  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    Capacitor is weak means motor is weak?

    Hmmm somehow I don't think so.

    Sorry Jack, If I've come across wrong again, but I was only explaining to OP in layman terms.
    Hold the motor shaft, in my experience if the strength of the motor is weak ( different levels of weakness )
    If capacitor is below 2 uf you'd hold/stop it with your little finger.
    OP stated that shaft on oil pump turned freely but sometimes motor didn't it just hummed , but ran freely when it had no load with the oil pump removed, Most likely cause is capacitor, I just gave him simple DIY testing advice.
    As he's only a DIY 'er,

    Yes, we ourselves can get more technical where explaining things to each other, which is good, and helpful.

    Sorry if caused confusion.
    Lets talk politics, it's safer than capacitor.!
    Thanks.


  • Posts: 3,858 ✭✭✭ [Deleted User]


    Wearb wrote: »
    Be glad it wasn't capacitors ;)
    Look at the trouble they can cause.

    Who would want Gary's job with us lot around stirring it :(

    Don't worry i'v been watching a box set of Jeremy Kyle.

    So I figured out: arguing or contributing to a on going argument will end in tears.

    Exchanging the vast knowledge that is obviously out there in a caring and sharing manor will lead to good karma for all.

    But if we could make sure the OP is sorted before the games begin then that would be lovely.


  • Moderators, Home & Garden Moderators Posts: 6,562 Mod ✭✭✭✭Wearb


    gary71 wrote: »
    Don't worry i'v been watching a box set of Jeremy Kyle.

    So I figured out: arguing or contributing to a on going argument will end in tears.

    Exchanging the vast knowledge that is obviously out there in a caring and sharing manor will lead to good karma for all.

    But if we could make sure the OP is sorted before the games begin then that would be lovely.

    Amazingly all the OP's questions have been answered here and no more help can be given to him until he rules out corrections that have been suggested to him. .................... hmmmmm lovely smell of roast beef coming from the kitchen..........Im off. :pac:


  • Registered Users, Registered Users 2 Posts: 4,013 ✭✭✭jimf


    Wearb wrote: »
    Be glad it wasn't capacitors ;)
    Look at the trouble they can cause.

    Who would want Gary's job with us lot around stirring it :(

    May god forgive you for suggesting that stirrers frequent this forum I would suggest your magna didn't work last nite and there is still a lot of sludge left over after all that Guinness


  • Posts: 3,858 ✭✭✭ [Deleted User]


    Wearb wrote: »
    Amazingly all the OP's questions have been answered here and no more help can be given to him until he rules out corrections that have been suggested to him. .................... hmmmmm lovely smell of roast beef coming from the kitchen..........Im off. :pac:

    There is no conclusion yet and in fairness to the OP how many posts should be on his thread after he last posted by the time he comes back?

    If a question has been answered then I think there's a bit of freedom to go off topic if we're mid fault finding then we should stay on topic and wait for the OP to come back.


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,562 Mod ✭✭✭✭Wearb


    jimf wrote: »
    May god forgive you for suggesting that stirrers frequent this forum I would suggest your magna didn't work last nite and there is still a lot of sludge left over after all that Guinness

    At least it wasn't pumping over. :D

    Ok Gary, that's my last off topic comment...................at least on this thread.


  • Registered Users, Registered Users 2 Posts: 29 JABKELL


    Wearb wrote: »
    You are right about it being an inefficient way to use it. Yes it is probably that small cylinder (photo?) It is strange that it runs when you do that and will not start when left longer. It needs investigating, but the capacitor is a cheap enough item to try anyway. Just be careful with the contacts, they can pack a wallop if charged. Your multimeter may not have a capacitance meter on it. It is measured in Micro Farads (symbol a bit like yF).

    Might just be a sticking pump. Was there any suggestions as to why the previous pump failed?

    I was told by a plumber, a neighbour of mine that the pump needed to be replaced because the boiler and locked out and wouldn't restart. That was last January. Since this recent problem two weeks ago, he has tried the new control box and wired connection to the fuel pump. This guy reckons the motors don't usually give trouble and suggested it may need a new fuel pump. The boiler is dated 1997. I've been living in house the past 7 years and last January was the first time the boiler, fuel pump gave any problems. So the previous fuel pump had been there for 6 years+.


  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    Motor doesnt give a lot of problems other than bearing which are normally apparent by the noise before giving up, the Capacitor is very common, and pumps are at times finicky and very reliant on good fuel.


