Grant Euroflame 70/90 HE utility

  • 29-11-2016 7:51pm
    #1
    Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭


    Have just gotten a call to attend a breakdown on the above. It hasn't been serviced in 3 years. 1/3rd tank of oil. Burned about 1800 liters kero since last service. RDB 2.2 burner.

    Reset light on burner illuminated. Nothing happens when pressed, not even a hum.

    I am a little stuck for time tomorrow so I need to hit the ground running on this. What do I check for?
    Control Box? Motor? PC?..maybe. Cap?...maybe. Seized pump?..maybe.
    Except for control box and motor, I would expect some sort of sound.
    Any thoughts?

    Please follow site and charter rules. "Resistance is futile"



Comments

  • Registered Users, Registered Users 2 Posts: 34 ServiceGuy


    Did they say if the reset light goes out when pressed. I find sometimes the customer doesn't hear the faint hum.


  • Registered Users, Registered Users 2 Posts: 871 ✭✭✭TPM


    if nothing at all check capacitor, then control box, then motor,
    some rdb control boxes have been known to give trouble always good to have a spare with you


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    ServiceGuy wrote: »
    Did they say if the reset light goes out when pressed. I find sometimes the customer doesn't hear the faint hum.

    Unlikely that there is a hum. I really went through that with customer.

    Please follow site and charter rules. "Resistance is futile"



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    TPM wrote: »
    if nothing at all check capacitor, then control box, then motor,
    some rdb control boxes have been known to give trouble always good to have a spare with you

    Those are my lines of thought. Was wondering if I was missing something?

    Please follow site and charter rules. "Resistance is futile"



  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    If reset light is illuminated and when pressed the capacitor is not buzzing.
    Firstly I would be checking for 230 volts across L and N under load .Also checking for 230 volts across L and E under load. i.e when reset button is pressed.
    Or you could connect up an electrical item drawing 2 or 3 amps and see if the power supply is ok.


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    agusta wrote: »
    If reset light is illuminated and when pressed the capacitor is not buzzing.
    Firstly I would be checking for 230 volts across L and N under load .Also checking for 230 volts across L and E under load. i.e when reset button is pressed.
    Or you could connect up an electrical item drawing 2 or 3 amps and see if the power supply is ok.

    Thanks
    I will keep that in mind. I have used my halogen standard light for such purposes in the past.

    Can't see why I need to press the reset button for the test though?

    Please follow site and charter rules. "Resistance is futile"



  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    If the lockout light is on its not drawing any power.it would be similar to connecting up the halogen light but not turning on the switch on the light.i may not be of help but for me getting 220 under load is the starting point.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Thanks Agusta

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 871 ✭✭✭TPM


    Wearb wrote: »
    Those are my lines of thought. Was wondering if I was missing something?

    thinking aloud
    photocell tends to leave motor running rather than doing nothing
    solenoid/coil would run but not fire
    oil problem same
    pump seized humming, key gone would run
    could be loose wire in control box

    and as agusta said check actual voltage(tbh i wouldnt have thought of that till I eliminated other stuff)


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    TPM wrote: »
    thinking aloud
    photocell tends to leave motor running rather than doing nothing
    solenoid/coil would run but not fire
    oil problem same
    pump seized humming, key gone would run
    could be loose wire in control box

    and as agusta said check actual voltage(tbh i wouldnt have thought of that till I eliminated other stuff)

    Yes I was thinking along the same lines. That was why I had written "maybe" on those items.

    I wrote here some while ago about getting a correct no load voltage and using a lamp to load it. Wires had been chewed by vermin. They were touching enough for multimeter to read correct voltage. But failed under load.

    Thanks for giving it some thought.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    at a guess id say you will probably hear the hum when you get there

    had 1 like this last year no hum red light on control box sorted it


    but sometimes they don't hum unless you put on a bit of music


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    red light on control box sorted it

    So I need a new red light ???

