Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Insulation specification thoughts

  • 30-11-2014 9:33pm
    #1
    Registered Users, Registered Users 2 Posts: 863 ✭✭✭


    Hi , have been a keen reader on here for past few months , recently got planning for 1.5 storey 289sq meter house and am now working together with architect on builders specification to go to tender with.
    I guess in general I am looking for a fairly decent level of air tightness and insulation .I will be using oil heating.
    I know there can a lot of different opinions on insulation ,so I was hoping for some short feedback on whether any concerns with the following my architect has drawn up :

    Floor :
    Concrete ground floor slab throughout shall be 150mm thick 30 N. concrete slab with a power floated finish, on 120 mm XtraTherm floor slab insulation board .

    External Walls :
    100mm Outer leaf , 100mm inner leaf ,. 100mm wide cavity insulated using 100mm XtraTherm cavity therm. drylined internally using 62mm thick insulated plaster boards

    First floor Ceiling :
    Line all internal partitions and ground floor ceilings with 12.7 gyproc plasterboard.
    Supply and lay 300mm thick fibreglass insulation quilt to all attic spaces with flat ceilings . All sloping areas and the flat roofed rear annex shall be insulated with 100mm XtraTherm or similar approved

    Roof :
    Fitted between the rafters and ceilings underneath shall be drylined using 63mm thick insulated plasterboard , incorporating a vapour check.
    *We are laying chipboard floor in attic for storage , maybe that is why specification also includes roof insulation, I need to confirm this.


Comments

  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    air-tightness?


  • Registered Users, Registered Users 2 Posts: 863 ✭✭✭Rooy


    Thanks for the response Bryan , in terms of the draft specification it specifies ". Allow for the insulation of an air tightness membrane and for testing and certifying same" .
    I have been reading through it over the weekend before meeting the architect again ,but this sounds possibly like it needs more detail added.


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    firstly, internal dry lining on a new house build is a bad specification.

    secondly, most of the specification is just barely on the minimum level required.

    has a provision BER assessment been carried out to show the whole house specification complies?

    if so, what level of air tightness was inputted and how was this measure treated in the specification?


  • Registered Users, Registered Users 2 Posts: 615 ✭✭✭Strolling Bones


    Rooy wrote: »
    Thanks for the response Bryan , in terms of the draft specification it specifies ". Allow for the insulation of an air tightness membrane and for testing and certifying same" .
    I have been reading through it over the weekend before meeting the architect again ,but this sounds possibly like it needs more detail added.

    That sounds like it was written by a badly performing student. How did you find this "architect"?


  • Registered Users, Registered Users 2 Posts: 1,445 ✭✭✭sky6


    Some of these methods sound out of date by modern standards. With the amount of money you'll be spending you need to get it right. Don't rush to build, Do plenty of research and talk to lots of people. Don't be afraid to contact the manufacturers to find out how they recommend it's fitted or done. Don't take or give any instructions verbally.
    Remember if your getting a Mortgage you will be paying it for a long time.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 863 ✭✭✭Rooy


    Thanks for the feedback guys , I guess it highlighted my shortcomings in an understanding of all this , great to get some comments , I can going to look to get an independent BER assessment on the initial specification and see what I can consider to change from there as well as seek further advice where possible.


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    Rooy wrote: »
    Thanks for the feedback guys , I guess it highlighted my shortcomings in an understanding of all this , great to get some comments , I can going to look to get an independent BER assessment on the initial specification and see what I can consider to change from there as well as seek further advice where possible.

    make sure the assessor is a qualified architectural technician


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    sydthebeat wrote: »
    firstly, internal dry lining on a new house build is a bad specification.

    Can you elaborate on this please, it has been spec'd into my own build by my BER assessor.

    Are you saying that installing the insulated board is not only bad but also unnecessary and if so should I be replacing it with another type of insulation?

    My spec is a 150mm bead cavity with sand/cement plaster and 50mm insulated board on all external walls.

    Minimum of 2 required on air tightness (hoping for better than that) and installing a MHRV system.


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    BarryM3 wrote: »
    Can you elaborate on this please, it has been spec'd into my own build by my BER assessor.

