thesis on external insulation (ewi)

  • 01-02-2011 3:15pm
    #1
    Registered Users, Registered Users 2 Posts: 38


    I weas just wondering if anyone could help me, I'm doing a thesis on external insulation for college. Many companies haven't got back to me as they don't like my questions as, I do have to find the faults in many systems. I am trying to find the best solution, but i know that mould growth can be a problem depandant on the facade.. breathability is another issue, cracking in the plaster has arisen also especially after the harsh cold december.

    Maybe some of ye could tell me of your experiences and what you thought of each system?
    Also, if there was someone that was thinking of doing it, I would like to do a thermal imaging test if possible on the house before and after to see the actual difference.
    Detail can be a major issue, as many cowboys '****' it on the wall and away. soffits shoud be removed and extreme detail has to be taken around the windows... especially the cills!!

    Any help would be greatly appreciated.
    Also, I am from Cavan and studying in Dublin. Not a young student either, so I won't wreck your head.
    Thanks.


«1

Comments

  • Registered Users, Registered Users 2 Posts: 154 ✭✭TiNcAn


    I was wondering if you could answer me a few questions. I have been searching the internet for quite some time now to come up with some reliable figures for the lifetime of an external insulation systems, particularly in Irish weather conditions. So far I have not have had nay luck so if there is anything you could share it would be greatly appreciated.

    I would also invite you to take some findings before and after if I choose to pursue external insulation.

    Much appreciated.


  • Registered Users, Registered Users 2 Posts: 597 ✭✭✭Supertech


    Cost is an issue aswell FarAdr. I looked at using it on a (very) small project recently which was to be grant assisted - a refurbishment of a small club house. EWI was coming in at about 3.5 times the cost of internal dry-lining on that particular job. Because the budget was so tight,and because there was other works which absolutely had to be carried out, we had no option but to go for the internal solution despite the obvious practical advantages of EWI over dry-lining. Agree with you regarding the detail - all existing junctions need to be examined when considering use of EWI aswell, but in fairness, as with most systems, once due thought is given to their application, acceptable solutions can be found in most instances.

    With regard to to your thesis, have a look at some of the NSAI Certified systems and check out the specific stipulations attached to the certs. this will give you a pointer to the areas which need specific attention with each system.


  • Registered Users, Registered Users 2 Posts: 162 ✭✭agrostar


    TiNcAn wrote: »
    I was wondering if you could answer me a few questions. I have been searching the internet for quite some time now to come up with some reliable figures for the lifetime of an external insulation systems, particularly in Irish weather conditions. So far I have not have had nay luck so if there is anything you could share it would be greatly appreciated.

    I would also invite you to take some findings before and after if I choose to pursue external insulation.

    Much appreciated.

    +1 with your concerns about the lifetime of ewi systems, i am currently in the planning process and hopefully with a bit of luck hope to be building in the summer. I was hopeing to find out important information about lifetime and performance of ewi but i cant find it anywhere:confused::confused::confused:


  • Subscribers Posts: 42,172 ✭✭✭✭sydthebeat


    agrostar wrote: »
    +1 with your concerns about the lifetime of ewi systems, i am currently in the planning process and hopefully with a bit of luck hope to be building in the summer. I was hopeing to find out important information about lifetime and performance of ewi but i cant find it anywhere:confused::confused::confused:

    check the nasi certification for external insulation here
    You really need to read each individual certification and observe the different "durability" assessments (there are generally in section 4.8 of the certs)

    some have 30 year durability, some have 60 years.... some have others.

    also find out what warranties are available with each system... and find out what will happen if the particular company goes out of business in the lifetime of the warranty.


  • Registered Users, Registered Users 2 Posts: 154 ✭✭TiNcAn


    I have read through the suppliers documentation but am still not convinced. It states that;
    The assessment indicates that the system should
    remain effective for at least 30 years, providing
    that it is designed, installed and maintained in
    accordance with this Certificate.

    which would suggest that it would last for at least 30 years. However the guarantee offered only lasts 10 years.

    This form of insulation has been around for quite some time especially in places such as Germany since the 1980s. It would be very helpful to have some first hand experiences with people who have external insulation for at least 2 years. Granted that there have been developments in the systems used but it would still be of great benefit.

    Sorry for the hijacking of the thread, just trying to clear up some of my concerns which I am having.


  • Advertisement
  • Subscribers Posts: 42,172 ✭✭✭✭sydthebeat


    i dont think your hijacking, i think your concerns are pertinent.

    other EWI certs are for 60 years.

    Im not too concerned that the guarantee only generally last 30% of the proposed durability period. When i buy a car i might get a 3 or 5 year warantee but id expect it to last a lot longer than that.. .subject to proper maintanence of course... same with building methods.


  • Registered Users, Registered Users 2 Posts: 154 ✭✭TiNcAn


    Upon going through the list of NSAI certified EWI suppliers I have found only three brands that offer a effective life expectancy of at least 60 years. These include 2 models from weber.therm and 1 from StoTherm. Every other model only offer at least 30 years.

    This would lead me to believe that these models are more durable and reliable brands of EWI. They also offer longer guarantees than most of their competitors with weber.therm offering 15 years and StoTherm offering 20 years.

    I am wondering would it be accurate to expect a full 60 years lifetime from a quality installed either of these two brands. The difficulty arises in that there is only laboratory data to back this data up and no real world tests as they have not been around for that long.

    It would also be of great benefit if someone could PM the details of a few contractors that supply these brands. I will have look myself but help would be appreciated.


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    As far as I know:

    The certs offering 30 years are the ones that were certified for retrofit only, not new build. This is where most of the work currently is so you can understand why it's the type of approval that companies apply for. NSAI certification is extremely expensive.

    The 60 years applys to new build.

    I can't say what but I can guess. On a new build everything should be stable and good. There is less risk of something else failing and affecting the EWI.

    If you fix EWI to a wall that has been dashed for 20 years, there is always a risk that the dashing could fail over time and bring the EWI with it.

    As I understand it, the materails for new build and retrofit are identical, so it has to come down to the substrate.

