  • 17-09-2018 02:21PM
    #1
    Registered Users, Registered Users 2 Posts: 2,930 ✭✭✭


    Hi,

    Can anyone help me diagnose an issue I'm having in my home network please.
    Networking is not my strong suit!

    My house was built in 2009 and I had it wired with cat5e and a network point put in every room in the house.

    All the network cables terminate in the hall into a network switch. An ebay looking job, Newlink 10/100 8 port.

    I have fibre with eir. The f2000 modem is in the office. I have one of the ports on the modem connected to the ethernet port in the room which in terms feeds all the other sockets in the house through the Newlink switch.
    For info I have the main pc connected directly to the modem and get 75mpbs down 20 up

    So even though every room has a socket, the only other ethernet socket really used is the one in the sitting room the connect all the av equipment.

    In the sitting room, I have a tP ac1350 router connected to the ethernet socket. Primarily to extend the wifi in the house but it also gets me a few extra ports for the devices there.

    I recently got an nvidia shield, and its complaining of the network being too slow when pumping the media files to it.

    Not sure, if I am interpreting this correctly but I ran a speed test on the Shield and it was saying it was only getting 10mbps.

    So I am just wondering where the bottleneck might be coming from and how to fix. Happy to check other things, test etc if more info required.

    Thanks.


«1

Comments

  • Registered Users, Registered Users 2 Posts: 18,489 ✭✭✭✭banie01


    As the switch in place is 10/100 that is a potential bottleneck in that actual throughput will likely be @2/3rds of maximum.

    The likelihood is the switch is defaulting to the lower duplex speed.
    Assuming all cables and terminations are good, I'd swap the switch for a gigabit capable unit.
    That will allow fibre speed to be available to all ports.


  • Registered Users, Registered Users 2 Posts: 401 ✭✭irishbuzz


    Probably worth doing speedchecks on some of the other ethernet sockets to see if they report similar. If they are all slow then check the speed on the line going into the switch also.

    Is the nvidia shield connected via ethernet or wifi?

    [EDIT] Ah I see now (after reading banie01's post) that you mentioned Cat5e (1000Mbps) rather than Cat 5 (100Mbps). Your switch (100Mbps) is certainly limiting you then.


  • Registered Users, Registered Users 2 Posts: 2,930 ✭✭✭TechnoFreek


    banie01 wrote: »
    As the switch in place is 10/100 that is a potential bottleneck in that actual throughput will likely be @2/3rds of maximum.

    The likelihood is the switch is defaulting to the lower duplex speed.
    Assuming all cables and terminations are good, I'd swap the switch for a gigabit capable unit.
    That will allow fibre speed to be available to all ports.

    Ah excellent, thanks for the quick reply.

    Any brand, model, specs I should look out for?

    Or any gigabit switch is fine?


  • Registered Users, Registered Users 2 Posts: 36,095 ✭✭✭✭ED E


    irishbuzz wrote: »
    [EDIT] Ah I see now (after reading banie01's post) that you mentioned Cat5e (1000Mbps) rather than Cat 5 (100Mbps). Your switch (100Mbps) is certainly limiting you then.

    Thats far from certain.

    Whats clear is the link is operating at fallback 10Mbps instead of expected 100Mbps. Whether thats internal fraying, bad termination, the switch, the port OR even that the electrician did two ports per cable which means 10Mb each anyways!

    Change the switch sure as its not expensive and you should be gig, but its not guaranteed to fix the issue.
    https://www.amazon.co.uk/TP-LINK-TL-SG108E-8-Ports-Gigabit-Ethernet/dp/B00K4DS5KU/ref=sr_1_3?ie=UTF8&qid=1537192470&sr=8-3&keywords=TP+8+port


  • Registered Users, Registered Users 2 Posts: 211 ✭✭lordlame


    €25 in stock @ Powercity

    https://powercity.ie/product/SG1008


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,930 ✭✭✭TechnoFreek


    Thanks guys, just ordered a gigabit switch. will report back on once installed.

    The bit about the electrican doing two ports per cable got my attention. I don't know if that's the case but I do know he (or his apprentice) made a balls of wiring each ethernet socket back in the day. Wired them in reverse 8 to 1 instead of 1 to 8.


