Smart immersion controller

  • 29-05-2022 10:39am
    #1
    Registered Users, Registered Users 2 Posts: 270 ✭✭


    Hi,

    Im looking to install a smart thermostat (timer) switch in my hot press and want it to be WiFi compatible and to work with Alexa and have it’s own app….


    thanks,

    YaK



Comments

  • Registered Users, Registered Users 2 Posts: 17,189 ✭✭✭✭Sleeper12


    Are you looking to control the hot water cylinder?

    Are you talking about the electric immersion? Or are you talking about controlling the hot water heater by the central heating?

    Do you have a motorised valve fitted on the heating so the hot water is a separate zone?



  • Registered Users, Registered Users 2 Posts: 270 ✭✭yak


    It’s the (electric) immersion in the hot water cylinder, it currently heats water independent of the heating system and would like to build on that by adding smart/remote control to it…


    would want a timer and ability to enable via apps/smart speakers.



  • Registered Users, Registered Users 2 Posts: 17,189 ✭✭✭✭Sleeper12


    You are very limited in choice for smart electric immersion timers but the one below should suit

    https://www.climote.ie/immersion/



  • Registered Users, Registered Users 2 Posts: 270 ✭✭yak


    Ya I saw that one and was put off by the price…. Was nearly 400quid and subscription after 12 months IIRC…


    I had looked at Optimum OP-BM/IHTWF01 Wi-Fi Enabled Universal Boiler Module, but still confused so looking for recommendations…





  • Registered Users, Registered Users 2 Posts: 17,189 ✭✭✭✭Sleeper12


    The problem is that you need a 16amp one for an immersion. Most smart timers are 3amp and for central heating



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    You can probably get a spark to fit something at the board with a contactor

    I can never see the point of smart controls for an immersion, just me but I reckon a lot of its overkill



  • Registered Users, Registered Users 2 Posts: 17,189 ✭✭✭✭Sleeper12


    I'm a real gadget freak but I would agree you. Personally I think spending the money splitting the C/H into 3 zones is better value for money. There is a much greater selection of smar controls for C/H



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Im a spark for donkey years and I like my gadgets too

    When it comes to the lights and appliances a lot is overkill

    Internal pirs for control of a lot of lights is the handiest thing you'll ever do for hallways and toilets and cupboards and exits not all these fancy smart bulbs



  • Registered Users, Registered Users 2 Posts: 270 ✭✭yak


    Optimum OP-BM/IHTWF01 Wi-Fi Enabled Universal Boiler Module/Immersion Heater Control, 230 V, White https://amzn.eu/d/fpLfF2W


    that one is 16amps AFAIK?


    I already have multi zone C/H, the immersion (timer/WiFi) switch is to supplement the existing manual switch that’s in place to reduce requirement to burn oil… I have to get a timer switch anyway, so why not get a WiFi one was my thinking!?!?



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    That's probably only a single channel so you'd still have to switch sink/bath if you need them both

    You still need a form of isolation such as the immersion switch too, you can't just replace the immersion switch with one of those



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 270 ✭✭yak


    Ya was planning to place it inline with the existing dual switch, immersion-existing switch- WiFi switch - mains. Then leave the existing switch in on/sink and use the WiFi switch as an simple on/off switch to allow current to the existing one. Will need to switch between sink/bath manually but will have remote/timed control of the immersion via the new switch…



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    I think you are misreading Kirks post. The safer option is to have the wifi switch at the immersion side of the existing switch. that way you maintain your means of isolation.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Ya the controller before the timer same as you'd do when adding an APT timer

    If you were using a 2 channel wireless controller you'd wire it DP switch first and then 2 channel controller and remove the immersion switch ,that gives you the isolation and control needed



  • Registered Users, Registered Users 2 Posts: 270 ✭✭yak


    Thanks for that, looks like putting the the new switch between the old switch and the immersion will require a stretch of new cable, I assume it’s better to use ~20amp cable (>16amp that the fuse in the existing switch is rated for), but does it matter how much bigger the cable is?



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    The way It usually works is the supply cable to the switch is protected by the MCB usually a 2.5 as that's standard practice to protect cables

    The immersion then is considered a fixed load so the flex is rated to supply the immersion load so probably a 1.5 as it's not going to be overloaded

    Anything except the immersion flex would be kept to 2.5



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Any new switches or controls would be fitted outside the hotpress

    You might also have the option of timers and controls at the board if there's no ancillary equipped supplied at the hotpress like a pump which regulations allow

    Haven't wired anything except the APTs and the. Economy7 controls, they would be the standards but I'd say the WiFi controls would be done as i described , always open to correction



  • Registered Users, Registered Users 2 Posts: 270 ✭✭yak


    Is there a reason that the switch should be installed outside the hot press? I was planning to install it beside the current on/off sink/bath switch inside the hot press (between the current switch and the immersion itself)?

    Post edited by yak on


  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Ya move everything out sounds like you need a electrician

    Immersion heaters are a nasty enough device , problems with the flexes, switching and clothes

    Post edited by kirk. on


  • Registered Users, Registered Users 2 Posts: 650 ✭✭✭inigo


    I hope it's ok to hijack this thread.

