    Registered Users Posts: 8


    Our immersion heater has corrosion around the heating element at top of the boiler (not the wiring itself but around and over the base plate where the reset button is on the element top). It trips the fuse box as a result - started 2 nights ago and I've left it tripped off since. I'm about to order the heating element to replace it altogether as to solve the corrosion is too big a task if not impossible and I don't want it spreading further through the system.

    I have a query as to the fact we never use electric immersion to heat our water/radiators. We always use oil and the boiler for central heating and water, but because this burnt-out element trips the fuse box controlling the heating controllers for the oil burner can't turn on either. Is it necessary to replace/wire up the immersion if heating is always done with oil? Do the immersion controls also control valves or the pump that's responsible for central heating? As a temp fix or to get heat on while waiting for part replacement can I unwire the immersion element so it won't trip the fuse but leave it locked and sealed in place and still use oil burner for heat & water?


    Thanks.

    Post edited by Wearb on


«1

Comments

  • Registered Users Posts: 8 Bita_dis_bita_dat


    *not corrosion but rather rust at the moment



  • Registered Users Posts: 23,260 ✭✭✭✭mickdw


    If you don't use the immersion, you can disconnect the wiring from the tank and leave the unit on/ in the tank as is.



  • Registered Users Posts: 23,260 ✭✭✭✭mickdw


    Just to add, the immersion is only for hot water. It doesn't heat rads.



  • Registered Users Posts: 8 Bita_dis_bita_dat


    Thanks for the reply, I was hoping it was possible. So literally disconnect wiring, secure it as to not shock someone/something, flip the fuse switch back on and use the central heating as normal?



  • Registered Users Posts: 23,260 ✭✭✭✭mickdw


    I'd disconnect the supply cable at the switch if this is going to be a semi permanent setup.



  • Advertisement
  • Registered Users Posts: 2,754 ✭✭✭Buffman


    That still looks wet in the photo so you probably still have a small leak. To fix the leak you'll have to replace it or blank it if you don't want an immersion element.

    As a temporary fix to get the oil going again I'd disconnect the element at the immersion switch on the element side and refit the switch so you don't have any live wires exposed.

    FYI, if you move to a 'smart' meter electricity plan, you CAN'T move back to a non-smart plan.



  • Registered Users Posts: 6,641 ✭✭✭10-10-20


    Yes, definitely isolate this at the switch, but please don't go isolating devices such as this unless you know how to safely do so.

    Also, by isolating this you aren't addressing the leak and that will either worsen over time. Finally, should your oil heating fail, you will then have no backup for heating the water. I'd suggest getting the immersion repaired instead.



  • Registered Users Posts: 8 Bita_dis_bita_dat


    Disconnected the immersion at the switch with no problem. Unfortunately, the same issue is happening - the central heating runs for a few mins but the fuse trips again still. The plot thickens...



  • Registered Users Posts: 3,949 ✭✭✭jimf


    most likely a water leak at the circulating pump valves at your boiler

    first place always to look

    Post edited by jimf on


  • Registered Users Posts: 3,466 ✭✭✭John.G


    If its the RCD (earth leakage) is tripping then ensure the live, the neutral and the earth are all disconnected at the switch and see if RCD still trips.



  • Advertisement
  • Registered Users Posts: 234 ✭✭elgicko


    Immersion completely different to radiator heating . All Immersion does is heat up water in tank, it does not interact with heating at all. View an immersion like a heating element in a kettle.


    The radiators are heated through a circuit, flow and return, look on this like a circuit. Part of the circuit is a coil of pipe going through the hot water tank, the water does not mix with the tank water As the water circulates the water in the tank gets hot as the water in the heating circuit heats it, similar to dropping a hot stone into cold water.



  • Registered Users Posts: 234 ✭✭elgicko


    Regarding your problem, there is a disparancey of voltage going through your RCD. Are you losing all power (except lights), if so, the RCD is doing its job and trips out because it detects the erratic voltage.


    There sounds to be a big problem with your immersion, replace it and see if the problem is resolved. Make sure the existing one is earthed. Be careful.


    Solid advice by John G. If it was me I would disconnect immersion at fuse box. If that solves you problem, you know it is the immersion.


    If you don't know what your doing leave it to the pro's



  • Registered Users Posts: 8 Bita_dis_bita_dat


    Just to clarify; it is just the circuit breaker that our central heating is connected to that is tripping. All other breakers in the fuse box are fine. I figured it was the immersion tripping it initially as moisture appeared around the wiring (only arrived and as I figure it could have happened from a slightly damp bed sheet that was thrown over the boiler to dry). However, having removed the immersion from the equation by disconnecting it entirely from it's circuit and then also turning off that circuit breaker but the central heating circuit is still tripping off after being on for 10-20 mins.

