Air in Rads

Options
  • 01-03-2013 10:30am
    #1
    Registered Users Posts: 429 ✭✭


    Hi All,
    Firstly my system looks like:
    9 rads upstairs, 9 downstairs. Large new 300L cylinder, large and small tank in the attic. 4.5 bar pump to 1 tap and 2 showers. Stove with circulating pump for rads and water.

    Few weeks ago the oil boiler would not fire unless I reset the limit switch on the thermostat on the boiler. Then it would fire OK.

    I asked the plumber to do 3 things, 1 fit a valve on boiler so I could drain the system without flooding the place, 2, replace the ballcock in the big tank as it was allowing water overflow, 3, fit an auto bleeder to one rad upstairs as I had to regularly bleed it. this was in advance of asking the sparky to replace what could have been a faulty thermostat. Plumber duely did all requested.

    Today I have to bleed 4/6 of the rads upstairs that I never had to bleed before. I do this every 3-4 nights. Oil boiler is now working fine and fires every time.
    Plumber is puzzled. No obvious leak. Lot of gurgling/fizzing in the rad with the auto bleed.

    I was up checking the levels in the big tank and set it to higher that the plumber had after replacing the ball cock, I noticed when using the pump (we have one tap and 2 showers on a 4.5 bar pump) that the overflow pipe kind of spat up a drop. Further there is a little black cap on a valve on the cylinder which when opened vented some air the other night

    Any ideas to find the root cause of all this air?

    Thanks,
    Paul


«1

Comments

  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    any signs of pitching?

    or if you tie up the ballcock in the morning. has it dropped anything in a few hours?


  • Registered Users Posts: 429 ✭✭Blowheads


    Hi,
    I didnt try that yet. Was a next step, but was half expecting to see water leak somewhere showing at this stage (ceiling or other) but since we are there now 3 years I didnt see anything I kinda ruled that out.

    Could you elaborate further on "pitching". I get the basics, but what is causing it and how could it be stopped? The 4.5 bar pump is beside the cylinder on the grounf, the big take is directly above the cylinder and the small tank is above that again


  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    when the stove or heating is on you get water coming out the vent over the small tank.

    as for leaks some you will never see as they will just drain away


  • Registered Users Posts: 429 ✭✭Blowheads


    OK, any ideas how to fix this issue, based in Galway. Cant be bleeding the bleeding rads day and night ;-)


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    OK, any ideas how to fix this issue, based in Galway. Cant be bleeding the bleeding rads day and night ;-)
    Auto air vents can also suck air into a system. I'd never leave one open. They can suck air in and almost guaranteed to leak at some stage


  • Advertisement
  • Registered Users Posts: 2,409 ✭✭✭sullzz


    OK, any ideas how to fix this issue, based in Galway. Cant be bleeding the bleeding rads day and night ;-)

    No ideas on how to fix it until you do what CORKGSXR said first , then report back with your findings.


  • Registered Users Posts: 2,409 ✭✭✭sullzz


    Dtp79 wrote: »
    Auto air vents can also suck air into a system. I'd never leave one open. They can suck air in and almost guaranteed to leak at some stage

    They only suck in air if you have water getting out , they are designed to be left open , if you leave them closed it would be cheaper to use a blank cap instead of fitting one at all , they leak as you are using cheap ones , use better quality ones or else use a penny valve before it so you don't have to drain down when replacing them , some people might even call it a maintenance valve:o


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    sullzz wrote: »

    They only suck in air if you have water getting out , they are designed to be left open , if you leave them closed it would be cheaper to use a blank cap instead of fitting one at all , they leak as you are using cheap ones , use better quality ones or else use a penny valve before it so you don't have to drain down when replacing them , some people might even call it a maintenance valve:o
    I don't use em at all sullz. I've seen good ones leak too


  • Registered Users Posts: 2,409 ✭✭✭sullzz


    Dtp79 wrote: »
    I don't use em at all sullz. I've seen good ones leak too

    What about on the flow to cylinder coil , or on high points of heating circuits


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    sullzz wrote: »

    What about on the flow to cylinder coil , or on high points of heating circuits
    Always manual vents. Usually 12 inches of 3/4 copper out of the tee and manual vent into that. The 12 inches of copper will accumulate any air trapped. Never had any problems so far. Once the air is out of the system it stays out


  • Advertisement
  • Registered Users Posts: 2,409 ✭✭✭sullzz


    Dtp79 wrote: »
    Always manual vents. Usually 12 inches of 3/4 copper out of the tee and manual vent into that. The 12 inches of copper will accumulate any air trapped. Never had any problems so far. Once the air is out of the system it stays out
    Nah you need auto vents , why do you think they are in system boilers


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp79 wrote: »
    Always manual vents. Usually 12 inches of 3/4 copper out of the tee and manual vent into that. The 12 inches of copper will accumulate any air trapped. Never had any problems so far. Once the air is out of the system it stays out
    What do you use on open vented gas boilers or on oil boilers?


