Power shower tripping circuit breaker but stays running

2»

Comments

  • Closed Accounts Posts: 173 ✭✭Henry...


    It's possible but does it happen

    The impedance of the main protective conductor is low compared to the fault paths through an Rcd N-E Fault


  • Registered Users, Registered Users 2 Posts: 211 ✭✭Bruthal.


    Henry... wrote: »
    It's possible but does it happen

    The impedance of the main protective conductor is low compared to the fault paths through an Rcd N-E Fault

    It does happen. I've seen cases. More likely in non neutralised houses and also supplied with the older overhead LV lines which was the cases where I seen it

    30 amps is 1000 times 30ma so not much needs to divert.


  • Closed Accounts Posts: 173 ✭✭Henry...


    Bruthal. wrote: »
    It does happen. I've seen cases. More likely in non neutralised houses and also supplied with the older overhead LV lines which was the cases where I seen it

    30 amps is 1000 times 30ma so not much needs to divert.

    Ya think I wasn't thinking that through, higher fault current will divert more