Closing cavity around window opening before fitting

2»

Comments

  • Registered Users, Registered Users 2 Posts: 9 Doingit


    Is it absolutely necessary to close the cavity before installing the windows? Wondered if we could install windows, apply airtight tape to inside (between frame and black) and then pump cavity right up against the frame! Would this work? Would it just move the dpc out of position?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Doingit wrote: »
    Is it absolutely necessary to close the cavity before installing the windows? Wondered if we could install windows, apply airtight tape to inside (between frame and black) and then pump cavity right up against the frame! Would this work? Would it just move the dpc out of position?

    the closure is needed as you need to strap the window back - you would normally do it to the inner wall - but that might be 200mm away - so you attached ply to block - window to ply

    https://www.facebook.com/media/set/?set=a.165903723614740.1073741829.154344008104045&type=3


  • Registered Users, Registered Users 2 Posts: 37 john f 4g63


    Doingit wrote: »
    Is it absolutely necessary to close the cavity before installing the windows? Wondered if we could install windows, apply airtight tape to inside (between frame and black) and then pump cavity right up against the frame! Would this work? Would it just move the dpc out of position?

    I am thinking of doing the window detail this way as at least the pumped insulation will fit nice and snug up against the window and there will be no insulation gaps.
    In order to get over the problem of fitting the windows in my 200mm cavity, my window thickness is 82mm therefore leaving a gap of 118mm to the internal leaf. As this is too wide for the window straps i am fixing a 3x2 on to the internal leaf in the cavity, the straps from the window can then be fixed to the 3x2 timber and will also just make the internal leaf so can be fixed to that as well.
    I will then use the air tight tape to stop the beads when pumping the cavity. This way i know the insulation will be fitted right up to my window and reveals.

    Well that's the plan anyway!! :)


  • Registered Users, Registered Users 2 Posts: 120 ✭✭dfader


    I am thinking of doing the window detail this way as at least the pumped insulation will fit nice and snug up against the window and there will be no insulation gaps.
    In order to get over the problem of fitting the windows in my 200mm cavity, my window thickness is 82mm therefore leaving a gap of 118mm to the internal leaf. As this is too wide for the window straps i am fixing a 3x2 on to the internal leaf in the cavity, the straps from the window can then be fixed to the 3x2 timber and will also just make the internal leaf so can be fixed to that as well.
    I will then use the air tight tape to stop the beads when pumping the cavity. This way i know the insulation will be fitted right up to my window and reveals.

    Well that's the plan anyway!! :)
    John,
    Interesting... seems like a reasonable low cost solution. Only thing I'd be concerned about is bead going in between the DPC and outer leaf. If you had PIR friction fitted between inner leaf and DPC on outer leaf this would not happen, but maybe I'm just coming up with a problem that does'nt exist because the DPC will be held tight enough once mortared over at cill and windows in? Would be good to see how this goes for you - post up a pic when done


  • Subscribers Posts: 42,921 ✭✭✭✭sydthebeat


    I am thinking of doing the window detail this way as at least the pumped insulation will fit nice and snug up against the window and there will be no insulation gaps.
    In order to get over the problem of fitting the windows in my 200mm cavity, my window thickness is 82mm therefore leaving a gap of 118mm to the internal leaf. As this is too wide for the window straps i am fixing a 3x2 on to the internal leaf in the cavity, the straps from the window can then be fixed to the 3x2 timber and will also just make the internal leaf so can be fixed to that as well.
    I will then use the air tight tape to stop the beads when pumping the cavity. This way i know the insulation will be fitted right up to my window and reveals.

    Well that's the plan anyway!! :)


    are you sure youre allowed to provide a combustible cavity barrier in an cavity?
    I dont think you are.


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    sydthebeat wrote: »
    are you sure youre allowed to provide a combustible cavity barrier in an cavity?
    I dont think you are.

    +1


  • Registered Users, Registered Users 2 Posts: 37 john f 4g63


    sydthebeat wrote: »
    are you sure youre allowed to provide a combustible cavity barrier in an cavity?
    I dont think you are.

    Is it the 3x2 timber you are referring to? If so do you know why?


  • Registered Users, Registered Users 2 Posts: 120 ✭✭dfader


    How about friction fitted pir between 3x2 and dpc and doubled up plasterboard over reveal


  • Subscribers Posts: 42,921 ✭✭✭✭sydthebeat


    Is it the 3x2 timber you are referring to? If so do you know why?

    The fire regulations, the prevention of spread of fire and smoke in cavities require non combustible cavity closers.

    From a personal point of view, I hope your Windows are fixed through your 3x2 into the blockwork or there is a risk of failure of fixing in the event of a fire.

    If the 3x2 has been covered in non combustible material ie plasterboard with min 30mins fire rating then I think you may be ok, I'd need to check it.

    But i think people should be looking at non combustible methods to close cavities in a wide cavity situation.


  • Registered Users, Registered Users 2 Posts: 120 ✭✭dfader


    sydthebeat wrote: »
    are you sure youre allowed to provide a combustible cavity barrier in an cavity?
    I dont think you are.

    Hmm forgot bout that. how about friction fitted pir between 3x2 and dpc and doubled up plasterboard over 3x2 and reveal


  • Advertisement
  • Subscribers Posts: 42,921 ✭✭✭✭sydthebeat


    dfader wrote: »
    Hmm forgot bout that. how about friction fitted pir between 3x2 and dpc and doubled up plasterboard over 3x2 and reveal

    Sounds good, does your frame allow for that thickness?


