Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Replace APT Timer with Heatmiser Thermostat

  • 29-10-2023 8:07pm
    #1
    Registered Users, Registered Users 2 Posts: 107 ✭✭


    I'm looking to replace an APT Timer for my boiler with a Heatmiser Wifi thermostat. Below is what is currently installed (a simple on/off thermostat for the boiler.)

    And I want to replace it with this:

    I've opened the cover on the thermostat to have a look at the wiring and this is what it looks like:

    And here's it's wiring diagram:

    Firstly can anyone tell me if it is voltfree or not? I'm guessing not. Also which of the two wiring diagrams for the new thermostat should I follow? I have an idea but I want to be sure I don't break anything.

    Any help is much appreciated!



Comments

  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    It's the diagram on the left.

    The wifi stat has a voltfree contact so needs a link for your setup

    The boiler needs a means of isolation nearby , an isolating switch or even a socket



  • Registered Users, Registered Users 2 Posts: 107 ✭✭Daniel112


    Thanks for the help. So terminal 1 cable from the APT Timer will go into A2 on the Heatmiser, Terminal 2 on the APT will go into L on the Heatmiser (with a cable running from L to A1 also to bridge them.) And finally Terminal 3 on the APT timer will go into N on the Heatmiser?

    Is that all correct?

    There is a fused switch underneath the APT timer (as shown on Photo 1 in my last post) That provides power to the APT timer & Boiler when switched on.



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Ya that's right



  • Registered Users, Registered Users 2 Posts: 46 pukeko


    Hi OP H

    How did you get on with this job? I have a similar setup so thinking of doing the same. Although my current APT timer has no isolation nearby - i presume your fuse at the switch there is 3A? Assume this is essential i.e. the Neo load rating is 3A

    thanks.



Advertisement