Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Electric Shower Replacement

  • 14-04-2019 5:33pm
    #1
    Registered Users, Registered Users 2 Posts: 3,133 ✭✭✭


    Hi. My Triton t90i has bitten the dust and I was hoping to replace it with a Triton 90sr as apparently they have the same footprint. The only issue is that the T90i was 8.5kw and the new model is 9kw. Would this make a difference? Don't want a fire hazard on my hands. Thanks.


Comments

  • Registered Users, Registered Users 2 Posts: 17,155 ✭✭✭✭Sleeper12


    Hi. My Triton t90i has bitten the dust and I was hoping to replace it with a Triton 90sr as apparently they have the same footprint. The only issue is that the T90i was 8.5kw and the new model is 9kw. Would this make a difference? Don't want a fire hazard on my hands. Thanks.


    All pumped electric showers are 9kw now. Technically you should have 10mm cable for 9kw but I see many electricians still using 6mm. I'd be more concerned about the size of the trip switch. You most likely have a 32amp but should have a 40amp rcbo


  • Registered Users, Registered Users 2 Posts: 3,133 ✭✭✭Mervyn Skidmore


    Sleeper12 wrote: »
    All pumped electric showers are 9kw now. Technically you should have 10mm cable for 9kw but I see many electricians still using 6mm. I'd be more concerned about the size of the trip switch. You most likely have a 32amp but should have a 40amp rcbo
    Is this suitable?


  • Registered Users, Registered Users 2 Posts: 17,155 ✭✭✭✭Sleeper12


    Is this suitable?


    Yes. That's a 40amp rcbo