Garage Consumer Unit Question - DIY Solar.

  • 03-04-2025 12:01PM
    #1
    Registered Users, Registered Users 2 Posts: 713 ✭✭✭


    Afternoon folks.

    Question about running a 6mm sq SWA cable between house and shed. My array will be max of 4kW (Inverter is a dual MPPT Solis 4kW) and installed on the garage roof and on the front wall. Array 1= Roof is ~20 degrees. Array 2 = Wall, 90 degrees. I will get my electrician to install a mini consumer unit in garage. An isolator switch for the board and also one 6A MCB for led lights, one for sockets (13A max, small work tools etc) and one for Inverter.

    My question is, is it just a 3 core cable to connect the garage to the house CU? Not a 5 Core etc? For example, the inverter MCB DOES NOT need to connecting to the house CU and then the House CU connections to the Garage Board separately using the other cores in the 5 core cable?

    House to Garage Solar.png

    Is the attached diagram correct?

    Note, no fireman's switch in garage as its 30M from house. Data cables will be ran also. Will need to get creative with the Inverter Clamp connection between shed and ESB Meter Tails. I have already an Eddi, Zappi and Harvi in operation.

    Thanks in advance.



Comments

  • Registered Users, Registered Users 2 Posts: 713 ✭✭✭bunderoon


    Anyone dealt with similar?



  • Moderators, Home & Garden Moderators Posts: 7,074 Mod ✭✭✭✭graememk


    Mines is down in the farmyard connected to the CU there.

    It actually goes from house CU to first yard CU then to the barn CU, solar is connected to the barn CU.

    My Solar is on a RCBO not a MCB, but as you have a RCBO in the house that should cover it.

    You may run into tripping issues on a 30mA rcbo, some solar rcbos are being changed to 100mA ones



  • Registered Users, Registered Users 2 Posts: 694 ✭✭✭JohnySwan


    I would go 10sq minimum from the house. Lose the rcbo feeding the garage for a double pole mcb, give the inverter its own double pole, bi directional rcbo. 100ma as pointed out above.



  • Registered Users, Registered Users 2 Posts: 713 ✭✭✭bunderoon


    Hey @graememk and @JohnySwan

    1. To protect the 10sq as it will be under ground, then into my attic, shouldnt it need protection? I assume an RCBO and if so, a 100mA as to avoid cascading issues as the Garage CU will have 32A 30mA RCBOs for Sockets (Patio and Garage) and the solar inverter RCBO will be 100mA as advised by Solis.

    I have updated my diagram.

    House to Garage Solar.png


  • Registered Users, Registered Users 2 Posts: 694 ✭✭✭JohnySwan


    An MCB is the normal method to supply a sub board.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 713 ✭✭✭bunderoon


    I've an electrician to do the AC side for me, but he isnt a solar installer. Thankfully he will be signing the NC6.

    Also, do I need a CT cable from the Inverter to the House CU or Meter?

    I have a Zappi and Eddi. Heat water and charge car between 2am and 5am. I have two CT clamps on the Harvi and the eddi is the v2 so it is the 'hub'. I have set up the first clamp in reverse so I can see what power I am using from the grid. Works well the last years since installed. The second harvi clamp is pointing towards grid and I have the solar Icon on the myenegi App, waiting for when the electrician does the AC. Do I need a Solis CT clamp? I dont have a battery or hybrid inverter.



  • Registered Users, Registered Users 2 Posts: 713 ✭✭✭bunderoon


    Besides the RCBO being more expensive, I assume there is no harm in having it? It can protect the cable incase of a break if future owners go digging in years to come.



  • Registered Users, Registered Users 2 Posts: 694 ✭✭✭JohnySwan


    The Mcb would provide that protection. The Rcbo could cause a nuisance.



  • Registered Users, Registered Users 2 Posts: 713 ✭✭✭bunderoon


    Fair enough, thanks. Mine being a 100mA shouldnt be, I guess.



  • Registered Users, Registered Users 2 Posts: 694 ✭✭✭JohnySwan


    Less likely than a 30ma but still could be. Why would you put one in if you don't require it?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 713 ✭✭✭bunderoon


    Because I made the mistake of ordering all whats in the picture to ensure that the electrician stays and does the job. So hard to get one these days and especially with a diy solar sign off - NC6.

    Did show him the job and it was fine. My only question mark was on the trip at the house CU.



  • Registered Users, Registered Users 2 Posts: 713 ✭✭✭bunderoon




  • Registered Users, Registered Users 2 Posts: 4,489 ✭✭✭...Ghost...


    That'll do the job.

    I had similar designs and mine is all done now about a month. My shed CU is just idle for now, as I opted to connect my second inverter direct to the main CU. The one mistake I made and will have corrected is that I used a spare 32A single pole MCB to supply the shed. While the shed will probably never see a load that will cause that breaker to trip, I'm going to replace with a double pole. Thankfully that particular breaker has space to the right of it, so it will be a 10 minute job next time the leccy man is in the area. I'm in no rush, because I don't need power to the shed right now anyway.

    Stay Free



  • Moderators, Home & Garden Moderators Posts: 7,074 Mod ✭✭✭✭graememk


    As far as I know the double pole mcbs are relatively new in Ireland, your single pole would be fine, if it's already wired up and done.



  • Registered Users, Registered Users 2 Posts: 4,489 ✭✭✭...Ghost...


    We need to add "buy me a beer" buttons here. You've just saved me a few more quid!

    Stay Free



  • Registered Users, Registered Users 2 Posts: 713 ✭✭✭bunderoon


    Thanksa million.

    Will go and get a double pole MCB online for the House CU. Was in CT Electrics thismorning and they only had single poles.

    Must create a DIY thread on my install when done.



  • Registered Users, Registered Users 2 Posts: 694 ✭✭✭JohnySwan


    No need for a double pole MCB, just make sure the sub board has a double pole isolator.



  • Registered Users, Registered Users 2 Posts: 713 ✭✭✭bunderoon


    There is a double pole isolater going into the garage CU when it gets installed. I thought a double pole MCB was 'preferred' at house CU to isolate both live and neutral of the swa going to the garage.



  • Registered Users, Registered Users 2 Posts: 694 ✭✭✭JohnySwan




  • Moderators, Home & Garden Moderators Posts: 7,074 Mod ✭✭✭✭graememk


    100ma is to counter act parasitic capacitance that can happen on solar.