Generator House Plug - Is It Allowed?

  • 08-02-2025 10:39AM
    #1
    Registered Users, Registered Users 2 Posts: 680 ✭✭✭


    Do Irish electrical regulations allow a generator plug, with a transfer switch, to be installed into a house so that electrical items still run during a power outage?

    I am on day 15 with no power, heat, water and do not want to be in this position ever again.

    I already have some experience of power stations, solar etc from camper van.

    If it is possible to install a generator switch with the transfer switch my scenario would be:

    EcoFlow Smart Generator outside powering an EcoFlow Delta 3 Pro inside the house that would power the house sockets.

    Asking here as the fantastic electrician that used to do jobs for me has gone to Australia so need an expert to guide me before I try to find someone locally if I can go ahead with this.

    Thanks

    https://uk.ecoflow.com/products/delta-pro-3-portable-power-station

    https://uk.ecoflow.com/products/dual-fuel-generator



«1

Comments

  • Registered Users, Registered Users 2 Posts: 597 ✭✭✭DayInTheBog


    I've a switch and generator. All are outside in a shed to run the house if needed



  • Registered Users, Registered Users 2 Posts: 2,470 ✭✭✭Lewis_Benson


    I ran my house off a 2kw generator for a week after the storm.

    Turned off the main breaker and turned off any high draw appliances.

    I backfed into a socket in the shed which powered all the sockets and lights.

    Not The ideal setup but it meant our freezers etc stayed frozen, could work from home and had tv and broadband so didn't go insane.



  • Registered Users, Registered Users 2 Posts: 83 ✭✭Trapeze
    Eze


    Isn't there an apt name on that kind ^^^ of arrangement 😱⚡️🔌



  • Registered Users, Registered Users 2 Posts: 58 ✭✭topofthewind


    it’s fine to do it provided you have a transfer switch (aka changeover switch) installed. This switch ensures that only the esb OR the generator can be connected at any one time.

    Using a plug from the generator to ‘back feed’ into your home’s supply is not considered to be a safe option as there is a risk to esb crews working on downed lines.

    i have a 16 amp socket (male) in my garage connected to the consumer unit in the house via a transfer switch. I can connect that socket from a generator, ac power bank or ac inverter connected to 12v batteries/running vehicle.

    Might work for you as you could connect your house directly to the genny at times. You could plug the genny out and plug in the power bank at other times. Power bank could be charged from a normal house socket while the genny is running and plugged in to the house.



  • Registered Users, Registered Users 2 Posts: 11,680 ✭✭✭✭downcow


    I was only off for a few hours but have a generator and was going to try this, I was strongly advised not to backfill with a three pin plug, as that plug is an absolute killer if anyone touches it. You can’t know that someone won’t unknowingly unplug that plug and touch the pins.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,470 ✭✭✭Lewis_Benson


    In my case I had turned off the main breaker so nothing can feed back into the grid.

    Yes the plug is dangerous to anyone who goes near it, I managed the whole setup, no one was going to be going near it. No different to the same setup if you have a transfer switch.

    These things are perfectly safe if managed correctly.



  • Registered Users, Registered Users 2 Posts: 58 ✭✭topofthewind


    @downcow Ya, they are known as ‘suicide cords’ in the US. That’s why my 16 amp socket is male. It has the exposed pins. The pins are never live while exposed however. The cable from the generator (or inverter/power bank) needs to have a female plug on the other end as it has no pins exposed if it gets plugged out while the genny is running.
    it’s the opposite to what normally happens in a house as the socket in a house is live and the plug is only ever energised when safely concealed in the socket.



  • Registered Users, Registered Users 2 Posts: 8,518 ✭✭✭Gusser09


    Lads consult an electrician before you potentially kill someone. A sparks will set this up for you safely.



  • Registered Users, Registered Users 2 Posts: 555 ✭✭✭SodiumCooled


    Leaving aside the issues around doing this correctly (I.e. not with a suicide plug) one issue I can see for the proposed setup of connecting the battery to the house is I don’t see a high output connector for a 16A socket or similar to hook into the hook up to your consumer unit. Most generators will have a 16a or 32A output (the blue plugs) for this type of connection.



  • Registered Users, Registered Users 2 Posts: 680 ✭✭✭ingalway




  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,837 ✭✭✭FishOnABike


    Generator or inverter output would be 230V AC with a round female socket to accept a 230V 16A plug like this

    Screenshot_20250208-184843.png

    Other end of the lead from the generator should have a female connector to connect to the house external power input.

    The house would need a changeover switch between the grid and generator and a male external power input to connect the lead from the generator to.



  • Registered Users, Registered Users 2 Posts: 1,566 ✭✭✭monseiur


    I guess the fact that the frequency is 60 instead of 50 Hz may rule that particular genny out ??



  • Registered Users, Registered Users 2 Posts: 4,908 ✭✭✭meercat


    this is so dangerous and potentially lethal

    Both poles live and neutral need to be isolated

    There’s a chance of reverse polarity either on the generator/connection leads/house wiring

    This could send a back feed along the esbn network.This could lead to your 230v actually stepping up when it meets an esbn transformer with possible 10,000volts on the system

    Absolute lunacy

    There’s reasons a change over switch is required



  • Registered Users, Registered Users 2 Posts: 2,009 ✭✭✭Lenar3556


    It’s a bad idea. Get a changeover switch fitted.

    Aside from the means of connection…you only achieved single pole grid isolation by opening the main breaker. So the neutral was still connected with the earth neutralised to this at the cutout - none of which was planned.



