    Hi everyone,

    I have a problem here. We bought new Creda 850DL 8.5kW Electric Shower

    http://www.argos.ie/static/Product/partNumber/8329769/Trail/searchtext%3EELECTRIC+SHOWER.htm#tabrev

    and the reason for selecting this one is we live in a hard water area and this has anti scale built in and we were tight on money so the price was also affordable currently.

    Now, problem is, it seems to take power in also water, but it doesn't start, what should we check in here? What may be wrong? When switched on, just one red light lights up, it makes sound like starts and then it dies.

    Any advice please?

    Thanks


«1

Comments

  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    Did you follow the commisioning procedure as per the manual?Is it connected too main's or tank water?


  • Registered Users, Registered Users 2 Posts: 40 mammu


    Thanks for reply. It is connected to the main´s, as was previous electric shower (some-kind of Mira shower) and installed as instruction says.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Who actually installed it, did the electrical connections etc?

    Are all connections tight?

    Was the water gate valve turned back on after the new shower replaced old, assuming there was a dedicated one on the t off to the existing shower?


  • Registered Users, Registered Users 2 Posts: 40 mammu


    Water gate valve is turned on, electrical connections seems to be very tight, it suppose to be easy to install, and as manual says, it is easy to install, but something seems to be wrong. The only light that lights up is power light, rest of them just dead.


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    Ive said before and ill say again all of these devices have have a sticker on them that says only too be installed by a trained professional!Not just some jack of all trades!

    Did an electrician do the wiring?You couldnt have carried out the commisioning prodcedure if there's no water coming threw it either


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭DublinDilbert


    Do you have to bleed/prime the pump on these? I know some showers you need to.


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    Do you have to bleed/prime the pump on these? I know some showers you need to.

    No there a mains shower. No Pump.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Is there any locking screw that needs to be removed on this particular one during commissioning? Im more familiar with the t-90 ones myself.

    But either way, electric showers are not an easy install for the DIY enthusiast, and problems are easy to get to the bottom of, for a person competent in such installations, whether it be a problem with the install, or the shower unit itself.

    Robbie7730


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    Bruthal wrote: »
    Is there any locking screw that needs to be removed on this particular one during commissioning? Im more familiar with the t-90 ones myself.

    But either way, electric showers are not an easy install for the DIY enthusiast, and problems are easy to get to the bottom of, for a person competent in such installations, whether it be a problem with the install, or the shower unit itself.

    No theres no screw on the element selector switch as with the t-90 and even if there was that doesnt explain why there's no water coming threw as if the selector switch was screwed in position it would be screwed in the cold position and water would still flow


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    No theres no screw on the element selector switch as with the t-90 and even if there was that doesnt explain why there's no water coming threw as if the selector switch was screwed in position it would be screwed in the cold position and water would still flow

    I was more thinking along the lines of the flow/temp dial being stuck at minimum, which would have a very low flow rate on most showers.

    A mains fed one would seem to have little to be wrong. One it has its mains water supply, gate valves open, no blockages in the water supply/filter and power to the solenoid when the start button is pressed, it should work.

    Again, someone who is any way competent with these showers, will find the problem easily enough when there to check it out.


  • Advertisement
  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    Bruthal wrote: »
    I was more thinking along the lines of the flow/temp dial being stuck at minimum, which would have a very low flow rate on most showers.

    A mains fed one would seem to have little to be wrong. One it has its mains water supply, gate valves open, no blockages in the water supply/filter and power to the solenoid when the start button is pressed, it should work.

    Again, someone who is any way competent with these showers, will find the problem easily enough when there to check it out.

    Well seen as they havent said who installed the shower and said two or three times it said easy too install i dont think they can confirm the solenoid valve is energising when the start button is held.Might be main stat etc but not a DIY repair.
    What area are you in mammu?


  • Registered Users, Registered Users 2 Posts: 10,153 ✭✭✭✭dodzy


    Ive said before and ill say again all of these devices have have a sticker on them that says only too be installed by a trained professional!Not just some jack of all trades!

