  • 22-08-2019 10:06pm
    #1
    Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭


    Hi Guys,

    Just back from looking at a house my sister bought. Lot of work to be done but one thing I noticed is that the ESB incomer is coming through tohe top of a door frame and into the cutout and metre which is mounted in a cabinet in the kitchen.

    Very surprised the ESB would do something like this, surely this is something they should fix FOC, no?


Comments

  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    Pics attached


  • Closed Accounts Posts: 702 ✭✭✭Portsalon


    Hi Guys,

    Just back from looking at a house my sister bought. Lot of work to be done but one thing I noticed is that the ESB incomer is coming through tohe top of a door frame and into the cutout and metre which is mounted in a cabinet in the kitchen.

    Very surprised the ESB would do something like this, surely this is something they should fix FOC, no?

    If it ain't broke then why should they fix it, FOC or otherwise?


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    As you know the best bet is to have the meter moved outside where they can read it.
    They may facilitate with that, but not if it's to a location indoors that they cant get to.

    The new 16.sq.mm from your board to the meter location
    will be your responsibility though.


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    Portsalon wrote: »
    If it ain't broke then why should they fix it, FOC or otherwise?

    Because it looks like absolutely terrible workmanship and it’s the ESBs cable not the customers


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    Stoner wrote: »
    As you know the best bet is to have the meter moved outside where they can read it.
    They may facilitate with that, but not if it's to a location indoors that they cant get to.

    The new 16.sq.mm from your board to the meter location
    will be your responsibility though.

    Agreed, would be much better suited in a metre cabinet outside, if you look at the attached pics of outside you can see the incomer coming down the wall, if the metre cabinet was to be situated on the side wall nearer the front of the house are they responsible for getting there cable to the cabinet? Presume they wouldn’t clip it along the wall, it would need to go to ground and then into a duct and back up into the cabinet?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    That's how it was done back in the day.....

    Sure ESb dude added an extra socket in my grandad house which bypassed the board.....

    Still there to this day.. nobody there though.


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    Outside pics


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    That's how it was done back in the day.....

    Sure ESb dude added an extra socket in my grandad house which bypassed the board.....

    Still there to this day.. nobody there though.

    Yep I suspected that’s how it was done alright but surely with the push on new regulations etc they should be accountable for fixing stuff like this?


  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    Yep I suspected that’s how it was done alright but surely with the push on new regulations etc they should be accountable for fixing stuff like this?

    Thing is it was ok so until major refurb they will state it's fine....

    Would the board be old screw fuse or MCB?


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    Thing is it was ok so until major refurb they will state it's fine....

    Would the board be old screw fuse or MCB?

    Board looks like it was changed last year, it’s now MCBs

    If she’s to put a metre cabinet on the external wall, are they responsible for getting there cable to it? Presumably it would need to go into ducting?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    Board looks like it was changed last year, it’s now MCBs

    If she’s to put a metre cabinet on the external wall, are they responsible for getting there cable to it? Presumably it would need to go into ducting?

    Would be a good time if possible to put meter outside of suits... Best place for it and leaves things tidier inside...

    Ducting should be fine once electrical standard.

    I'm not 100% on if they would charge or not and it's possible they will.


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    Cheers for the replys, just thought it looked crap and said I’d see what insight everyone had!!


  • Registered Users, Registered Users 2 Posts: 173 ✭✭EHP


    The ESB will most likely charge for moving there meters and will run the cable down the external of the wall into the new meter cabinet outside if you want. The new cabinet can also be a surface cabinet if needed, best request a site visit from one of there engineers and they'll advise you on what needs to be done for them to move the meters.


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    Board looks like it was changed last year, it’s now MCBs

    If she’s to put a metre cabinet on the external wall, are they responsible for getting there cable to it? Presumably it would need to go into ducting?

    If the board was recently changed then new tails should be connected into the meter
    a certificate is required for this
    Pic 3 indicates this is not done
    This would be a more immediate concern

    (Just noticed she recently bought it but my concern still stands)


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    I have no words.

    Sweet mother of Jeebus.

    I hope the black stuff isn't mold - meaning the installation is damp on top of the trainwreck it already is..

    Sorry, that's not helpful OP, I would not feel safe in that house.