    Are you saying that installing the insulated board is not only bad but also unnecessary and if so should I be replacing it with another type of insulation?

    My spec is a 150mm bead cavity with sand/cement plaster and 50mm insulated board on all external walls.

    Minimum of 2 required on air tightness (hoping for better than that) and installing a MHRV system.

    The current building regulations are of a quite high standard.
    They are designed in essence to avoid the "warm up - cool down" frequencies that we were all brought up with in irish homes, where we get out of bed to a freezing cold house. Now we try to maintain a constant comfortable temperature using the least amount of fuel as possible.

    One factor which helps in regulating temperature so not to have highs and lows is "thermal mass". This means dense materials such as concrete absorb the heat during the day, whether by solar gain, or by generated energy, and store this heat and releases it back at night time when temps drop and theres a bigger demand.

    Another factor which helps regulate this air tightness, which basically means cutting out any unwanted draughts. In order to achieve as high a possible an air tightness, the construction should be kept as homogeneous as possible and the details as simple as possible.

    by specifying thermal liners on the external walls, the thermal mas is reduced significantly. While its arguable that this deflects the heat generated quicker than block walls, it also means that the rooms cool down quicker also. This results in a pattern of heating up / cooling down that we are trying to avoid. It also means that more heat needs to be generated at times when temps are lower such as evening and night time.

    when it comes to air tightness, thermal liners are a bad idea. It becomes extremely hard to guarantee good detail because less care is taken with things such as the initial block work, chasing etc as "sure it will be covered over" mindset kicks in. Imagine how difficult it is in making a timber joist floor air tight if the air tight layer is 50mm inside the external walls.

    also, you end up having a break in your insulation continuity at ever location of an internal wall meeting an external, and at first floor junctions. Whilst you still have the cavity insulation, your extra insulation is broken at all these points and these areas run the risk of condensation being localized and intensified, whcih can cause additional issues.

    the solution is either to
    1. increase the cavity width to account for the internal insulation, say to 200mm (this may need your structural enginners input)
    2. install a cavity board insulation such as xtratherms full fill cavity board in your 150mm cavity.

    in my opinion both the options above are better solutions than using internal dry lining.

    its much easier to treat internal blockwork for air tightness, than dry lining.


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    Thanks for that Syd.

    If you were in my shoes, i.e committed to 150mm cavity what would you do?

    Edit to add: I understand the thermal mass concept and it's benefits and downsides. We have chosen not to go this route due to our lifestyles and daily habits.

    If someone could show me that I would be no worse off by ditching the insulated board I would be quite happy to delete it off my spec and spend the money elsewhere.


  • Advertisement
  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    BarryM3 wrote: »
    Thanks for that Syd.

    If you were in my shoes, i.e committed to 150mm cavity what would you do?

    committed as in the blockwork is significantly up already?


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    Foundations, rising walls and floor filled in with stone


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    BarryM3 wrote: »
    Foundations, rising walls and floor filled in with stone

    id change my cavity specification to full fill insulation such as ive linked to above.

    have you anyone working on the construction details of your build, especially from an air tightness point of view?


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    And would you delete the application of insulated board then?

    Yes, I've a BER assessor who is working with my structural engineer/Architect in creating necessary detailing and liaising with the contractor in all areas including air-tightness, cold bridging etc. I need to check but I think the contractor is in turn out-sourcing the air-tightness procedures.

    In relation to the full fill Vs cavity bead I did some research a while back on both and came to the (possibly wrong?) conclusion that while the cavity board can give better U value results it is very much dependent on an almost flawless installation which is extremely difficult and realistically unlikely to achieve. I remember something about it losing a significant % of it's performance if a gap of something like 2mm at any point?


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    BarryM3 wrote: »
    And would you delete the application of insulated board then?

    Yes, I've a BER assessor who is working with my structural engineer/Architect in creating necessary detailing and liaising with the contractor in all areas including air-tightness, cold bridging etc. I need to check but I think the contractor is in turn out-sourcing the air-tightness procedures.