    Another one :rolleyes:

    Replacing a shower is not bloody rocket science for anyone who is a competent DIY person.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    dodzy wrote: »
    Another one :rolleyes:

    Replacing a shower is not bloody rocket science for anyone who is a competent DIY person.

    The competent DIY`r will just replace the shower, but rarely check the circuit supplying it even for suitable size of cable, rarely if ever, check the RCD, check the connections at the MCB board, and at the shower isolator, none of which are rocket science either.


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    dodzy wrote: »
    Another one :rolleyes:

    Replacing a shower is not bloody rocket science for anyone who is a competent DIY person.

    Ha ha ha!!Really??

    I take it so your a competent DIY person?Why dont you resolve the issue here for the OP so?

    As Bruthal said most often the biggest issue in changing a shower is the general electric's in the house,bonding issue's etc etc.

    You'd be horrified at some job's ive gone too after a "compentent DIY'er" changed the shower and i was called after over other issue's!


  • Registered Users, Registered Users 2 Posts: 10,153 ✭✭✭✭dodzy


    MrMac84 wrote: »
    Ha ha ha!!Really??

    I take it so your a competent DIY person?Why dont you resolve the issue here for the OP so?

    As Bruthal said most often the biggest issue in changing a shower is the general electric's in the house,bonding issue's etc etc.

    You'd be horrified at some job's ive gone too after a "compentent DIY'er" changed the shower and i was called after over other issue's!

    Slow down there MrMac. My point is simply that swapping out a shower is not a job which is above a competent DIY person IMO. Too many posts on these forums where the first line of reply is " dont touch it / your'e not competent / not registered / bla bla bla, without offering any actual advice.

    I would be very comfortable swapping out / installing a shower and I am not a registered plumber / electrician. If I post a question for advice on the operation of a unit, the response "if you have to ask, then you shouldn't be doing it" wears itself out after a while.

    If you take care in your work, are comfortable in the vacinity of electrics & plumbing, observe common sense in relation to isolation of power / water, refer to installation instructions for installation & comissioning details and carry out your work with care and attention, then there is absolutely no reason a DIY person could not complete this task. In short, if you are worried at all about the installation, then don't take it on.

    Oh, and for whats it worth, I've seen some botch work by certified professionals. Embarrasing stuff.


    @OP. As has been suggested, ensure electrical connections are correctly fitted & TIGHT.

    Not familiar with this model but potentially airlocked ? Have you allowed water to flow from the 1/2 supply right at the shower connection point prior to final fitting to unit?


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    dodzy wrote: »
    Slow down there MrMac. My point is simply that swapping out a shower is not a job which is above a competent DIY person IMO. Too many posts on these forums where the first line of reply is " dont touch it / your'e not competent / not registered / bla bla bla, without offering any actual advice.

    I would be very comfortable swapping out / installing a shower and I am not a registered plumber / electrician. If I post a question for advice on the operation of a unit, the response "if you have to ask, then you shouldn't be doing it" wears itself out after a while.

    If you take care in your work, are comfortable in the vacinity of electrics & plumbing, observe common sense in relation to isolation of power / water, refer to installation instructions for installation & comissioning details and carry out your work with care and attention, then there is absolutely no reason a DIY person could not complete this task. In short, if you are worried at all about the installation, then don't take it on.

    Oh, and for whats it worth, I've seen some botch work by certified professionals. Embarrasing stuff.


    @OP. As has been suggested, ensure electrical connections are correctly fitted & TIGHT.

    Not familiar with this model but potentially airlocked ? Have you allowed water to flow from the 1/2 supply right at the shower connection point prior to final fitting to unit?

    And can you explain too me so how a competent DIY person would know if the pipe used too feed the shower is installed correctly or if the fuse/mcb/rcb/rcbo is the correct size or if the cable has the correct polarity or if the fuseboard is upto date too take the new shower or if the bonding of the house is upto date cuz i would LOVE too know how a person who "would be very comfortable swapping out / installing a shower and I am not a registered plumber / electrician. is able too tell all this cuz i must have been wasting my time spending 4 years with FAS learning about this.