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    Wearb wrote: »
    So I need a new red light ???



    only available to agusta and myself in limerick

    red lights are hard to come by


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    only available to agusta and myself in limerick

    red lights are hard to come by

    Yeah lots of them down that way alright ;)

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    bandit country


  • Registered Users, Registered Users 2 Posts: 871 ✭✭✭TPM


    Wearb wrote: »

    I wrote here some while ago about getting a correct no load voltage and using a lamp to load it. Wires had been chewed by vermin. They were touching enough for multimeter to read correct voltage. But failed under load.

    thats where the extension lead comes in handy


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    If power under load is confirmed ok
    pull motor wires lug from control box
    test for 230 across the lugs where the blue and the black wire go,
    if you dont get 230,new control box

    you can also test motor with different power source if required, blue wire is live,black wire is neutral,if capacitor,motor turning freely,motor ok,motor will start


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    agusta wrote: »
    If power under load is confirmed ok
    pull motor wires lug from control box
    test for 230 across the lugs where the blue and the black wire go,
    if you dont get 230,new control box

    you can also test motor with different power source if required, blue wire is live,black wire is neutral,if capacitor,motor turning freely,motor ok,motor will start
    Probably can use a jumper to bypass CB to see if motor turns. Often did it on the mectron.

    Please follow site and charter rules. "Resistance is futile"



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    bandit country

    Ok I suppose I have to drag it out of you. What was wrong with your humming burner (above). Capacitor?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    it wasn't humming and it was the control box


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    it wasn't humming and it was the control box

    Ok. Get it now.
    I must send down a box of commas with the sloe gin. :)

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    thanks very much they will never arrive


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Wearb wrote: »
    Probably can use a jumper to bypass CB to see if motor turns. Often did it on the mectron.
    Yes ,if motor turns at least you know what side of the burner the fault is on


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    thanks very much they will never arrive

    You just don't want to make Tom jealous by admitting you got it last year. Cheers.

    Ah F it. I can't get used to calling him Tom. SCUDO.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 871 ✭✭✭TPM


    if i have 230v, cap checked ok and resistance on the motor I change the controlbox, its nearly as quick as bypassing the control box and generally tends to be the fault, when no humming that is
    HHHHHhhhhhhhhhhhhhhmmmmmmmmmmmmmmmmmmmmm


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Tom doesnt feel right for me either,its scudo again so :)


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    402754.jpg

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    did you put on a bit of guns and roses and what was wrong with it or do we have to drag it out of you

    nice cap reading


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    did you put on a bit of guns and roses and what was wrong with it or do we have to drag it out of you

    nice cap reading

    WHAT WAS WRONG WITH IT? Move away from that plume and wipe the specs :)))

    Strange one. No hum when I turned it on. Not a peep out of it. Went out and brought in a few tools and while setting up the multi meter, away she fires. Left it running a few minutes and turned it on and off a few times without problems.
    Anyway tried the cap and as you can see, it was at less than 50%. Pulled the burner to visually check nozzle area and combustion area. All good. PC as clean as a whistle.
    New cap in it now. FGA done to cover rear.
    Hopefully that's it sorted.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    ServiceGuy wrote: »
    Did they say if the reset light goes out when pressed. I find sometimes the customer doesn't hear the faint hum.

    Sorry serviceguy. I missed your post.

    What does the light going out when pressed indicate ?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    oh ya out of the plume now all that ould high co isn't good for the brain


    that's another new one about cap rdb burners never cease to amaze

    usually some kind of a hum


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    oh ya out of the plume now all that ould high co isn't good for the brain


    that's another new one about cap rdb burners never cease to amaze

    usually some kind of a hum

    New to me also. Also the delayed start even with that cap.

    Maybe it saw the lump hammer in my tool tray :(. And decided it better fire up.

    Please follow site and charter rules. "Resistance is futile"



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    403760.JPG

    Is this a PRV?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 871 ✭✭✭TPM


    a good old aav ;)

    Prv pressure relief valve


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    grant aav with the cap missing


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    agusta wrote: »
    grant aav with the cap missing
    agusta wrote: »
    grant aav with the cap missing

    Yes it's on a grant.on top of the boiler. I never noticed one like it before- with a side outlet.