    STO offer a 20 year warranty only if you pay a hefty premium for it afail i.e. it's an extended warranty, not the standard one.


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    TiNcAn wrote: »
    I am wondering would it be accurate to expect a full 60 years lifetime from a quality installed either of these two brands. The difficulty arises in that there is only laboratory data to back this data up and no real world tests as they have not been around for that long.

    NSAI certification is not a warranty, so no, it's not accurate to expect a full 60 years lifetime from a quality installer of those brands.

    You'll also find that the warranties are massively complicated and ultimately you'd be hard pressed to prove that the system failed and not something else.


  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    Supertech wrote: »
    Cost is an issue aswell FarAdr. I looked at using it on a (very) small project recently which was to be grant assisted - a refurbishment of a small club house. EWI was coming in at about 3.5 times the cost of internal dry-lining on that particular job. Because the budget was so tight,and because there was other works which absolutely had to be carried out, we had no option but to go for the internal solution despite the obvious practical advantages of EWI over dry-lining. Agree with you regarding the detail - all existing junctions need to be examined when considering use of EWI aswell, but in fairness, as with most systems, once due thought is given to their application, acceptable solutions can be found in most instances.
    .

    Yeah, cost does seem to be a big issue, but some people have no alternative but to insulate externally as the work which is required internally after dry lining is excessive of that externally.
    What I mean is that you may have to move out of your home, there are decoration costs and storage, the removal of a kitchen etc and the reinstalling of all electrical appliances/sockets etc..and then theres the fact that your losing square footage of your living space, which in many parts of the country mainly Dublin is how your home is valued.
    I suppose with regards a clubroom these problems aren't so much an issue, as there is limited services and decoration but as the saying goes different horses for different courses.
    Also with drylining there can be problems also which take a long time to arise. Seemily bad insulation options or approaches to insulating a home can cause mould growth which in turn causes asthma. As the insulation is stopping vapour penetrating the fabric, it can cause damp spots within the drylining, particularly with corners and floor junctions etc. Then theres the issue of cold bridging if this is your thing... and external insulation when applied in the correct manner prevents this.. wrapping your home in a blanket.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    i dont think your hijacking, i think your concerns are pertinent..[/QUOTE]

    God, no all information with regards this subject is greatly appreciated, as I said I want to hear everything that people know and have experienced with the product.
    At first I didn't realise that there were so many products and alternatives for EWI, but there is so much to be looked at.
    Firstly, know what your building is constructed with, and your foundation type and whether you have dpcs etc. There is a serious lack of investigation when people insulate a house. For instance, an old stone wall was built from rubble, bricks and whatever could be thrown in along with lime perhaps. This is where I have found a serious issue. these walls were built to breathe, that it how they dry out and this is why lime renders are used on such buildings.They also move with the seasons and therefore anything rigid is a big no no. What they are insulated with has to be flexible and move with the house, and be able to breathe and let the wall dry out. Breathability is the main concern when retrofitting an old house I have learned.
    Thats just touching that topic.. I still have to investigate it further.
    If its a sustainable you want to take, there are many options; woodfibre, rockwool, sheeps wool, hempcrete to name but a few... where these seem to be lacking is resistance, they need a greater depth to achieve the same results as the chemical options such as eps xps.
    What I have found is that proper detailing of these cannot be compromised, and make sure you have someone with the knowhow or qualification to show you how to achieve the best result... including removing the soffit and insulating above to the rafters to achieve a tight seal of insulation. If possibe, and I know that it has extra cost, remove the windows and bring them in line with the insulation in some way or other.. also get the sill cut in line with the blockwork.. this adds a greater insulation value and prevents the risk of a cold bridge or cracking at the sill.
    I could go on but I'm sure this is long enough, however you may need to look at insulating below the ground in some circumstances also.


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    sas wrote: »
    As far as I know:

    The certs offering 30 years are the ones that were certified for retrofit only, not new build. This is where most of the work currently is so you can understand why it's the type of approval that companies apply for. NSAI certification is extremely expensive.

    The 60 years applys to new build.

    .

    Turns out this was incorrect.

    I contacted NSAI and asked them because this is particularly relevant to me right now.

    You will notice that the certs with 60years were some of the first EWI ones issued. Basically, the practise back then (and I think it was a requirement which has since been dropped) was for systems for new build to have a 60 year life expectancy. The problem with that is that this 60 years is outlandish when compared to everywhere else in Europe and we were put under pressure.

    Most of the NSAI certs are based on ETAs which have a 25 year period specified on them. It's alot easier for a company to get NSAI certification of 30 years when a ETA for 25 is already in place. It actually sounded very "finger in the air" type testing to get from 25 to 30 years. I was told that companys are encouraged to go for the 30 year option if an ETA exists for the system in question.

    Once a system is in use for a period of time, they may then be able to apply to get from 30 years to 60 years.

    For the earlier certs (60 years) they (NSAI) sometimes recommended a slightly thicker render for example. By the sounds of it however, there wasn't alot of testing done.

    I've always been very dubious about agrement certs. I haven't changed that opinion after my conversation with them.


  • Registered Users, Registered Users 2 Posts: 4 Rockfall


    Some inaccuracies there I'm afraid.

    NSAI Agrément certified external insulation systems, as well as other building systems, for a 60 year design life as this was a requirement of the DoEHLG to obtain a Floor Area Compliance Certificate for a dwelling in order for it to be eligible for the first time buyers grant. This requirement has not been dropped due to pressure from Europe, but actually as a result of the first time buyers grant being dropped in the recent budget.

    ETAs certify for a design life of anything between 10 and 30 years. In order for NSAI Agrément to certify a design life of 30 years for a system, they have to visit sites where the product has been used for a considerable period of time to obtain info on history of use, maintenance requirements etc.

    60 year certified systems always have a double thickness of render compared to 30 year systems, unless the manufacturer in question insists on an equally thick render for a retrofit 30 year system.


