  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,532 Mod ✭✭✭✭2011


    gilbarry1 wrote: »
    ET101 Rule 555.3.2 states:
    “A circuit supplying auxiliary equipment associated with water services and water systems (e.g. pumps) shall be protected by an RCD having a rated residual operating current not exceeding 30mA”

    Not applicable in this case, here is why:
    Rule 555.3.2 is a subset of 555.3 which means that it only applies to "water-heating appliances".

    The original question from the OP in the very first post on this thread is about "submersible pumps in bored wells" so an RCD is not a requirement.

    As RCD protection is not required by ET101 and direct contact is almost impossible in addition to the reasons I gave in this post I would not supply pumps such as this from an RCD.