Luke warm water from tank

  • 15-06-2014 08:37AM
    #1
    Registered Users, Registered Users 2 Posts: 635 ✭✭✭


    Hi there,

    I have recently had a plumber install a new boiler and EPH contols T37.

    I have a simple question I can't seem to find the answer to the manuals.
    My hot water cylinder is connected to zone one via a wired EPH WRP cylinder stat.

    Should I see the cylinder temp showing up on my control panel, as I do not?
    The only ones that show up are the ones connected wirelessly (ZONE 2 + 3)
    The boiler fires up and the water is heated, but after 1.5 hours its still only lukewarm. Cylinder stat is set to 65 degrees so it should be much hotter!!


    Many thanks


Comments

  • Registered Users, Registered Users 2 Posts: 25 Leaksireland


    It's probably best to call the plumber as they have the best understanding of your system


  • Registered Users, Registered Users 2 Posts: 1,492 ✭✭✭roy rodgers


    jusmeig wrote: »
    Hi there,

    I have recently had a plumber install a new boiler and EPH contols T37.

    I have a simple question I can't seem to find the answer to the manuals.
    My hot water cylinder is connected to zone one via a wired EPH WRP cylinder stat.

    Should I see the cylinder temp showing up on my control panel, as I do not?
    The only ones that show up are the ones connected wirelessly (ZONE 2 + 3)
    The boiler fires up and the water is heated, but after 1.5 hours its still only lukewarm. Cylinder stat is set to 65 degrees so it should be much hotter!!


    Many thanks[/QUOTE

    I would install about 2 of them EPH controls packs a week.
    and I have come across a few faulty cylinder stats in my time that are closing the motorized valve when the water is only luke warm.
    The stat will need to be replaced I'd say.

    you don't see the temperature on the programmer for the water with that type of stat it would have to be a RF stat and programmer.