, which took some amount of tracking down to get (https://spares-direct.co.uk in Belfast). But it is far superior to the €1 per meter crap.

    Inside the house, a pair of 1” x ¾” x ¾” 318’s linked the new 1” incommer into the upstairs and downstairs ¾” circuits. My main sitting room and hall rads branched off the dining room, over ½” pipes. I needed to add another rad into the sitting room, so this section of pipework had to be upgraded to ¾” or I could have ended up with flow issues. So while it was a pain, it was the proper thing to do.

    So a last word on the Copper pipework. I am sorry I didn’t get “tectite” ( https://www.pipelife.ie/plumbing-systems/plumbing-heating-fittings/tectite.html ) push fittings.

    The 1” compression joints were an absolute nightmare to seal fully. I had to use PTFE tape on several of the olives. The Fill & Flush became invaluable, being able to pressurise and leak-test pipe sections (once you capped off both ends and have a pressure gauge connected), or being able to almost flush the whole system through at will, especially to flush through a single rad if required (by closing all others).

    I also bought Climaflex for insulating the indoor underfloor pipework https://www.amazon.co.uk/Climaflex-Pipe-Insulation-Foam-Lagging/dp/B07FMC58NB

    The electrical connections are very straight forward. There are two wires needed for the outdoor unit – a 2.5mm T&E for the AC power, and a 2 wire 0.75mm cable for the eBus, linked back to where you locate the indoor controller.

    I bought the SensoComfort Wireless Controller VRC 720f/3, who’s receiver is also linked to the ebus. I also bought an https://ebusd.de dongle, to extract all of the data locally from the system, for feeding into Home Assistant (and to upload data to heatpumpmonitor.org). It is USB powered, which I powered from a mains to USB adapter https://www.aliexpress.com/item/1005007009749779.html?channel=twinner , which I then buried inside the controller itself. I ran a spare Cat5 out to the outdoor unit, but I don’t see an immediate need for it.

    I also linked my TADO Extension Kit controller to a port on the indoor controller, which enables the TADO to control the On/Off of the Heat Pump. The Extension Kit can do a Potential Free NO or NC connection.

    As a cheap extra option, while doing the install, I bought and installed the Cooling Plug to enable to cooling function of the unit. This one is about £7 (part No. 0020266328) and is officially for a Vaillant Gas Boiler, but it works perfectly. The official AroTherm one is over £300 – go figure !!!



Comments

  • Registered Users, Registered Users 2 Posts: 7,647 ✭✭✭10-10-20


    Hi ya, well done.

    So did you have to get somebody in to gas the unit or how did that work?



  • Moderators, Home & Garden Moderators Posts: 6,343 Mod ✭✭✭✭graememk


    It comes prefilled, as it's a monobloc.

    The refrigerant never leaves the heatpump



  • Registered Users, Registered Users 2 Posts: 2,200 ✭✭✭Paul Kiernan


    Good job, championc. So are the boiler and heatpump both connected in parallel to the heating circuit? Or did you disconnect the boiler? Do you still have option of using the combi for DHW and if so how is it tied into the EDDI/Tubes setup?



  • Registered Users Posts: 6,202 ✭✭✭championc


    It is paralleled, with level / disconnects on the flow and return, so those can easily be reopened and the levers to the heat pump closed off.

    However, it became apparent on day one, that it had no problem whatsoever reaching 50 Deg or more in the circuit. But of course, this was quite easy with no stupid buffer tank to worry about. So I could absolutely run this like a gas boiler. Yes, it wouldn't be efficient, but it will do it.

    On that basis, the gas boiler no longer has power.

    As I said in the post, the DHW is completely separate. It has it's own 140l tank in the attic and is heated with the Eddi on night rate and the tubes on good days. I might need to boost it 5 days a year during the day. That small bit of power can come from my batteries



  • Registered Users, Registered Users 2 Posts: 1,622 ✭✭✭THE ALM


    Great job championc.

    Have a Viessmann just gone live last week so will be interesting to see the data of the two units. I have a bit of tweaking to do regards the setup and the weather compensation but think I am about where I want to be.



  • Advertisement
  • Registered Users Posts: 6,202 ✭✭✭championc


    @10-10-20 The flow and return pipes from the rads run to the outdoor unit, into a heat exchanger inside the unit. So the units' circuit is tiny.

    The Vaillant uses R290 Propane, and apparently it's only a cup full of it.



  • Registered Users Posts: 6,202 ✭✭✭championc


    It's certainly worth getting your data up on heatpumpmonitor.org (you don't have to make it public). You can visually see, at a glance, what it's doing and when. Yes, you can see it in Home Assistant too I'm sure, but this is nice and clean, for only a few quid per year



  • Registered Users, Registered Users 2 Posts: 7,647 ✭✭✭10-10-20


    It is paralleled, with level / disconnects on the flow and return, so those can easily be reopened and the levers to the heat pump closed off.

    On that basis, the gas boiler no longer has power.