  • Registered Users, Registered Users 2 Posts: 120 ✭✭dfader


    sydthebeat wrote: »
    Sounds good, does your frame allow for that thickness?
    he should step back the blockwork on inner leaf maybe 30mm to allow for this


  • Registered Users, Registered Users 2 Posts: 37 john f 4g63


    dfader wrote: »
    How about friction fitted pir between 3x2 and dpc and doubled up plasterboard over reveal

    That is another option I am considering as the pir has a better u value then the bead but the only reason I didn't want to do it this way is this must be done before the windows are fitted so this might leave a small gap between both. I know they usually pump foam in here then but I am hoping a avoid this.


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    That is another option I am considering as the pir has a better u value then the bead but the only reason I didn't want to do it this way is this must be done before the windows are fitted so this might leave a small gap between both. I know they usually pump foam in here then but I am hoping a avoid this.

    the window boys will have a spray foam - now make sure you get the really good stuff - but it has a good U-value - no idea on name - but mine is a blueish colour


  • Registered Users, Registered Users 2 Posts: 37 john f 4g63


    dfader wrote: »
    he should step back the blockwork on inner leaf maybe 30mm to allow for this

    Hadn't mentioned on earlier post but will be finishing the internal reveals with plaster slab all around.
    Do you think if I used a fire slab here it would be ok or is the problem still there over having a 3x2 in my cavity?

    Just to answer the question about where the window straps will be fitted... They will be fixed to both 3x2 and the internal block work.


  • Registered Users, Registered Users 2 Posts: 37 john f 4g63


    fclauson wrote: »
    the window boys will have a spray foam - now make sure you get the really good stuff - but it has a good U-value - no idea on name - but mine is a blueish colour

    Does the pir insulation have to be used around windows and then spray foam the gap as I know this is what most do or would it be ok just to let the beads pump right up against the window?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    come on FC you know better than that


  • Registered Users, Registered Users 2 Posts: 35 adrianegan3


    Did you have to step back the inner block work 12mm to allow for the plywood


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    You need to step back the inner leaf enough to get both your insulation and your ply

    see picture


    432581.jpg


  • Registered Users, Registered Users 2 Posts: 35 adrianegan3


    fclauson wrote: »
    You need to step back the inner leaf enough to get both your insulation and your ply

    see picture

    Thanks for that great detail drawing any advise on where I could more detailed photos and info on passive build . Books etc


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Suggest you

    a) join the Passive Institute Ireland
    b) follow https://twitter.com/ElrondBurrell
    c) google "passive house"
    d) don't ever take "asha that will work probably!" as a response to any question
    e) be very nerdy about detail, maths, design, and implementation

    follow my 4 Ps when building
    Pragmatic
    Practical
    Passive Certified
    Price Sensitive


  • Registered Users, Registered Users 2 Posts: 54 ✭✭ExtaticFob


    Hi all. Looking for some advice as a first time self builder who may have made a bags of cavity closing around our windows. Keeping it short, we have our cavity fully filled with 150mm insulation and windows are in. We don’t have cavity closets installed. We do have the gap filled with expandable foam. Question is, do we need to take the windows out to put the closers in? I’ve attached pics. Any help / advice greatly appreciated.


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    can we have a pic from the outside too

    expanding foam is not airtight - what air tightness are you going for


  • Registered Users, Registered Users 2 Posts: 54 ✭✭ExtaticFob


    fclauson wrote: »
    can we have a pic from the outside too

    expanding foam is not airtight - what air tightness are you going for

    Thanks for the reply. We’re going to be taping inside with air tightness tape. We’re also putting an insulated board on it. That might not answer your question but there’s a lot of learning as we go. Requested photo attached.


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    ExtaticFob wrote: »
    Thanks for the reply. We’re going to be taping inside with air tightness tape. We’re also putting an insulated board on it. That might not answer your question but there’s a lot of learning as we go. Requested photo attached.

    Ok - see my tech arch picture further back in this post
    you need to look at how you are going to make it
    a) insulated correctly with no cold bridge around the window (this will require thermal modelling probably)
    b) airtight

    if you fail on (a) you could end up with a cold bridge (read mold) around the wind frame on the window return because the wall/frame fall below the threshold temp

    read about FRSI in the (google FRSI calculations)


  • Registered Users, Registered Users 2 Posts: 54 ✭✭ExtaticFob


    fclauson wrote: »
    Ok - see my tech arch picture further back in this post
    you need to look at how you are going to make it
    a) insulated correctly with no cold bridge around the window (this will require thermal modelling probably)
    b) airtight

    if you fail on (a) you could end up with a cold bridge (read mold) around the wind frame on the window return because the wall/frame fall below the threshold temp

    read about FRSI in the (google FRSI calculations)

    I’ll check that out. Thanks again. In your experience is there a way around this without removing the windows? As well as the inconvenience, we are getting the external wall plastered from tomorrow.


  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    ExtaticFob wrote: »
    I’ll check that out. Thanks again. In your experience is there a way around this without removing the windows? As well as the inconvenience, we are getting the external wall plastered from tomorrow.

    It’s jot clear if there is a DPM/EPDM folded out over/down side of the windows etc?
    Did your eng/arch do a detailed drawing done