Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Question about MCB rating?

  • 29-10-2020 7:50am
    #1
    Registered Users Posts: 9


    Morning guys and girls :)

    What is the biggest MCB that you are permitted to use with a 10sq cable?


Comments

  • Registered Users, Registered Users 2 Posts: 1,523 ✭✭✭Lenar3556


    Ninja1000 wrote: »
    Morning guys and girls :)

    What is the biggest MCB that you are permitted to use with a 10sq cable?

    It depends on a number of factors but 40A would typically be comfortable.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    Lenar3556 wrote: »
    It depends on a number of factors but 40A would typically be comfortable.
    Indeed. And quite often 50A would be fine.

    As above it depends on how it is installed, ambient temperature, grouping and other derating factors etc. and also the maximum temperature for the switchgear and terminals it is connected to (generally 70 degrees C).