Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Showers on 5 core cable?

  • 10-02-2020 4:16pm
    #1
    Registered Users, Registered Users 2 Posts: 1,611 ✭✭✭


    I'm building a house and have 3 en suites which all touch each other.

    3 instant showers 9kw each.

    House will have three phase.

    Can the electrcian wire them with 5 core 10mm or will it need 3 lenghts of 10mm t&e?

    BIG difference in price for the cable.


«1

Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    Each shower is an independent single phase load. As such it would make sense to have a cable per load. If you had a 3 phase load then a 5 core may make sense.

    The cable for each shower should be sized separately. It may not necessarily be a 10 sq. depending on a few factors (such as length of run) a larger cable size may be required.


  • Registered Users, Registered Users 2 Posts: 1,611 ✭✭✭cgarrad


    The run length (15m x 3) is the reason I wanted to try and reduce the cable cost ;-D

    So it's a definite no?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    cgarrad wrote: »
    The run length (15m x 3) is the reason I wanted to try and reduce the cable cost ;-D

    So it's a definite no?

    How do you propose to terminate a 5 core 10 sq. cable at the isolator for the first shower ?
    You won’t have enough terminals or space.


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    Can I ask why your putting in a 3 phase connection? Are you running a guesthouse or something where there is potential to run 3 showers together?

    Sorry I know I’m not helping just curious


  • Closed Accounts Posts: 3,292 ✭✭✭TheBoyConor


    Unless you have a very, very good reason to justify putting in 3p, then you should not be doing it. It costs substantially more in the long run.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    2011 wrote: »
    How do you propose to terminate a 5 core 10 sq. cable at the isolator for the first shower ?
    You won’t have enough terminals or space.

    This could work if he put a sub board up outside one of the bedrooms but would look pretty crappy. And just ran the 10sq t+e from there but if it was my house I know what I’d be doing.

    Also if cable ever fails you now have zero working showers


  • Closed Accounts Posts: 75 ✭✭Xwebstar


    TheBully wrote: »
    This could work if he put a sub board up outside one of the bedrooms but would look pretty crappy. And just ran the 10sq t+e from there but if it was my house I know what I’d be doing.

    Also if cable ever fails you now have zero working showers

    The cable wont fail but there's no saving when you factor in a sub-board and the 3P cable has to be protected at the Main DB too


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    TheBully wrote: »
    This could work if he put a sub board up outside one of the bedrooms but would look pretty crappy. And just ran the 10sq t+e from there but if it was my house I know what I’d be doing.

    True.
    But as the cable runs are only 15m it is hardly worth it.


  • Closed Accounts Posts: 3,292 ✭✭✭TheBoyConor


    Better off running 3 cables.

    A subboard introduces more complexity, additional components and more joints/connections - all additional potential failure points.

    Keep it simple stupid. Even if it does cost a bit more on cable. Sure the subboard and the labour of installing it all will eat up any saving on cable costs. It is only 15 meters anyway.

    Also, the heat will dissipate from 3 seaparate cables much easier than a 5 core one.


  • Registered Users, Registered Users 2 Posts: 1,611 ✭✭✭cgarrad


    TheBully wrote: »
    Can I ask why your putting in a 3 phase connection? Are you running a guesthouse or something where there is potential to run 3 showers together?

    Sorry I know I’m not helping just curious

    Was going with future proof, electric car and 3 showers. Think a lot of people will want it in a few years.


  • Advertisement
  • Closed Accounts Posts: 75 ✭✭Xwebstar


    Who's idea was this anyhow, there's no big saving on 45m of cable

    Sure leave out the earthrod and the main isolator they're hardly ever used


  • Registered Users, Registered Users 2 Posts: 1,020 ✭✭✭dazed+confused


    On one side there seems to be crazy spending here and penny pinching on another.

    I would relook at your priorities.

    As stated already, avoid three phase at all costs and I would also recommend a maximum of two instant showers in a house.


  • Closed Accounts Posts: 3,292 ✭✭✭TheBoyConor


    What is the reason for 3 instant showers anyway?

    Would it not make no sense to make the main bathroom an instant shower, then mixer showers in the ensuites.