  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    The flamco aav's don't leak.

    The also come with a valve to close when you take it off in future.

    About double the price


  • Registered Users Posts: 2,409 ✭✭✭sullzz


    Yeah I tend to use the flamco flexvent ones , never once had an issue with them


  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    Aib bank in blackpool has 4 flamcos in the ceiling over the main foyer. Not a hope of getting at them without ripping down the ceiling.

    Theres trust for ya


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    corkgsxr wrote: »
    The also come with a valve to close when you take it off in future.
    Do they? I didn't know that.
    Mine just come in a red & white narrow box but no valve!


  • Registered Users Posts: 2,409 ✭✭✭sullzz


    shane0007 wrote: »
    Do they? I didn't know that.
    Mine just come in a red & white narrow box but no valve!

    Mine dont come with a valve either , I presumed he was talking about a different one from flamco .


  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    shane0007 wrote: »
    Do they? I didn't know that.
    Mine just come in a red & white narrow box but no valve!

    Maybe bad description. If you unscrew the body from the hex bolt it has a rubber spring valve that closes as you split it


  • Registered Users Posts: 2,409 ✭✭✭sullzz


    :eek: I'd be waaaay to afraid to try that , ill take your word for it;)


  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    sullzz wrote: »
    :eek: I'd be waaaay to afraid to try that , ill take your word for it;)

    No they work really well feck all comes out. Its abit redundant. You only need it if they give trouble. But they don't.

    Its like the lifetime warranty with oil tanks. They only fail if you're base is wrong. He must do nothing


  • Advertisement
  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    shane0007 wrote: »
    What do you use on open vented gas boilers or on oil boilers?
    Just manual vents. Once the air is out its out. I only find auto air vents " handy " when filling a system on your own and dont Have to stand over it on the initial fill. Once the system is bled there should be no issue and there never is


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    corkgsxr wrote: »
    Maybe bad description. If you unscrew the body from the hex bolt it has a rubber spring valve that closes as you split it
    Thanks. I did not know that either. Good to know. I only had 2 faulty ones but they were not leaking, they just would not let air out!


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp79 wrote: »
    Just manual vents. Once the air is out its out. I only find auto air vents " handy " when filling a system on your own and dont Have to stand over it on the initial fill. Once the system is bled there should be no issue and there never is
    If you are installing manual air vents on boilers then you should inform your customers that they may not have any manufacturer's warranty. This is a condition of warranty that an AAV is installed on the boiler. What happens if a pump gland weeps beside the boiler? There are many many reasons why air will get into a boiler & if you are not there to remove it every time, then the air pocket will cause extremely high temperatures within the boiler & could result in a warped boiler. This is also why the AAV cap should not be tightened.


  • Registered Users Posts: 429 ✭✭Blowheads


    Ok, have tired up the ball cock in small tank so let's see. However also a test, whenever the tap runs from the pump then it is pitching back a small bit back into the main tank after turning the tap off


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    shane0007 wrote: »
    If you are installing manual air vents on boilers then you should inform your customers that they may not have any manufacturer's warranty. This is a condition of warranty that an AAV is installed on the boiler. What happens if a pump gland weeps beside the boiler? There are many many reasons why air will get into a boiler & if you are not there to remove it every time, then the air pocket will cause extremely high temperatures within the boiler & could result in a warped boiler. This is also why the AAV cap should not be tightened.
    To be honest I've never fit an open vented gas boiler. If there's an aav with the boiler then yes I'd leave that one open. As for oil, I've seen endless aav s leaking, usually down onto the burner in outdoor modules. Probably leaking months if not years


  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    the glowworm aavs are a fecker for leaking


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    corkgsxr wrote: »
    the glowworm aavs are a fecker for leaking
    Not the only ones!


  • Registered Users Posts: 429 ✭✭Blowheads


    Ok, sorry to come back to the original thread topic, but, after day 1, there is no sign of pitching into the small tank nor has te water level dropped. Slight water came out of the valve on cylinder but only a few dropps.. only oil on,no stove yest. next steps??


  • Moderators, Motoring & Transport Moderators Posts: 6,521 Mod ✭✭✭✭Irish Steve


    Are you still having problems with air getting into the upstairs radiators?

    Shore, if it was easy, everybody would be doin it.😁



  • Advertisement
  • Registered Users Posts: 429 ✭✭Blowheads


    Yep, thats the crux of the problem