Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Shock from a light switch, no RCD on lights?

  • 17-03-2023 8:43pm
    #1
    Registered Users, Registered Users 2 Posts: 12,417 ✭✭✭✭


    Hi folks,

    Earlier today my wife got a shock from one of the light switches when turning the light off


    Luckily she's fine, not more than a sore finger and tingling for a while afterwards

    We took the light switch apart and everything seems fairly normal. It's a double switch controlling two sets of lights

    The live wires all seems solidly in the terminals


    The 4 neutrals were all in one terminal block covered in electrical tape, again they all seemed solid


    The 4 earth wires were in the same terminal block (different terminal), again all solid. The earth wires from the metal back box goes to the same terminal block and also seems solid in the terminal

    No signs of exposed wiring on the live or neutral wires, or scorching or melting on the switch itself. The switch works fine, so evidence of sticking which would imply a short

    There were some exposed bits of the earth wires where the sheathing didn't fully cover it. But no sign of damage to the earth wires

    Tbh, we're a bit mystified as to what could have gone wrong

    We've wrapped the exposed earth wires in electrical tape just to be sure. Also replaced the tape around the terminal block for ten neutral and earth wires, and put some tape in between the two just to add some separation

    Also put some tape over the screws on the switch to give some isolation from anything conductive

    Anyone got any ideas? Is it advisable to replace the switch or get an electrician to be on the safe side?

    We also noticed there's no RCD on the lighting circuits (except bathroom lights). Is that normal? I thought RCDs were required on all circuits, we just have them on sockets and the appliances?

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



Comments

  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    You should replace the switch anyhow , damp is the usual reason for shocks at switches

    Make sure the screws / backbox are not live for any reason, use a phase tester if you have to

    RCDs on lighting circuits except bathrooms is relatively new



  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    Is this a metal switch

    you may have an induced voltage if the earthing isn’t correctly connected. You could still get a shock off the retention screws. Need to get it checked by a competent electrician. As Kirk has already said,rcd protection on all lighting circuits is a relatively new regulation.



  • Registered Users, Registered Users 2 Posts: 12,417 ✭✭✭✭the_amazing_raisin


    Standard plastic household switch, with a metal back box

    I'm guessing the shock must have come through the screws since they're connected to the earth wires

    I think you're right, get a sparks out to checo the earthing. Couldn't see anything in the switch that looked like live or neutral could be touching the earth wires, but I guess there could be a fault elsewhere which isn't being earthed properly?

    House was built in 2017, so I guess the RCD requirements must be very new


    Is it possible to swap out an existing MCB for an RCD? I've seen some slim ones that only take up a single space in the CU, like an MCB

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 12,417 ✭✭✭✭the_amazing_raisin


    Her hands were dry, but I guess it's possible some water could have gotten into the switch earlier

    Might just get the sparks out to be safe and look at replacing the MCBs with RCDs, my main worry is one of the kids getting a zap off the switch

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Why do you say water is a possibility

    It's mostly damp ive seen with plastic switches

    Unless it's a shock off a screw- unlikely or a metal switch with earthing issue



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,417 ✭✭✭✭the_amazing_raisin


    Kids tend not to dry their hands properly when coming out of the bathroom, which is right beside the kitchen where the dodgy switch is

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    That's them there off another thread

    They're 1P+N rcbos , the neutral isn't switched

    They've 2 flyleads, N in and FE( the white leads at the top)



  • Registered Users, Registered Users 2 Posts: 7,476 ✭✭✭The Continental Op


    I've also seen what I call "tracking" on mains light switches. What I believe happens is that once damp gets in you can get an arcing between the live and any earth and from then on a "track" is formed that can conduct electricity on the surface of the plastic. Even if it dries out and is perfectly dry you can still get a shock from the path that has formed.

    This is an effect you see far more on higher voltage equipment, car ignition systems can suffer from it and in the old days of points and distributors distributors often suffered from it. However I've seen and felt the effect on a couple of kitchen and bathroom lights as well as plugs and sockets used outside. Everything looks fine but you get a shock from the switch or the plug. If that is the problem normally close examination will show a dark carbonised line of the tracking somewhere on the plastic. Most recently I had this on a plug top that was left plugged in outside in a very damp shed. I couldn't see what was the problem until I opened up the plug top and there was a black line that went all the way around the join between the two halves so no way could you pull the plug out when it was live without getting a shock (and the RCD tripping).

    Wake me up when it's all over.



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Got a rattle off a fuseholder at the fuseboards once or twice

    Seems to be just gunk on them

    Never went near one afterwards without gloves on



  • Registered Users, Registered Users 2 Posts: 1,543 ✭✭✭Pataman


    Is it possible it was a static shock from her earthed through the switch?



  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    A few points:

    1) I doubt that your wife got a shock because there was no RCD protection on the circuit. Many of use have received electric shocks from circuits that have RCD protection! She got a shock because she touched something that was at a higher potential than something else that she was in contact with (probably the floor).

    2) From what you have said it would seem that you have not verified that the switchbox is earthed. Just because earth cables are connected to it does not mean it is earthed. I would use a wander lead and suitable Ohm meter to measure the resistance between the backbox and the main earth terminal. I suspect that you will find this resistance to be unacceptably high. If the resistance was low this tells its own story i.e. your wife did not get a sock from the screws.

    3) Also I would carry out an earth fault loop impedance test at the light switch and ensure that the installation is neutralized.

    4) As your wife's hands were dry the most likely reason is that the screws were live. This could be due to a voltage appearing on the earth cable due to an earth fault on a completely different circuit. You could test for this by measuring the voltage between the backbox and a neutral or earth earth point. Do this when all other circuits and appliances are switched on.



  • Registered Users, Registered Users 2 Posts: 12,417 ✭✭✭✭the_amazing_raisin


    It's possible, however she could feel it in her hand an hour later, which seems to indicate she got more than the average static shock

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 12,417 ✭✭✭✭the_amazing_raisin


    Thanks for that, we've an electrician coming out for some other work so I'll speak to them about performing the checks you mentioned

    I agree that there's nothing there to definitely prove the earth wires are connected properly

    The switch is working fine for now, we've got the screws covered with electrical tape and we're trying to avoid using those lights just in case

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    It's a stretch to believe the box is live

    Assuming the MET isn't live you'd need a couple of issues for the screws to be live and even then you'd have to make contact with them

    Never say never though

    Post edited by kirk. on


  • Registered Users, Registered Users 2 Posts: 2,358 ✭✭✭Antenna


    That there was still an effect an hour later sounds severe.

    Was she earthing herself with the other hand when this happened with the lightswitch ?

    In other words the other hand in contact with perhaps a stainless steel sink or metallic (earthed) electrical appliance such as a kettle etc (as you say this switch was in the kitchen).

    A mains shock will have a rapid trobbing effect, (the voltage is a sine wave, at 50 cycles a second), whilst a static shock is a sting effect for an instant (rapid discharge)



  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    Maybe just probing around the switch and screws , even the walls, with a phase tester might tell something.



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Check backbox >> replace switch

    Thats a better version of a phase tester below , works with gloves on




Advertisement