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    Balls, I'm having a shocking run on this thread
    Rockfall wrote: »
    Some inaccuracies there I'm afraid.
    NSAI Agrément certified external insulation systems, as well as other building systems, for a 60 year design life as this was a requirement of the DoEHLG to obtain a Floor Area Compliance Certificate for a dwelling in order for it to be eligible for the first time buyers grant. This requirement has not been dropped due to pressure from Europe, but actually as a result of the first time buyers grant being dropped in the recent budget.

    Cool. I most definitely was not told this by this NSAI however.
    Rockfall wrote: »
    ETAs certify for a design life of anything between 10 and 30 years. In order for NSAI Agrément to certify a design life of 30 years for a system, they have to visit sites where the product has been used for a considerable period of time to obtain info on history of use, maintenance requirements etc.

    There was no mention of site visits etc. when I asked about going from 25 to 30 years. I was left with the impression that basically 25 years or 30 years, there's not much in it so we (NSAI) won't be overly worried given that the testing had already been done by someone else.

    Thanks for clarifying.


  • Closed Accounts Posts: 4 biddyearly


    Hi There

    I did a thesis on Insulated Concrete Formwork which would be kinda similar to external Insulation, Afterwards i worked as a site Engineer on an ICF Development. We encountered problems with this system in terms of cracking etc. If i can be of any help pm me.


  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    biddyearly wrote: »
    Hi There

    I did a thesis on Insulated Concrete Formwork which would be kinda similar to external Insulation, Afterwards i worked as a site Engineer on an ICF Development. We encountered problems with this system in terms of cracking etc. If i can be of any help pm me.

    Hi,
    tell us more please.
    where and in what situations was the cracking etc?


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    biddyearly wrote: »
    Hi There

    I did a thesis on Insulated Concrete Formwork which would be kinda similar to external Insulation, Afterwards i worked as a site Engineer on an ICF Development. We encountered problems with this system in terms of cracking etc. If i can be of any help pm me.

    This isn't by any chance the development in Limerick (I think, or maybe Ennis) where the BRE did an investigation and as I recall ultimately it can down to the plastering contractor having made a mess of it.

    I.e. system good, application bad.


  • Registered Users, Registered Users 2 Posts: 4 Rockfall


    sas wrote: »
    There was no mention of site visits etc. when I asked about going from 25 to 30 years. I was left with the impression that basically 25 years or 30 years, there's not much in it so we (NSAI) won't be overly worried given that the testing had already been done by someone else.

    Thanks for clarifying.


    No problem. I'd love to know who you were talking to in NSAI as they didnt give you the right info at all, and actually did a huge disservice to NSAI Agrément as a result.


  • Registered Users, Registered Users 2 Posts: 39 badger81


    ah great, i thought icf was 'the' thing. i've since had my mind changed to external insulation and nowi find myself doubting this method,
    i swear this decision is almost as difficult as dealing with offaly co co

    badger pullin his hair out


  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    its actually ridiculous the amount of stuff that is out there. As I have stated, im trying to do a thesis on it and every day something new is found out and considerations which should be taken into account. just with the render itself, we discussed that if a child or adult even is puckin a sliotar at the wall, its small hard and fierce pressure behind it, will it damage the render and let water seep through? its a case that might not be taught of, but it happens, and then theres hanging flower baskets or something of the like, this creates holes which in turn lets water penetrate.
    Should a cavity be left behind to let water out if it does get in? and if you do leave a cavity behind, then your insulated render won't be as strong as its not on a solid substrate (wall) and can buckle and bend easier...
    There really is so much to consider, but don't believe all the bull*hit that company sales reps tell ya, cos obviously they are getting a cut and will promote their product and demote others.
    Hope ya come to a conclusion anyway!!!


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 39 badger81


    FarAdr wrote: »
    its actually ridiculous the amount of stuff that is out there. As I have stated, im trying to do a thesis on it and every day something new is found out and considerations which should be taken into account. just with the render itself, we discussed that if a child or adult even is puckin a sliotar at the wall, its small hard and fierce pressure behind it, will it damage the render and let water seep through? its a case that might not be taught of, but it happens, and then theres hanging flower baskets or something of the like, this creates holes which in turn lets water penetrate.
    Should a cavity be left behind to let water out if it does get in? and if you do leave a cavity behind, then your insulated render won't be as strong as its not on a solid substrate (wall) and can buckle and bend easier...
    There really is so much to consider, but don't believe all the bull*hit that company sales reps tell ya, cos obviously they are getting a cut and will promote their product and demote others.
    Hope ya come to a conclusion anyway!!!


    I had not even thought of some of those things!!!!
    Ah crap I give up......... Beaten by a house in my head :(


  • Registered Users, Registered Users 2 Posts: 162 ✭✭agrostar


    Hey FarAdr hows the Thesis coming along?

    I was talking to an architect and he was saying that the EWI may be prone to rodent attack... Dont no if this problem has been highlighted to you before or if it is even an issue........... I must investigate further into this issue myself because if i was to use EWI i dont think id care for rats to be tunneling into the insulation.:(:(


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    badger81 wrote: »
    I had not even thought of some of those things!!!!
    Ah crap I give up......... Beaten by a house in my head :(
    FarAdr wrote: »
    its actually ridiculous the amount of stuff that is out there. As I have stated, im trying to do a thesis on it and every day something new is found out and considerations which should be taken into account. just with the render itself, we discussed that if a child or adult even is puckin a sliotar at the wall, its small hard and fierce pressure behind it, will it damage the render and let water seep through? its a case that might not be taught of, but it happens, and then theres hanging flower baskets or something of the like, this creates holes which in turn lets water penetrate.
    Should a cavity be left behind to let water out if it does get in? and if you do leave a cavity behind, then your insulated render won't be as strong as its not on a solid substrate (wall) and can buckle and bend easier...
    There really is so much to consider, but don't believe all the bull*hit that company sales reps tell ya, cos obviously they are getting a cut and will promote their product and demote others.
    Hope ya come to a conclusion anyway!!!

    Couple of things to keep in mind.

    An EWI system is soft relative to a typical block wall. Anything that is hit against it will have alot of the energy taken out of it and it won't return with any momemtum. So although the initial strike could cause damage, the likelihood of it being multiple strikes is lessened. It's basically the same as kicking a "flat" ball against a wall. Not too many kids will do that for very long.