  • Registered Users, Registered Users 2 Posts: 10,153 ✭✭✭✭dodzy


    And can you explain too me so how a competent DIY person would know if the pipe used too feed the shower is installed correctly or if the fuse/mcb/rcb/rcbo is the correct size or if the cable has the correct polarity or if the fuseboard is upto date too take the new shower or if the bonding of the house is upto date cuz i would LOVE too know how a person who "would be very comfortable swapping out / installing a shower and I am not a registered plumber / electrician. is able too tell all this cuz i must have been wasting my time spending 4 years with FAS learning about this.
    Google :D

    No, but seriously, particularly in relation to swapping out a like for like ( or similar ) is not as difficult as you are making out. I ran 10mm2 approx 12mtrs from fuse board to shower unit with 45Amp RCBO. Drained the tank in the attic. Drilled a 17mm hole in same. Fitted approx 4mtrs of 1/2" qualpax to shower wall. Connected up everything, release air from system and running fine. The OPs job is changing; not full installation. Big difference.

    I've replaced a few ( mainly old Triton T90si ) with new models for family / friends and it is NOT a difficult job. Surely you cannot say this task is above a competent DIY person ?


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    dodzy wrote: »
    Google :D

    No, but seriously, particularly in relation to swapping out a like for like ( or similar ) is not as difficult as you are making out. I ran 10mm2 approx 12mtrs from fuse board to shower unit with 45Amp RCBO. Drained the tank in the attic. Drilled a 17mm hole in same. Fitted approx 4mtrs of 1/2" qualpax to shower wall. Connected up everything, release air from system and running fine. The OPs job is changing; not full installation. Big difference.

    I've replaced a few ( mainly old Triton T90si ) with new models for family / friends and it is NOT a difficult job. Surely you cannot say this task is above a competent DIY person ?


    And in each one of those did you check for correct earthing and bonding of the hotpress,bath etc?Did you check the size of the main's tails too support the new shower?Seen as you were the "expert" who replaced the shower say there was a fault and a person was killed in the shower (as happened in Blackrock 12 years ago) would you feel comfortable on the stand explaining too the Judge where you gained your expertise?

    Also you ran 10mm2 cable too shower?No pull cord or local isolation switch?Im also interested in where you fed the RCBO from?Did you check the main fuse was a 63 amp fuse?


  • Registered Users, Registered Users 2 Posts: 40 mammu


    Well seen as they havent said who installed the shower and said two or three times it said easy too install i dont think they can confirm the solenoid valve is energising when the start button is held.Might be main stat etc but not a DIY repair.
    What area are you in mammu?

    Im in Portlaoise..however, talking about installing, then yes my husband did it, he is not professional but has done it few times before without any problems. Now seems, that if this shower is broken or faulty, we can not swap it anymore in the shop, because it had to be installed by professional and another thing is who says anyway if it is faulty at all or broken? So no choice, we must call out somekind of professional..


  • Registered Users, Registered Users 2 Posts: 10,153 ✭✭✭✭dodzy


    And in each one of those did you check for correct earthing and bonding of the hotpress,bath etc?Did you check the size of the main's tails too support the new shower?Seen as you were the "expert" who replaced the shower say there was a fault and a person was killed in the shower (as happened in Blackrock 12 years ago) would you feel comfortable on the stand explaining too the Judge where you gained your expertise?

    Also you ran 10mm2 cable too shower?No pull cord or local isolation switch?Im also interested in where you fed the RCBO from?Did you check the main fuse was a 63 amp fuse?

    1. No
    2. No
    3. No
    4. 10sq - yes
    5. Yes. Double pole isolator switch
    6. ?
    7. Yes - 63A

    Anyway, you are like a dog with a bone now, so I'll leave it. You are an obviously well trained FÁS sparks, and as such, I feel could have been more helpful to the OP.