  • Registered Users, Registered Users 2 Posts: 22,608 ✭✭✭✭Tell me how


    Steve wrote: »
    I have no words.

    Sweet mother of Jeebus.

    I hope the black stuff isn't mold - meaning the installation is damp on top of the trainwreck it already is..

    Sorry, that's not helpful OP, I would not feel safe in that house.

    That might be an angle to approach the ESB with.
    It's not a good installation, they don't have easy access to meter, you're willing to do preparatory work for meter in new location. Would mean cutting tales for them instead of running new cable from supply.
    Be better for everyone involved.

    Might be worth approaching local office for a chat.

    When were the pictures taken? Did you say an MCB board had been fitted?


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    That might be an angle to approach the ESB with.
    It's not a good installation, they don't have easy access to meter, you're willing to do preparatory work for meter in new location. Would mean cutting tales for them instead of running new cable from supply.
    Be better for everyone involved.

    Might be worth approaching local office for a chat.

    When were the pictures taken? Did you say an MCB board had been fitted?

    Took pics the other night, there’s a small board beside the metre with breakers in it. To be fair to house needs a rewire either way but she only noticed the esb incomer the other night.

    I’ll give the esb a call and request a site visit next week


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    EHP wrote: »
    The ESB will most likely charge for moving there meters and will run the cable down the external of the wall into the new meter cabinet outside if you want. The new cabinet can also be a surface cabinet if needed, best request a site visit from one of there engineers and they'll advise you on what needs to be done for them to move the meters.

    That’s good to know, having to recess the cabinet on the external wall would be a major pain in the...


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    Took pics the other night, there’s a small board beside the metre with breakers in it. To be fair to house needs a rewire either way but she only noticed the esb incomer the other night.

    I’ll give the esb a call and request a site visit next week

    It’s unlikely esbn will do anything for you. If you want the service repositioned or altered then there will be a charge. They will require a certificate from a rec to do so. They possibly will serve you with a notice of potential hazard for the current installation. My advice is to get a rec out beforehand


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    meercat wrote: »
    It’s unlikely esbn will do anything for you. If you want the service repositioned or altered then there will be a charge. They will require a certificate from a rec to do so. They possibly will serve you with a notice of potential hazard for the current installation. My advice is to get a rec out beforehand

    Surely though they need to disconnect and move there part? REC is only responsible for removing tails?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 22,608 ✭✭✭✭Tell me how


    Surely though they need to disconnect and move there part? REC is only responsible for removing tails?

    I think the poster is implying they will not do anything without payment.


  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    I wonder if one were to want a day/night meter as it's a free installation would the guy do the new installation if it were put outside as it would require the same work pretty much.


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Esb won’t come out and do anything just because it looks bad, that’s the way it was ran back in the day and that’s the way every older terraced house in the country is still fed! If you want to reposition the meter outside, you will have to mount a box in the wall, and provide a red duct from the bottom right corner of that box to the bottom of your pole! Esb will request a cert from your electrician who prob won’t very the house, my advise is get house rewired, if you intend on putting meter cabinet outside then do that during the rewire and get your Rec to run his cables out to it! if you cannot put cabinet outside, the meter must wait up inside as is but you still need to rewire house!
    But ESB will not do anything here FOC


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    I wonder if one were to want a day/night meter as it's a free installation would the guy do the new installation if it were put outside as it would require the same work pretty much.

    How is it the same work pretty much?


  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    TheBully wrote: »
    How is it the same work pretty much?

    Ah cause it is... If it's beside the line coming in and all up to scratch it ain't to difficult....


    Not saying it will work but sure you never know....


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Ah cause it is... If it's beside the line coming in and all up to scratch it ain't to difficult....


    Not saying it will work but sure you never know....
    The esb won’t but a meter up outside without it being in a cabinet recessed into the wall and ducted to the bottom of the pole! The OPs service is clipped along the house then bundle wired up to the top of the pole! The OP has lots of work to do before they will mount it outside


  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    TheBully wrote: »
    The esb won’t but a meter up outside without it being in a cabinet recessed into the wall and ducted to the bottom of the pole! The OPs service is clipped along the house then bundle wired up to the top of the pole! The OP has lots of work to do before they will mount it outside

    Well obviously....
    Not talking about now.... Of course loads needs doing as has been discussed.