    Nothing of any meaningful weight should be hung off EWI. So hanging baskets or satellite dishes should be mounted elsewhere.

    You suggested leaving a cavity in the system? Where do you suggest the cavity be left? I don't believe it was clear from your post.

    As regards minor damage and water ingress. In the case of EPS insulation, I don't see any cause for concern. EPS when submerged absorbs little water. No amount of driving rain will simulate being submerged in my opinion. So you would have time to identify and repair any such damage. In the insulation materials being used water absorption may be more of an issue but I don't know enough about them to comment.

    This is my take on it. EWI systems have been used successfully in european countries for decades. Irish companies did not invent these systems, they are not new. Do they not have sporty children, rain or rodents in other parts of europe. I believe alot of "concerns" being thrown around are by poorly educated building professionals who'd rather keep doing what they've always done than adapt to something new. The same people would likely recommend drylining over EWI.

    Disclaimer: I'm building my own home and will be using EWI on it. Starting in 4 weeks all going well. I'm not a construction professional and my opinions are just that.


  • Registered Users, Registered Users 2 Posts: 534 ✭✭✭PaulieBoy


    sas wrote: »

    This is my take on it. EWI systems have been used successfully in european countries for decades.
    Tends to be a dryer climate than our constantly damp climate. That must be factored in. Constant damp will break down pretty much anything.
    All I have seen turns me right off such systems. Workmanship is dire! Pipes, gutters etc all buried behind the insulation all just sitting there waiting to cause problems, I saw an outdoor tap fitting buried behind the insulation, tap leaking! No way to fix it without doing major damage to the insulation. Mad stuff. The pricing is such that to make a living costs are being cut, I know for a fact that one supplier told potential fitters to go easy on the adhesive! It's expensive and margins are tight. It's the great new frontier for the cowboy.
    I would not touch it. Just my two cents.


  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    sas wrote: »
    Couple of things to keep in mind.

    An EWI system is soft relative to a typical block wall. Anything that is hit against it will have alot of the energy taken out of it and it won't return with any momemtum. So although the initial strike could cause damage, the likelihood of it being multiple strikes is lessened. It's basically the same as kicking a "flat" ball against a wall. Not too many kids will do that for very long.

    Nothing of any meaningful weight should be hung off EWI. So hanging baskets or satellite dishes should be mounted elsewhere.

    You suggested leaving a cavity in the system? Where do you suggest the cavity be left? I don't believe it was clear from your post.

    As regards minor damage and water ingress. In the case of EPS insulation, I don't see any cause for concern. EPS when submerged absorbs little water. No amount of driving rain will simulate being submerged in my opinion. So you would have time to identify and repair any such damage. In the insulation materials being used water absorption may be more of an issue but I don't know enough about them to comment.

    This is my take on it. EWI systems have been used successfully in european countries for decades. Irish companies did not invent these systems, they are not new. Do they not have sporty children, rain or rodents in other parts of europe. I believe alot of "concerns" being thrown around are by poorly educated building professionals who'd rather keep doing what they've always done than adapt to something new. The same people would likely recommend drylining over EWI.

    Disclaimer: I'm building my own home and will be using EWI on it. Starting in 4 weeks all going well. I'm not a construction professional and my opinions are just that.

    Yeah, your right that it is around years, in Ireland since 1966 in fact, but there are considerations that should be accounted for. Things that people don't even think about. The detailing around windows and doors, even below dpc level and at soffit level being most important.
    I'm not trying to put people off using it, I wouldn't do that, sure every product needs taught, and every product will have faults.
    With regards water ingress, that depends on what you use, sure theres wood fibre, rockwool batts, closed cell insulation such as phenolic. the first two will sag when wet and the third can warp and twist and soak up water. Its stated that if an insulation takes in 10% of its own weight in water, its performance will be reduced by 30%.
    Its also to do with dew point within the wall, moisture within the wall which can come from the inside, and this in itself can cause problems and may often not be visible.
    When it comes to cracking plaster etc, it is going to be softer, sure its not on a solid substrate, and is susceptible to cracking, and along with this, if its not correctly applied could even happen at board joints. Then theres the fact that most renders will be of a coloured nature, repairing these to the exact same colour will be problematic. I think theres a thing called freeze thaw that can affect to, have to look at it more.
    A cavity may be left between the insulation and the wall possibly, just a small one. I seen a system that uses strips of 10mm eps to create a 10mm cavity for moisture etc, but again, dependant on what your applying to, and what your applying. I have also discussed with a professional putting the cavity behind the render, so you'd probably have a cementitious board or ply to fix the render to so its solid and then a cavity and your ewi. However, the problem here is making the cavity and do you fix your timber or whatever back to the wall, creating a cold bridge, which you are trying to eliminate? Also, with the render on the boards externally, is there need for movement joints.
    There is more than you think, this is why I'm looking into it, and I myself am an Architectural Technologist, but back studying with the lack of opportunity out there.


  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    (quote)Hey FarAdr hows the Thesis coming along?

    I was talking to an architect and he was saying that the EWI may be prone to rodent attack... Dont no if this problem has been highlighted to you before or if it is even an issue........... I must investigate further into this issue myself because if i was to use EWI i dont think id care for rats to be tunneling into the insulation.
    PaulieBoy wrote: »
    Tends to be a dryer climate than our constantly damp climate. That must be factored in. Constant damp will break down pretty much anything.
    All I have seen turns me right off such systems. Workmanship is dire! Pipes, gutters etc all buried behind the insulation all just sitting there waiting to cause problems, I saw an outdoor tap fitting buried behind the insulation, tap leaking! No way to fix it without doing major damage to the insulation. Mad stuff. The pricing is such that to make a living costs are being cut, I know for a fact that one supplier told potential fitters to go easy on the adhesive! It's expensive and margins are tight. It's the great new frontier for the cowboy.
    I would not touch it. Just my two cents.