    @OP. I think it is fair to assume that the previously installed Mira mains fed unit was of a similar rating 8.5kw to the Creda unit. Live, neutral, earth and water supply. Thats it. If you believe it to be faulty, just rebox it and bring it back to Argos. They will change it, no problem. They will NOT give you the 3rd degree in relation to who fitted the unit. They WILL replace it.


  • Advertisement
  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    dodzy wrote: »
    1. No
    2. No
    3. No
    4. 10sq - yes
    5. Yes. Double pole isolator switch
    6. ?
    7. Yes - 63A

    Anyway, you are like a dog with a bone now, so I'll leave it. You are an obviously well trained FÁS sparks, and as such, I feel could have been more helpful to the OP.
    Like a dog with a bone?No!

    What i am tho is extremly annoyed at gangsters like you running around thinking "ah sure this is easy" It's people like you who get innocent people killed!The step's i listed in my last post are not just me showing off that im a FAS trained spark's.They are THE FIRST THING you must check BEFORE carrying out ANY work in realation too an electric shower!

    The fact you dont even understand the question about how you fed the RCBO is another extremly worrying point.Ill put it in layman's terms so you might understand.Did you feed it from the lighting circuit or the socket or do you even know the difference?

    And @ OP ive an extremley good idea whats wrong with your shower (if any mod wants too PM to ask me ill explain too them) and have come across this problem many time's before in similar model's and just exchanging the shower for a different one you could easyily run into this problem again as it occur's during installation.


  • Registered Users, Registered Users 2 Posts: 22 coxyboy


    And if someone thinks they know whats wrong would they not help out OP.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    coxyboy wrote: »
    And if someone thinks they know whats wrong would they not help out OP.

    There have been suggestions given, here are some possibilities again,

    Gate valve not opened after refit.

    Blockage in water supply (unlikely)

    Problem with power supply to shower, bad connection etc.

    Faulty shower, (from a faulty solenoid valve, or internal wiring connection bad or a wire not connected, faulty start button, clogged filter), all of which are easily tested by someone that is familiar with the workings of a shower, and with a multimeter.

    Mains pressure dropped into house (unlikely the problem, but could cause problems if has dropped)


  • Registered Users, Registered Users 2 Posts: 528 ✭✭✭EURATS


    Bruthal wrote: »

    There have been suggestions given, here are some possibilities again,

    Gate valve not opened after refit.

    Blockage in water supply ([SIZE="1"]unlikely[/SIZE])

    Problem with power supply to shower, bad connection etc.

    Faulty shower, ([SIZE="1"]from a faulty solenoid valve, or internal wiring connection bad or a wire not connected, faulty start button, clogged filter[/SIZE]), all of which are easily tested by someone that is familiar with the workings of a shower, and with a multimeter.

    Mains pressure dropped into house ([SIZE="1"]unlikely the problem, but could cause problems if has dropped[/SIZE])


    If it was a straight swap and commissioning procedure adhered to correctly...box it up and bring it back. Wouldn't be the first faulty appliance to come from Argos(or any other shop)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    EURATS wrote: »
    If it was a straight swap and commissioning procedure adhered to correctly...box it up and bring it back.
    Correct commissioning wouldnt work if there was for example, a bad connection in the supply to the shower, or a problem with the water supply.

    Wouldn't be the first faulty appliance to come from Argos(or any other shop)

    Well if I was installing it, Id do the tests. No point bringing back if a spade (as example) is simply disconnected from its terminal, or similar.

    It possibly/probably is a problem in the shower. Id test and find. For the handyman with not much understanding of shower workings, its put up, doesnt work, take down, replace. And hope the problem was indeed the shower.

    But either way, suggestions are put up, including just take down and replace. The OP can decide based on all suggestions.


  • Registered Users, Registered Users 2 Posts: 528 ✭✭✭EURATS


    Bruthal wrote: »
    Correct commissioning wouldnt work if there was for example, a bad connection in the supply to the shower, or a problem with the water supply.




    Well if I was installing it, Id do the tests. No point bringing back if a spade ([SIZE="1"]as example[/SIZE]) is simply disconnected from its terminal, or similar.