  • Registered Users, Registered Users 2 Posts: 2,930 ✭✭✭TechnoFreek


    lordlame wrote: »
    €25 in stock @ Powercity

    https://powercity.ie/product/SG1008

    Thanks, actually had ordered this exact same one before you linked it!


  • Closed Accounts Posts: 5,013 ✭✭✭tsue921i8wljb3


    Poor advice given here. You really should have done some diagnosis before spending money on a switch that is unsure of fixing your issues.

    Do you have a laptop? If so you should try connecting by Ethernet to each outlet you have. Assuming you are using Windows

    Right Click Network Icon on taskbar beside clock click Open Network and Internet Settings

    Network Sharing Center
    Connections
    Click Ethernet to get Ethernet Status
    Does speed say 100 Mbps or 10Mbps

    Try all ports on the Newlink and the TP link router also.

    If you are getting 100Mb connected directly to the Newlink and 10Mb through the cabling in your walls the issue is the cabling, most likely the terminations.


  • Registered Users, Registered Users 2 Posts: 24 SonicWind


    I also have the f2000 eircom modem...its only got 10/100 ethernet ports....upgrading your switch wont do a thing...your limited by the source...


  • Closed Accounts Posts: 5,013 ✭✭✭tsue921i8wljb3


    SonicWind wrote: »
    I also have the f2000 eircom modem...its only got 10/100 ethernet ports....upgrading your switch wont do a thing...your limited by the source...

    More nonsense. It actually has 1Gb ports and even if it had not 100Mb ports should not be operating at 10Mb. 100Mb should be fine for his use case.


  • Advertisement
  • Closed Accounts Posts: 4,456 ✭✭✭The high horse brigade


    SonicWind wrote: »
    I also have the f2000 eircom modem...its only got 10/100 ethernet ports....upgrading your switch wont do a thing...your limited by the source...

    No it hasn't, it has gigabit ports. Here is is bridged to my router running at gigabit full duplex

    461507.jpg


  • Registered Users, Registered Users 2 Posts: 24 SonicWind


    Sorry, my bad, mixed it up with the older model I have... must *break* this one and get one of those new ones...


  • Closed Accounts Posts: 4,456 ✭✭✭The high horse brigade


    No harm in adding a gigabit switch, it may not fix the issues though.
    A few things. Is the tP ac1350 setup as an access point or router? Have you tried bypassing it and plugging direct into the Shield?


  • Registered Users, Registered Users 2 Posts: 401 ✭✭irishbuzz


    ED E wrote: »
    irishbuzz wrote: »
    Ah I see now (after reading banie01's post) that you mentioned Cat5e (1000Mbps) rather than Cat 5 (100Mbps). Your switch (100Mbps) is certainly limiting you then.
    Thats far from certain.

    Whats clear is the link is operating at fallback 10Mbps instead of expected 100Mbps. Whether thats internal fraying, bad termination, the switch, the port OR even that the electrician did two ports per cable which means 10Mb each anyways!

    You are indeed correct. I should have said it was certainly limiting his capabilities rather than indicating it was the smoking gun of his slow connection.


  • Registered Users, Registered Users 2 Posts: 13,947 ✭✭✭✭Johnboy1951


    Hi,

    Can anyone help me diagnose an issue I'm having in my home network please.
    Networking is not my strong suit!

    My house was built in 2009 and I had it wired with cat5e and a network point put in every room in the house.

    All the network cables terminate in the hall into a network switch. An ebay looking job, Newlink 10/100 8 port.

    I have fibre with eir. The f2000 modem is in the office. I have one of the ports on the modem connected to the ethernet port in the room which in terms feeds all the other sockets in the house through the Newlink switch.
    For info I have the main pc connected directly to the modem and get 75mpbs down 20 up

    So even though every room has a socket, the only other ethernet socket really used is the one in the sitting room the connect all the av equipment.

    In the sitting room, I have a tP ac1350 router connected to the ethernet socket. Primarily to extend the wifi in the house but it also gets me a few extra ports for the devices there.

    I recently got an nvidia shield, and its complaining of the network being too slow when pumping the media files to it.

    Not sure, if I am interpreting this correctly but I ran a speed test on the Shield and it was saying it was only getting 10mbps.

    So I am just wondering where the bottleneck might be coming from and how to fix. Happy to check other things, test etc if more info required.

