    Hi All,

    Is it permissible to switch a shower via a contactor, being switched via the pullcord? I wouldn't have classed a contactor as a form of isolation as the contacts could weld together. Apparently due to the difficulty in connecting 10mm² to the pullcord isolator this is now the preferred method ???

    Annex 537A page 448 says no, I did find a safe electric newsletter mentioning it but that was with the ET101.

    Interested in hearing the opinions.


    Thanks



Comments

  • Registered Users Posts: 6,367 ✭✭✭iwillhtfu


    It would certainly make sense and easy to mount in the DB. I've seen a few isolators melted due to cables being crammed into a back box. No fear of contacts welding as it's unlikely the shower will be on when closing and if rated correctly should be more than able to switch the load comfortably. Similar to a typical master/slave set up for more than one electric shower



  • Registered Users Posts: 1,052 ✭✭✭Tuco88


    I agree, and I found damage was done by miss use of the isolator too if you ask me (Switching the shower on/off with it kinda stuff)

    Well I just wanted to know it was acceptable from an inspection/Safe Electric point of view. The book says no?



  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,532 Mod ✭✭✭✭2011


    This is an acceptable way to switch the shower but for isolation purposes it would not be considered acceptable



  • Registered Users Posts: 1,052 ✭✭✭Tuco88


    This is much my point. I am curious that this has been allowed for showers ??? apparently 👀

    Thanks for the feedback on this.



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    It was allowed by mistake at some point god knows how

    Its clearly not a method of local isolation

    The isolator isn't designed to switch load current anyhow the shower controls are designed for that purpose

    Shower just needs a quality pull cord or wall switch



  • Advertisement
  • Registered Users Posts: 4,727 ✭✭✭meercat


    This is the newsletter you mentioned ( bottom of page 6)

    my inspector says no

    ive contacted them recently with the number of fires at distribution boards whilst shower was operational



  • Registered Users Posts: 195 ✭✭JL spark


    Not with that 10sq LSF ,

    don’t care how good you think the connection is ,



  • Registered Users Posts: 4,958 ✭✭✭kirk.




  • Registered Users Posts: 4,727 ✭✭✭meercat


    Yes id agree. However I’d say more issues will arise with the terminations of 10mm into a shower pull cord switch. It’s nearly impossible to do get the cables and terminations done safely into such a tight space



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    Probably is I'm almost retirement age not involved

    I never had any issues with the old 10sq t+E and crabtree pullcords I was using

    I guess the new cable is more difficult to connect ?



  • Advertisement
  • Registered Users Posts: 1,052 ✭✭✭Tuco88


    That' the one... That's covering the 4th edition too so it's old news now too.

    Very interesting the opinions on the topic, I can't understand why they don't do a update or "newsletter" abut this and put it to bed once and for all. If it's not this it's the old cooker and separate oven and hob fiasco.



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    It was just a mistake by one of the higher ups that caught on

    Back in the day it was allowed to loop the incoming tail across the incoming side of a 2 pole neozed switchfuse on all electric homes , another workaround gone wrong



  • Registered Users Posts: 209 ✭✭Bruthal.


    Definitely not an acceptable isolation method. It is possible for the contactor to be closed via someone else remotely at the DB or becoming energised via a wiring fault. Unlikely as that may seem, it's just not a clean solid isolation method like a local isolator.



  • Registered Users Posts: 1,052 ✭✭✭Tuco88


    A 45amp wall isolator switch with a deep box is probably the way to go.


    Thanks for the feedback lads.



  • Registered Users Posts: 4,958 ✭✭✭kirk.


    47mm flush box with a 35mm extension and pull-cord should be handy enough if the terminals take the earths

    Drop the cables down slightly for terminating and push back up

    What's the minimum size link between back box and CPC? Would 4mm do?