    It possibly/probably is a problem in the shower. Id test and find. For the handyman with not much understanding of shower workings, its put up, doesnt work, take down, replace. And hope the problem was indeed the shower.

    But either way, suggestions are put up, including just take down and replace. The OP can decide based on all suggestions.


    To be honest..if the op had any clue(I suspect he does) he would have tested the water supply when the unit was out if there was any suspicions in relation to it.
    In relation to the power supply..he can check connections for piece of mind but I have my suspicions that the supply isn't the issue.

    In relation to the unit itself..the op should check for obvious loose connections but apart from that..box it up an bring it back.

    The shower should only require being plumbed up, connected for power..and then the commissioning. Any issues with the shower itself...back to the shop..not repairs.


  • Registered Users, Registered Users 2 Posts: 10,153 ✭✭✭✭dodzy



    And @ OP ive an extremley good idea whats wrong with your shower (if any mod wants too PM to ask me ill explain too them) and have come across this problem many time's before in similar model's and just exchanging the shower for a different one you could easyily run into this problem again as it occur's during installation.
    Why the secrecy ? Share the knowledge as it is obviously an easy fix if you have come across it many times before. No need for PMs.


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    dodzy wrote: »
    Why the secrecy ? Share the knowledge as it is obviously an easy fix if you have come across it many times before. No need for PMs.

    Im a professional hence why ive encountered it many time's.If any one thinks im lieing then a mod can PM me and ill explain it to them.But im not going too post up how it can be resolved here and have gangster's like you running around tomorow telling people you can fix electric shower's and getting someone hurt.Either yourself or a "customer"


  • Registered Users, Registered Users 2 Posts: 528 ✭✭✭EURATS



    Im a professional hence why ive encountered it many time's.If any one thinks im lieing then a mod can PM me and ill explain it to them.But im not going too post up how it can be resolved here and have gangster's like you running around tomorow telling people you can fix electric shower's and getting someone hurt.Either yourself or a "customer"


    Gangsters? That's more than a little over the top. Care to pm me what u think the issue is?

    A new shower shouldn't need to be "fixed".


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    EURATS wrote: »


    Gangsters? That's more than a little over the top. Care to pm me what u think the issue is?

    A new shower shouldn't need to be "fixed".
    you can't expect him to make this info public
    the diagnostics and software for these showers cost a fortune


  • Registered Users, Registered Users 2 Posts: 528 ✭✭✭EURATS


    M cebee wrote: »
    you can't expect him to make this info public
    the diagnostics and software for these showers cost a fortune


    Ur having a laugh.

    I don't actually need this "INFO" as I have never needed "software" or "diagnostics" to get a new shower up and running.


  • Registered Users, Registered Users 2 Posts: 10,153 ✭✭✭✭dodzy


    MrMac84 wrote: »
    Im a professional hence why ive encountered it many time's.If any one thinks im lieing then a mod can PM me and ill explain it to them.But im not going too post up how it can be resolved here and have gangster's like you running around tomorow telling people you can fix electric shower's and getting someone hurt.Either yourself or a "customer"

    Get a grip FFS. You are talking pure sh1te and you know it. You're just one of these "professionals" that only post the same crap time after time. " if you are not certifed, then dont touch it, you haven't got a clue, etc".

    Post the fix for the OP. You might be surprised what some gangsters are capable of.


  • Registered Users, Registered Users 2 Posts: 10,153 ✭✭✭✭dodzy


    EURATS wrote: »
    Ur having a laugh.

    I don't actually need this "INFO" as I have never needed "software" or "diagnostics" to get a new shower up and running.

    Mceebee was taking the piss, I wager ;)


  • Registered Users, Registered Users 2 Posts: 528 ✭✭✭EURATS


    dodzy wrote: »

    Mceebee was taking the piss, I wager ;)


    Well is hard to know any more considering the mystery shower solutions being spouted


  • Registered Users, Registered Users 2 Posts: 2,454 ✭✭✭cast_iron


    dodzy wrote: »
    GYou're just one of these "professionals" that only post the same crap time after time. " if you are not certifed, then dont touch it, you haven't got a clue, etc".
    To be fair, people might well "have a clue", but that can often be the problem.