    In relation to the full fill Vs cavity bead I did some research a while back on both and came to the (possibly wrong?) conclusion that while the cavity board can give better U value results it is very much dependent on an almost flawless installation which is extremely difficult and realistically unlikely to achieve. I remember something about it losing a significant % of it's performance if a gap of something like 2mm at any point?

    that is true and i would have held a similar opinion up to having reviewed a few projects using the product lately, and, ONCE DUE CARE is applied and the product is installed correctly in accordance with datasheets, then id have no problem recommending it. It was outr standard spec up to last year to pump the cavities and, while i still believe in it as a specification, ive seen cases where DPC trays are put in taut which means the beads cant fill the areas behind. Again its a case of block layers not caring understanding whats coming after them....

    so in your particular case, if you haunt your blocklayer and make sure the cavities are clean and the insulation is installed correctly, id still prefer this to using thermal lining boards.
    on a risk versus reward basis id view the dry lining as a higher risk for less reward.


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    Thanks Syd,

    I will speak to the contractor and his blocklayers and suss out the option of using the board and their personal experiences.

    One final aspect.... supposing, for whatever reason, we retain the bead filled cavity option....would you keep the insulated boards or bin em?


  • Registered Users, Registered Users 2 Posts: 12,748 ✭✭✭✭galwaytt


    sydthebeat wrote: »
    The current building regulations are of a quite high standard.
    They are designed in essence to avoid the "warm up - cool down" frequencies that we were all brought up with in irish homes, where we get out of bed to a freezing cold house. Now we try to maintain a constant comfortable temperature using the least amount of fuel as possible.

    One factor which helps in regulating temperature so not to have highs and lows is "thermal mass". This means dense materials such as concrete absorb the heat during the day, whether by solar gain, or by generated energy, and store this heat and releases it back at night time when temps drop and theres a bigger demand.

    Another factor which helps regulate this air tightness, which basically means cutting out any unwanted draughts. In order to achieve as high a possible an air tightness, the construction should be kept as homogeneous as possible and the details as simple as possible.

    by specifying thermal liners on the external walls, the thermal mas is reduced significantly. While its arguable that this deflects the heat generated quicker than block walls, it also means that the rooms cool down quicker also. This results in a pattern of heating up / cooling down that we are trying to avoid. It also means that more heat needs to be generated at times when temps are lower such as evening and night time.

    when it comes to air tightness, thermal liners are a bad idea. It becomes extremely hard to guarantee good detail because less care is taken with things such as the initial block work, chasing etc as "sure it will be covered over" mindset kicks in. Imagine how difficult it is in making a timber joist floor air tight if the air tight layer is 50mm inside the external walls.

    also, you end up having a break in your insulation continuity at ever location of an internal wall meeting an external, and at first floor junctions. Whilst you still have the cavity insulation, your extra insulation is broken at all these points and these areas run the risk of condensation being localized and intensified, whcih can cause additional issues.

    the solution is either to
    1. increase the cavity width to account for the internal insulation, say to 200mm (this may need your structural enginners input)
    2. install a cavity board insulation such as xtratherms full fill cavity board in your 150mm cavity.

    in my opinion both the options above are better solutions than using internal dry lining.

    its much easier to treat internal blockwork for air tightness, than dry lining.

    I won't point you in the direction of a scheme of 60+ houses being built now with 100mm insulated board on the inside so !! :)

    Ode To The Motorist

    “And my existence, while grotesque and incomprehensible to you, generates funds to the exchequer. You don't want to acknowledge that as truth because, deep down in places you don't talk about at the Green Party, you want me on that road, you need me on that road. We use words like freedom, enjoyment, sport and community. We use these words as the backbone of a life spent instilling those values in our families and loved ones. You use them as a punch line. I have neither the time nor the inclination to explain myself to a man who rises and sleeps under the tax revenue and the very freedom to spend it that I provide, and then questions the manner in which I provide it. I would rather you just said "thank you" and went on your way. Otherwise I suggest you pick up a bus pass and get the ********* ********* off the road” 



  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    galwaytt wrote: »
    I won't point you in the direction of a scheme of 60+ houses being built now with 100mm insulated board on the inside so !! :)

    a block build?

    wouldnt at all surprise me that a developer will choose the quickest, driest method which ticks the paper exercise of Part L compliance.