    Thanks.

    You did not state to what device the Shield is connected, nor whether wired or wireless.

    If it is connected to the tP ac1350 then it could be that.
    If it is connected by wireless then it could be that.
    Also as stated, it would easily be a bad connector on any of the wiring in the line back to the F2000.

    What is the max speed of your connection? 100Mb/s?


    .


  • Registered Users, Registered Users 2 Posts: 2,930 ✭✭✭TechnoFreek


    The Nvidia shield is wired and I connected it directly to the ethernet socket in the sitting room. was getting 10mbps that way.

    the ac1350 removed from the equation.

    By bad wiring, what would that look like? Anything visible? I can inspect that tonight.

    I'll also see if I can get a loan of a laptop to try troubleshoot my way back through the sockets and the newlink switch


  • Registered Users, Registered Users 2 Posts: 13,947 ✭✭✭✭Johnboy1951


    The Nvidia shield is wired and I connected it directly to the ethernet socket in the sitting room. was getting 10mbps that way.

    the ac1350 removed from the equation.

    By bad wiring, what would that look like? Anything visible? I can inspect that tonight.

    Damage might be visible, but it could be a bad connection on a wire in a connector.

    Bring something like a laptop around to all your ethernet sockets and check what the wired connection speed is.
    It might just be a problem with one of them.

    The TP AC1350 is capable of 1Gb I think.


  • Registered Users, Registered Users 2 Posts: 2,930 ✭✭✭TechnoFreek


    Thanks for all the help so far. Will do some testing and report back. Perhaps the existing switch is at fault but if not, I don't mind having spend 20 quid to replace it anyway!


  • Closed Accounts Posts: 5,013 ✭✭✭tsue921i8wljb3


    The Nvidia shield is wired and I connected it directly to the ethernet socket in the sitting room. was getting 10mbps that way.

    the ac1350 removed from the equation.

    By bad wiring, what would that look like? Anything visible? I can inspect that tonight.

    I'll also see if I can get a loan of a laptop to try troubleshoot my way back through the sockets and the newlink switch

    The back of each socket should have a connector block that the individual wires are punched down into. If one of these wires is broken, not connected or connected in the wrong order you will have issues.



  • Registered Users, Registered Users 2 Posts: 13,947 ✭✭✭✭Johnboy1951


    The back of each socket should have a connector block that the individual wires are punched down into. If one of these wires is broken, not connected or connected in the wrong order you will have issues.




    Did you watch that video? :)

    I would hazzard a guess that the keystone shown would go faulty, if it ever connected properly.
    The solid brown wire was not properly punched down! :D

    In fact the video could be used as a demo of how bad workmanship can happen when not paying attention. ;)


  • Advertisement
  • Closed Accounts Posts: 5,013 ✭✭✭tsue921i8wljb3


    Did you watch that video? :)

    I would hazzard a guess that the keystone shown would go faulty, if it ever connected properly.
    The solid brown wire was not properly punched down! :D

    In fact the video could be used as a demo of how bad workmanship can happen when not paying attention. ;)

    I did not actually. Just searched for something relevant and in HD.


  • Registered Users, Registered Users 2 Posts: 13,947 ✭✭✭✭Johnboy1951


    I did not actually. Just searched for something relevant and in HD.

    I only wondered if you had spotted it, is all. :)


  • Registered Users, Registered Users 2 Posts: 26,247 ✭✭✭✭Eric Cartman


    that newline stuff is cheap as chips, have had that exact model switch cause intermittent packet collision issues for me before , get a netgear GS108T , its 'smart' so semi managed but gigabit , a lot better and well under 100 quid. It will also show you link speeds in a web browser and help (not completely but assist in) diagnosing network cable issues.


  • Closed Accounts Posts: 5,013 ✭✭✭tsue921i8wljb3


    that newline stuff is cheap as chips, have had that exact model switch cause intermittent packet collision issues for me before , get a netgear GS108T , its 'smart' so semi managed but gigabit , a lot better and well under 100 quid.

    Ah jasus lads it's up to near a hundred now before he has even ascertained what is wrong. He has a couple of devices connected by Ethernet, it's hardly a busy network. Smart switch is complete overkill.