    If the job is just a swap like for like old and new shower, then the DIYer with a bit of knowledge will probably manage a shower swap quite well. They are not that difficult a job to do.

    However, just because the customer "just wants the old shower swapped for a new one", doesn't mean that that is a safe thing to do and just walk away thinking you've done a grand job.

    While MrMac might appear a bit OTT, most of the above questions you answered no to really should be checked when installing a new shower, whether the customer asked for it or not. The customer should be advised if anything needs seeing to. Newer showers can draw alot more current and require more rigorous safety protection than back in the day when they were originally wired up and fitted.

    Knowing/checking that the job is not just a straight swap is where only the professional will usually beat the DIYer hands down (and why it is usually advised), even though the DIYer might well do a better job of "the straight swap".


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    dodzy wrote: »
    Oh, and for whats it worth, I've seen some botch work by certified professionals. Embarrasing stuff.
    Embarrassing for who? Hardly the competent ones.
    Not familiar with this model but potentially airlocked?

    Be doing well to see airlocks on a mains fed supply if the dynamic pressure is adequate to properly operate the shower. Maybe you were thinking it might be a tank fed one, which can have that problem alright.


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    cast_iron wrote: »
    To be fair, people might well "have a clue", but that can often be the problem.

    If the job is just a swap like for like old and new shower, then the DIYer with a bit of knowledge will probably manage a shower swap quite well. They are not that difficult a job to do.

    However, just because the customer "just wants the old shower swapped for a new one", doesn't mean that that is a safe thing to do and just walk away thinking you've done a grand job.

    While MrMac might appear a bit OTT, most of the above questions you answered no to really should be checked when installing a new shower, whether the customer asked for it or not. The customer should be advised if anything needs seeing to. Newer showers can draw alot more current and require more rigorous safety protection than back in the day when they were originally wired up and fitted.

    Knowing/checking that the job is not just a straight swap is where only the professional will usually beat the DIYer hands down (and why it is usually advised), even though the DIYer might well do a better job of "the straight swap".

    Thanks cast_iron

    If you had an old 6kw shower in your house and some Handy Man fitted a 9.5kw and done no upgrades that would be ok so would it?These RULES and REGULATIONS arent just there for the craic.They are in place too save live's.The above mentioned questions need too asked and answered BEFORE the shower is replaced.If you are not competent enough too answer these questions then you dont belong next or near the job!

    @EURATS If you think im talking **** then so be it.That's your opinion.But people should read my post's correctly before attacking me what i said was
    And @ OP ive an extremley good idea whats wrong with your shower (if any mod wants too PM to ask me ill explain too them) and have come across this problem many time's before in similar model's and just exchanging the shower for a different one you could easyily run into this problem again as it occur's during installation.
    The problem with this shower in my opinion occured during the installation.If they get a replacement shower the could easyily occur again.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    EURATS wrote: »
    To be honest..if the op had any clue(I suspect he does) he would have tested the water supply when the unit was out if there was any suspicions in relation to it.
    In relation to the power supply..he can check connections for piece of mind but I have my suspicions that the supply isn't the issue.

    In relation to the unit itself..the op should check for obvious loose connections but apart from that..box it up an bring it back.

    The shower should only require being plumbed up, connected for power..and then the commissioning. Any issues with the shower itself...back to the shop..not repairs.

    If the op does know much about the workings of showers, then they will find diagnosing the problem fairly simple.

    But the op asked a question, and posters gave some answers.

    Maybe he let a big lump of bosswhite into the piping, or kinked it:D


  • Registered Users, Registered Users 2 Posts: 129 ✭✭uncle betty


    MrMac84 wrote: »
    And can you explain too me so how a competent DIY person would know if the pipe used too feed the shower is installed correctly or if the fuse/mcb/rcb/rcbo is the correct size or if the cable has the correct polarity or if the fuseboard is upto date too take the new shower or if the bonding of the house is upto date cuz i would LOVE too know how a person who "would be very comfortable swapping out / installing a shower and I am not a registered plumber / electrician. is able too tell all this cuz i must have been wasting my time spending 4 years with FAS learning about this.

