Testing and Verification of Electrical Installations

  • 15-10-2014 10:58am
    #1
    Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭


    Following a suggestion by maxamillius this sticky has been created for all posts relating to the testing and verification of electrical installations.

    This is an important topic because only ETCI completion certificates signed by the Holder of a valid Qualified Certifier Number (QC No) are processed for transmission to ESB. To obtain a QC No, Registered Electrical Contractors (RECs) must, successfully complete the City and Guilds Certificate in Electrical Testing and Verification of Electrical Installations 2407.

    Please post relevant information, links and questions relating to this topic here.


«1

Comments

  • Registered Users, Registered Users 2 Posts: 142 ✭✭zombiekiller


    So to do this you must have your own meter, yes


  • Registered Users, Registered Users 2 Posts: 263 ✭✭Par1


    So to do this you must have your own meter, yes

    Not necessarily, you may use a borrowed meter for course


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    prob a stupid question

    but how do the chefs make the lunches while the hotels are being tested?

    are the lunches all cooked before the testing and verification starts?


  • Registered Users, Registered Users 2 Posts: 263 ✭✭Par1


    prob a stupid question

    but how do the chefs make the lunches while the hotels are being tested?

    are the lunches all cooked before the testing and verification starts?

    Testing is refined to purpose built work stations. The hotels wiring installation will therefore be uninterrupted, your lunch should be grand.


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    So as a refresher,,,what are the tests that must be completed in a domestic installation after it has been connected to esb?


  • Advertisement
  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    final circuit maximum fault loop impedance tests

    rcd trip testing


  • Registered Users, Registered Users 2 Posts: 142 ✭✭zombiekiller


    PRE CONNECTION TESTS

    Continuity of electrode and bonding conductors.

    Continuity of all and the max resistance value of protective conductors

    Polarity

    Insulation resistance test

    Erroneous connection test

    POST CONNECTION

    Operation of RCD

    L-E fault loop impedance


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    PRE CONNECTION TESTS

    Continuity of electrode and bonding conductors.

    Continuity of all and the max resistance value of protective conductors

    Polarity


    Insulation resistance test

    Erroneous connection test

    POST CONNECTION

    Operation of RCD

    L-E fault loop impedance

    Don't suppose you fancy explAining how those tests are carried out?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Don't suppose you fancy explAining how those tests are carried out?

    Hi maxamillus, which tests do you want an explanation of?


  • Registered Users, Registered Users 2 Posts: 263 ✭✭Par1


    2011 wrote: »
    Hi maxamillus, which tests do you want an explanation of?

    He probably wants the tests he quoted from zombiekiller explained for him.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 263 ✭✭Par1


    These to be exact

    Originally Posted by zombiekiller View Post
    PRE CONNECTION TESTS

    Continuity of electrode and bonding conductors.

    Continuity of all and the max resistance value of protective conductors

    Polarity


    Insulation resistance test

    Erroneous connection test

    POST CONNECTION

    Operation of RCD

    L-E fault loop impedance


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    Don't suppose you fancy explAining how those tests are carried out?



    http://local.ecollege.ie/Content/APPRENTICE/liu/electrical_notes/LL227.pdf


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9



    Not the most inspiring of documents

    I think they've been copying and posting those same visual checks for 30yrs


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    Not the most inspiring of documents

    I think they've been copying and posting those same visual checks for 30yrs

    I guess that's because the same problems keep occurring?

    Both RECI and ECCSA have published their own guides (not sure if still available though) we used the RECI one during the course in Baldoyle.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Not the most inspiring of documents

    I think they've been copying and posting those same visual checks for 30yrs

    That's nothing, Ohm's Law has remained unchanged for well over 100 years :D:D

    Seriously though, what do you see wrong with thier description of the visual inspection?


  • Registered Users, Registered Users 2 Posts: 142 ✭✭zombiekiller


    The reci book on testing and verification mentioned above is only 15 euro. Explains all the testing procedures gives tables on acceptable an unacceptable values on the different tests. And the the list of visual inspections is the page i had open on the test which helped to get the last one or two visual faults.


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    Can you buy that book online?i remember we had one in phase 2 which was quite good!


  • Registered Users, Registered Users 2 Posts: 142 ✭✭zombiekiller


    You can ring reci and pay over the phone.


