Fault code 40/41 on gas boiler

  • 10-02-2014 10:37am
    #1
    Closed Accounts Posts: 1,576 ✭✭✭


    Does anyone know what these fault codes mean???the boiler is a VOKERA MYNUTE HE,this is the second failure in 4 months,the last failure was the thermister which was replaced and worked fine until this morning when the boiler started flashing the codes 40 & 41

    Thanks in advance


Comments

  • Registered Users, Registered Users 2 Posts: 12,089 ✭✭✭✭P. Breathnach




  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11



    Thanks for that,will read the manual once i get home,is it a big/small job???


  • Registered Users, Registered Users 2 Posts: 12,089 ✭✭✭✭P. Breathnach


    I'm no expert. It's a doddle on my system, but obviously I know nothing about your installation.

    Don't trick around with gas boilers unless you know what you are doing.


  • Registered Users, Registered Users 2 Posts: 157 ✭✭seamusmacc


    maybe this should move to Home > Rec > Home & Garden > Plumbing & Heating


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    I'm no expert. It's a doddle on my system, but obviously I know nothing about your installation.

    Don't trick around with gas boilers unless you know what you are doing.
    i wouldn't dare touch it,havent a clue about them,made one or 2 calls (not experts) and they said that from previous experience of this problem the quickest fix is a new boiler,whether true or not I don't know,but I was told it wont be cheap :mad:


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 312 ✭✭Gasherbraun


    V.W.L 11 wrote: »
    i wouldn't dare touch it,havent a clue about them,made one or 2 calls (not experts) and they said that from previous experience of this problem the quickest fix is a new boiler,whether true or not I don't know,but I was told it wont be cheap :mad:

    Low water pressure is normally rectified by simply letting more water into the system to increase pressure. There is normally a valve located close to the boiler with a pressure gauge but do not do this if you are not 100% confident that you have the right gauge.

    As for needing a new boiler I guess anything is possible depending on the age of the boiler and what is causing the pressure drop (in my experience - I am not an RGI - most boilers lose pressure over time through small leaks, evaporation etc) but I have never seen a boiler changed due to low pressure.


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    Low water pressure is normally rectified by simply letting more water into the system to increase pressure. There is normally a valve located close to the boiler with a pressure gauge but do not do this if you are not 100% confident that you have the right gauge.

    As for needing a new boiler I guess anything is possible depending on the age of the boiler and what is causing the pressure drop (in my experience - I am not an RGI - most boilers lose pressure over time through small leaks, evaporation etc) but I have never seen a boiler changed due to low pressure.
    there is 0bar on the pressure gauge,it usually reads between 0.5 & 1.0 (I think)but I wont go near it at all,no visible leaks on it,its about 6 years old now,but was not used for about 3 of that,the house was vacant,now in recent months it has given trouble twice,would it be connected to the thermistor or have anything to do with that?the pressure pressure pump that is?because they said the rest of it looked ok when they fixed it just before christmas


  • Registered Users, Registered Users 2 Posts: 8,869 ✭✭✭Ray Palmer


    V.W.L 11 wrote: »
    there is 0bar on the pressure gauge,it usually reads between 0.5 & 1.0 (I think)but I wont go near it at all,no visible leaks on it,its about 6 years old now,but was not used for about 3 of that,the house was vacant,now in recent months it has given trouble twice,would it be connected to the thermistor or have anything to do with that?the pressure pressure pump that is?because they said the rest of it looked ok when they fixed it just before christmas

    A minor leak can reduce the pressure over time. Effectively a central heating system is one big loop. In order to get the heated water around it you need it to be a certain pressure for the system to work. A little leak can cause this to drop. The problem is finding a leak that is small.

    Before you go searching for a leak get them to put in the standard central heating sealant. I probably spent a grand trying to find a leak and that solved my problem and took 10 minutes

    In saying that you can probably find your top up valve and top up the system. Check for what pressure it should be at normally 1.5-2. Keep an eye on it over the week if the pressure is dropping check you rads for any leaks, tighten if needed. If still losing pressure do the sealant. Valve is probably beside your hot water tank not your boiler from my experience.