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Well obviously....
    Not talking about now.... Of course loads needs doing as has been discussed.
    Esb then need to pull new cables into new cabinet and run them up pole!
    All I’m saying that simple getting them to hang a day and night meter will not get them to do that free of charge!


  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    TheBully wrote: »
    Esb then need to pull new cables into new cabinet and run them up pole!
    All I’m saying that simple getting them to hang a day and night meter will not get them to do that free of charge!

    Look I get that but I've seen things done well outside what the plan was and no issues....

    Some can be lucky.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Look I get that but I've seen things done well outside what the plan was and no issues....

    Some can be lucky.
    Maybe, but it’s never gonna happen for this guy


  • Registered Users, Registered Users 2 Posts: 22,608 ✭✭✭✭Tell me how


    TheBully wrote: »
    Maybe, but it’s never gonna happen for this guy

    How do you know?

    The area office are going to call to review. You're probably right, but stranger things have happened. There could be a transformer on a nearby pole that they're due to change and they might say, you know what we'll role it all in to one job as long as customer fulfils their obligations.
    You're probably right, but I wouldn't say it's a done deal.

    Likely need for a duct to pole is probably biggest issue for OP, as well as house rewire need for new very.


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    How do you know?

    The area office are going to call to review. You're probably right, but stranger things have happened. There could be a transformer on a nearby pole that they're due to change and they might say, you know what we'll role it all in to one job as long as customer fulfils their obligations.
    You're probably right, but I wouldn't say it's a done deal.

    Likely need for a duct to pole is probably biggest issue for OP, as well as house rewire need for new very.
    For a start they won’t change a transformer unless it’s blown or else extra capacity is needed from the traffo ie. new houses! esb will only relocate meter for a charge!
    It sounds to me though that the OP will not be putting a cabinet outside though due to work involved!


  • Registered Users, Registered Users 2 Posts: 22,608 ✭✭✭✭Tell me how


    TheBully wrote: »
    For a start they won’t change a transformer unless it’s blown or else extra capacity is needed from the traffo ie. new houses! esb will only relocate meter for a charge!
    It sounds to me though that the OP will not be putting a cabinet outside though due to work involved!

    I worked with ESB before, I've seen backs scratched on both sides.

    I wouldn't expect then to do it for free, I'd still definitely be having a conversation and seeing what story is.


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    I worked with ESB before, I've seen backs scratched on both sides.

    I wouldn't expect then to do it for free, I'd still definitely be having a conversation and seeing what story is.

    They might clip a new service and tidy it up for free in the upcoming smart meter rollout! But that’s about it, they don’t mind meter being inside if it’s read annually or has a smart meter installed! If the OP is willing to to the prep work to move meter they will charge!


  • Registered Users, Registered Users 2 Posts: 173 ✭✭EHP


    I've been involved with meter relocations several times. The ESB have never in my experience moved meters for free and will not move them without a cert from a REC. They will allow there cable to run on surface down the outside of the house into either a recessed cabinet or a surface cabinet. If a REC is completing a test for a meter relocation they only need to test the board and one fixed appliance in the dwelling. If the house passed an insulation resistance test, has a good earth reading to the cooker for example, has RCBO for the shower and correct bonding in hot press plus earth bar then a cert for relocation can be issued. The house may not need rewire for this.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    Thanks for all the reply’s, the house is absolutely going to be rewired.

    Just so I’m clear, does the rewire need to happen before moving the esb incomer? Surely then you are left with no connection to esb so how do you certify?


  • Registered Users, Registered Users 2 Posts: 173 ✭✭EHP


    Thanks for all the reply’s, the house is absolutely going to be rewired.

    Just so I’m clear, does the rewire need to happen before moving the esb incomer? Surely then you are left with no connection to esb so how do you certify?

    Rewire would happen before the meters are moved you would have a temporary connection from the existing meters until they are moved best bet is get your REC out and they will explain the steps.


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Thanks for all the reply’s, the house is absolutely going to be rewired.

