Private profiles - please note that profiles marked as private will soon be public. This will facilitate moderation so mods can view users' warning histories. All of your posts across the site will appear on your profile page (including PI, RI). Groups posts will remain private except to users who have access to the same Groups as you. Thread here
Some important site news, please read here. Thanks!

Is air to heat good enough for commercial???

  • 16-09-2018 2:19am
    #1
    Registered Users Posts: 588 ✭✭✭ MorganIRL
    Registered User


    My question is would air to heat be good enough to heat a 9 bedrooms in a hotel & bar and function room, circa 7-8000 m², will be doing an upgrade and have access to piped gas, but trying to weigh up all my options of, kerosene, gas, renewable (if avail).


Comments

  • Registered Users Posts: 160 ✭✭ al2009
    Registered User


    Do you mean air to air heat pumps?


  • Registered Users Posts: 588 ✭✭✭ MorganIRL
    Registered User


    I know them as air to heat, I think they are mostly know as air to water heat pumps, that heat buildings etc.


  • Registered Users Posts: 11,364 ✭✭✭✭ KCross
    Registered User


    To heat that size building it would need to be a significant sized Heat pump and hence significant money. I would expect that the wiser choice in that case for a heat pump would be Geothermal as you have economies of scale.

    Is your premises well insulated?

    And I'd say the biggest issue you'd have is that, I presume, you dont have underfloor heating, just steel rads? That wouldn't work very well with a heat pump. You'd probably have guests telling you the rads are cold! :)


  • Registered Users Posts: 2,765 ✭✭✭ taytobreath
    Registered User


    a good condensing gas burner would be better suited in my opinion


  • Registered Users Posts: 588 ✭✭✭ MorganIRL
    Registered User


    Don't have the access for geothermal, I think the option is looking more likely like a gas boiler as I have access to piped gas, it'll be the obvious answer with the size of the building etc.
    KCross wrote: »
    To heat that size building it would need to be a significant sized Heat pump and hence significant money. I would expect that the wiser choice in that case for a heat pump would be Geothermal as you have economies of scale.

    Is your premises well insulated?

    And I'd say the biggest issue you'd have is that, I presume, you dont have underfloor heating, just steel rads? That wouldn't work very well with a heat pump. You'd probably have guests telling you the rads are cold! :)


  • Advertisement
  • Registered Users Posts: 10,991 ✭✭✭✭ Calahonda52
    Registered User


    a good condensing gas burner would be better suited in my opinion


    This will only work if the rads are designed to match the water temp from the condensing boiler, which generally run cooler that non-C, leading on average to 22% less heat output

    google delta T in rad design, or look up any rad supplier specs:
    Non-C Delta T normally 60, is 50 for condemning: hence the issue