Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Radiator/Hot water issue

  • 22-06-2019 7:05pm
    #1
    Registered Users Posts: 2,293 ✭✭✭


    Hi folks,

    Have a relatively new house (less than 2 years old) and it came with a Climote system. We can control the upstairs, downstairs and water separately through the system.

    In the past week, every time I try heat the water it’s turning on the rads downstairs.

    Contacted Climote and they’re of the opinion it’s a plumbing issue. Anybody got any ideas on what the issue is and if it’s an expensive fix?

    Any advice is much appreciated.


Comments

  • Registered Users Posts: 2,293 ✭✭✭All_in_Flynn


    Hi folks,

    Have a relatively new house (less than 2 years old) and it came with a Climote system. We can control the upstairs, downstairs and water separately through the system.

    In the past week, every time I try heat the water it’s turning on the rads downstairs.

    Contacted Climote and they’re of the opinion it’s a plumbing issue. Anybody got any ideas on what the issue is and if it’s an expensive fix?

    Any advice is much appreciated.


    Just bumping this to see if any advice can be offered?


  • Posts: 0 [Deleted User]


    Try turning on the heat upstairs only to see if the down stairs rads come on also.

    If they do then your zone valve for down stairs is most likely defective and would need looking at.


  • Registered Users Posts: 2,293 ✭✭✭All_in_Flynn


    gary71 wrote: »
    Try turning on the heat upstairs only to see if the down stairs rads come on also.

    If they do then your zone valve for down stairs is most likely defective and would need looking at.

    Thanks I’ll try this