  • Registered Users, Registered Users 2 Posts: 26,247 ✭✭✭✭Eric Cartman


    Ah jasus lads it's up to near a hundred now before he has even ascertained what is wrong. He has a couple of devices connected by Ethernet, it's hardly a busy network. Smart switch is complete overkill.

    not when you have media devices that could do with QoS and impending faster connections , and its not like I'm telling him to buy a 500 quid layer 3 switch, its 70 odd notes for a much better environment especially with media streaming devices or a NAS.


  • Closed Accounts Posts: 5,013 ✭✭✭tsue921i8wljb3


    not when you have media devices that could do with QoS and impending faster connections , and its not like I'm telling him to buy a 500 quid layer 3 switch, its 70 odd notes for a much better environment especially with media streaming devices or a NAS.

    I don't particularly agree with you but that is our separate opinions. He really needs to ascertain what his issue is first before adding new hardware that may not solve the problem.


  • Registered Users, Registered Users 2 Posts: 14,013 ✭✭✭✭Cuddlesworth


    not when you have media devices that could do with QoS and impending faster connections , and its not like I'm telling him to buy a 500 quid layer 3 switch, its 70 odd notes for a much better environment especially with media streaming devices or a NAS.

    He has a 70mb VDSL connection and what is clearly a 10mb link back to it using his in wall cabling.

    You don't need QOS on that network, it will do nothing.
    You don't need 1 gig backbone on that network, it will do nothing.
    You don't know if he needs a new switch, your assuming he does.
    A 100mb switch doesn't do collisions. A hub or half duplex connection does.

    What he needs to do is check the wiring at both ends of the inwall cable and look at the patch leads connecting to them.


  • Registered Users, Registered Users 2 Posts: 2,930 ✭✭✭TechnoFreek


    Hey guys, bit of a an update.

    Got my hands on a laptop with a 10/100 port.I connected directly to the router, just before the switch, just after the switch and connected directly to the sitting room ethernet socket.
    All saying 100mbps in the Network and Sharing Centre.

    Ran a speed test on both the laptop and nvidia shield tv separately connected to the ethernet socket in the sitting room and through the tp router, 75 up and 20 down. Pretty much the full speed eir provide me with

    I did also click out the ethernet sockets to have a look at the wiring at the back, jiggled around, nothing seemed amiss. Didn't check that the colours were wired correctly but can I assumed if I'm getting my full fibre speed, they should be ok?

    So i'm not really sure what to say now as all seems in order.

    Also, is there a way to test the home lan speed as opposed to the broadband speed?
    I get the messages on the shield about slow network when serving media files from my nas. I checked the nas by the way and it says gigabit in its network settings.


  • Closed Accounts Posts: 4,456 ✭✭✭The high horse brigade


    Hey guys, bit of a an update.

    Got my hands on a laptop with a 10/100 port.I connected directly to the router, just before the switch, just after the switch and connected directly to the sitting room ethernet socket.
    All saying 100mbps in the Network and Sharing Centre.

    Ran a speed test on both the laptop and nvidia shield tv separately connected to the ethernet socket in the sitting room and through the tp router, 75 up and 20 down. Pretty much the full speed eir provide me with

    I did also click out the ethernet sockets to have a look at the wiring at the back, jiggled around, nothing seemed amiss. Didn't check that the colours were wired correctly but can I assumed if I'm getting my full fibre speed, they should be ok?

    So i'm not really sure what to say now as all seems in order.

    Also, is there a way to test the home lan speed as opposed to the broadband speed?
    I get the messages on the shield about slow network when serving media files from my nas. I checked the nas by the way and it says gigabit in its network settings.

    It could be the NAS. What make and model is it? To test the NAS speed copy a large file from the NAS to your laptop and take note of the speed it transferring at once it settles. Make sure both are using wired not wireless

    Did you do a speedtest on the Shield? You can get the speedtest app for the Shield from the Aptoide store
    https://en.aptoide.com/


  • Advertisement
  • Closed Accounts Posts: 5,013 ✭✭✭tsue921i8wljb3


    You can test the network using LAN Speed test or iPerf if you're feeling adventurous. You will need two machines to use these tests though.

    https://totusoft.com/lanspeed

    From what you have said the network seems OK. It might just be a configuration issue. I'm not familiar with the Shield.


Advertisement