Do Condensing Boilers operate in condensing mode?

  • 11-02-2025 04:32PM
    #1
    Registered Users, Registered Users 2 Posts: 1,264 ✭✭✭


    Not very often according to this article

    https://www.theheatinghub.co.uk/why-our-condensing-boilers-do-not-condense



Comments

  • Registered Users, Registered Users 2 Posts: 160 ✭✭steamdave


    If the plume of condensate visible at the exhaust, then ours works in condensing mode most of the time.

    Don't know anything about the theory, but I believe the boiler needs to be sized accurately to the house to achieve the condensing mode.

    Dave



  • Registered Users, Registered Users 2 Posts: 9,131 ✭✭✭10-10-20


    Post edited by 10-10-20 on


  • Registered Users, Registered Users 2 Posts: 14,748 ✭✭✭✭ednwireland


    surely there shouldn't be a plume of condensate if it's condensing.

    talked to a guy at grants once and he said once they are hot they stop condesing unless you have something like underfloor heating which lowers the return temp low enough. as I was querying standard boilers ratings and he said there wasn't much difference with standad rads just the ratings were artificially capped for non condensing boilers this was 20 years ago.

    winter 2010/2011 killed that boiler

    My weather

    https://www.ecowitt.net/home/share?authorize=96CT1F



  • Moderators, Home & Garden Moderators Posts: 6,542 Mod ✭✭✭✭Wearb


    Would you mind elaborating on the above please?



  • Registered Users, Registered Users 2 Posts: 2,059 ✭✭✭Lenar3556


    You are supposed to have a 20 degree differential between flow and return for condensing to occur. But you can usually achieve that on radiators if you put the effort in to balancing them correctly. Most of the time it’s not done correctly.

    Note however that even when not condensing, modern condensing boilers are still a good bit more efficient than a decent standard efficiency boiler from 20 years ago. The secondary heat exchanger in the vortex for example has flue glass temps down to about 50 degrees vs 200+ on the older equivalent.

    I am not sure what active condensing does on top of that, but I’d be surprised if it was any more than 1 or 2% more to be obtained.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,683 ✭✭✭KildareP


    How is it that traditional non-condensing boilers never plumed then?



  • Registered Users, Registered Users 2 Posts: 1,312 ✭✭✭Busman Paddy Lasty


    AFAIK the return temperature has to be below the condensation dew point. Normally around 55 degrees.

    So no, boilers installed and commissioned with a flow temp of say 70 degrees likely won't go condensing mode.



  • Registered Users, Registered Users 2 Posts: 2,059 ✭✭✭Lenar3556


    Just reduce the flow rate using lock shields and pump speed until you get the desired return temp.



  • Registered Users, Registered Users 2 Posts: 1,312 ✭✭✭Busman Paddy Lasty


    Don't know how and I don't think I need to. I run the flow temp at 55 degrees so it will return sub 50.

    I'll try find a good YT video on it. On a crisp cold day if you can see a large white plume you are seeing condensing that had not happened inside the boiler.



  • Registered Users, Registered Users 2 Posts: 23 Tomek7


    I had a condensing boiler installed a few years back and it was eating gas like crazy very inefficient. Turned out the installer commissioned it with the water temperature to the radiators at 70degrees Ce. I turned it dow to 55degrees Ce. And the thing is a gas sipper now. Went from two tank of gas to one the next winter. It runs longer through out the day but barley uses gas.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,059 ✭✭✭Lenar3556


    If that works for you then happy days.

    Just watch your hot water cylinder, ideally it should be a little hotter to deal with legionella. In some cases houses need higher flow temps than that as radiators wouldn’t have been sized for 50deg.



  • Registered Users, Registered Users 2 Posts: 2,059 ✭✭✭Lenar3556


    That shouldn’t affect the overall efficiency and much though.

    70 degree flow temps will heat the house faster and use more gas during this time, but the boiler should then switch off. Lower flow temps will achieve the same but more slowly.

    Do you have room thermostats?



  • Registered Users, Registered Users 2 Posts: 1,312 ✭✭✭Busman Paddy Lasty


    Thanks for the advice. Should have told you mine is a combi! Hot Water set to 62 degrees. Rads 55.



