Distribution board has 63A fuse and ESB fuse is 80A. How do I utilise the extra 17A

I have the "increased supply" (16kVA) from ESB Networks and they have confirmed to me that the fuse on the ESB side of the meter is an 80A fuse. I believe the standard fuse is a 60A fuse (12kVA supply).

The main fuse on the distribution boards is rated 63A
I have a few electric hungry devices, the two main ones being:

- Heat Pump
- Electric Car

The heat pump runs at 22.5A (it takes more starting current but it has a soft starter) and the car runs at 32A and they run daily at the same time (during night rate electricity). The car, in particular, draws a constant 32A for several hours every day. The heat pump cuts in/out as it sees fit so its "on time" is variable but they do run at the same time at least once a day.

Add in a few other devices and I am close to the main distribution board fuse which is, by default, 63A is every house.

So, my question, to all those RECI certified electricians out there is what is allowed, from a domestic regulation perspective, to "unlock" the extra 17A between 63A(on the board) and 80A(in the meter box)?

Example: Can I simply take the 40A C-Type RCBO on the distribution board that controls the car charger and wire it outside the main 63A fuse on the board? i.e. connect it direct to the supply coming into the distribution board or do I have to wire a second distribution board or what other options are there?

Note: I dont want to go down the route of priority switches. I want to utilise the 80A. I paid for it so I want to use it.

I am obviously not planning on doing this myself. I will be getting a certified electrician to do it but I want to hear what my options are before I get someone out.

The house was built in 2011 and the tails were upgraded to allow for the increased supply so I should be able to draw the 80A without burning the house down!

thanks
KCross
KCross is offline  
Advertisement
14-11-2016, 23:22   #2
2011
Moderator
 
Join Date: Apr 2009
Posts: 9,574
Has the main fuse ever blown?
2011 is offline  
14-11-2016, 23:23   #3
Tuco88
Registered User
 
Tuco88's Avatar
 
Join Date: Jul 2013
Posts: 867
It's there for good fuse discrimination, you will not be able to "tap into" into it, we'll you shouldn't and it would be very poor practice to to so.

In the event of a fault or overload you will want your 63amp mcb or fuse to trip.Allowing you to fix or reset the problem. If the 80amp goes the ESB will have to be called and paid for ,and will want to know why it happened.

You will need to look at your incomer, I'm not sure if a 100 amp supply is available.
Tuco88 is offline  
14-11-2016, 23:56   #4
KCross
Registered User
 
Join Date: May 2010
Posts: 7,917
@2011, no it hasn't blown but I don't have the car long (a few months) and the heat pump is going to be running more with the winter coming so I'm thinking it's a possibility. Would rather get ahead of it if possible.

@tuco88, I must be missing something then. If a standard connection (12kVA) with a 60A ESB fuse is the normal, what use is the increased supply (16kVA-80A) if all I can do is still just go to 60A like everyone else? The form I filled in when requesting the connection said a continuous 70A was allowed on the supply. Your response doesn't make sense to me. Can you explain what the increased supply has given me?
KCross is offline  
15-11-2016, 00:20   #5
Tuco88
Registered User
 
Tuco88's Avatar
 
Join Date: Jul 2013
Posts: 867
With a 12kva mic supply, A consumer unit will have a 50 amp followed by the ESB 63/60 amp fuse. For discrimination tails protection so on.

With a 16 kva mic supply, A consumer unit will have a 63amp followed by the ESB 80amp.

There is a 20 kva mic available and a 29 kva single phase mic available also if I remember thats a 100/125 amp ESB fuse.

Your 63amp fuse/mcb won't blow/operate at 63amps on the button it will draw more current depending on fuse/mcb characteristics.

Have you measured the loads accurately?
Tuco88 is offline  
Thanks from:
Advertisement
15-11-2016, 01:07   #6
KCross
Registered User
 
Join Date: May 2010
Posts: 7,917
Ok, I misunderstood the rating on the fuse board of a standard connection then. I thought everyone had a 63A fuse. Apparently not.

In relation to measuring the load, I know the car charger is drawing 6.6kW. The car shows me that being drawn and I have also got a kWh meter attached to it so I know that's right. It draws that power continuously.

The heat pump draws various power levels depending on demand. The best I have to calculate that is one of those clip on meters. Not sure if you'd consider that accurate but the amp figures I quoted above are from the manufactures data sheet so I presume they are reasonably accurate.

I presume I'd have to pay for the next MIC up? What work would need to be done inside the house to support it? Would the CU have to be changed?

Last edited by KCross; 15-11-2016 at 09:41.
KCross is offline  
15-11-2016, 05:17   #7
Dardania
Registered User
 
Dardania's Avatar
 
Join Date: Aug 2008
Posts: 3,573
+1 to tuco88 noting on measuring the actual draw to each appliance. And their advice generally

E.g. With the heat, the onboard display might say 6.6kw but does that account for conversion losses in the charger? So it might be a bit higher.

And for the heat pump data sheet, again the manufacturer might be noting a max demand worst care load there-the reality might be you can reduce that amount to something more reasonable. Don't some of those heat pumps have a resistive heater to boost water temperature or similar? The Laod quoted might include that. So measure the actual load - you have a split cool ammeter you are clamp on so you should be able to get a feel for it.