  • Registered Users, Registered Users 2 Posts: 29 JABKELL


    scudo2 wrote: »
    Sorry about this JARBELL
    Just check motor strength as I've explained, if its weak try a new capacitor.
    If not call good service engineer. Ask boiler manufacture or oil company for somebody local and good, or tell us where you live and one of us might be able to help.
    Let us know how you get on. Ta

    scudo2 I think I'll get a new capacitor tomorrow and try that, especially as there inexpensive and I know the one on my burner hasn't been changed in at least 7 years.(it could be the original).

    Based in Co. Meath.


  • Registered Users, Registered Users 2 Posts: 29 JABKELL


    jimf wrote: »
    For your sake hope it is just a capicator but if not then pump would be next to eliminate after that motor bearings would also be a possibility. Ive had 3 riello 40 series with fcuked motor bearings this week

    jimf I checked the motor bearings when I had the burner out,( fuel-pump out and fan housing off). They seemed fine to me with no play or signs of breakdown.when I do get the burner running as described (bit of fiddling)there is no noticeable bearing noise.


  • Advertisement
  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    JABKELL wrote: »
    scudo2 I think I'll get a new capacitor tomorrow and try that, especially as there inexpensive and I know the one on my burner hasn't been changed in at least 7 years.(it could be the original).

    Based in Co. Meath.

    Good service engineer in Athboy if your stuck.
    PM. crock! " Its his name here."

    But his Mammy named him David.
    He also does a 20% discount if you mention me !!!!!

    Best of luck and let us know how you get on.
    Thanks


  • Registered Users, Registered Users 2 Posts: 4,013 ✭✭✭jimf


    scudo2 wrote: »
    Good service engineer in Athboy if your stuck.
    PM. crock! " Its his name here."

    But his Mammy named him David.
    He also does a 20% discount if you mention me !!!!!

    Best of luck and let us know how you get on.
    Thanks

    You get 30% if you don't mention him at all


  • Registered Users, Registered Users 2 Posts: 29 JABKELL


    jimf wrote: »
    You get 30% if you don't mention him at all

    LOL :D
    I say nothing so !!!


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    He's based near Kells, not Athboy. Sure he would like to help if needed, discounts were not authorised with him, any interaction as such should be kept too PM only.

    Yelling discounts got you in hot water before, that an end to it, see you in a week.


  • Registered Users, Registered Users 2 Posts: 29 JABKELL


    Well today i went and got a capacitor,(the original one in the burner is dated 1997) fitted the new one but the problem persists. Fiddled around to get the boiler restarted, I knocked on and off the boiler a few times and did notice a strange sound as the fuel pump/motor slowed down. Thinking now I may need to get a new fuel pump. I didn't seem to get long out of the last one, its only in 11 months!! Or maybe contact a good service engineer as suggested above.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    JABKELL wrote: »
    Well today i went and got a capacitor,(the original one in the burner is dated 1997) fitted the new one but the problem persists. Fiddled around to get the boiler restarted, I knocked on and off the boiler a few times and did notice a strange sound as the fuel pump/motor slowed down. Thinking now I may need to get a new fuel pump. I didn't seem to get long out of the last one, its only in 11 months!! Or maybe contact a good service engineer as suggested above.

    In my opinion, you should get a service engineer in as a fuel pump needs to be set to the correct working pressure to suit the make & model boiler. It would also avoid costly plug & play fault finding. With a vacuum gauge a partial blockage in the line be the cause of the failing pumps or water in your oil tank. A decent service engineer will be able to identify all of these. Problem could also be a motor issue.


  • Moderators, Home & Garden Moderators Posts: 6,562 Mod ✭✭✭✭Wearb


    JABKELL wrote: »
    Well today i went and got a capacitor,(the original one in the burner is dated 1997) fitted the new one but the problem persists. Fiddled around to get the boiler restarted, I knocked on and off the boiler a few times and did notice a strange sound as the fuel pump/motor slowed down. Thinking now I may need to get a new fuel pump. I didn't seem to get long out of the last one, its only in 11 months!! Or maybe contact a good service engineer as suggested above.

    You never got an explanation as to why the last pump gave up the ghost. Sometimes it is impossible to figure it out, but it is always necessary to thoroughly investigate it, because of the cost of the pump and likelihood of the new one also going the same way. I suppose in hindsight, it would have been better to have had a good boiler service person out originally, but if we all could see the future we would never make mistakes.