    I'm not out of FAS that long and there was no mention of a shower installation at any stage. Not in theory, and not in the practical.

    So you didn't spend four years learning about that in any case. And if you didn't do that, I highly doubt you got into the size of pipe used to feed the shower.

    And by the way, what does this mean ?
    The fact you dont even understand the question about how you fed the RCBO is another extremly worrying point.Ill put it in layman's terms so you might understand.Did you feed it from the lighting circuit or the socket or do you even know the difference?

    IS that really what you wanted to say, layman's terms or not ?

    I think you have a bit of an attitude problem to be honest.


  • Registered Users, Registered Users 2 Posts: 528 ✭✭✭EURATS



    I'm not out of FAS that long and there was no mention of a shower installation at any stage. Not in theory, and not in the practical.

    So you didn't spend four years learning about that in any case. And if you didn't do that, I highly doubt you got into the size of pipe used to feed the shower.

    I think you have a bit of an attitude problem to be honest.


    Well said.

    Such a magical mystery tour..is laughable and ignorant.

    The man has an airlock, not enough pressure or a bollox'd shower.


    If its an airlock, there should be a bleed valve on the unit. Open it a little(careful) until u hear a hiss and get water. Close it up and problem solved.
    If its a lack of pressure..you will need to change to tank fed pumped shower.


  • Advertisement
  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    I'm not out of FAS that long and there was no mention of a shower installation at any stage Not in theory, and not in the practical.

    So you didn't spend four years learning about that in any case. And if you didn't do that, I highly doubt you got into the size of pipe used to feed the shower.

    And by the way, what does this mean ?



    IS that really what you wanted to say ?

    I think you have a bit of an attitude problem to be honest.

    So bonding never came up?Correct tails on consumer unit never came up? Where too take the supply in a consumer unit for a large draw i.e cooker's and shower's never came up?Ye didnt terminate 6mm2 or 10mm2 cables correctly?

    Jesus alot has changed so in FAS since i quailified.Cuz those things were part of my course and all apply too shower's

    Yes i have an attitude towards people who think they can do my job as good as me (or any other electrician for that matter)Just because an electrical item works doesnt mean it's done correctly or safely.


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    EURATS wrote: »
    Well said.

    Such a magical mystery tour..is laughable and ignorant.

    The man has an airlock or a bollox'd shower.


    If its an airlock(which it is), there should be a bleed valve on the unit. Open it a little(careful) until u hear a hiss and get water. Close it up and problem solved.

    There's no bleed valve on those shower's!


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    EURATS wrote: »
    If its an airlock(which it is), there should be a bleed valve on the unit.

    No bleed valve needed on a mains fed shower, so I doubt that one has one.

    They are needed on pump showers because without it, the pump will be running dry when first turned on.

    The mains water shower simply opens the solenoid valve when it is turned on, and the mains pressure will force any air through, with no worry of dry running of any pump.


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    Bruthal wrote: »
    No bleed valve needed on a mains fed shower, so I doubt that one has one.

    Best not get on the lad's back's.Their expert's sure.Were spouting non sence about rules and regulation's and things that will slow them down.
    The mira sport is the only mains shower i can think of off hand with a bleed valve


  • Registered Users, Registered Users 2 Posts: 129 ✭✭uncle betty


    MrMac84 wrote: »
    So bonding never came up?Correct tails on consumer unit never came up? Where too take the supply in a consumer unit for a large draw i.e cooker's and shower's never came up?Ye didnt terminate 6mm2 or 10mm2 cables correctly?

    Jesus alot has changed so in FAS since i quailified.Cuz those things were part of my course and all apply too shower's

    Yes i have an attitude towards people who think they can do my job as good as me (or any other electrician for that matter)Just because an electrical item works doesnt mean it's done correctly or safely.

    What's wrong with you ? Bonding, cookers, termination ? ? ?