    The ensuites will eb the ones most likely to be used at planned predictable times for which the HWC will be at temperature. Then for the unpredicatbel showers, visitors etc, they can use the instant shower.

    Electric showers are very expensive to run.

    Also, no power, no shower. Remember that. If you have a stove or whatever, your mixer showers will still work grand, albeit by candle light.


  • Closed Accounts Posts: 75 ✭✭Xwebstar


    I'm assuming op is making provision for car charging and maybe 3P heat pumps etc.


  • Closed Accounts Posts: 75 ✭✭Xwebstar


    An instantaneous electric shower on each phase of a domestic supply was all the fashion


    About 20 years ago..


  • Closed Accounts Posts: 3,292 ✭✭✭TheBoyConor


    I can't see that ESB will be willing to install 3p supplies into private dwellings into the future. The demand it would place on the grid would be too great.


  • Registered Users, Registered Users 2 Posts: 876 ✭✭✭TheBully


    I can't see that ESB will be willing to install 3p supplies into private dwellings into the future. The demand it would place on the grid would be too great.

    They will give it to you no problem if your willing to pay for it, nobody in their right mind would install it just for a few showers in this day and age though


  • Registered Users, Registered Users 2 Posts: 1,053 ✭✭✭Tuco88


    Are you allowed to use a common neutral over 3 showers like that? I wouldn't see it as good practice.


  • Registered Users, Registered Users 2 Posts: 34,105 ✭✭✭✭listermint


    Tbh whatever about the showers 3 phase may well be the future in construction. With the move to electrical based heating and of course the vehicles as pointed out. The expense in the long run is old thinking.


  • Registered Users, Registered Users 2 Posts: 2,789 ✭✭✭slavetothegrind


    You should really look at a plumbing solution here, much more cost effective in the long run.
    A pumped hot water supply to all three showers from afully insulated pressurised cylinder, even an electrically heated one, is a better solution.
    And only 6kw.


  • Advertisement
  • Closed Accounts Posts: 75 ✭✭Xwebstar


    Tuco88 wrote: »
    Are you allowed to use a common neutral over 3 showers like that? I wouldn't see it as good practice.

    I don't think there's any regulations that say you can't

    No benefit over 15m runs


  • Registered Users, Registered Users 2 Posts: 34,105 ✭✭✭✭listermint


    You should really look at a plumbing solution here, much more cost effective in the long run.
    A pumped hot water supply to all three showers from afully insulated pressurised cylinder, even an electrically heated one, is a better solution.
    And only 6kw.

    Not only better. But much nicer shower to use tbh. Thermostatic heads. Like a hotel.

    Tbh I don't like electric showers and I've had a few and have a brand new silent Triton there. It's nothing in comparison to my pumped system.


  • Registered Users, Registered Users 2 Posts: 17,155 ✭✭✭✭Sleeper12


    I'm in the shower repair business. Electric showers are 90 percent of my business. They are a wonderful invention. Very handy not having to heat a tank of water before getting into the shower. A energy rated. Cheaper to have a 10 minute shower in this than heating water in the cylinder by immersion or by gas. You use less water. So many positives but but they are a compromise at best.

    There is nothing like a power shower. Yes you have to heat the water first, you use more water & it's not as cheap to run as an electric shower but it's invigorating. If I were you I'd have at least One of the showers on a bar mixer. with a diverter to a rain head & connected to a 2 or 3 bar pump. At least one & maybe Two. I definitely wouldn't have Three electric showers in the house. One or maybe Two. Install a priority board so only one can be used at a time & forget about 3 Phase. There are thousands of homes in Ireland manage perfectly with an EV & electric shower without issue

    If you go down the road of Three phase you will save very little by not running three separate cables. Not a sparks here bet there is something in the regs saying that an electric shower must have it's own dedicated supply. You can't connect a bathroom fan to the supply for exapmle. I've no idea if sharing the neutral would break this rule or not. Plenty of good skarks here can answer that better than me.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Sharing the neutral won't overload the neutral anyway. Current will be that of 1 shower with 2 showers on and be 0 with 3.