    If it is the pump that's gone. Ask yourself these questions; do you regularly lift up back of tank to get last out of it? Do you buy small amounts and run out often? Do you buy from reputable sources? Have you a good quality filter on your tank? Has your tank been checked for water? etc.etc.


  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    To be honest if its the original Mectron burner i would think about replacing it rather than throw money at it.


  • Registered Users, Registered Users 2 Posts: 4,013 ✭✭✭jimf


    I'd be leaning towards motor bearings at this stage if the burner slowed noticeably at full revs not all bearings start noising before failure I could be wrong I was wrong once before I think twas back in 1995 I said yes when I should have said no


  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    Tut tut!! humour :eek: toys will be thrown. :(


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,013 ✭✭✭jimf


    Tut tut!! humour :eek: toys will be thrown. :(

    Omg am I going on holidays


  • Registered Users, Registered Users 2 Posts: 249 ✭✭crock!


    jimf wrote: »
    Omg am I going on holidays
    Hello guys
    Im going to see this boiler on sat morning and i suspecked its the pump from further info with client.he says boiler smells off unburned fuel that wasnt there before.pump is week. Pump was changed in jan this year so i will check for water in tank.the burner is rbl but as far as i know there is shrowd around this burner which is a g5.to put in change a burner which is what i would perfer because of age wouldnt i be better with an rdb2.2 rather than changeing it to rbl which would be hassle trying to make it fit.i could make it back into bf with no hassle with rdb.
    What do ye think?


  • Registered Users, Registered Users 2 Posts: 4,013 ✭✭✭jimf


    if you haven't seen it yourself crock maybe your jumpin the gun a bit how does customer know pump is weak

    could be something as simple as low fuel pressure or gammy nozzle

    was it serviced when pump was changed and set up properly

    it might be just poor combustion over the last few months had 1 last week and the fumes would cut the eyes out of you

    customer could have been playing with it himself we know they say I never touched it in me arse they dont


  • Registered Users, Registered Users 2 Posts: 249 ✭✭crock!


    jimf wrote: »
    if you haven't seen it yourself crock maybe your jumpin the gun a bit how does customer know pump is weak

    could be something as simple as low fuel pressure or gammy nozzle

    was it serviced when pump was changed and set up properly

    it might be just poor combustion over the last few months had 1 last week and the fumes would cut the eyes out of you

    customer could have been playing with it himself we know they say I never touched it in me arse they dont

    He told me it was serviced by a guy who changed the nozzle once in three years.of course some one could of fiddled with it but that wouldnt give an intermitten fault on a start up with an unusual noise.he says when it wont start that he bleeds it and then it starts after doing this once or twice.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Sounds like a riello R40 G5BF shrouded.HWOS have one 15-26kw,maybe not big enough,expensive though


  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    crock! wrote: »
    He told me it was serviced by a guy who changed the nozzle once in three years.of course some one could of fiddled with it but that wouldnt give an intermitten fault on a start up with an unusual noise.he says when it wont start that he bleeds it and then it starts after doing this once or twice."

    What nozzle is in it and is that whats always been in it ?

    The later Statesman 70/90 did come with a RDB1.


  • Registered Users, Registered Users 2 Posts: 249 ✭✭crock!


    agusta wrote: »
    Sounds like a riello R40 G5BF shrouded.HWOS have one 15-26kw,maybe not big enough,expensive though

    Hwos ?


  • Registered Users, Registered Users 2 Posts: 4,013 ✭✭✭jimf


    crock! wrote: »
    He told me it was serviced by a guy who changed the nozzle once in three years.of course some one could of fiddled with it but that wouldnt give an intermitten fault on a start up with an unusual noise.he says when it wont start that he bleeds it and then it starts after doing this once or twice.

    could be a lot of things is the customer far from you

    partially blocked filter maybe vacuum gauge would tell you a lot


  • Registered Users, Registered Users 2 Posts: 4,013 ✭✭✭jimf


    crock! wrote: »
    Hwos ?


    heating world of spares


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 249 ✭✭crock!


    jimf wrote: »
    could be a lot of things is the customer far from you

    partially blocked filter maybe vacuum gauge would tell you a lot
    No he isnt far from me.he says filter had a bit crap on it.i will check it for flow of oil.i think its water in tank damaged pump.new pump put in in jan