Any way to bypass the water cyclinder in a vented system?

  • 25-06-2022 8:52am
    #1
    Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭


    At the moment I can have/control the boiler heating the hot water in the cycling without heating the water in the radiators. But when it is heating the water in the radiators, it is also heating the water in the hot water cyclinder.

    Any way to bypass the cyclinder and have the boiler exclusively heating the water in the radiators?

    I would guess it should save the boulder having to heat 180ltr tank when heating radiators.



Comments

  • Registered Users, Registered Users 2 Posts: 6,313 ✭✭✭Ubbquittious


    If you have a valve on the coil of the cylinder you could do it. I have such a system & controller to operate that valve so it can run the cylinder for a certain time then switch to rads.

    but if there is a solid fuel stove then it's a bad idea to do this



  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Have you got a timer with two zones one may be labeled HW?, you should also have either a 3 way motorized mid position valve or two separate 2 way motorized valves, (both shown below), have a look around.





  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    Yes I have one of those motorised valve which allows me to do hot water only.

    But when heating is on also heats the cyclinder.

    I see the below valve next to the cyclinder. Would I need to replace this one for a motorised one so I can isolate the heating and skip the cyclinder?




  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Which type of motorized valve is installed, a 2 way or a 3 way and have you got a timer/programmer? (can't see the valve in your photo, above).

    I can see the red gate valve so yes that should be replaced with a 2 way motorized valve but it will need wiring to a timer, that's why I asked what type of timer you have installed, if any.

    Post edited by John.G on


  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego




  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Two zones can mean that you have one zone valve serving the downstairs rads and the other serving the upstairs rads or you may have one zone valve serving both upstairs and downstairs and the other zone serving the HW cylinder, is the M.valve shown or the other one installed on the any one of the HW cylinder pipes (coil) either the flow or the return.

    Can you post a photo of the timer.



  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    The motorised valve is installed downstairs to the pipe which goes up to the he cyclinder so I believe one zone serves all radiators and the other one the hot water cyclinder. But I am sure when the boiler is heating the water for all radiators it is also heating the water in the cyclinder. Does it make sense?

    The timer is one of these new fancy ones (Tado) with an app where I can select heating or hot water.



  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Yes, that makes sense. Ensure both systems off and then select rads only on while watching or listening to see if the HW M.valve also opens.



  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    I'll do that whenever I get home but I have the feeling that when I switch the heating on the hw m.valve also opens. Very confident that does that.

    If that was the case.......has it been set up by the plumber to do that? And could I change that setting so remains closed when I switch the heating?



  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Not familiar with the Tado system but will read up on it, best talk to the plumber as he would certainly would not set it up intentionally to operate as above.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    It was installed almost 10 years ago......only now it is bothering why it heats cyclinder too as the price of heating oil has gone off the roof.

    This is a photo of the thermostat and how it is meant to be wired. Does the below makes sense so the hw m.valve doesn't open when switching the heat?




  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    That looks typical S plan wiring to me except that it doesn't show a CH roomstat but that (they) might be wireless stats that are controlled by the TADO and as long as any one is looking for room heat then the CH wireless relay is closed to open the motorised valve via its brown&blue wires, a internal (end) switch in the M.valve then switches on the boiler via the permanently live grey wire and the (now switched) orange wire. The HW works similarly except that the M.valve is energised via the cylinder stat. I don't see any reason for the HW to come on with the CH. Try switching in the CH only then turn down the cylinder stat until you hear a click (or turn it right down) and check that the HW M.valve closes.



  • Registered Users, Registered Users 2 Posts: 1,709 ✭✭✭wiz569


    If there is only one 2-way valve then its working as intended surely, you would need another 2-way or else one 3-way instead no?



  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    Is it possible that I don't have a cyclinder stat? I can't see any around the cylinder.



  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Post 8 says 2.

    It would be most unusual, there may be a sensor inserted in a dry cylinder pocket, if so, you should see a wire coming out somewhere ~ 18" up from the cylinder bottom. You may have both room stat and cylinder stat settings in your App or whatever its called. If so do as I asked above and then turn down the cylinder stat setting to say 30C and see if the M.valve closes. (CH only ON)



  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    100% no thermostat in the cyclinder. I checked everywhere and no wires anywhere or any stat.

    I guess there is a stat at the boiler with the water temperature for that cylinder?



  • Registered Users, Registered Users 2 Posts: 1,709 ✭✭✭wiz569


    Post 8 only says "the" motorised valve that I can see John? And the pic in post 6 is a 2-way no?