    Just so I’m clear, does the rewire need to happen before moving the esb incomer? Surely then you are left with no connection to esb so how do you certify?

    You don’t need to have an esb connection to certify, your REC will do his checks dead, earth fault loop, insulation resistance etc!
    He esb will more than likely move it before you start your rewire if you chat to the area office but they won’t re connect up without a cert! But my advice is rewire, have your electrician run his new tails out to the new cabinet that you have mounted! Have your end done and that way esb will be in and out in one day otherwise you will be left with no supply on site for duration of works


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    All makes sense, appreciate the input folks


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    TheBully wrote: »
    Esb won’t come out and do anything just because it looks bad, that’s the way it was ran back in the day and that’s the way every older terraced house in the country is still fed! If you want to reposition the meter outside, you will have to mount a box in the wall, and provide a red duct from the bottom right corner of that box to the bottom of your pole! Esb will request a cert from your electrician who prob won’t very the house, my advise is get house rewired, if you intend on putting meter cabinet outside then do that during the rewire and get your Rec to run his cables out to it! if you cannot put cabinet outside, the meter must wait up inside as is but you still need to rewire house!
    But ESB will not do anything here FOC
    Wrong. Duct for ESB must enter in bottom LEFT corner.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Risteard81 wrote: »
    Wrong. Duct for ESB must enter in bottom LEFT corner.

    Apologies, you are correct! It’s the bottom left! Jeez


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    Will they clip down the wall and enter in the top of the cabinet is surface mount?

    Running a duct will mean digging up the driveway


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Will they clip down the wall and enter in the top of the cabinet is surface mount?

    Running a duct will mean digging up the driveway
    The only way they will mount a meter outside is if it’s ducted, they will not go in any other way


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Will they clip down the wall and enter in the top of the cabinet is surface mount?

    Running a duct will mean digging up the driveway

    Also cabinet cannot be surface mounted, will have to be recessed into wall! If I was you I’d just leave it in the house by sounds of it!!


  • Registered Users, Registered Users 2 Posts: 173 ✭✭EHP


    TheBully wrote: »
    The only way they will mount a meter outside is if it’s ducted, they will not go in any other way

    They will run down the wall on surface in existing installations where the cable is already on surface but will only enter on the bottom of the meter cabinet.


  • Registered Users, Registered Users 2 Posts: 173 ✭✭EHP


    TheBully wrote: »
    Also cabinet cannot be surface mounted, will have to be recessed into wall! If I was you I’d just leave it in the house by sounds of it!!

    Cabinets can be surface mounted where necessary have to use a cabinet rated to IP54 or higher not 100% on the ip rating but definitely can be surface mounted if needed.


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    TheBully wrote: »
    Also cabinet cannot be surface mounted, will have to be recessed into wall! If I was you I’d just leave it in the house by sounds of it!!

    Esbn will accept a suitable, surface mounted cabinet outside with a gland into the side of the box(near the top corner,if cable is clipped down the wall)

    Ehp beat me to it(too slow typing)


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    meercat wrote: »
    Esbn will accept a suitable, surface mounted cabinet outside with a gland into the side of the box(near the top corner,if cable is clipped down the wall)

    Ehp beat me to it(too slow typing)

    Esb will only accept that if the house does not have a cavity


  • Registered Users, Registered Users 2 Posts: 3,391 ✭✭✭5500


    Not to hijack the Ops thread but similar situation with a family member who has an overhead main line running In above a garage door like the OPs, then into the garage where the consumer unit and meter are. They want the main cable moved about 6 inches up as they plan on changing the garage doors, but with the main coming in the top of the frame it might not be possible as ia/dangerous pulling out the old frame and fitting new where the wire is located.

    The house was recently rewired and they contacted esb to come out to install a new meter and tails, but the rep on the phone just said whoever called would take a look at the wire coming in.

    I think the charge for the tails and meter from esb was €200, but to do what they want would a whole new run of cable have to come from the pole, then to the house, down the wall and in a hole slightly higher or are esb able to reuse the cable in situ which might cut down on the cost ?


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    You can see the cable coming down in the first pic, clipped to the wall.

    If we were to surface mount the cabinet nearer the front of the house they would need to extend or run a new cable from the pole and clip it down the wall id imagine