In practice your hair ighest load experienced will possibly be the heat pump starting up (in rush for a few secs) and the car pulling full current at the same time.
If you have a C curve MCB in the consumer unit, it should allow a bit of excess current for that start up until things settle down.
Dardania is offline  
15-11-2016, 09:41   #8
KCross
Registered User
 
Join Date: May 2010
Posts: 7,917
Quote:
Originally Posted by Dardania View Post
+1 to tuco88 noting on measuring the actual draw to each appliance. And their advice generally

E.g. With the heat, the onboard display might say 6.6kw but does that account for conversion losses in the charger? So it might be a bit higher.

And for the heat pump data sheet, again the manufacturer might be noting a max demand worst care load there-the reality might be you can reduce that amount to something more reasonable. Don't some of those heat pumps have a resistive heater to boost water temperature or similar? The Laod quoted might include that. So measure the actual load - you have a split cool ammeter you are clamp on so you should be able to get a feel for it.

In practice your hair ighest load experienced will possibly be the heat pump starting up (in rush for a few secs) and the car pulling full current at the same time.
If you have a C curve MCB in the consumer unit, it should allow a bit of excess current for that start up until things settle down.
Im confident of the car charger figures. I've an app that connects to the car and it gives realtime power graphs. I've also cross checked the total power consumed over a charge as there is a kWh meter attached to the charger. The car is definitely drawing a constant 6.6kW's for several hours at a time.

The HP during normal operation draws 40A max on startup and settles to 22.5A when running. During the very cold weather it occassionally has to supplement its power by adding in resistive heating. It is capped at 4kW extra resistive heating and in that mode its max operating current is 40A. This is a rare occurrence but it can happen which is why I think I might have a problem come the winter as that resistive heating has not been used since I got the car. I can disable the extra 4kW easy enough but I'd rather not.

With the heat pump and the car charging together I am almost certainly in the 50A+ bracket and possibly more with resistive heating added in. I think I am cutting it fine. All it would take would be an oven or something to be turned on along with the base house load for lights/TV's etc and I could blow that 63A fuse.

Is there no such thing as a 70A consumer unit fuse? That extra few Amps would be enough.

What confuses me is the section of the ESB form (NC2) which says that 70A is max allowed for a 16kVA connection. In reality it seems that 63A is the max since thats whats in the consumer unit.
https://esbnetworks.ie/docs/default-...tion-(nc2).pdf

Here is the section that describes the currents on that form
Attached Images
File Type: jpg ESB_NC2_Form.jpg (70.4 KB, 1255 views)
KCross is offline  
15-11-2016, 11:36   #9
2011
Moderator
 
Join Date: Apr 2009
Posts: 9,574
I haven't wired a domestic installation in a very long time, however I am sure that the "standard" 12 kVA 2supply has a 63A switch fuse in the main distribution board backed by an 80A ESB fuse.
2011 is offline  
Advertisement
15-11-2016, 11:50   #10
KCross
Registered User
 
Join Date: May 2010
Posts: 7,917
Quote:
Originally Posted by 2011 View Post
I haven't wired a domestic installation in a very long time, however I am sure that the "standard" 12 kVA 2supply has a 63A switch fuse in the main distribution board backed by an 80A ESB fuse.
That isnt what the ESB engineer told me on the phone yesterday. He said 12kVA supply has a 60A fuse and 16kVA supply has an 80A fuse. What you are saying is also at odds with what @tuco88 said above about 50A in CU followed by 63A. Maybe they changed their practices?

Otherwise, whats the point of paying for the increased supply?

Last edited by KCross; 15-11-2016 at 12:01.
KCross is offline  
15-11-2016, 12:50   #11
2011
Moderator
 
Join Date: Apr 2009
Posts: 9,574
Quote:
Originally Posted by KCross View Post
That isnt what the ESB engineer told me on the phone yesterday. He said 12kVA supply has a 60A fuse and 16kVA supply has an 80A fuse. What you are saying is also at odds with what @tuco88 said above about 50A in CU followed by 63A. Maybe they changed their practices?

Otherwise, whats the point of paying for the increased supply?
Like I said, it's been a while, I could be wrong
I work exclusively in the industrial sector (excuses, excuses.......)

Last edited by 2011; 15-11-2016 at 14:45.
2011 is offline  
15-11-2016, 19:35   #12
17larsson
Registered User
 
Join Date: Sep 2012
Posts: 347
2011 is right. The standard ESB 12kVa supply is 80A fuse at the supply and 63A at the customers end
17larsson is offline  
Thanks from:
15-11-2016, 20:18   #13
Dardania
Registered User
 
Dardania's Avatar
 
Join Date: Aug 2008
Posts: 3,573
Interesting wording on page 91 of this:
https://www.esbnetworks.ie/docs/default-source/publications/national-code-of-practice

...MCB of not less than 63A...

Maybe there's a higher rated MCB possible? I've seen adjustable , albeit lower current ones for precisely matching a motor overload - maybe you could get a 70A MCB?
Dardania is offline  
15-11-2016, 20:21   #14
Water John
Registered User
 
Join Date: May 2014
Posts: 14,312
One would wonder is this area being deliberately obfuscated.
Water John is online now  
Thanks from:
15-11-2016, 20:53   #15
Steve
Life is hard, deal with it.
 
Steve's Avatar
What meter have you OP?

The max I've seen direct is 63A fed with 16sq, above that you need CT's.
Steve is offline  
Post Reply

Quick Reply
Message:
Remove Text Formatting
Bold
Italic
Underline

Insert Image
Wrap [QUOTE] tags around selected text
 
Decrease Size
Increase Size
Please sign up or log in to join the discussion

Thread Tools Search this Thread
Search this Thread:

Advanced Search



Share Tweet