  • Banned (with Prison Access) Posts: 873 ✭✭✭Casey78


    Hi
    Sorry if I'm hijacking the thread but would anyone know where I would be able to get periodic inspection stickers to put on a fuse board once I have tested the installation. Something with a tested by/date of test/date of next test due?
    I have found ones used for PAT testing online but nothing for a periodic circuit inspection.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Casey78 wrote: »
    Hi
    Sorry if I'm hijacking the thread but would anyone know where I would be able to get periodic inspection stickers to put on a fuse board once I have tested the installation. Something with a tested by/date of test/date of next test due?
    I have found ones used for PAT testing online but nothing for a periodic circuit inspection.

    I used this company to make up all sorts of stickers for me. Every board I did had a small sticker with my company name & contact details on it. Not an expensive solution, they will make up any sticker you like and it looks professional.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 125 ✭✭sharkbite1983


    PRE CONNECTION TESTS

    Continuity of electrode and bonding conductors.

    Continuity of all and the max resistance value of protective conductors

    Polarity

    Insulation resistance test

    Erroneous connection test

    POST CONNECTION

    Operation of RCD

    L-E fault loop impedance

    Im booked in to the 2 day intensive course for a couple of weeks time, Id be confident Id know how to do any of those tests, except the Erroneous, which Ive never even heard of! Can anyone tell me whats that about?:)

    EDIT: I googled it, its just meggering between phases I think?


  • Registered Users, Registered Users 2 Posts: 263 ✭✭Par1


    Im booked in to the 2 day intensive course for a couple of weeks time, Id be confident Id know how to do any of those tests, except the Erroneous, which Ive never even heard of! Can anyone tell me whats that about?:)

    EDIT: I googled it, its just meggering between phases I think?

    An erroneous connection is a just a physical connection between circuits..easy enough to determine during the testing procedure and becomes apparent if one exists. That will be covered during course don't worry too much about it


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    Hi lads.
    My boss is sending me on the course so I can sign off on certs etc my self after testing installations, im just wondering if there's any good walk through booklets or videos people have or know about too remind my self and get me back familiar with all the different test before I go on the course.im obviously fully qualified lads just looking for some refresher info


  • Registered Users, Registered Users 2 Posts: 1,626 ✭✭✭crasy dash


    Have a look at this http://www.amazon.co.uk/Practical-Inspection-Certification-Electrical-Installations/dp/0080969070/ref=sr_1_1?ie=UTF8&qid=1425216077&sr=8-1&keywords=christopher+kitcher

    I have read it and found it fairly accurate and i came from having no understanding of testing circuits.

    A quick google wil help you find it:)


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    MrMac84 wrote: »
    Hi lads.
    My boss is sending me on the course so I can sign off on certs etc my self after testing installations, im just wondering if there's any good walk through booklets or videos people have or know about too remind my self and get me back familiar with all the different test before I go on the course.im obviously fully qualified lads just looking for some refresher info

    Are there any particular aspects that you are unsure of ?


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    2011 wrote: »
    Are there any particular aspects that you are unsure of ?

    Nothing in particular.. I've carried out all tests previously but it's more too read over/watch too remind my self of procedures, different settings etc


  • Registered Users, Registered Users 2 Posts: 4 Anton Savage


    Hi

    Can someone help me with a regulations question?
    I don't have a regs book handy and would like to know what exactly are the regulations 554.4 and 554.6 in relation to rcd protection on socket circuits. I know they are exemptions to the rule as in these type of circuits don't require rcd protection but I'm just need to know exactly the type of circuits they are and in what type of installation they would be used.
    Thanks.


  • Registered Users, Registered Users 2 Posts: 2 JoJo222


    Hey guys, quick question.. on a periodic inspection report you have to record the max resistance of the protective conductor. That is a pre-connection test and the periodic inspection is on a live board which is in a factory, not to sound like a complete ape but how else would you test this? I've completed the RECI testing course and have tested a good few houses but am in a new job and am not very familiar with periodic inspections. would really appreciate any feedback.


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    JoJo222 wrote: »
    Hey guys, quick question.. on a periodic inspection report you have to record the max resistance of the protective conductor. That is a pre-connection test and the periodic inspection is on a live board which is in a factory, not to sound like a complete ape but how else would you test this? I've completed the RECI testing course and have tested a good few houses but am in a new job and am not very familiar with periodic inspections. would really appreciate any feedback.


