Oil boiler kicking in when timers off

Hi. I’ve a warm flow oil boiler. Runs 3 zones but water taken off it atm. Lately it’s started kicking in and running for a few minutes throughout the day and night. I’ve checked the motorised valves and all working fine. I changed room thermostat downstairs also. It works fine when turned on from the control panel. When control panel off and it kicks in by itself it doesn’t heat any of the rads so at least that’s ok. What would be next to check
Dazzler13 is offline  
Advertisement
19-01-2021, 13:35   #2
Wearb
Moderator
 
Wearb's Avatar
 
Join Date: Nov 2010
Posts: 4,941
With the recent temperatures it likely just a frost stat kicking in to protect the boiler from damage. I wouldn't expect this to be happening today.
Wearb is offline  
Thanks from:
19-01-2021, 13:41   #3
Dazzler13
Registered User
 
Dazzler13's Avatar
 
Join Date: Jan 2021
Posts: 7
Quote:
Originally Posted by Wearb View Post
With the recent temperatures it likely just a frost stat kicking in to protect the boiler from damage. I wouldn't expect this to be happening today.
Yeah it started a few weeks ago when temperatures were down but wasn’t too worried as I thought it was just the frost stat. But it never stopped
Dazzler13 is offline  
19-01-2021, 14:15   #4
Wearb
Moderator
 
Wearb's Avatar
 
Join Date: Nov 2010
Posts: 4,941
Quote:
Originally Posted by Dazzler13 View Post
Yeah it started a few weeks ago when temperatures were down but wasn’t too worried as I thought it was just the frost stat. But it never stopped
If its doing it today it needs further investigation.
Wearb is offline  
Thanks from:
19-01-2021, 20:51   #5
Tom44
Registered User
 
Join Date: Jan 2015
Posts: 871
Possible a,
Fault motorized valve (if you have zoned system) internal micro switch sticking on, even if valve is off.
Tom44 is offline  
Thanks from:
Advertisement
20-01-2021, 12:51   #6
Dazzler13
Registered User
 
Dazzler13's Avatar
 
Join Date: Jan 2021
Posts: 7
Yep. It looks like the micro switch is stuck. Thanks. I’ve got a new one different model. Only thing is that in the new one the grey wire says normally connected to boiler and pump and orange wire normally to the 230v opposite from the old one. Does it make any difference
Dazzler13 is offline  
20-01-2021, 13:15   #7
youtheman
Registered User
 
Join Date: Dec 2007
Posts: 1,100
All microswitches are wired in parallel such that any zone valve indicating open will start the boiler. So you just need to identify the pair of wires feeding the old microswitch and disconnect from your wiring centre and duplicate the wiring setup with the new valve.
youtheman is offline  
20-01-2021, 13:27   #8
Dazzler13
Registered User
 
Dazzler13's Avatar
 
Join Date: Jan 2021
Posts: 7
Quote:
Originally Posted by youtheman View Post
All microswitches are wired in parallel such that any zone valve indicating open will start the boiler. So you just need to identify the pair of wires feeding the old microswitch and disconnect from your wiring centre and duplicate the wiring setup with the new valve.
Thanks. I know it’s orange and grey on both valves it’s just that the new valve the colours are opposite to old one. So do I swap or just go with old colour wiring
Dazzler13 is offline  
20-01-2021, 13:44   #9
youtheman
Registered User
 
Join Date: Dec 2007
Posts: 1,100
It shouldn't make any difference. If you have 3 zone valves then all 3 orange should be connected to one terminal and all 3 grey to another terminal. But you can 'mix and match', e.g. orange/orange/grey on one terminal and then grey/grey/orange on the other. All 3 switches are wired in parallel for either option.
youtheman is offline  
Thanks from:
Post Reply

Quick Reply
Message:
Remove Text Formatting
Bold
Italic
Underline

Insert Image
Wrap [QUOTE] tags around selected text
 
Decrease Size
Increase Size
Please sign up or log in to join the discussion

Thread Tools Search this Thread
Search this Thread:

Advanced Search



Share Tweet