    My post was not complicated in any way, it was very clear as regards what I was referring to.

    I don't think I made any reference to bonding whatsoever. Or cookers. Or termination of cables.

    As for my course, no, nothing came up about whether I should connect an RCBO to a light, or a socket ;-)

    I'm sure that showers aren't detailed anywhere in my module books, because it's such an obvious omission.

    I must check the domestic installation diagram to see if there's even a shower circuit included in it.

    In fact, I'd have to check my notes to see whether RCBO's are mentioned at all in them.

    At this stage, you aren't getting the job of going in there and sorting it out anyway. It isn't going to be your problem, no more than it is mine, if someone gets hurt.

    So why not either give the OP the fix they seek, or else just leave it altogether ?


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    What's wrong with you ? Bonding, cookers, termination ? ? ?

    My post was not complicated in any way, it was very clear as regards what I was referring to.

    I don't think I made any reference to bonding whatsoever. Or cookers. Or termination of cables.

    As for my course, no, nothing came up about whether I should connect an RCBO to a light, or a socket ;-)

    I'm sure that showers aren't detailed anywhere in my module books, because it's such an obvious omission.

    I must check the domestic installation diagram to see if there's even a shower circuit included in it.

    In fact, I'd have to check my notes to see whether RCBO's are mentioned at all in them.

    At this stage, you aren't getting the job of going in there and sorting it out anyway. It isn't going to be your problem, no more than it is mine, if someone gets hurt.

    So why not either give the OP the fix they seek, or else just leave it altogether ?

    And my post's are very clear also.Theres a hell of alot more too a shower then just 3 cables!Hence why were talking about bonding etc etc!
    Well if theres no mention of an RCBO in your course notes from phase 2,4&6 then you did a different apprentship too me


  • Registered Users, Registered Users 2 Posts: 528 ✭✭✭EURATS



    Best not get on the lad's back's.Their expert's sure.Were spouting non sence about rules and regulation's and things that will slow them down.
    The mira sport is the only mains shower i can think of off hand with a bleed valve

    Well u are such an "expert" that u told him u knew his problem but wouldn't tell him how to sort it. Nothing worse than a unhelpful "expert".


  • Registered Users, Registered Users 2 Posts: 129 ✭✭uncle betty


    And my post's are very clear also.Theres a hell of alot more too a shower then just 3 cables!Hence why were talking about bonding etc etc!
    Well if theres no mention of an RCBO in your course notes from phase 2,4&6 then you did a different apprentship too me

    What I dislike is your beating me over the head with your little bit of knowledge about bonding, termination and so on - it was totally uncalled for, and condescending.

    It'll almost certainly be Phase 2 of course, but if you or anyone else can refer me to the relevant module where RCBO's were detailed, I'd appreciate it.

    EDIT - as I thought, there is only definitional mention of RCBO's in the Apprentice Notes (2.2.3, pp 8, 31). The provided diagram on p.36 has no illustration of an RCBO circuit, whether shower or otherwise.

    http://www.ecollege.ie/site/liu/electrical_notes/LL223.pdf


  • Registered Users, Registered Users 2 Posts: 10,153 ✭✭✭✭dodzy


    We're spouting nonsense about rules and regulations and things that will slow them down. I know how to fix the problem, but I'll be damned if I'm sharing the knowledge I have gained with a few shams who fancy themselves as being DIY competent. I'm gonna keep all that information to myself, and if anybody asks for advice, sure I'll just knock them back with the usual "I'm a qualified and registered sparks and you are not bullsh1t. You would think that this forum is for the sharing of information or something!"
    I took the liberty of fixing your post for you.


  • Registered Users, Registered Users 2 Posts: 62 ✭✭DELTATIP


    Bruthal wrote: »
    The competent DIY`r will just replace the shower, but rarely check the circuit supplying it even for suitable size of cable, rarely if ever, check the RCD, check the connections at the MCB board, and at the shower isolator, none of which are rocket science either.


    And like wise most if not all electricains wont check either -get off your high horse -