    But 3 showers over 3 phases should be single phase circuits.


  • Registered Users, Registered Users 2 Posts: 1,053 ✭✭✭Tuco88


    Id be more worried with the common neutral getting broken. Less risk with a separate cable for each one.


  • Closed Accounts Posts: 75 ✭✭Xwebstar


    That risk is there for a 3P sub-board or panel in any type of installation with 1P loads

    Certainly better to avoid the sub-board here as there is no need for it


  • Registered Users, Registered Users 2 Posts: 212 ✭✭JL spark


    3 phase heat pump / Air to water ,
    Showers off that with a central pump for pressure, by far the best solution in my opinion,


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Tuco88 wrote: »
    Id be more worried with the common neutral getting broken. Less risk with a separate cable for each one.

    It wouldn't be a huge issue probably. Self monitoring etc.

    Although not ideal if one shower was on cold only


  • Registered Users, Registered Users 2 Posts: 1,053 ✭✭✭Tuco88


    Would a 3phase RCD still work correctly in such case?

    5 Core cable one phase for each shower and shared neutral across the 3...


  • Advertisement
  • Closed Accounts Posts: 75 ✭✭Xwebstar


    Tuco88 wrote: »
    Would a 3phase RCD still work correctly in such case?

    5 Core cable one phase for each shower and shared neutral across the 3...

    It's not allowed or not recommended

    I can't recall which


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    Tuco88 wrote: »
    Would a 3phase RCD still work correctly in such case?

    5 Core cable one phase for each shower and shared neutral across the 3...

    It would work, yes.


  • Closed Accounts Posts: 75 ✭✭Xwebstar


    It may also work but you'll be breaking another rule by creating a potential nuisance

    I can't remember which specific rule that is but it's there somewhere


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    Xwebstar wrote: »
    It may also work but you'll be breaking another rule by creating a potential nuisance

    I can't remember which specific rule that is but it's there somewhere

    You are correct that it isn’t permitted but that is not the question thy was asked :)


  • Registered Users, Registered Users 2 Posts: 1,053 ✭✭✭Tuco88


    2011 wrote: »
    It would work, yes.

    Once the current in, is the same as the return current so..

    I was just curious to if the current returning on the neutral would have any effect in different scenarios... As to when all or just 1 or 2 showers are on?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Tuco88 wrote: »
    Would a 3phase RCD still work correctly in such case?

    5 Core cable one phase for each shower and shared neutral across the 3...

    They do.


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    Tuco88 wrote: »
    Once the current in, is the same as the return current so..

    I was just curious to if the current returning on the neutral would have any effect in different scenarios... As to when all or just 1 or 2 showers are on?

    Assuming the circuits are all healthy the phasor sum of the currents flowing in will be opposite and equal to the currents flowing out regardless of how many showers are switched on. As such the RCD will not trip.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Tuco88 wrote: »
    Once the current in, is the same as the return current so..

    I was just curious to if the current returning on the neutral would have any effect in different scenarios... As to when all or just 1 or 2 showers are on?

    Yes the vector sum over the 3 phases and N will be 0 once no current is taking another path (earth fault).

    If the neutral was left out and the 3 neutrals of the showers connected together in a star setup, the RCD still functions properly, as the vector sum of the 3 phases are still 0 with no neutral used.

    So 3 phases to a motor with no neutral used, and an RCD will function properly to monitor the phases for residual current.


  • Registered Users, Registered Users 2 Posts: 6,256 ✭✭✭Ubbquittious


    How much to get 3 phase in a house? Opens up possibilities so it does. Be tempted to get it for fluting around


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    How much to get 3 phase in a house? Opens up possibilities so it does. Be tempted to get it for fluting around

    How long is a piece of string? There is no fixed price as there are so many variables. There is also an increased fixed fee. At this time our focus should be on reducing energy consumption and costs.


  • Registered Users, Registered Users 2 Posts: 1,053 ✭✭✭Tuco88


    Thanks for the info lads.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,611 ✭✭✭cgarrad


    So it looks like while doable the 3 single phase runs would be better.

    Thanks for all the info, way more than I expected :D


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    cgarrad wrote: »
    So it looks like while doable the 3 single phase runs would be better.