    I can't find a Prv on it anywhere except one in the hot press upstairs. Is that an acceptable arrangement?

    Please follow site and charter rules. "Resistance is futile"



  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Is it a grant utility boiler..., the aav comes with the boiler


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    agusta wrote: »
    Is it a grant utility boiler..., the aav comes with the boiler

    Yes. As the thread name says. I would have expected it where that AAV is or nearby.

    Please follow site and charter rules. "Resistance is futile"



  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    You will probably find it behind the carcass of the press beside the boiler on the flow.You might also see a 1/2" pipe coming outside the house which would be the pipe plumbed off the prv


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    agusta wrote: »
    You will probably find it behind the carcass of the press beside the boiler on the flow.You might also see a 1/2" pipe coming outside the house which would be the pipe plumbed off the prv

    Thanks Agusta. I will give another look.
    Didn't see any piping that might be attached. Having said that, the condensate pipe goes into the wall inside, but no sign of it outside. Must drop in the cavity and connect to something underground.
    If there is something similar at the back of the boiler cabinet, it would be very difficult to see.

    I will have to remove some worktop to get a good look.
    I will talk to customer about it. At least there is a prv on the system, just too far away for comfort.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Wearb wrote: »
    Thanks Agusta. I will give another look.
    Didn't see any piping that might be attached. Having said that, the condensate pipe goes into the wall inside, but no sign of it outside. Must drop in the cavity and connect to something underground.
    If there is something similar at the back of the boiler cabinet, it would be very difficult to see.

    I will have to remove some worktop to get a good look.
    I will talk to customer about it. At least there is a prv on the system, just too far away for comfort.
    There just might be a removable back fitted on the inside of the press beside the boiler.If not i agree that removing the counter top is the best option,where is the circulating pump located.
    I would be more worried about where the condensate pipe is going.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    agusta wrote: »
    There just might be a removable back fitted on the inside of the press beside the boiler.If not i agree that removing the counter top is the best option,where is the circulating pump located.
    I would be more worried about where the condensate pipe is going.

    Circulating pump is on RH side outside casing- as you face front of boiler. It is neatly boxed in with a full length MDF L shaped removable panel.

    Please follow site and charter rules. "Resistance is futile"



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Just been reading the manual on this. It seems that Grant doesn't request a PRV on an open system. All mentions of a PRV are referenced to a sealed system.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 871 ✭✭✭TPM


    and grant also do a system kit for the outdoor module that locates the circulating pump on the flow pipe and leaves the highest point in the casing.
    great idea if you like your pumps prone to airlocking and running dry


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    TPM wrote: »
    and grant also do a system kit for the outdoor module that locates the circulating pump on the flow pipe and leaves the highest point in the casing.
    great idea if you like your pumps prone to airlocking and running dry
    could you explain a little more.., just trying to understand


  • Registered Users, Registered Users 2 Posts: 24 Johnny Macwilliams


    Wearb wrote: »
    403760.JPG

    Is this a PRV?

    Oh sweet Jesus


  • Registered Users, Registered Users 2 Posts: 1,019 ✭✭✭anthonyos


    When I did my plumbing apprenticeship I learned that the prv is the first connection from the boiler always it worrys so me that there are guys out there that don't know the difference between aav and a prv .I there was a joke of some kind to follow but it was a genuine question


  • Registered Users, Registered Users 2 Posts: 871 ✭✭✭TPM


    agusta wrote: »
    could you explain a little more.., just trying to understand

    you can buy a system kit from grant for the vortex outdoor module
    it comes with pump, safety valve, aav, pre made pipe work etc.

    when you put it all together it locates the pump on top of the boiler on the flow pipe, if system pressure drops or there is air in the system it tends to let the pump run dry and/or overheat