    Thesis going ok so far, its just a matter of cutting down words at this stage and put in the most relevant information. I have to make an argument at the end of the day, then I have to do research myself.. thermal imaging and stuff.
    Haven't came across the rodent thing as of yet, but I shall be looking into it, again could be useful. I think the problem ther though is how did the rats get at the insulation... I suppose below dpc would be the answer.. sure ya can't render the plinth to the foundation, or can ya...

    Think paulieboy may have hit it there with regards climate, and we all know the cowboys (heaven knows i've even worked for a few in the good times) Thats another problem with the state, there isn't proper building standards authority. I know that in the North they have a rep comes out and visits the buildings at certain stages to check workmanship. Like getting your Architect to sign off the house is just a joke to be honest, There are some good ones out there but most see that it means more work and time out of making money. Some will sign off without even looking, sure you can't see behind a closed wall... sorry ranting here.

    With regards climate though, and what works across Europe should work here, thats bulls**t. Timber cladding was seen as the future and sustainable here for the past ten years, with many buildings in Dublin and across the country being clad in untreated cedar and the likes... 'sure it'll age naturally'.. look at them buildings now, rotten, and cladding changes colour from the sun so the top of your cladding under the soffit for example is a different colour from the rest and each facade is different. Now the wood federation are looking at how to clad and writing books on what went wrong.. I was at a lecture with them last week by the way. Now they want to put it right and treat everything. This just proves that following Europe isn't always the way.
    Also, in building or doing anything in the West of Ireland is even worse, its seen to have some of the worst weather conditions in Europe, and the dampest or moistest air... It is advised not to clad tall there.
    I know thats a bit off the point but it may make some people think....


  • Registered Users, Registered Users 2 Posts: 534 ✭✭✭PaulieBoy


    FarAdr wrote: »



    Thesis going ok so far..
    Good to hear!
    You should consider going to one of the "training courses" offered by the suppliers, posing as a potential installer. It's the old "get in and out" as quick as you can to make money. The results are there to see for anybody with a keen eye. As noted "trainees" are told to use as little adhesive etc as possible as the price is now on the floor! Insulation is not supposed to get wet. I've seen houses being washed out of it with insulation exposed. Were blow heater used to dry them out before the finish was applied ? You know the answer to that !
    The system is a "hack" to insulate a building, it may work if applied correctly in the appropriate setting. It's not something you would let a cowboy builder install in a damp climate.
    I feel sorry for the honest people that are throwing their money away on this.
    Totally off topic but our damp climate is totally wrong for timber frame houses for the exact same reason, bad detailing and constant attack will see premature wood decay in the frame. It's Ireland!


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    PaulieBoy wrote: »
    Tends to be a dryer climate than our constantly damp climate. That must be factored in. Constant damp will break down pretty much anything.
    All I have seen turns me right off such systems. Workmanship is dire! Pipes, gutters etc all buried behind the insulation all just sitting there waiting to cause problems, I saw an outdoor tap fitting buried behind the insulation, tap leaking! No way to fix it without doing major damage to the insulation. Mad stuff. The pricing is such that to make a living costs are being cut, I know for a fact that one supplier told potential fitters to go easy on the adhesive! It's expensive and margins are tight. It's the great new frontier for the cowboy.
    I would not touch it. Just my two cents.

    The "our climate is different" argument is thrown around alot. I've not seen anyone produce the numbers to show the over all affect on building systems however. I don't dispute that we get alot of rain. We do get quite a bit of wind too and have a relatively mild climate which combined does contribute to the overall drying effect. If you've got something concrete on this please provide link as I'm sure the OP would find it useful for his thesis.

    The rest of what you posted is about cowboy suppliers and cowboy builders. This applies across every system. There's companies going around pumping all sorts of stuff into cavities for next to nothing and home owners are only too glad to let them do it. I've no issue with pumped cavities as long as it's a material that is suitable for it. You get my point however.


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    FarAdr wrote: »
    but there are considerations that should be accounted for. Things that people don't even think about. The detailing around windows and doors, even below dpc level and at soffit level being most important.

    By people who do you mean? I believe that there should be accountability for anything work that is carried out on a home. The detailing becomes the responsibility of the applicator and the home owner shouldn't have to worry about it. As with all systems, there are specific details (for openings as you've mentioned). The one that concerns me most with EWI systems is at door thresholds. I'm still not 100% sure how I'll detail this for my own home.
    FarAdr wrote: »
    With regards water ingress, that depends on what you use, sure theres wood fibre, rockwool batts, closed cell insulation such as phenolic. the first two will sag when wet and the third can warp and twist and soak up water. Its stated that if an insulation takes in 10% of its own weight in water, its performance will be reduced by 30%.

    I personally don't like the render systems with wood fibre. My opinion on it is if you're using it on a TF, it needs a cavity. The phenolic one has been discussed widely on various forums since it was pulled from certain IAB certs. Quoting % in a sweeping manner like you did is very misleading. Every single insulant will be affected differently by water. However, in alot of cases the materials need to be standing in water to soak it up, driving rain isn't going to do it. This needs to be clear.
    FarAdr wrote: »
    Its also to do with dew point within the wall, moisture within the wall which can come from the inside, and this in itself can cause problems and may often not be visible.
    When it comes to cracking plaster etc, it is going to be softer, sure its not on a solid substrate, and is susceptible to cracking, and along with this, if its not correctly applied could even happen at board joints. Then theres the fact that most renders will be of a coloured nature, repairing these to the exact same colour will be problematic. I think theres a thing called freeze thaw that can affect to, have to look at it more.

    In an externally insulated masonry wall, the dewpoint will most likely be out in the insulation itself, which means a well installed vapour layer will prevent any issues. The renders are semi flexible so they can take a certain amount of movement. Repairing to match the existing colour is also a problem in drying dashing for example. However with that you don't have the option of repainting to bring everything back to a clean base again. It's perfectly possible to paint EWI systems.
    FarAdr wrote: »
    A cavity may be left between the insulation and the wall possibly, just a small one. I seen a system that uses strips of 10mm eps to create a 10mm cavity for moisture etc, but again, dependant on what your applying to, and what your applying. I have also discussed with a professional putting the cavity behind the render, so you'd probably have a cementitious board or ply to fix the render to so its solid and then a cavity and your ewi. However, the problem here is making the cavity and do you fix your timber or whatever back to the wall, creating a cold bridge, which you are trying to eliminate? Also, with the render on the boards externally, is there need for movement joints.