  • Registered Users, Registered Users 2 Posts: 85 ✭✭ferryman35


    We are putting the finishing touches to the outside of our build and I would recommend the full fill board as recommended here hands down.

    Because you are filling the cavity it is not so difficult to get a tight fit of the insulation to the inner leaf. The edges of the boards are rebated and 'slot' into each other, so you've actually to work to get an open gap. The corner boards come pre-mitred so jointing there isn't so difficult either. If you wanted a really good result you could tape the joints in the boards and it might especially be worth doing at the corners.

    The only downside of this product is that there can be a bit of waste an the sloped parts of the gable walls. (And the blocklayers won't want anything that slows them down!)

    You'll find many benefits as you progress into your build with having masonry rather than plasterboard walls to work with

    You're also at the stage that it would be prudent to consider using quinnlites for your first and last courses on the internal leaf and you'll find more threads about that measure in the forum. Though I tried I wasn't as successful as I hoped to be getting my guys to do this, but I got them some places!!

    And another good tip that you'll find here is to locate your meter cabinet on a garage wall rather than the house wall if you are building a suitably located garage.

    The recommendations you've been given here are spot on, and much more progressive than many of the specifications that seem to be going into even pretty expensive builds at the moment.

    We finished ours off with a rockwool based warm roof construction and the builders are amazed at the heat they can feel when they step inside - and its just a shell!! It's not just placebo....you'd take your jacket off to walk around inside.


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    So, here is the ultimate question.

    150mm full full cavity and no insulated board
    or
    150mm bead fill cavity and insulated board

    Which is better overall? Anecdotally and U value wise?

    It just seems to me that ditching the insulated board will reduce the insulation quality of the house more than the full fill board can make up?

    Ferryman - In relation to QuinnLites, I have that spec'd into the plans.

    Is having plasterboard covered masonry walls really that big a deal, surely you can just drill deeper holes and affix to the masonry behind the board where required?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 558 ✭✭✭beyondpassive


    Drylines eliminates mass from the building and affects the aility of the interior to maintain stable heat and deal with overheating. Drylining is also a fire risk but less about that. One issue is that the dryling stops and starts at partitions, suspended floors and eaves. When i look at my own refurb with its drylining, you can see heat escaping at the 1st floor floorplate, where the heating pipes occur.

    In my view your better with a lesser U-Value and higher mass. Personally i think drylining should be allowed for new build.


  • Registered Users, Registered Users 2 Posts: 85 ✭✭ferryman35


    the quoted u-value for 150mm full fill well meets the regulations, so if you have a good installation, then you should expect a good result. Anecdotally is harder to quantify.

    At the end of your project, all the components of your build have to function as a system, and it is how you combine the different elements that will determine your success. Insulation is only part of the equation - you also need to keep airtightness, ventilation and the heating system in mind.

    The best demonstration I saw of thermal mass in action was after the sun had set during the summer evenings....you could feel the heat radiating back from the blocks in the cooler night air. It works....

    In a new house that I saw, with insulated board on the internal walls and hole in the window vents, the tiniest fire had heated the sitting room so hot and stuffy that we couldn't stay in it. Yet a part of the house that didn't have heating on was freezing - too cold to stand in without your jacket.

    You won't reduce the insulation value of your house but you will make it a whole lot more comfortable......and you don't have he risk of condensation & mould.

    And your second question.....yes you can drill deeper holes and fix to the masonry behind, but then if you're fixing something heavy you should be using spacer blocks (don't see those in too many places!?.....you need special fixings for lights, pictures, hanging shelves, more complicated for airtightness, probably wiring if its done right and fitted furniture.

    There are places where insulated boards are a very good solution but I think there are better options for new builds.


  • Registered Users, Registered Users 2 Posts: 9,555 ✭✭✭antiskeptic


    BarryM3 wrote: »
    So, here is the ultimate question.