    Yes, needs to be electrically isolated as well as by at least one valve (though you could say that having two valves seals it off too well and leaves the heat-exchanger prone to frost damage). If it's not electrically isolated then the frost protection cycle could start up on a sealed circuit and cause the PRV to release.



  • Registered Users Posts: 6,202 ✭✭✭championc


    Well won't be an issue, as I ain't going back now. Bibwould happily disconnect the gas fully in the morning.

    Our Combi was non-condensing non-modulating, so likely only around 65% efficient at best. So a COP of even 2 is a total plus for me.



  • Registered Users Posts: 6,202 ✭✭✭championc


    Not the best of comparisons yet, but an indication of what I hope is to come. We used 45kWh of electricity, delivering 181kWh of heat.

    In September last year, we used 425kWh of gas. So looking back at TADO graphs, we turned on the heating on 15 Sept 2023. The Vaillant went live on 14 Sept 2024, although it was subsequently off for about 4 days last week adding another rad



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 7,647 ✭✭✭10-10-20


    Cognisant of the fact that you'll be further insulating the house next year, did the house require much work in the way of increasing the rad sizes for the lower delta-T? I presume you were originally spec'd for a delta-T of 50C to 60C, so are now working off what - 35C delta-T?



  • Registered Users, Registered Users 2 Posts: 2,200 ✭✭✭Paul Kiernan


    So the Vaillant has everything needed to drive the heating e.g. pump, expansion vessel (things that would be in your combi!)? So you can just connect to flow/return and Bob's your uncle.

    What do you mean when you say "you could run it like a boiler, but it wouldn't be efficient"? I presume you mean you don't turn it on when it's cold and turn it off when it's hot but rather run it constantly at a steady temperature?



  • Registered Users Posts: 6,202 ✭✭✭championc


    Heatpunk confirmed my current rads, except the sitting room, would work at a design temp of 45°c at -5°c.

    In addition, the sitting room rad was backing onto the hallway (easier for the plumbers at the time) rather than being located under a window. So I was almost happy to have the excuse to do it properly, and put one under the window.

    In fairness, it's a huge window, and the window sill is about 37cm off the floor, so there wouldn't have been room for a proper rad. I added a 2m x 0.3m K2, which is now buckets for the room.



  • Registered Users Posts: 6,202 ✭✭✭championc


    The unit has a pump inside and some form of automatic air vent. But I had to add my own external expansion tank and AAV valve too.

    By saying I could run it like a boiler, I meant running it at conventional gas boiler temperatures. Only heating rads water is pretty quick.

    And as I mentioned, I have it linked to my TADO. The TADO controls the call for heat. So you can see from the data that the heat pump is off from 23:00 till 09:00 daily



  • Moderators, Education Moderators, Home & Garden Moderators Posts: 8,232 Mod ✭✭✭✭Jonathan


    Can you sketch the rough layout of HP, garden and the pipe run to the house? Do your flow and return pipes cross the side passage (assuming you have one)? My boiler is vented into the side passage way so trying to get pipes to there would be a bit tricky. And mounting a HP in the side passage itself would surely lead to microclimating (and a pain trying to get past with the bikes/bins).



  • Registered Users Posts: 6,202 ✭✭✭championc


    The gas boiler backed onto the side passage of our Semi-D, about half way along.

    So the pipes went back 3m, across the door of the side gate, and then a long the side of the back garden wall.

    The house faces south, so it faces East, across the back of the house.

    Look at the piping pic in the post, and it will make perfect sense



  • Registered Users, Registered Users 2 Posts: 7,647 ✭✭✭10-10-20


    Where did you purchase the Vaillant from, championc?



  • Registered Users Posts: 6,202 ✭✭✭championc


    Secon Renewables in the UK. They arranged the courier / pallet shipment. Said they were well used to sending stuff to Ireland



  • Moderators, Education Moderators, Home & Garden Moderators Posts: 8,232 Mod ✭✭✭✭Jonathan


    You'll have to excuse the crap drawing, but where is your side gate? Is it location 1 or location 2? Mine is in location 1, so I'd have to follow the red pipe route, or else get decking or something to get pipe work across the path at location 2.



  • Registered Users Posts: 6,202 ✭✭✭championc


    Like 2, but flip the whole pic on the horizontal. And both pipes side by side, flow and return

    I'll draw it in the morning



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 7,647 ✭✭✭10-10-20


    Take a photo and have a dog in it for scale. 😀



  • Registered Users Posts: 6,202 ✭✭✭championc




  • Registered Users, Registered Users 2 Posts: 2,200 ✭✭✭Paul Kiernan


    One potential installer (i.e. very expensive quote giver!) told me that they usually install the HP high on the side passage wall so that (i) it's higher than the typical 2m boundary wall for good air flow and (ii) you can pass underneath with your bikes, wheelbarrow, etc.



  • Registered Users Posts: 6,202 ✭✭✭championc


    Wouldn't like that. You cannot escape the vibrations, however small, being into your walls. And if you want to wrap the house later.

    The smallest of droning sounds would be heard inside



  • Registered Users, Registered Users 2 Posts: 7,647 ✭✭✭10-10-20