    Isn't it just a matter of using a long wander lead? Obviously you need to "null" the meter to compensate for the test leads.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2 JoJo222


    in a factory environment? some of the boards are over 500m from the switch room


  • Registered Users, Registered Users 2 Posts: 470 ✭✭17larsson


    Take a loop reading at the board and subtract that from your loop readings at your outlets


  • Registered Users, Registered Users 2 Posts: 270 ✭✭liveandnetural


    a question aimed at the industrialist among us

    in terms of recording test value reading onto (test record sheets) have any seen any beter system than the standared test record sheet aviable from either of the two saftey bodies
    i have seen some of the larger contractor groups using xl templates to create a simplfied record sheets just woundering has anyone seen or used a software based one or a system for industrial use for recording machine Installation setup and ongoing modifications?

    all inputs welcome


  • Banned (with Prison Access) Posts: 873 ✭✭✭Casey78


    Hi.
    Would anyone have on file an editable copy of a test record sheet for PIRs?
    I've been trying to make one up on MS WORD but just can't get it right..

    I have recently got a contract Periodic Testing for a business chain so rather than filling them out by hand as I was doing I wanted to fill them out on the laptop as I test.
    I don't want to be scanning them onto the PC either.
    As I said I have tried unsuccessfully to throw something together on word.
    I'm just not that good with it.
    Any help would be great thanks.


  • Registered Users, Registered Users 2 Posts: 710 ✭✭✭Hoagy


    Casey78 wrote: »
    Hi.
    Would anyone have on file an editable copy of a test record sheet for PIRs?
    I've been trying to make one up on MS WORD but just can't get it right..

    I have recently got a contract Periodic Testing for a business chain so rather than filling them out by hand as I was doing I wanted to fill them out on the laptop as I test.
    I don't want to be scanning them onto the PC either.
    As I said I have tried unsuccessfully to throw something together on word.
    I'm just not that good with it.
    Any help would be great thanks.

    Try Excel, it's much more suitable for test records.


  • Registered Users, Registered Users 2 Posts: 1,626 ✭✭✭crasy dash


    Just curious lads what testers are electricians using for testing these days.

    Have a friend who is after getting a job installing pre pay meters.

    Part of the contract he got, is he has to have his own test gear.

    I have used robin kewtech personally.

    I'm sure megger fluke etc have multifunction meters.

    Let me know what meter you use and any faults you have with them.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 62 ✭✭Gashmuncher


    Just to stir this one up again, it is my opinion that the vast majority of electricians, even those who are deemed to be QCs (Qualified Certifiers) simply do not know how to correctly test an electrical installation as per part 6 of the wiring rules. Most electricians do not even understand what the objectives of each of the required test are. It is critical that electricians actually understand the fault they are looking, and in my opinion most don't. Attempting to test an installation by following a series of steps which are listed in a book is a recipe for disaster. What is required is an understanding of what can go wrong and an understanding of what each test is actually telling you. The tests are designed to highlight the normal mistakes which electricians can and do make which are easily overlooked and can leave an installation in a dangerous condition.

    See below for overview of the required tests and the actual fault you are looking for.
    Test 1,2,3,&4 are pre connection tests and are done with the installation dead. Gets 5&6 are post connection tests and can only be done after power is switched on.

    TEST 1
    Continuity of protective and bonding conductors.
    This test is simply to confirm that all earth conductors are "electrically sound and correctly connected" This is done by simply measuring the resistance of the earth cables. A low reading (generally less than .5 ohm,) indicates a good earth. There are a number of ways to do this test but the simplest is a wander lead. The test needs to be done with a proper "low ohm meter" which can accurately measure very low values of resistance. A multimeter will not measure low ohm values (less than10 ohms) accurately. The thing to note here is that unlike a disconnection of the live or neutral, the circuit will work normally if no protective conductor is present. If the earth is inadvertently left disconnected everything will seem to be normal but in the event of an earth fault there are no protective measures in place.

    TEST 2
    Continuity of ring main circuits. Another simple low ohms test test to confirm that both legs of live ,neutral and earth are correct in a ring main circuit. Again note that if an open ring on any conductor exists this is not easily detected as the circuit will appear to work normally. At the same time, particularly if the ring is protected by a 32amp MCB a very dangerous situation can arise if the ring is open. The test is simple. Measure the resistance between the two lives , neutrals and earths. Rembering that 100 meters of 2.5 cable measures 0.7 ohms it is fairly obvious that we will normally expect to get reading less than an ohm and and as all conductors are the same length and the same cable size the lives and neutrals should match. In the case of twin and earth cable the earth is a smaller cable and therefore should have a higher resistance.