    If you put a cavity between the insulation and the wall, the cavity will need to be ventilated assuming moisture will get to it. A ventilated cavity on the warm side of insulation renders the insulation pointless.

    Assuming it was possible to mount a render board outside EWI in a thermal bridge free manner, no one would every do it because it would be simply too expensive. I researched such systems when I was considering TF and it was cost restrictive then before you factor in combining it with an EWI system.
    [/QUOTE]
    FarAdr wrote: »
    There is more than you think, this is why I'm looking into it, and I myself am an Architectural Technologist, but back studying with the lack of opportunity out there.

    How do you know how much I know ;)

    It's an interesting topic. The impression I have from reading your posts is that it's title will be "Why not to use EWI systems in Ireland". Am I close?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    FarAdr wrote: »
    With regards climate though, and what works across Europe should work here, thats bulls**t.

    I hope you can choose more elegant language to make your point in your thesis.

    Alot of the points you put forward earlier I pointed out would be equally relevant elsewhere in Europe. Mechanical damage, rodents etc.

    As regards the climate, as I said in an earlier response, I would like to see studies to back up the claims that these systems aren't suitable. I could point to NSAI certs that say they are.

    If there is a problem with my home down the line, then I will be very vocal. I wouldn't like to see anyone get themselves in trouble, particularly with such an expensive system. I'll give Duncan a shout to take a look or have my favourite construction mag down for a look too.

    Incidently if you'd like to take a look once the job gets underway in 4 - 6 weeks time drop me a pm.


  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    PaulieBoy wrote: »
    Good to hear!
    You should consider going to one of the "training courses" offered by the suppliers, posing as a potential installer. It's the old "get in and out" as quick as you can to make money. The results are there to see for anybody with a keen eye. As noted "trainees" are told to use as little adhesive etc as possible as the price is now on the floor! Insulation is not supposed to get wet. I've seen houses being washed out of it with insulation exposed. Were blow heater used to dry them out before the finish was applied ? You know the answer to that !
    The system is a "hack" to insulate a building, it may work if applied correctly in the appropriate setting. It's not something you would let a cowboy builder install in a damp climate.
    I feel sorry for the honest people that are throwing their money away on this.
    Totally off topic but our damp climate is totally wrong for timber frame houses for the exact same reason, bad detailing and constant attack will see premature wood decay in the frame. It's Ireland!
    I think ill look into that, I'm meeting with a few suppliers this week and next to ask questions so i might ask about training.As the fella said below, cowboys are across the board for every trade and system. Sure everyone trys to jump on the band wagon for new systems.. make a few bob!! just like the tarmaccing a few years back. The solution to cowboys is to get certified fitters to install the system and keep a close eye.. They have to be insured after all. With regards what your saying about the blow heaters your right. Last week I asked a supplier about moisture already within the wall, and his solution was a dehumidifier...I know it works, but again, how do you measure it completely? I still think the external insulation is a good system if applied correctly, its getting the best overall solution for each building is the problem.
    I do however disagree with the statement on timber frame, yes if they get left open to the elements and the frames lie out in the rain without protection they will suffer, but as for heating them, this is the main benefit.. and I suppose workmanship comes into it again as everything, but the way many have been left in recent years would no doubt put people in the frame of mind that all timber frames have been left out to rot for a period of time which isn't the case.
    sas wrote: »
    The "our climate is different" argument is thrown around alot. I've not seen anyone produce the numbers to show the over all affect on building systems however. I don't dispute that we get alot of rain. We do get quite a bit of wind too and have a relatively mild climate which combined does contribute to the overall drying effect. If you've got something concrete on this please provide link as I'm sure the OP would find it useful for his thesis.

    The rest of what you posted is about cowboy suppliers and cowboy builders. This applies across every system. There's companies going around pumping all sorts of stuff into cavities for next to nothing and home owners are only too glad to let them do it. I've no issue with pumped cavities as long as it's a material that is suitable for it. You get my point however.

    There is information and facts to back up our climate and I shall have a look for them and post them. As you say every system has its cowboys.. but also every system has its flaws. Its gaining the best possible solution at that particular time for a particular budget that people aim for I think. Its like the multi foil insulations... said to be 10 times greater than all others with regards thickness... not the case, because if its compressed, it loses its air which is what it needs to perform. And in fixing it, whether it be across studs behind plasterboard or whatever, it has to be compressed in areas, so therefore its not an ideal solution. Suppose you can't always believe whats on the tin.

    Oh and just as you have said about all sorts being pumped into cavities, I worked for a fella who build a new house there and he was told by a supplier, pump the cavity with rockwool... I dont think this is advisable.. we all know it sags and when wet will shrink etc etc and measuring the amount or area which has been covered with it would be very hard... And he himself was a builder.. he was also told it performs better than 'silver beads' as I think they are called. Good salesmen could sell anything to those who do not know or investigate. Just my opinion...


  • Registered Users, Registered Users 2 Posts: 534 ✭✭✭PaulieBoy


    sas wrote: »
    As regards the climate, as I said in an earlier response, I would like to see studies to back up the claims that these systems aren't suitable. I could point to NSAI certs that say they are.
    It's not my job to convince you we live in a "damp" climate. You may consider otherwise, that's your call. The reason it get's "thrown around a lot" is because it's true! We do live in a damp climate. Fact.
    I am not saying it's not suited to a damp climate. I am saying that because it's used in Europe for years does not mean it's suited to our climate, which was the point a poster was making.
    I am not making any claims, just asking questions of those that do.
    It's an unproven system in this country at this point.
    Second, poor workmanship in hanging a door, or fitting a kitchen is one thing, poor workmanship in doing something that is critical to ensure the long life of the product is entirely another. Bad detail in this damp climate is a guarantee that you will have problems, problems that may not surface in another climate.
    If I was about to shell out thousands for a "system" I would like to be 100% sure it's the one for me. NASI certs, and some sales literature from a guy that was selling cheap electricity last week would not convince me.
    Sorry about that!