    150mm full full cavity and no insulated board
    or
    150mm bead fill cavity and insulated board

    Which is better overall? Anecdotally and U value wise?

    It just seems to me that ditching the insulated board will reduce the insulation quality of the house more than the full fill board can make up?

    Ferryman - In relation to QuinnLites, I have that spec'd into the plans.

    Is having plasterboard covered masonry walls really that big a deal, surely you can just drill deeper holes and affix to the masonry behind the board where required?

    What about downstairs internal walls (or some of them) of blockwork to give you thermal mass and insulate the external walls internally as planned. We went lightweight block on the insulated slab in places - more for sense of solidity.

    What of your floors? Are they concrete and would that not contribute to thermal mass?

    -

    For what it's worth. I've had experience of renovating/living in two identical houses, one with 60mm insulation in the cavity and one with 60mm insulated slab on all external walls. I get the thermal mass argument but:

    - the internal slab version seems more forgiving of builder sloppiness. I couldn't believe what I saw bricklayers doing and went through 4 of them on one build, firing 3 for unforgiveable workmanship.

    - the idea of 4'x2'vpieces of insulation, successfully T&G knitted with it's neighbour bottom/top/right/left then clamped tight to a wall strikes me as the height of wishful thinking on site. Perhaps the methods proposed here differ from that. 8x4 gives less margin for error internally.

    - I don't see the advantage of "slowly releasing the heat back into the room" when I'm in bed. Zero thermal mass (were such a thing possible) means rapid heat up times which are easy/cheapest of all to sustain for the time you need them and which don't waste heat being given back when you're not around to enjoy it.


    Without question and based on comparative experience, especially given the realities of building on site, I'd plump to live in a polyisocyanurate box every time. Remember, thermal mass leaks heat to ground: you get up in the morning to a non ice-box house (yeay!), head out to IKEA for the afternoon, come home, hit the heating ... and wait. Match of the Day is winding up before you're up to speed.

    In an ideal world perhaps.


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    Remember, thermal mass leaks heat to ground: you get up in the morning to a non ice-box house (yeay!), head out to IKEA for the afternoon, come home, hit the heating ... and wait. Match of the Day is winding up before you're up to speed.

    In an ideal world perhaps.

    you see this is where you are wrong, with a high thermal mass home if your gone for the afternoon and the heating is off, the thermal mass help regulate the heating so thats theres NOT a sudden drop in temperature while youre out.

    they are designed to regulate over 24 hours, not 4 or 5.

    the only time id recommend a low thermal mass house is when there is definitely no body in house at all for 8 - 10 hours a day every day....

    so for the likes of offices etc it may be a reasonable spec.


  • Registered Users, Registered Users 2 Posts: 9,555 ✭✭✭antiskeptic


    sydthebeat wrote: »
    the only time id recommend a low thermal mass house is when there is definitely no body in house at all for 8 - 10 hours a day every day....[/quote

    Like (effectively) night time? Every night time I'm snug under the blankets and need no heat being released into the house. Yet lots of the heat I've on to keep me snug for Grand Designs is being absorbed by the walls to be given back out when I'm asleep.

    The trouble (I find) with thermal mass is that it's too slow to react to changing requirements: some days folk are out lots of the day, sometimes not. Sometimes you stay in on a Saturday, sometimes you're out for the day. With thermal mass, you're kind of committed to maintaining even temperature 24/7. Without it, you can zap on the heat when you need to zap it on, and get a return quickly.

    It's not like you can have no thermal mass such as the house turns to an ice box as soon as you open the front door to take in your Bombay Pantry delivery...


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    Drylines eliminates mass from the building and affects the aility of the interior to maintain stable heat and deal with overheating. Drylining is also a fire risk but less about that. One issue is that the dryling stops and starts at partitions, suspended floors and eaves. When i look at my own refurb with its drylining, you can see heat escaping at the 1st floor floorplate, where the heating pipes occur.

    In my view your better with a lesser U-Value and higher mass. Personally i think drylining should be allowed for new build.

    I get the thermal mass point, in my circumstances it's not crucial as our lifestyle dictates large periods of empty house.