    TEST 3
    Insulation Resistance, this test seems to be little understood by most electricians. The whole point of the test is to ensure that all live and neutral conductors are separated electrically from the earth conductors by a minimum of 1 mega ohm. Unlike the first two tests we are looking for a very high reading. It is important to understand that 1 mega ohm is a high reading. Most electricians do not seem to know that 1 mega ohm is one million ohms. (1,000,000) 1 million of anything is a lot, and 1 mega ohm is a lot of resistance. Readings in the order of 10 mega ohms ar perfectly acceptable and normal. It is a requirement that the test is carried out at 500 volts. The simple way to ensure that this voltage does not damage any electronic equipment is to short the live and neutral conductors together and the test between the shorted live and neutral to earth. This ensures that there is no actual voltage across the live and neutral and therefore no potential to damage equipment. Any reading over 1 mega ohm is a pass. It is impossible to obtain readings of greater than 200 or greater than 500 or greater than 999 mega ohm all the time. The most common insulation resistance fault found is a short between neutral and earth.

    TEST 4
    Erroneous connections between circuits. This simple test is to ensure that the lives from different circuits are not inadvertently connected together. Erroneous means in "error" . The test is to ensure that circuits are not connected together in error. Again the problem with this fault is that everything will work and seen to be normal. But it is possible that two separate MCBs can be feeding the same circuit. The test is in effect a continuity test to ensure that with all other MCBs on, each circuit disconnects from the live.

    TEST 5
    Live to earth loop impedance.

    TEST 6
    RCD trip times


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Just to stir this one up again, it is my opinion that the vast majority of electricians, even those who are deemed to be QCs (Qualified Certifiers) simply do not know how to correctly test an electrical installation as per part 6 of the wiring rules.

    I agree, that is why I started this sticky.
    It is critical that electricians actually understand the fault they are looking, and in my opinion most don't.

    Many electricians can never carry out any testing, nor are they expected to. Large electrical contractors will have a dedicated testing team. This is a shame, because knowing how to test is another string to your bow and makes you far more employable.
    TEST 1
    Continuity of protective and bonding conductors.
    This test is simply to confirm that all earth conductors are "electrically sound and correctly connected" This is done by simply measuring the resistance of the earth cables.

    I generally split this test into two as they have different aims:

    1) Bonding conductors:

    This is a case of measuring the resistance between extraneous conductive parts that are simultaneously accessible. For example measuring the resistance between the outer casing of a motor and a pipe that is close to the motor. If the resistance is low then in the event that the casing becoming live the potential difference between it and the pipework (or touch voltage) will be minimal. A wander lead is generally not required for this as conductive parts are generally close enough ti each other for the test instrument leads to reach.This is not always achieved by using cables. For example when wiring a milking parlour in the distance past I had all of the feeding troughs for the cattle welded together so that the became one unit. This ensured that they were all at a common potential. I know that cables linking the troughs were unlikely to last in this environment.

    2) Continuity of protective conductor:
    A low reading (generally less than .5 ohm,) indicates a good earth.

    This applies to the CPC (Circuit Protective Conductor). "A good earth" is not the aim of "equipotential bonding" although it is generally a consequence of it. The aim of equipotential bonding is to keep simultaneously conductive parts at the same potential by connecting them to each other, whereas the aim of the CPC is to ensure that in the event of an earth fault the disconnection times for the associated protective device(s) are met by providing a low resistance path to earth. Remember a low resistance to earth permits a large earth fault current to flow which means that the protective device to operates quicker.

    TEST 2
    Continuity of ring main circuits. Another simple low ohms test test to confirm that both legs of live ,neutral and earth are correct in a ring main circuit. Again note that if an open ring on any conductor exists this is not easily detected as the circuit will appear to work normally. At the same time, particularly if the ring is protected by a 32amp MCB a very dangerous situation can arise if the ring is open. The test is simple. Measure the resistance between the two lives , neutrals and earths.

    ... so generally the tester will disconnect the lives and the neutrals at the distribution board to carry out this test.

    TEST 3
    Insulation Resistance, this test seems to be little understood by most electricians. The whole point of the test is to ensure that all live and neutral conductors are separated electrically from the earth conductors by a minimum of 1 mega ohm.