  • Subscribers Posts: 42,172 ✭✭✭✭sydthebeat


    as regards where the information is, theres plenty of meteorigical information available out there for public consumption see met eireann and other european databases.

    this data is co-related and used in software such as WUFI and used to work out condensation risks in construction build ups. Obviously this information and the way its used is only available to purchasers of the software, as it has been assessed and gathered in depth by the manufacturers...... so the information is out there.


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    Thanks syd.

    What I was looking for was information outlining how our entire climate (not just the rain component) affected systems such as EWI.


  • Registered Users, Registered Users 2 Posts: 534 ✭✭✭PaulieBoy


    sas wrote: »
    Thanks syd.

    What I was looking for was information outlining how our entire climate (not just the rain component) affected systems such as EWI.
    Sorry. I thought you had that information-your above post indicates so-and that you had actually got proof that this system is in fact up to our climate ?
    Sorry if I have that all wrong!
    Regardless, at the end of the day you pays your money and you takes your chances :-)


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    WUFI.... and I know the very fellow that has the rights to wufi in ireland. We've had lectures with him. I actually have a colleague that got a free licence from wufi for his thesis.... great programme, but very hard to learn.. that certain man isn't much help either, as he fears competition.
    Dunno if I said it before sas, but i did hear that mould can grow on certain facades... not sure which they stated.. or where it was that it happened.. could have been the west. Again not to put you off... and i got back as far as your groundworks there.... foundations were mad...


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    PaulieBoy wrote: »
    Sorry. I thought you had that information-your above post indicates so-and that you had actually got proof that this system is in fact up to our climate ?
    Sorry if I have that all wrong!
    Regardless, at the end of the day you pays your money and you takes your chances :-)

    I can point to NSAI certificates that cover this country. I don't believe I indicated anymore than that.


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    FarAdr wrote: »
    Dunno if I said it before sas, but i did hear that mould can grow on certain facades... not sure which they stated.. or where it was that it happened.. could have been the west. Again not to put you off... and i got back as far as your groundworks there.... foundations were mad...

    Yeah, it's a concern on the north facade alright. Could result in an annual clean up operation. You're not putting me off, I've built with block on the flat, I've no other option.

    Depends on how much greenery there is in close proximity to the house.

    That house that was renovated that you mentioned has had ongoing problems with it the owner told me. It's completely surround by mature trees however.

    I've actually heard this with alot of the coloured renders, not just the EWI ones.

    I can handle a bit of elbow grease type maintenance.

    Mould tends to be one of those things that sets in fast. A friend of mine finished his EWI job a year ago and nothing so far afaik. There's hope basically.


  • Subscribers Posts: 42,172 ✭✭✭✭sydthebeat


    i think you are getting 'mould' mixed up with 'moss'.

    mould is a bacterial mass indicate a rot or decay. moss can grow on surfaces after being carried from nearby vegetation by winds. Moss grows on a lot of surfaces and i wouldnt say that its a problem specific to acrylic renders, though they certainly are affected by it.


  • Registered Users, Registered Users 2 Posts: 251 ✭✭manufan16


    Hi all, very interesting reading above!

    I am building ICF soon enough and the only area that is bugging me is the external render.
    Could I have your opinions or findings from research on the idea of building a block leaf outside of the ICF rather than the render directly applied to the EPS?

    Many thanks in advance.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    manufan16 wrote: »
    Hi all, very interesting reading above!

    I am building ICF soon enough and the only area that is bugging me is the external render.
    Could I have your opinions or findings from research on the idea of building a block leaf outside of the ICF rather than the render directly applied to the EPS?

    Many thanks in advance.

    insulated concrete formwork?? its kind of a different topic in a way. Are you on about block on flat, externally insulating which in turn won't be external as your going to build another leaf? Sorry, I'm kind of lost.
    is this what your on about and then a block leaf outer?
    http://www.youtube.com/watch?v=nUoWsmRD9mA


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    sydthebeat wrote: »
    i think you are getting 'mould' mixed up with 'moss'.

    mould is a bacterial mass indicate a rot or decay. moss can grow on surfaces after being carried from nearby vegetation by winds. Moss grows on a lot of surfaces and i wouldnt say that its a problem specific to acrylic renders, though they certainly are affected by it.

    Probably, I tend to interchange the two when talking about green stuff on render.

    Thanks


  • Registered Users, Registered Users 2 Posts: 251 ✭✭manufan16


    FarAdr wrote: »
    insulated concrete formwork?? its kind of a different topic in a way. Are you on about block on flat, externally insulating which in turn won't be external as your going to build another leaf? Sorry, I'm kind of lost.
    is this what your on about and then a block leaf outer?
    http://www.youtube.com/watch?v=nUoWsmRD9mA

    hi FarAdr,
    Yes the Youtube video is the ICF construction method Im talking about with a block leaf outer, i have my construction drawings specified in the Kore system.
    They recommend the weber ext render but the feedback from my build being out to tender was some contracters proposing a 4inch block leaf on its side, tied to the EPS with a 25mm gap between EPS and Block then sand and cement finish rather than the render directly applied to the EPS.

    I hope I am not hijacking this thread but posted here as biddyearly advised early in thread that she had done a thesis on ICF and worked as a site engineer on an ICF build and ecountered problems with cracking on the ext render, that why Id like to hear opinions from posters on this thread


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    manufan16 wrote: »
    hi FarAdr,
    Yes the Youtube video is the ICF construction method Im talking about with a block leaf outer, i have my construction drawings specified in the Kore system.
    They recommend the weber ext render but the feedback from my build being out to tender was some contracters proposing a 4inch block leaf on its side, tied to the EPS with a 25mm gap between EPS and Block then sand and cement finish rather than the render directly applied to the EPS.

    I hope I am not hijacking this thread but posted here as biddyearly advised early in thread that she had done a thesis on ICF and worked as a site engineer on an ICF build and ecountered problems with cracking on the ext render, that why Id like to hear opinions from posters on this thread

    Biggest problem I've heard of it any of these renders is that they are simply not tolerant of the cold while being applied. In some cases the render needs to be applied above 4 degrees and the temps must stay above 4 degress for 48hours afterwards. I don't see too many builders willing to wait for those types of conditions.