  • Registered Users, Registered Users 2 Posts: 12,089 ✭✭✭✭P. Breathnach


    Boilers vary in their specifications, so it's worth reading the manual. That should tell you what the correct pressure range is. Normally adding some water to bring the pressure up is user maintenance, and does not require a specialist (subject to Gasherbraun's words of caution).


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    Boilers vary in their specifications, so it's worth reading the manual. That should tell you what the correct pressure range is. Normally adding some water to bring the pressure up is user maintenance, and does not require a specialist (subject to Gasherbraun's words of caution).
    I can get the cover off the boiler and inside it is a small water tank,what i do or how i do it from there though is the mystery,it was fine yesterday when it was on but half way through the timer it cut out and hasnt worked since


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 5,775 ✭✭✭jd


    V.W.L 11 wrote: »
    I can get the cover off the boiler and inside it is a small water tank,what i do or how i do it from there though is the mystery,it was fine yesterday when it was on but half way through the timer it cut out and hasnt worked since

    You should not need to take covers off boilers etc.
    For instance, my valve is beside the water tank, nowhere near the boiler. Twisting it (anticlockwise in my case) will increase the pressure in the system

    293204.jpg


  • Registered Users, Registered Users 2 Posts: 18,982 ✭✭✭✭murphaph


    If your (sealed) system is losing pressure even after topping up then there are 2 causes: a straightforward leak somewhere or the expansion vessel has lost gas pressure. I would do as ray says and use a common sealing agent first (if you can't see any signs of limescale which would indicate a leak) and if that doesn't do the trick then the following is quite likely the cause:

    The expansion vessel has 2 chambers separated by a rubber membrane. One chamber contains a gas (usually carbon dioxide) at higher pressure than the hot water circuit and the other contains water in the hot water circuit at system pressure. The expansion vessel slowly leaks carbon dioxide over the years and eventually cannot exert enough pressure on the membrane to maintain the correct water system pressure. You can drain the system and check the gas pressure in the expansion vessel with a car tyre manometer and if it's low, the gas can be topped up with regular air using a pump with a gauge on it. If the membrane itself is knackered then opening the valve to release carbon dioxide will also release water. If that happens the expansion vessel needs replacing.

    I had this fault myself recently and from my bit of research that I did in older boilers the expansion vessel is often (like 80% of the time) the cause of such a problem,

    HOWEVER: I feel confident working on such things and working on the water circuit is allowed in Germany (not the gas part though!) by laymen but if you are not 100% confident that you can handle such a thing then it should be entrusted to a professional!


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    It is now showing codes 48/49/50/51/52 what do they mean???i have the heating on at present but there is zero pressure on the pressure bar


  • Registered Users, Registered Users 2 Posts: 5,775 ✭✭✭jd


    http://cdn0.vokera.co.uk/wp-content/uploads/2009/04/mynute-he-user-manual.pdf
    AL52 Call engineer

    did you try and increase the pressure in the system? Not sure it's the best idea to have heating on with zero pressure.


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    Is this the valve


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    jd wrote: »
    http://cdn0.vokera.co.uk/wp-content/uploads/2009/04/mynute-he-user-manual.pdf
    AL52 Call engineer

    did you try and increase the pressure in the system? Not sure it's the best idea to have heating on with zero pressure.
    I switched it off after a few minutes,not willing to risk it


  • Registered Users, Registered Users 2 Posts: 12,089 ✭✭✭✭P. Breathnach


    OP, you're making me nervous! I have the impression that you don't know enough about your boiler, and that you should not try to do anything with it unsupervised.

    A few things can be done by the user, like bringing the water pressure up. But it looks to me as if you don't really understand your system. If you have a neighbour/friend/family member with a similar gas-fired system, you might be able to have somebody explain to you what is what.