    In relation to the stop/start of the drylining - I must be missing something. As we will have all external walls wet plastered internally also, then the adding of the insulated drylining - even if done badly - is a positive surely? OK, onthe internal walls (without wet plaster) there could be some escape but that is within the thermal envelope of the house so no big deal?
    ferryman35 wrote: »
    the quoted u-value for 150mm full fill well meets the regulations, so if you have a good installation, then you should expect a good result. Anecdotally is harder to quantify.

    Yes, that will meet regulations but will adding the insulated board not improve the U value. As is always said, the regs are a minimum rather than an absolute target.
    ferryman35 wrote: »

    In a new house that I saw, with insulated board on the internal walls and hole in the window vents, the tiniest fire had heated the sitting room so hot and stuffy that we couldn't stay in it. Yet a part of the house that didn't have heating on was freezing - too cold to stand in without your jacket.

    The MHRV should go some way to ensuring the even distribution of the heat. For example we are speccing a vent to be placed in close proximity to the stoves
    ferryman35 wrote: »
    You won't reduce the insulation value of your house but you will make it a whole lot more comfortable......and you don't have he risk of condensation & mould.

    Surely by removing any form of insulation you are reducing the insulation value of your house? I'm sure there's a 'law of diminishing returns' argument but that aside deleting any insulation will reduce the absolute number?

    ferryman35 wrote: »
    There are places where insulated boards are a very good solution but I think there are better options for new builds.

    For clarity, are you saying that taking into account my particular build/spec that I am better off in everyway without the insulated boards... Trust me, I would love that to be right as I could save a nice few quid - but I ain't convinced....yet! :D
    What about downstairs internal walls (or some of them) of blockwork to give you thermal mass and insulate the external walls internally as planned. We went lightweight block on the insulated slab in places - more for sense of solidity.

    What of your floors? Are they concrete and would that not contribute to thermal mass?

    All my walls (on both floors) are blockwork and the floors are concrete too.


  • Registered Users, Registered Users 2 Posts: 9,555 ✭✭✭antiskeptic


    BarryM3 wrote: »
    All my walls (on both floors) are blockwork and the floors are concrete too.

    Would those who champion thermal flywheels consider there to come a point where you simply have too much of it? And therefore consideration need be given to internal surface insulation simply in order to reduce the amount of it? (I have visions of it taking weeks to get the thermal flywheel up to speed - just before you head off to some winter sun :pac:)

    Irrespective of detailing, isn't there going to be loss to foundations via internal block walls (and in the case of upstairs floors also concrete, losses to external walls). Even (time)distribution of heat vs. increased heat loss need also be a consideration.


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    I give up trying to explain the principles here.... you can lead a house to water. ...


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    I understand the principles Syd, ultimately the question I am asking - and no one has really answered yet is this:

    Putting thermal mass argument aside for a moment (as it doesn't suit my lifestyle)-are you saying I would be better off without insulated boards than with them?

    I totally accept the thermal mass principle. My current rent a house has crappy insulation and the coldness coming off the walls is really noticeable.

    There seems to be an undertone here that if you don't agree with it you don't understand it - which I think is unfair at best...

    Being vague and flippant is not big and it's not clever either!


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    Would those who champion thermal flywheels consider there to come a point where you simply have too much of it? And therefore consideration need be given to internal surface insulation simply in order to reduce the amount of it? (I have visions of it taking weeks to get the thermal flywheel up to speed - just before you head off to some winter sun :pac:)

    Irrespective of detailing, isn't there going to be loss to foundations via internal block walls (and in the case of upstairs floors also concrete, losses to external walls). Even (time)distribution of heat vs. increased heat loss need also be a consideration.

    There is specific detailing to stop cold bridging at the points you mentioned.


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    BarryM3 wrote: »
    I understand the principles Syd, ultimately the question I am asking - and no one has really answered yet is this:

    Putting thermal mass argument aside for a moment (as it doesn't suit my lifestyle)-are you saying I would be better off without insulated boards than with them?

    I totally accept the thermal mass principle. My current rent a house has crappy insulation and the coldness coming off the walls is really noticeable.