  • Registered Users, Registered Users 2 Posts: 23 Tomek7


    It effects the efficiency greatly because the boiler gets it efficiency from the condensing process wich does not happen when you have it set to 70 degrees.



  • Moderators, Home & Garden Moderators Posts: 6,542 Mod ✭✭✭✭Wearb


    It doesn't effect it greatly. A flow of 70 will mean a returnof a good bit less than 70. As already stated. Condensing boilers are more efficient even when not in condensing mode. We see the difference all the time when servicing. The flue gas temperature will be much lower than a standard efficiency boiler, even when the condensing boiler isn't obviously condensing.



  • Registered Users, Registered Users 2 Posts: 2,059 ✭✭✭Lenar3556


    That’s not the case. The ability of a boiler to condense is a product of its return temperature. It is entirely possible to a have a flow temp of 70 degrees (or higher) and a return temperature of 50 degrees and setting this is part of the commissioning process. The boiler is designed to operate with a 70 degree flow temp and achieve its stated efficiency.

    If yours was using much more gas there is something else at the root of that, probably a lack of heating controls.



  • Registered Users, Registered Users 2 Posts: 23 Tomek7


    The house has two zones with heating controls. The root of the problem was it was not condensing because the flow was too high at 70 degrees. You can argue all you want but when this was changed and only this the boiler became super efficient. And after this I read in almost all literature that a condensing boiler should not work at more than 60 degrees and that is why you have separate piping for the hot water tank because it needs to be hotter. But I guess the plumber installing this unit was thinking like you.



  • Moderators, Home & Garden Moderators Posts: 6,542 Mod ✭✭✭✭Wearb


    ^^^^

    Just because you've had a certain experience and extracted certain information from your research, doesn't necessarily mean that that can be applied to all or most cases.

    I'm not writing this to have a personal go at you, but so that readers don't get the idea that your experience will be a successful solution to other similar problems.



  • Registered Users, Registered Users 2 Posts: 2,059 ✭✭✭Lenar3556


    Lowering the boiler flow temperature from 70 to 55 will reduce the output of the radiators and cylinder by about 30% (roughly), and you will have a fuel saving of approximately the same amount. That is where your saving is coming from.

    It has little or nothing to do with the efficiency of a new boiler or condensing. The flue gas temperature is already so low leaving the boiler the remaining latent heat to be recovered by condensing is actually quite small.



  • Registered Users, Registered Users 2 Posts: 9,131 ✭✭✭10-10-20


    Sorry folks, brain-farted up above!

    Plume is the indication of lower flue discharge temps (due to secondary internal condensation), so you can get more rapid condensation in the air around the flue. Older boilers had higher discharge temps so the condensation wasn't often seen as the moisture dispersed in the air before it condensed.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,708 ✭✭✭John.G


    My 20 year old SE (non condensing) Firebird Oil Fired boiler has a flue gas temperature of ~ 230C, if I was to install a HE (condensing) boiler I would expect the flue gas temperature to fall to at least 100C (without trying too hard) due to the extra heat exchanger and a efficiency gain of ~ 6%, boilers don't start condensing util the flue gas temperature falls to 50/55C and won't fully condense until the flue gas temperature falls to ~ 25C/30C, reducing the boiler flow temperature is the easiest way to get at least partial condensing as most rads are oversized to T50 standards, you will often see the T50 standard quoted at, flowtemp/returntemp/roomtemp, 75C/65C/20C which is a T50 rad, ((75+65)/2)-20, 50C. Quite often, depending on rad sizing, house insulation, a outside air temperatures of say 7C to 10C may only require rad outputs as low as 25% of their rated T50 output, simply adjusting the boiler flow temperature (which weather compensation does automaticall) can result in extra condensing and a nice gain in boiler efficiency. You can see, below, that once down to ~ 50% rad output that the rad/boiler return temps are down to ~ 47C, leading to a reasonable boiler efficiency but once down to 25% rad output then return temp is only 36C ( the very limit of OF boiler return temp) to give very high boiler efficiencies.

    image.png



  • Registered Users, Registered Users 2 Posts: 1,312 ✭✭✭Busman Paddy Lasty


    Found a handy graph in the article. 60 degree return temp = 88% efficiency. 40 degree return temp = 94% efficiency.

    So even if not considered to be in condensing mode, 88% ain't a bad number.