    Cut off the electical feed to the boiler (there should be a switch somewhere near the boiler) and after a few seconds, turn it back on. See if there are any error codes. If you are back to the original code, then it is a water pressure problem, and that should be an easy fix: open the tap and watch the pressure gauge until working pressure is reached, then close the tap.

    Any other code, and I suggest that you call in a registered gas engineer.

    RTFM!


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    OP, you're making me nervous! I have the impression that you don't know enough about your boiler, and that you should not try to do anything with it unsupervised.

    A few things can be done by the user, like bringing the water pressure up. But it looks to me as if you don't really understand your system. If you have a neighbour/friend/family member with a similar gas-fired system, you might be able to have somebody explain to you what is what.

    Cut off the electical feed to the boiler (there should be a switch somewhere near the boiler) and after a few seconds, turn it back on. See if there are any error codes. If you are back to the original code, then it is a water pressure problem, and that should be an easy fix: open the tap and watch the pressure gauge until working pressure is reached, then close the tap.

    Any other code, and I suggest that you call in a registered gas engineer.

    RTFM!

    I havent a clue sure i admitted that,go back 2/3 posts and you'll see i put up a picture is that the valve???there's nothing else on it other than that,everything else is located internally in the boiler,its a council property and they wont come out and f**king fix it


  • Registered Users, Registered Users 2 Posts: 5,775 ✭✭✭jd


    Did the council give you a file of manuals for the appliances etc in the house.
    Try turning the valve for 5 seconds (DON'T FORCE IT) and see if the pressure increases.


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    jd wrote: »
    Did the council give you a file of manuals for the appliances etc in the house.
    Try turning the valve for 5 seconds (DON'T FORCE IT) and see if the pressure increases.

    All they gave me day 1 was a set of keys,no files for the appliances,will try that and let you know,did you look at the photo of the valve i posted?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,089 ✭✭✭✭P. Breathnach


    V.W.L 11 wrote: »
    I havent a clue sure i admitted that,go back 2/3 posts and you'll see i put up a picture is that the valve???there's nothing else on it other than that,everything else is located internally in the boiler,its a council property and they wont come out and f**king fix it
    I saw the picture, but there wasn't enough information in it for me to be sure. Yes, it looks like the valve - that's as far as I can go. The problem I have with saying yes or no is that I can't judge the scale. There should also be a gas feed pipe with a valve. The gas feed is a much thinner pipe.

    If you're sure it's a water pipe, go for it.


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    I saw the picture, but there wasn't enough information in it for me to be sure. Yes, it looks like the valve - that's as far as I can go. The problem I have with saying yes or no is that I can't judge the scale. There should also be a gas feed pipe with a valve. The gas feed is a much thinner pipe.

    If you're sure it's a water pipe, go for it.

    That valve is located underneath the boiler and is connected to a gold coloured metal pipe,not like a thin looking pipe as posted by a previous poster,i aint confident at all about whether it is or not tbh,i havent gone near it since last night and dont fancy it until i can ascertain whether or not thats the valve


  • Registered Users, Registered Users 2 Posts: 12,089 ✭✭✭✭P. Breathnach


    I'm glad you are being cautious.

    The gas control valve should be open for the boiler to work. The water feed valve should be closed except when water is being let in to bring the system pressure up. Turn the tap while keeping an eye on the pressure gauge; if nothing seems to happen, you might have turned off the gas feed. You can turn it back on, and look around for another valve.


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    I'm glad you are being cautious.

    The gas control valve should be open for the boiler to work. The water feed valve should be closed except when water is being let in to bring the system pressure up. Turn the tap while keeping an eye on the pressure gauge; if nothing seems to happen, you might have turned off the gas feed. You can turn it back on, and look around for another valve.

    Is the water feed valve definately located on the outside of the boiler???


  • Registered Users, Registered Users 2 Posts: 12,089 ✭✭✭✭P. Breathnach


    V.W.L 11 wrote: »
    Is the water feed valve definately located on the outside of the boiler???
    I'd expect it to be.