    There seems to be an undertone here that if you don't agree with it you don't understand it - which I think is unfair at best...

    Being vague and flippant is not big and it's not clever either!

    firstly, ive been anything but vague and flippant in this thread, ive posted measured and lengthy explanations.

    secondly, the reason i said im out is because you seem to be asking the same question over and over expecting someone to give you the answer you want rather than the answer you need.

    my very first line said
    internal dry lining on a new house build is a bad specification.
    and i still stand by that opinion, and other posters here have backed that up.

    im not going to go over the reason its a bad specification again.

    so good luck with the build.


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    With respect Syd, you said that you believe that thermal mass is the way forward, I've said - that aside (due to legitimate lifestyle reasons) why is insulated board bad in itself and you are repeating the same thing.... ie Thermal Mass is better. From what I can see you are saying it's a bad idea for no reason other than you think thermal mass is better, bit of a weak argument to be fair!

    It's like saying a Ferrari is a better car than a Fiesta so no-one should ever buy a Fiesta. Well it depends whether you are going to the shops or to a racetrack.

    Anyway, I'll revert to the spec of the BER assessor I've employed and go back into my box and never question anything/anyone in here again!


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    BarryM3 wrote: »
    With respect Syd, you said that you believe that thermal mass is the way forward, I've said - that aside (due to legitimate lifestyle reasons) why is insulated board bad in itself and you are repeating the same thing.... ie Thermal Mass is better. From what I can see you are saying it's a bad idea for no reason other than you think thermal mass is better, bit of a weak argument to be fair!

    It's like saying a Ferrari is a better car than a Fiesta so no-one should ever buy a Fiesta. Well it depends whether you are going to the shops or to a racetrack.

    Anyway, I'll revert to the spec of the BER assessor I've employed and go back into my box and never question anything/anyone in here again!

    with respect as well barry, in my post here,
    http://www.boards.ie/vbulletin/showpost.php?p=93309790&postcount=10
    where i gave the reasons its bad specification, i included three reasons, not just thermal mass.

    did you just not see these reasons, not understand them or just ignore them?

    so, as you can imagine, im seeing this as you having a myopic view on this and are wanting someone to say go ahead with what you have, and to be fair, antiskeptic is saying as much, although with a very loose grasp of the science in my opinion. Id be of the opposite view, for reasons ive said.


  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    The 3 reasons you said were (paraphrasing)

    Thermal Mass - As we've covered - this does not suit my lifestyle. We are away for long periods and lead a very non timetabled life.

    Air Tightness - to which I replied this without an answer
    Barry wrote:
    In relation to the stop/start of the drylining - I must be missing something. As we will have all external walls wet plastered internally also, then the adding of the insulated drylining - even if done badly - is a positive surely?

    Continuity of insulation - I'm currently researching it and it seems that if detailed correctly and with sufficient ventilation it's not much of an issue

    So, I seen them all, understood them (I think) and also replied to them citing my own situation and wonderings... So of the 3, 1 is simply saying that Thermal Mass is better which isn't an argument against insulated board in itself, 2 is the air tightness element which I don't see can make a difference as I am not doing any less work in achieving this just by adding an insulated board later. I really don't see the correlation here? I will be doing an air tightness test before any boarding goes up - lets say I get a 1 at this point, how can adding the insulated board days/weeks later affect this result? Maybe it can.... I dunno, which is why I asked the question in the first place.

    I most certainly don't have a myopic view on it, I would love to be shown in a clear and concise way why I don't have to spend '000s on the stuff but I haven't seen a sufficient argument put forward yet to help me reach that decision.


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    BarryM3 wrote: »
    ..... I would love to be shown in a clear and concise way why I don't have to spend '000s on the stuff......

    youve some onto a public free website looking for advice as to how to save 000's ?????


    i love your optimism

    anyway... im out.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 230 ✭✭BarryM3


    No, I've paid/am paying a host of professionals and also done my own research of which this is one aspect.

    In any case - as I thought - it appears once again you are unable or unwilling to answer specific questions other than 'thermal mass GOOD, insulated board BAD'.