    ...and to ensure the integrity of resistance between phase and earth and phase and neutral. Additionally in three phase installations the the resistance between phases is very important :)
    Unlike the first two tests we are looking for a very high reading. It is important to understand that 1 mega ohm is a high reading. Most electricians do not seem to know that 1 mega ohm is one million ohms. (1,000,000) 1 million of anything is a lot, and 1 mega ohm is a lot of resistance.

    In industrial installations we generally test at 1kVDC and would not be satisfied with a 1 MΩ result. Insulation resistance testing is not carried out this way in ATEX areas as the risk of a spark is considered more of a hazard that an issue with the insulation resistance. Instead a suitable multimeter is used.
    TEST 4
    Erroneous connections between circuits.

    I find that there errors as well as most others are generally found during the "visual inspection" which is why I think it is the single most important test. During this part of the test most issues (such as reverse polarity, damaged conductors / apparatus, poor installation) are detected.

    TEST 5
    Live to earth loop impedance.

    Refer to table A61C in ET101:2008 (for max. disconnection times 0.4 s)
    TEST 6
    RCD trip times

    See Annex 61G in ET101:2008


  • Registered Users, Registered Users 2 Posts: 62 ✭✭Gashmuncher


    Fully agree with all above. The actual Insulation Resistence (IR) limit required in the rules for explosive atmospheres is 10meg ohm and Normal installations is 1 meg ohm. While I agree that it is normal to look for values in excess of these limits it is also important to understand that an IR reading over the mimium required, fully complies with part 613.3 of ET 101 the wiring rules. I came across an situation where an electrician replaced 200 meters of 5 by 50 Square cable because the mimium IR was 375 meg ohm.


  • Registered Users, Registered Users 2 Posts: 3 Tdude


    Hi,I'm just wondering how to test for max earth fault loop impedance at a light when there is no Earth at the fitting?Thanks for any feedback!


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    Why is there no Earth at the fitting?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    If there is no cpc then there obviously is no earth fault loop and therefore the impedance of same cannot be tested.


  • Registered Users, Registered Users 2 Posts: 3 Tdude


    Why is there no Earth at the fitting?

    It's an old property


  • Registered Users, Registered Users 2 Posts: 3 Tdude


    Risteard81 wrote: »
    If there is no cpc then there obviously is no earth fault loop and therefore the impedance of same cannot be tested.
    Thanks for reply,so for the test record sheet results is it n/a?fittings are class II so they don't require a new Earth to be pulled in


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Tdude wrote: »
    Thanks for reply,so for the test record sheet results is it n/a?fittings are class II so they don't require a new Earth to be pulled in

    There should be an earth available even if it is not required for that particular light so that it can be connected should the light be changed for a different type in the future.

    I would not write "N/A" as this suggests that an earth is not required when the regulations state otherwise.


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    Aren't you, in instances such as this, supposed to highlight that the installation does not meet current guidelines on the report?


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    I'm not sure whether we are discussing a PIR here or otherwise.
    If it is a PIR (Periodic Inspection Report) then I would record "N/A" but I would also be making a coded observation relating to the lack of the cpc at each point in the wiring. If it is installation work then you need to ensure that the existing installation is adequate to support your additions/alterations.


  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    I don't mean to sound like a smart arse but if you have to ask that question you obviously don't have a full understanding of what you're doing. It might be no harm to get someone to go through testing with you.


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    report noted, i dont see any indication that the op can't test, they just want to know what to write into the cert in this instance, I dont see why the op cant ask this question here


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    I think that electricians should always be encouraged to ask questions rather than pretend to have all of the answers. There is far to much of this going on in my opinion.


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    2011 wrote: »
    I think that electricians should always be encouraged to ask questions rather than pretend to have all of the answers. There is far to much of this going on in my opinion.

    I did my senior trades in 1989, with just the odd few courses since then. I sometimes wonder what I've forgotten, always interesting to see questions here and rediscover lost knowledge that I hadn't had cause to use since my apprenticeship or even learn something new.

    I'd have very little tolerance for an electrician not knowing the basics but not all questions are straight forward and many of us occasionally find ourselves suddenly faced with a situation we barely covered in a theory class many years previously.

    The electrical trade is extremely varied with some doing just house wiring and others working on complex industrial equipment, but due to jobs changing we often have to move into areas where there may be some holes in our knowledge. (During interviews is usually when I find dusty brain cells struggling to remember which formula applies etc.)

    Would anyone else be interested in a thread where we challenge each other to answer questions on obscure and maybe some less obscure areas of our trade?