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    I'd expect it to be.

    I'll upload a full photo of the boiler soon and you can see for yourself the layout of it.


  • Registered Users, Registered Users 2 Posts: 71 ✭✭jjdub1


    @VWL11 the picture you posted is NOT the valve others are talking about... It looks EXACTLY like the picture jd posted (between the copper pipe and the silver flexible hose).

    It won't be on,at or near the body of the boiler, It will be at your water tank. You should have a pressure gauge near your tank also, this correlates to the guage on your boiler, the valve will be beside or near it.
    You turn this for 10-15 seconds and you will see the pressure rise on the gauge (1.5 - 2.0 is normal).

    If you live in an apartment check behind the door of the 'hotpress' there should be a diagram of all the valves and their purpose.
    It's fairly common that to have to 'top-up the pressure' at this valve from time to time (a dripping toilet bowl or a leak in a radiator will cause the pressure to drop) so finding out what to do now will save you hassle in the future.


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    This is the actual boiler


  • Registered Users, Registered Users 2 Posts: 71 ✭✭jjdub1


    DO NOT touch the boiler ...


  • Advertisement
  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    This is whats below the boiler


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    Pressure gauge


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    jjdub1 wrote: »
    DO NOT touch the boiler ...

    I found it


  • Registered Users, Registered Users 2 Posts: 12,089 ✭✭✭✭P. Breathnach


    The yellow valve is the gas connection.

    When fitted properly, the valve is open when the handle is parallel to the pipe, and it looks as if that is the case here.


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    jjdub1 wrote: »
    DO NOT touch the boiler ...

    I wouldnt dream of it


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    The yellow valve is the gas connection.

    When fitted properly, the valve is open when the handle is parallel to the pipe, and it looks as if that is the case here.

    Pressure valve is in the hot press see pic above your last post


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,089 ✭✭✭✭P. Breathnach


    V.W.L 11 wrote: »
    I found it
    Now pressurise the system! I'd go with the 1.5 to 2 bar idea, even though the gauge on the boiler suggests that up to 3 bar is okay.


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    Now pressurise the system! I'd go with the 1.5 to 2 bar idea, even though the gauge on the boiler suggests that up to 3 bar is okay.

    Its at 1 bar now and is working fine now,thanks to all who advised i really appreciate it


  • Registered Users, Registered Users 2 Posts: 71 ✭✭jjdub1


    Phew !!!! :)


  • Registered Users, Registered Users 2 Posts: 78,647 ✭✭✭✭Victor


    Moved from Accommodation & Property

    Moderator


  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    Now pressurise the system! I'd go with the 1.5 to 2 bar idea, even though the gauge on the boiler suggests that up to 3 bar is okay.

    Up to 3 bar is not "ok" 3bar is the safety valves lifting point , 1 bar cold is sufficient , low water pressure switch comes into play below 0.5 .


  • Advertisement
  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    Egass13 wrote: »
    Up to 3 bar is not "ok" 3bar is the safety valves lifting point , 1 bar cold is sufficient , low water pressure switch comes into play below 0.5 .
    the highest it has hit is 1.5 bar


  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    V.W.L 11 wrote: »
    the highest it has hit is 1.5 bar

    Well that's normal , if you have it at 1 cold and it's going up as far as 3 during operation then there is a problem with the expansion vessel. Between 1 and 2 during operation is correct


  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    V.W.L 11 wrote: »
    the highest it has hit is 1.5 bar

    Well that's normal , if you have it at 1 cold and it's going up as far as 3 during operation then there is a problem with the expansion vessel. Between 1 and 2 during operation is correct


  • Closed Accounts Posts: 1,576 ✭✭✭V.W.L 11


    Egass13 wrote: »
    Well that's normal , if you have it at 1 cold and it's going up as far as 3 during operation then there is a problem with the expansion vessel. Between 1 and 2 during operation is correct

    Cheers for that,hopefully it doesn't break down due to pressure problems anymore though