  • Registered Users, Registered Users 2 Posts: 2,470 ✭✭✭Lewis_Benson


    Thanks for the info both, I'll ask my electrician about getting a switch fitted.



  • Registered Users, Registered Users 2 Posts: 24,257 ✭✭✭✭ted1


    that only brakes the live. Natural Is still connected. You res to fully isolate from the grid.

    You are. It managing anything correctly !!!



  • Registered Users, Registered Users 2 Posts: 555 ✭✭✭SodiumCooled


    Breaking the neutral seems to be very much up for debate with different electricians having different advice on it and has been a topic of major discussion here before. Some more knowledgable than me suggest that only the live needs to be broken and in fact the neutral should not be broken by a change over switch to in order to maintain the neutral/earth bonding in the meter box.

    It is hard to know the correct way as there are some qualified people adamant one way is correct and others that the other way is.



  • Registered Users, Registered Users 2 Posts: 24,257 ✭✭✭✭ted1


    you must have a changeover switch,


    https://www.facebook.com/share/v/1ATonJ8nAP/?mibextid=wwXIfr


    Only live and neutral come into the house.

    The only way to electrical isolate is to physically disconnect all incoming cables. Having neural connected isn’t isolating.



  • Registered Users, Registered Users 2 Posts: 664 ✭✭✭MakersMark


    As above, changeover switch is the safe way to do it.

    Good luck



  • Registered Users, Registered Users 2 Posts: 793 ✭✭✭Slightly Kwackers


    Ditto!

    I suspect it is breaking a few regs though, but I find the power outages in my area are frequent and the ESB website poor at providing information.

    It cannot happen as I have my own interlock devised, but can you actually kill or injure a linesman by backfeeding? I would have thought the first thing they would do is isolate, then ground what was being worked on anyway?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 555 ✭✭✭SodiumCooled


    Yes you must have a change over switch but it is not clear if the change over needs to or even should switch the neutral.

    If you switch the neutral then you must handle neutral bonding and keeping in mind you can’t neutral bond in two places it is not so straight forward.

    I am in the middle of debating this with both my own and the solar electrician so I will update the outcome of that also.

    Have a look at this thread: https://www.boards.ie/discussion/2058002722/generator-change-over-switch/p1



  • Registered Users, Registered Users 2 Posts: 793 ✭✭✭Slightly Kwackers


    I wonder if the poster meant breaker?

    I used the main isolator to disconnect into the CU, this is a DP device.



  • Registered Users, Registered Users 2 Posts: 2,009 ✭✭✭Lenar3556


    The only official guidance I have ever across calls for full changeover. If neutral earth bonding is required, it should be provided at the generator - but most generators don’t have a ‘neutral’ - it’s two phases at 115V.



  • Registered Users, Registered Users 2 Posts: 2,009 ✭✭✭Lenar3556


    You certainly could injure/kill ESB staff.
    Earthing of lines they are working will have no effect as the generator isn’t earthed.



  • Registered Users, Registered Users 2 Posts: 2,470 ✭✭✭Lewis_Benson


    Why would the main breaker on the distribution board only break live or neutral, and not both?



  • Registered Users, Registered Users 2 Posts: 58 ✭✭topofthewind


    Does the neutral earth bonding happen at the consumer unit? That’s how it looks at my CU with the earth extended outside to the grounding rod from the same din rail.



  • Registered Users, Registered Users 2 Posts: 793 ✭✭✭Slightly Kwackers


    How would that work, because the first thing the feed to the house hits is a transformer.

    if there was no reference to earth from the generator supply, would that not reduce risk anyway as there would surely be less tendency for current to complete an earth path to the generator?

    The other thing is that if the power from the generator fed back through the CU and company fuses, wouldn't one side be grounded anyway in home installations?

    I would fit a dedicated c/o switch, but it seems like a considerable amount of expense and time to basically arrange a feed from a small generator that is fine operating in the shed, but too noisy to put near the house.

    I think of it like the light fittings I purchased from Amazon. It's dangerous if no one knows the system, but as I live here alone, I do what I deem acceptable to myself in terms of risk.

    I did photograph and report two items of electrical gear bought from Amazon by the way, who assured me they are mad keen on safety.

    I notice others picked up too but the switch and lampholders reported are still on sale!

    I certainly don't offer this as justification for letting my standards fall below what is expected regarding safety, but I know the risks and my twin male supply lead is under lock and key :-)



  • Registered Users, Registered Users 2 Posts: 58 ✭✭topofthewind


    AFAIK a main risk from backfeeding is from someone leaving the main breaker on or switching it on during backfeeding.

    Another risk comes from the twin male connecting cable being unplugged while live which exposes the live pins to touch.

    A third risk is from overload to the socket that is used to backfeed, e.g. a 7000watt generator used and demand for 7000w from various appliances in the house all passing through a socket and wiring rated below this.

    The neutral not being switched however , if it is a risk, is still present in many changeover switches installed by qualified electricians. I can’t see how the backfeeding is any worse in this regard than one of these installations.



  • Registered Users, Registered Users 2 Posts: 793 ✭✭✭Slightly Kwackers


    Thanks, you are correct, but the DIY "death cable" that people tend to use for occasional domestic power back up via their generator, would have fuses in both plugs.

    Could this be promoted as a safety feature with twin male 13A power cords on sale eventually :-)



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 24,257 ✭✭✭✭ted1


    there also no interlock stopping another household member and switching the main fuse back up.

    You Risk connecting a non synchronous generator to the grid or back feeding., and yes AC does pass through transformers. …

    Post edited by ted1 on