  • Registered Users, Registered Users 2 Posts: 558 ✭✭✭beyondpassive


    When looking at a modern house its better to think less about the house you live in and more about your going to live in.

    Its not a question of Mass v thermal resistance, you need to have a balance of both. Overheating in summer is where mass can be useful. A two foot stone wall has mass but little thermal capacity, while a double insulated wall has a good u-value but little thermal stability.

    Attached is a photo of my renovation. Note the heat loss at the first floor and where the partitions occur.


  • Registered Users, Registered Users 2 Posts: 404 ✭✭ml100


    ferryman35 wrote: »
    the quoted u-value for 150mm full fill well meets the regulations, so if you have a good installation, then you should expect a good result. Anecdotally is harder to quantify.

    At the end of your project, all the components of your build have to function as a system, and it is how you combine the different elements that will determine your success. Insulation is only part of the equation - you also need to keep airtightness, ventilation and the heating system in mind.

    The best demonstration I saw of thermal mass in action was after the sun had set during the summer evenings....you could feel the heat radiating back from the blocks in the cooler night air. It works....

    In a new house that I saw, with insulated board on the internal walls and hole in the window vents, the tiniest fire had heated the sitting room so hot and stuffy that we couldn't stay in it. Yet a part of the house that didn't have heating on was freezing - too cold to stand in without your jacket.

    You won't reduce the insulation value of your house but you will make it a whole lot more comfortable......and you don't have he risk of condensation & mould.

    And your second question.....yes you can drill deeper holes and fix to the masonry behind, but then if you're fixing something heavy you should be using spacer blocks (don't see those in too many places!?.....you need special fixings for lights, pictures, hanging shelves, more complicated for airtightness, probably wiring if its done right and fitted furniture.

    There are places where insulated boards are a very good solution but I think there are better options for new builds.


    Hi Ferryman35,

    how did the full fill cavity board work out, we are considering it for our new build, my spec will be 100mm external leaf, 150mm cavity with full fill board and 100mm inner leaf block. We will be installing ASHP and MHRV.

    I haven't got any calculations done yet but my architect doesn't think we will need any internal dry lining, I guess I'm wondering if it would be better to add it at this stage as when we were looking at pumping the cavity he was recommending 62.5mm internal dry lining or does it not add that much?


    I've noticed the full fill board being used on a few sites that I've passed in Dublin, it seems to be getting used more now.

    /ml100


  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    dont go near internal dry lining!!!

    if your going for ASHP im assuming UFH as well.... add the MHRV into this and you need decent thermal mass to regulate and maintain temps in the house.

    150 full fill will give you a u value of approx 0.13, thats definitely good enough for modern builds. You might end up having to include a PV cell or two to reach the renewable requirement


  • Registered Users, Registered Users 2 Posts: 404 ✭✭ml100


    thanks syd, yes we are going with UFH (upstairs and downstairs) and 2 stoves downstairs so hopefully that will cover the renewable requirement, if not whats a better option: PV cell or solar panel ? and then there's the windows to research :(


  • Advertisement
  • Subscribers Posts: 42,576 ✭✭✭✭sydthebeat


    ml100 wrote: »
    thanks syd, yes we are going with UFH (upstairs and downstairs) and 2 stoves downstairs so hopefully that will cover the renewable requirement, if not whats a better option: PV cell or solar panel ? and then there's the windows to research :(

    bang for buck its the pv cells


  • Registered Users, Registered Users 2 Posts: 1,336 ✭✭✭tonc76


    I'm about to begin a renovation of a detached rural house built in the 1970s.

    The house is structurally sound but need to be gutted and modernised save for double glazing windows and doors that were installed 6 years ago. At present I need to install ventilation and insulation as none exist and will be installing a new heating system, rewiring etc.

    Can I get opinions on insulation as follows:
    • External
    • Fill cavity and dryline
    • Dryline only with a view to filing cavity next year if needed

    I understand that from a cost point of view the above are €€€, €€ & € in order.

    What are the main advantages of one over the others?

    All opinions appreciated.

    Thanks