    I also want to change my manual controller with something "smart". It's electricity only, two elements. At the moment I have a Horstmann E7 (not electronic). I plan to have an electrician do the work.

    @yak, did you make the change eventually? What smart device did you use and how did you find it?

    I'm considering the Optimum OP-BM/IHTWF01 Wi-Fi Enabled Universal Boiler Module/Immersion Heater Control but there are quite a few reviews that mention device failures after few months-2 years.

    Another option is this.

    I was wondering if I should change the manual controller completely for two smart switches, one for each element, and either isolate them somehow if they are on the same circuit or put them on separate circuits. Or should I have some manual controller/switch in case the smart switch fails?

    Any recommendations other than the Optimum or the Xuelili?

    EDIT: Or maybe what I need is the electronic version of the Horstmann E7??



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    You need to keep a DP isolator.The E7s have that built-in or fit a new one with the smart control y

    Other problem is you can't use just 2 separate controls for a dual immersion you need the changeover as well to prevent 2 heaters coming on together as the dual immersion are not designed for that



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Yes. Perhaps best option is to control it before the dual switch, but then you'd need a DP isolator nearby. The other option would be to pick whether it's the bath or sink that you'd like to control and put your wifi switch on that leg. Perhaps you'd have to make it obvious that the existing switch is the DP isolator. You'd need to ask an electrician if that would be ok. Perhaps Kirk (above) would know.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Simplest is always single pole smart control and a standard dual immersion switch

    The same way that electronic devices are not allowed for local isolation

    If you wanted smart control of sink and bath you would need some sort of interlock in the controller to prevent the 2 coming on ,smart settings on their own wouldn't suffice



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    There might be something smart off the shelf with interlock for immersion or you can set it up that way

    The E7 has double pole isolation and sink boost with interlock all built in

    So you can probably set it up to work with smart control of bath which probably isn't much use really though



  • Registered Users, Registered Users 2 Posts: 650 ✭✭✭inigo


    Thank you for the replies!

    Ideally I would like the whole thing (on/off, sink/bath) on wi-fi, but I would be more than happy if I could control only the boost/sink/top element "smartly".

    We don't take baths and only heat the whole tank occasionally to prevent bacterial growth.

    @kirk. Pardon my ignorance, with simplest way do you mean this?

    MAINS -> SMART SWITCH -> MANUAL SINK/BATH SWITCH -> IMMERSION



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Probably manual dual immersion switch>> smart switch

    Feed sink throu smart control

    Bath control is then completely manual



  • Registered Users, Registered Users 2 Posts: 650 ✭✭✭inigo


    MAINS -> MANUAL ON/OFF + SINK/BATH SWITCH -> SMART SWITCH -> IMMERSION???

    That way with the switch ON and SINK I can leave the power ON all the time and control the SINK with the smart switch? The advantage being if the smart switch fails I still have the bath option? Disadvantage being bath is completely manual?

    In my suggestion (smart -> manual) if the smart fails I'm without hot water...

    Would others have a preference?



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    I think that if you go down the latter route, you'll need a double pole isolator before the smart switch.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Ya you said u only use bath for legionnaires so off top of my head..

    Immersion switch to smart (on the sink leg only)

    There's no need for extra isolators the standard immersion switch is the isolator once it's <2m from the heater



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    A smart control doesn't need any isolation

    The only thing to watch there is if the control itself needs fusing at 3amp or whatever and there's a relay in it for the immersion



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    So there isn't a need for isolation between the smart controller and the mcb/rcbo?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    No

    But i suggested immersion switch >> smart control

    So that that case there is an isolator between smart and rcbo

    But other way round it doesn't matter , smart control doesn't need isolation



  • Registered Users, Registered Users 2 Posts: 650 ✭✭✭inigo


    So in that case I presume it would be safe to leave it ON and SINK all the time and turn on/off with the smart control?



  • Registered Users, Registered Users 2 Posts: 25,620 ✭✭✭✭coylemj


    See this thread on the same topic, I have a smart immersion timer and I've included a photo and description of how it works.

    If you're getting a smart device and you have a Sink/Bath switch which does not have a red LED to show it's receiving power, I'd strongly advise that you swap it for one that does have a light. It will be essential if there is a problem because the first thing you will need to check is whether the timer is sending power to the switch.

    Start from my post at #7 and see my reply to some follow-up questions at #10

    https://www.boards.ie/discussion/2057852343/smart-immersion



  • Registered Users, Registered Users 2 Posts: 650 ✭✭✭inigo


    Thank you. Good tip re LED. I've posted on the other thread too. I think things are becoming clearer in my head thanks to all the responses!



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    I think i forgot the changeover with the controller here

    The immersion switch is a simple device but it throws up a few problems with smart control

    It controls the heater but there's also the isolation and changeover



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 650 ✭✭✭inigo


    I'm afraid I don't know what you mean. Which problems are you referring to? Would you mind elaborating a bit, please?

    Post edited by inigo on


  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    It's an old post I'm talking about not related to your setup



  • Registered Users, Registered Users 2 Posts: 491 ✭✭The lips


    I am interested in doing the same as the OP, sink/bath switch to keep dual element capability and smart switch controlling the power to that.

    What was the resolution of this thread?