    Next, I was gonna try switching the fuse in the circuit breaker and test and see does it stay on, maybe it's just the MCB 🤷‍♂️ It's odd that it stays on for approx 15mins before tripping - nothing on the circuit that I can see that's tripping it after that time, tested it with the pump on or off and its the same, and nothing switched on in the house bar the fridge when testing also. See my other post trying to identify my MCB if you have any insight in the matter - https://www.boards.ie/discussion/2058227277/what-is-this-style-of-mcb-called-see-attached-image/p1?new=1

    Post edited by Bita_dis_bita_dat on


  • Registered Users Posts: 3,949 ✭✭✭jimf


    any mice chewing wires



  • Registered Users Posts: 3,466 ✭✭✭John.G


    Just to be clear, you a say a circuit breaker or MCB is tripping, if so, this will only trip under overload conditions, can you clearly identify the one in question in case its a combined overload and earth leakage circuit breaker known as a RCBO in which case it can be either a overload condition or a earth leakage problem.



  • Registered Users Posts: 4,426 ✭✭✭maestroamado


    I am guessing the problem internal in the element... i do not see anything wrong with the wiring and of course its always dry... taking a wire off at the switch prob best option...



  • Registered Users Posts: 23,260 ✭✭✭✭mickdw


    He has disconnected the immersion entirely now and still has a problem.



  • Registered Users Posts: 23,260 ✭✭✭✭mickdw


    The immersion is a red herring.

    Do you have an outdoor burner?



  • Registered Users Posts: 3,466 ✭✭✭John.G


    We are (or at least I am) going around in circles until we know the type of circuit breaker is, post #14 might suggest a RCD/RCBO but just don't know, also "having removed the immersion from the equation by disconnecting it entirely from it's circuit and then also turning off that circuit breaker but the central heating circuit is still tripping off after being on for 10-20 mins."

    Just to repeat that disconnecting the immersion entirely means disconnecting the Live, the Neutral and the Earth wires.



  • Registered Users Posts: 3,949 ✭✭✭jimf


    if your boiler is wired as it should be it should be protected by a 5amp supply

    it will be very sensitive so easily tripped

    it could be caused by a faulty boiler stat as well as a mouse chewing wires that flex slightly when hot

    it is obvious your burner is the cause get somebody to check it over



  • Advertisement
  • Registered Users Posts: 234 ✭✭elgicko


    If you have disconnected the immersion from the fuse box, the MCB - disconnect live/neutral/earth. If the problem persists the issue is not the immersion.


    What is tripping after above completed? Is it the heating (boiler) MCB or RCD?


    How old is boiler? is it gas or oil? Could be an internal issue with the boiler!


    You are getting close to calling an expert if the problem.is the boiler, could be a lot of.different things.



  • Registered Users Posts: 8 Bita_dis_bita_dat


    MCB is tripping.

    Trips when the boiler isn't running. Yesterday it would run for approx 20 mins then trip again with nothing else running in the house. Today I disconnected the wires from the MCB and reconnected them again (was gonna switch out the fuse.) and it ran for over an hour with the boiler on, so we got the house heated. The MCB tripped again then.

    Don't know the exact age of the boiler, could be due to being replaced. Runs on Oil.

    It's close to that alright, was just trying to identify the issue really - thought it was the immersion first so was came here for thoughts.



  • Moderators, Home & Garden Moderators Posts: 6,209 Mod ✭✭✭✭Wearb


    AFAIK Only a qualified electrician is allowed to take the cover off the consumer unit (fuse box). Not to mention removing wires from within.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users Posts: 4,426 ✭✭✭maestroamado


    in your own home you do as you please... thankfully...



  • Registered Users Posts: 4,426 ✭✭✭maestroamado


    if the live is disconnected the circut is broken...



  • Registered Users Posts: 234 ✭✭elgicko


    You are getting different problems, there is no consistency. Could be anything


    Switch out the MCB for the heating (not immersion), make sure you turn off the consumer unit at the main fuse and be careful not to go near the main lives going into he 63amp fuse. if that doesn't work, call a sparks to diagnose


    Valiant effort!!



  • Moderators, Home & Garden Moderators Posts: 6,209 Mod ✭✭✭✭Wearb


    That is certainly not the case. So be careful of the advice that you give.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users Posts: 4,426 ✭✭✭maestroamado


    Give an example of what you say... i am not giving advise but you are...for me people can do as they please in their owned private property...



  • Moderators, Home & Garden Moderators Posts: 6,209 Mod ✭✭✭✭Wearb


    That information is widely available and known amongst the trades. There is lot of electrical work that's not allowed in your own home unless you have the proper qualifications. If you do not believe me, then ask over in the electrical forum. The same goes for working with gas.

    MOD NOTE:I have tried to keep this thread from having posters suggest dangerous (and illegal) practices, without being heavy handed. From here on I will infract any any such suggestions. Don't reply to this as it will only take the thread further off topic.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users Posts: 1,920 ✭✭✭Andrea B.


    Full circle.

    If you have a switch at immersion with on/off _sink bath:

    Switching to off, isolates live and neutral of element from circuit.

    Assuming switch fuctioning, when off, if your rcd/rcbo/mcb still continues to trip, you have an electrical fault elsewhere.