  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Looks that way all right, still doesn't solve your problem though, have you any photo of the actual wiring center close up and we might spot something there.



  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Post no 6 says "Just posted the photo. Two zones." so 2 X 2way valves??, also Galego says he can have HW only (no rads) but not Rads only (no HW)

    Post no 8 also states "The motorised valve is installed downstairs to the pipe which goes up to the he cyclinder so I believe one zone serves all radiators and the other one the hot water cyclinder."

    But whole set up a bit confusing.



  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Can you post a photo of the two M.valves please.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,709 ✭✭✭wiz569


    I have a feeling that the OP may think that a 2-way valve creates two zones, whereas its actually just a motorised gate valve, definitely need more info and pics.



  • Registered Users, Registered Users 2 Posts: 1,261 ✭✭✭Gant21


    The op has the paddy spec plumbing installation. Hw on its own or hw and ch.



  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Maybe his one does 😁😁



  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    Here you go.




  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    Wiring doesn't tell me much, switched live label looks like suitable for a 3 way valve.



  • Registered Users, Registered Users 2 Posts: 1,261 ✭✭✭Gant21


    The threesome I don’t think so ops clock has two outputs. As you previously mentioned we need to see all valve(s).



  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    I am only able to find one motorised valve. To me looks like a zone 2 type. See photo below. There is a manual valve nearby.





  • Registered Users, Registered Users 2 Posts: 8,448 ✭✭✭ongarite


    Tado only supports 2 zones so from your description it's setup for heating only & water+heating?

    Do you have 3 zones, downstairs heat, upstairs heat & water with motorised valve for each?

    Really useful discussion on smart home heating. Some Tado users on there who can help

    https://www.boards.ie/discussion/2057758281/home-heating-automation

    Post edited by ongarite on


  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    If only one zone valve then still a mystery to me, if this zone valve is supplying the CH and the HW cyl coil then both must be teed off after (downstream of) the M.valve so how can the HW cyl coil only be supplied with the M.valve shut and boiler only firing, if the HW cyl coil is supplied upstream of the M.valve then it does work in the fashion it is? so post 23 correct.

    Post edited by John.G on


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    Yes it seems that way. Hw on its own or hw and ch.

    A gravity hot water system.

    Is there anything which I could do in order to separate the ch from the hw?



  • Registered Users, Registered Users 2 Posts: 1,466 ✭✭✭monseiur


    Assuming the house is occupied (not a holiday home) and a certain amount of domestic hot water is required daily, is there much of a saving to be made by not heating the water in the cylinder. Once heated and with a good lagging jacket it should cost very little extra to keep heated to the same temperature as rads.



  • Registered Users, Registered Users 2 Posts: 3,657 ✭✭✭John.G


    If the HW is gravity fed boiler may have 4 pipes, a flow & return on left side and same on the right. You ideally need a fully pumped system with another motorized valve for HW control.



  • Registered Users, Registered Users 2 Posts: 254 ✭✭Deanicus


    I have tado on a 2 zone system, 2xCH and 1XHW, so it is possible

    I vaguely remember when wiring it up, I had to use a jumper wire between the HW terminal and the live one, in order to get it working correctly.

    Having said that, at the time I was on and off with support trying different things as it wasn't working correctly so my memory could be flawed. Might be worth getting onto Tado support as you can email them your pics with a description of your system and they might figure out the issue if it is not how your system is configured

    Check the last post here where I describe it a little better: https://www.boards.ie/discussion/2057524795/3-channel-to-2-channel-controller/p2



  • Registered Users, Registered Users 2 Posts: 1,709 ✭✭✭wiz569


    It won't work with only one 2-way valve regardless of how it's wired tbh.



  • Registered Users, Registered Users 2 Posts: 254 ✭✭Deanicus


    Absolutely. Thought there might still be doubt on the system configuration so if it is supposed to be separate I'm suggesting the wiring in the tado extension kit might need to be changed



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,250 ✭✭✭Galego


    Hi all,

    I think i have managed to figure out the system.

    1- L linked to 4 -> does not fire boiler, makes M.Valve move.

    2- L linked to 3 -> fires boiler and again, boiler heats the water in the cylinder. Not radiators.

    3- L linked to 3 and 4 -> fires boiler and heats water in the radiator, and HW cylinder as well. Moves the M.Valve.

    In summary. Tado wired in Gravity mode, HW terminal 3 goes live for either HW or CH timed events. Terminal 4 only goes live for CH only, and this is used only to open the valve to the rads.



  • Registered Users, Registered Users 2 Posts: 11,395 ✭✭✭✭Furze99