Electric Shower & Central Heating on Same Circuit - RCD Switch Tripping

Options
  • 24-10-2023 6:56pm
    #1
    Registered Users Posts: 121 ✭✭


    So the RCD switch on my fusebox trips every 4-5 days on average. Sometimes twice in one day, sometimes not again for 2 weeks. I am trying to get to the bottom of what is causing it and I'm thinking it might be due to the electric shower and central heating sharing the same MCB B20 switch. Am I correct in saying this is underrated for an electric shower on its own, never mind with the CH as well?

    Would this trip the RCD switch or should it be tripping the MCB switch? The MCB one never trips, but when I flip it the fusebox starts humming, which none of the other switches do.

    Note I don'tknow a whole lot about this, terms could be wrong, I'm just referring to what is written on the switches themselves.



«1

Comments

  • Registered Users Posts: 4,958 ✭✭✭kirk.


    Is it a power shower, what's the model

    A power shower and CH on same mcb wouldn't be related to your issue

    The fault could be anything connected to the RCD



  • Registered Users Posts: 121 ✭✭Demosthenes


    No, electric shower - a Triton T90si. Looking online it seems the T90si is an 8.5kw unit, which would need a 40amp MCB. The existing one is an MCB20, which I assume means it's 20amps?

    Would the electric shower intermittently overload the MCB and then flip the RCD?



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    No it would trip MCB on overload

    Post up a close up pic of board

    You'll need a REC to investigate fault and shower wiring



  • Registered Users Posts: 4,729 ✭✭✭meercat


    A t90 should be on a 40a rcbo

    a rec really needs to look at this. Do not use your shower until then.



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    Post up a pic of board anyhow you could be mistaken

    If it's on a B20 ya the rest of its probably not safe



  • Advertisement
  • Registered Users Posts: 4,729 ✭✭✭meercat


    Also does your rcd trip even when your shower is not being used



  • Registered Users Posts: 121 ✭✭Demosthenes


    I've been reading through this old thread https://www.boards.ie/discussion/2057559329/electric-shower-fault/p1 which seems to suggest it is likely either a failing element in the shower (which should trip the switch while showering, which does not happen) or the RCBO is undersized (I don't have an RCBO but I do likely have an undersized RCD doing the same job if I'm not mistaken?) Granted there also is a level of disagreement in that thread from multiple people who seem to know what they are talking about.

    RCD that trips is top left, MCB with the CH and electric shower is the 4th MCB in from top left.




  • Registered Users Posts: 4,958 ✭✭✭kirk.


    You've a B40 there and a contactor

    Have you 2 electric showers or maybe that's for something else



  • Registered Users Posts: 121 ✭✭Demosthenes


    Yes 2 electric showers - never used together. Just checked and the isolater switch on the wall was off for the 2nd one when the RCD tripped - does this rule that out as an issue? That 2nd electric shower is connected to the top right B40, also a Triton T90si, while the first electric shower is connected to the B20 beside it, which I reckon is the problem one.



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    What's the contactor top right for looks like you've half a priority board , no sensing relay😁

    Is that the entire board in the pic

    Call a Rec and as meercat said don't use showers



  • Advertisement
  • Registered Users Posts: 121 ✭✭Demosthenes


    Yes both showers are off when I flip the B40. The priority board only allows one electric shower to power at any one time if Google is correct - so should the 1st electric shower be connected to this and the B20 beside it as well, which seems to be the case?



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    You've no sensing relay in board and you said one shower is on the B20

    Looks like there's some bodge job at the board

    Switch off showers and call a Rec



  • Registered Users Posts: 121 ✭✭Demosthenes


    Sorry replies seem to be bugging out for me and some comments only just appearing.

    Just to fill in the gaps, RCD has never tripped while the shower is running, only at random times and always when we are out of the house so far. Entire board is in the photo.

    We recently bought the house, it was a one-off self build and the only previous owner did a lot of the work himself- have found other issues throughout the house.

    I rang a Rec last week, he recommended seeing could I narrow things down a bit from "RCD switch keeps tripping" before he called out as it could be a long day of trying to figure it out otherwise. It sounds like there's a few glaringly obvious issues so I think that's it narrowed down enough 😅

    Thanks both for your help, very much appreciated.