    Yes
    Thanks for all the info, way more than I expected :D

    If we see confusion we always add to it :D


  • Registered Users, Registered Users 2 Posts: 838 ✭✭✭autumnalcore


    Just had three phase removed from my house added by previous owners you'd be mad to add it. invest the money in insulation, highly insulated water/buffer tanks, solar water heating. and you won't be needing a three phase heat pump, electric showers and will save a fortune in the long run


  • Registered Users, Registered Users 2 Posts: 9,760 ✭✭✭Effects


    Be tempted to get it for fluting around

    What kind of fluting around do you want to do with 3 phase?


  • Registered Users, Registered Users 2 Posts: 1,611 ✭✭✭cgarrad


    Just had three phase removed from my house added by previous owners you'd be mad to add it. invest the money in insulation, highly insulated water/buffer tanks, solar water heating. and you won't be needing a three phase heat pump, electric showers and will save a fortune in the long run

    Had to get an upgrade as it was on a legacy 8kva, €1000 either way so mad not to get it in my eyes.


  • Registered Users, Registered Users 2 Posts: 93 ✭✭irishfire


    cgarrad wrote:
    Had to get an upgrade as it was on a legacy 8kva, €1000 either way so mad not to get it in my eyes.


    Late to the game but once it's registered as a domestic connection the standing change should be the same for single/three phase. Your only variables are Urban/Rural & 24h/Dual Tariff meter

    Obviously not the norm however so needs to be careful organised to make sure you don't end up registered as commercial, can be changed afterwards but easier to get it right from the start


  • Registered Users, Registered Users 2 Posts: 1,611 ✭✭✭cgarrad


    I just signed up thru Bonkers for the cheapest bundle, paying standard standing charge and PSO.

    14.8 cent unit rate as well.


  • Registered Users, Registered Users 2 Posts: 838 ✭✭✭autumnalcore


    cgarrad wrote: »
    Had to get an upgrade as it was on a legacy 8kva, €1000 either way so mad not to get it in my eyes.

    Fair enough thats cheap there must have already been three phase on the pole.

    8kva sounds terrible but in reality its probably fused 12kva at least at the cutout its a bit like a fair usage policy.


  • Closed Accounts Posts: 43 Xwebstar2


    Fair enough thats cheap there must have already been three phase on the pole.

    8kva sounds terrible but in reality its probably fused 12kva at least at the cutout its a bit like a fair usage policy.

    May have been an older setup

    25amp ESB fuse was common in old houses


  • Closed Accounts Posts: 1,069 ✭✭✭Xertz


    3P makes sense in most continental countries because that’s how they’ve opted to load balance on their networks. ESB just always preferred hefty single phase connections, even where 3P is available.

    Single phase in say Spain is often limited to 16amps, which is ridiculously small. I know I had that in a studio apartment and tripped the main breaker quite regularly. In Ireland single phase is pretty beefy.

    My view of it is you’re introducing a lot of unnecessary complexity and cost.

    Also definitely consider a modern hot water storage system with a heat pump and solar inputs. You’ll have much more pleasant showers.

    A lot of the calculations around immersions being hugely inefficient are based on the old copper tanks, which are ludicrously badly insulated and the use of just a resistance element.

    A good tank is almost like a thermos flask and you’ll get very, very little heat loss, if it’s installed correctly. Add a pump and you’ll have very good water pressure and far more luxurious showers.

    Also if you’re using locally pumped electric power showers they are very noisy. Whereas a central pump (well located and isolated on an anti vibration pad) is likely to be far less annoying.

    Just be very aware of where you site the pump.

    Ours is in a basement and you wouldn’t really know it’s running at all. However some are located right in the middle of the bedroom areas with a hot press. Definitely creates extra noise.

    Also bear in mind a hot press with a modern hot water heater will neither have space to store towels nor will it be hot. They’re fridge freezer sizes units and they don’t bleed heat so, you’ll just have a big appliance in a press. If you can site or somewhere like a ground floor, a garage or a basement it makes a lot more sense noise wise.


  • Advertisement
Advertisement