    How are they planning to tie the block and icf?


  • Registered Users, Registered Users 2 Posts: 1,632 ✭✭✭heinbloed


    A major problem can occures with freezing temperatures. The outer surface doesn't get warm, water in it and below it(between render and EPS) freezes and deterioates the system. Ice cristalls are sharp and expand.

    The major problem here in Ireland is the ignorance of the laws of physics. The material and it's specifications are not investigated. Get the ability to withstand windload guaranteed in writing (incl. the calculation and/or independant test results) from the person who fixes the system and plasters it, from the contractor. And check the weather map for your local max. wind load meassured in the last 50 years.
    Most would run away from this exercise.

    Here are two warnings on external wall systems, well the links toward them:

    http://www.enbausa.de/daemmung-fassade/aktuelles/artikel/architekt-will-wdvs-im-neubau-verbieten-lassen-1933.html

    (the former chief of the German architects association about the freezing-and-destruction effect described above)

    and

    http://www.heise.de/tp/r4/artikel/34/34113/1.html

    ( an alarming article about the chemicals contained in the EWS, mainly the biozides, hazardous waste, incl. reputeable sources and links).

    Try google 'translate' for both articles. The former was also reported recently in the English building and construction press.
    If you need help translating phrases let me know.

    The facit of both articles is that the EWIS won't last for more than 30 years on average. And therefore are a waste of money and resources (energy). Both make a point for the monolithic wall in new builds, EWIS only to be used for renovation projects with a high energy safing potential and the economics of the exercise to be calculated for not more than 30 years.


    PS

    Here an interview with Maeckler:

    http://www.heise.de/tr/artikel/Nachhaltig-bauen-nicht-verpacken-1205269.html

    (title translated: "sustainable building instead of wrapping" )


  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    looked through them there, sent christophs office an email to see if I can get any info off him. He does seem to have a point with the whole build a building that'll last 150 years. What is tried and tested.
    There are many theories about the systems, more good than bad, but maybe it is because it hasn't been tested here too much as of yet. Time may tell. Aeroboard I think done testing here from their office which was externally insulated in 1966, and they state that its still the same.... they would though!

    It is the whole moisture thing that baffles me, its said that its been tested over europe, but as stated, we do have a damper climate. And it may open a whole can of worms..
    Systems are covered for what 30 odd years? Is it enough for something that is intended to last a lifetime, or a persons?

    Manufan16...
    There was an apartment building constructed in Ballinagh in Cavan using what you are saying but with brick on the outer facade. Didn't look into it much as it was approx 6years ago.. first I had seen of the technology. I do know that there was a house on Grand designs done with it also... could have been called the tower house or water tower... maybe if you looked it up, the constructor may have a practice or something and you could get in touch with regards directly applying the render.


  • Registered Users, Registered Users 2 Posts: 1,632 ✭✭✭heinbloed


    There is a failed EWIS exercise to be seen for the general public at Orchard Road in Cork, opposite the VW dealer.
    Cracks, mould, algea, lichens or moss.
    The building is unoccupied since it was build except for the lower floors facing the main road.
    I came across when they did the job (external insulation) and had my doubts. 2 moths ago I saw it again - almighty. Maybe now in the hands of NAMA.
    Who do banks employ to control where the morgages/ loans go ? Irish specialists for foreign methods?

    Check also Cork University hospital. There the external insulation system at the southside as well as on the westside of the new wing seem to delapitate. Parts of the new extension aren't occupied yet. Visit it, you can the see the fascade elements warping, some parts missing (taken-off for forensic inspection?).
    The job there is published in the
    Schueco book ( a fascade system company ) "Facades-Building Envelopes for the 21st Century" on page 423 (only the glass fascade shown there, the aluminia fascade covering the insulation material not done yet when going to print), ISBN 978-3-7643-9959-7. Publisher is Birkhaeuser, Switzerland.

    There are plenty of amateurs here in Ireland who do not understand what they're doing on-site.


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Lots of info etc

    But given that I am about to build in Wexford would you

    a) block-cavitiy with bead-block
    which has a U value of about 0.15 - but if you have a wider than normal cavity then you have problems inserting windows with zero cold bridge

    b) block externally insulated with Wood-fiber then render
    woodfiber used as it "breaths"
    U value of about 0.19 - but then you have issues mentioned in this artical

    Francis


  • Registered Users, Registered Users 2 Posts: 1,632 ✭✭✭heinbloed


    Fclausson asks 'what would you do?'

    If I was unfamiliar with building technologies I would ask and pay a civil engineer to answer my questions. In writing and signed.

    Using organic matter on the outside of an exposed structure will cause eternal ongoing overhead costs.


  • Registered Users, Registered Users 2 Posts: 38 FarAdr


    fclauson wrote: »
    Lots of info etc

    But given that I am about to build in Wexford would you

    a) block-cavitiy with bead-block
    which has a U value of about 0.15 - but if you have a wider than normal cavity then you have problems inserting windows with zero cold bridge

    b) block externally insulated with Wood-fiber then render
    woodfiber used as it "breaths"
    U value of about 0.19 - but then you have issues mentioned in this artical

    Francis

    Hi Francis,

    Still undesided as to what I think is the best... I'm definately nowhere near gone off the subject no matter what heinbold says. For new build, the way I look at it is I wouldn't use woodfibre... or this is my opininon for now. I have a tutor who is currently constructing a house using ewi. He himself has a masters in facades. He using a three lettered company, not hard to guess who. And he using the higher grade eps.... and using 150 of it.. as he says, it'll not get you passiv hous but it'll be damn good. And in using 150, its certified and guaranteed by the company.
    Cannot say enough how critical the detail is... and moreso workmanship!! we've all seen the best of contractors, who do great jobs... but this is specialist, and its the tiny areas that have to be looked at.
    With regards impact, the agremont certs state the conditions of impact.
    If able to, i'm going to conduct a test for my dissertation on impact and see what each system can withhold.