  • Registered Users Posts: 4,958 ✭✭✭kirk.




  • Registered Users Posts: 4,729 ✭✭✭meercat


    Your rcd tripping may be a separate issue


    your showers are definitely wired incorrectly though


    an insulation resistance test by a competent rec should identify the faulty circuit reasonably quick



  • Registered Users Posts: 121 ✭✭Demosthenes


    Just as a minor update on this, electrician has stated this is a slightly older setup, where the B20 is operating the switch and the B40 is operating the showers. Only one shower gets power at any one time. Switch off the B40 and neither work, switch off the B20 and only the last used shower works. If one shower is on the other can't get power. From googling it would seem to be a non-priority switch, although he didn't specifically refer to it as one.


    Search for the RCD offender continues. I replaced a recently discovered faulty wired heated/back-lit mirror in the bathroom a few days back and still no luck.

    Next target is the microwave/convection grill that also came with the house. It stops every 59 seconds and being too busy to investigate, we figured we were just using it wrong. Turns out the 59 second stop is essentially an error message for damper-related component failure, so that is currently unplugged and waiting to see does the RCD trip again.



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    There'd have to be a sensing relay at a minimum for priority control

    It's not in the picture anyhow



  • Registered Users Posts: 121 ✭✭Demosthenes


    Think I might have solved that. The control is done manually by the switch on the wall beside each of the showers. Power on with the wall switch at one shower cuts power at the opposite shower and vice versa. When you power on one of them you can hear a 'thunk' noise from the fusebox which I assume is it connecting the requested circuit and disconnecting the opposite one.


    So with one shower circuit always disconnected by the wall switches, there is no need for a sensing relay at all I think?



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    There's probably a sensing relay or board somewhere if it's automated

    Hard to make sense of this setup



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    I get that now

    Shower isolator energizes contactor breaking supply to 2nd shower

    You'd only have priority with one contactor , wouldn't operate ' vice versa'

    Post edited by kirk. on


  • Advertisement
  • Registered Users Posts: 4,958 ✭✭✭kirk.


    Your RCD issue is probably separate anyhow

    Are you sure you're not a spark you're fairly well clued in 😁



  • Registered Users Posts: 115 ✭✭Pod123


    Sorry to jump on thread but the attached keeps tripping, for instance last night it tripped at 8 and at 12 it tripped,I reset it and tripped this morning at 7 o clock,never trips when pushed back up,no new appliance in the house ,outdoor sockets are switched off,any one able to tell what it might be,thanks.

    It's the one left of the picture with the yellow button



  • Registered Users Posts: 6,722 ✭✭✭10-10-20


    Hi, when you say "outdoor sockets are switched off," do you mean that the sockets are switched off at the plug socket or do you have an isolation switch in doors which you are referring to?

    That device in the photo is an RCD (with damaged markings) so the issue here is a current leakage from live to earth - that can be caused by a faulty device or water ingress into a socket, cable device, etc. Best start by answering my first question as the majority of these RCD issues are rain/damp related.



  • Registered Users Posts: 115 ✭✭Pod123


    Turned off by a switch in the house

    This switches off all sockets outside.



  • Registered Users Posts: 4,958 ✭✭✭kirk.



    Those are not exact times are they ?

    Sounds like some type of nuisance trip or similar



  • Registered Users Posts: 4,729 ✭✭✭meercat




  • Registered Users Posts: 4,958 ✭✭✭kirk.


    Doesn't sound like an immersion unless it's going on at those times , they'd usually be an instantaneously trip



  • Registered Users Posts: 115 ✭✭Pod123


    No there not the exact times as I was trying to remember them but would be pretty close

    We never turn on the immersion, all hot water is heated by oil boiler.

    It's just frustrating as it doesn't trip when pushed back up

    Thanks for all replies I will keep ye posted.



  • Registered Users Posts: 4,729 ✭✭✭meercat




  • Advertisement
  • Registered Users Posts: 4,729 ✭✭✭meercat


    Check that it hasn’t been turned on inadvertently