Climote wall unit not working, no heating. Can it be overriden?

  • 01-12-2023 09:00PM
    #1
    Registered Users, Registered Users 2 Posts: 4,111
    ✭✭✭


    Hi, as the title says - the Climote wall unit is not working. It's in a loop of initialising.

    I tried the restart button on the bottom, no joy.

    We're without heating for the weekend as their support is during office hours only. Just wondering would anyone know can this be overriden somehow to turn the heating on?



    20231201_194903.jpg




Welcome!

It looks like you're new here. Sign in or register to get started.

Comments

  • Moderators, Home & Garden Moderators Posts: 6,527 Wearb
    Mod ✭✭✭✭


    Someone else will know more, but for now, is there a unit near the boiler or somewhere that this sends signal to?



  • Registered Users, Registered Users 2 Posts: 23,911 mickdw
    ✭✭✭✭


    There is a reset button on the bottom surface around thr centre of the unit.

    You.would need to push upwards with a small object.

    Climote have gone into liquidation so that may be the issue but try reset anyway.

    You could also as a first attempt just turn your esb main switch off and on to see if it comes back.

    The control unit can be removed from back plate exposing the wiring. Some are wired with just a simple power in and power out so if you got someone who knew what you were doing they could easily remove the climote function entirely to create an always on as a stopgap.



  • Registered Users, Registered Users 2 Posts: 4,111 joker77
    ✭✭✭


    Thanks for the messages, I didn't know Climote have gone into liquidation, that's definitely worrying.

    Yea the first thing I tried was to shut off the mains power - turn it off and turn it on again. No joy.

    I then had a look at the climote website, and found the reset button. Tried that twice.

    I'm out of options. I don't see anything near the boiler - any idea what that would look like?



  • Registered Users, Registered Users 2 Posts: 565 G-Man
    ✭✭✭


    A local handyman would fit a simple timer in its place until you decide on what your next plan is.. ..There is much to choose from for long term thermostat.

    There is unlikely to be another bypass near the boiler found without risking damaging something.. Try the local handyman and be prepared for his simple solution to fit such a timer..There is too much variation in types of thermostat for him to commit to fixing that one exactly.



  • Moderators, Home & Garden Moderators Posts: 6,527 Wearb
    Mod ✭✭✭✭


    I just watched an installation video. It isn't like Hive which I'm familiar with.

    There isn't a receiver like there is with Hive. For now it probably best to have your previous controller reinstalled.



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,527 Wearb
    Mod ✭✭✭✭


    BTW. If you can find your zone valve for heating and set it to manual, it might give you heating for now.



  • Registered Users, Registered Users 2 Posts: 4,111 joker77
    ✭✭✭


    Thanks, what would this look like?



  • Registered Users, Registered Users 2 Posts: 2,577 XsApollo
    ✭✭✭


    They should be in your hot press, like a yellow ( usually ) box on the pipe. One for each zone and water.

    there should be a lever on the side that you can move them manually, open it and the boiler should fire.

    IMG_2273.jpeg




  • Moderators, Home & Garden Moderators Posts: 6,527 Wearb
    Mod ✭✭✭✭


    Like above. They can be white or silver also.

    The lever/slider will be slow to move (will take a slow push of 10/15 seconds) about 3/4 way along its travel there will be a notch that you will need to lock the lever into. Have a look at YouTube for zone valves and find one that shows manual opening.



  • Registered Users, Registered Users 2 Posts: 4,111 joker77
    ✭✭✭


    Excellent! Thanks both - you've saved the weekend!!

    20231202_100707.jpg

    There are 2 yellow boxes beside each other, one on the pipe coming from the hot tank which I'm assuming is the water, the other being the heating.



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,527 Wearb
    Mod ✭✭✭✭


    Yes. Give it a go. Remember there will be resistance, so go slowly. If you get the wrong one, just disengage it from retaining slot and go to the other one.

    It'll be a bit of a chore turni g it on and off, but well worth it to have a warm place.



  • Registered Users, Registered Users 2 Posts: 2,577 XsApollo
    ✭✭✭


    Looks like 1 zone for heating and one for water,

    But if you have upstairs and downstairs each zoned, there should be another one lurking around.



  • Registered Users, Registered Users 2 Posts: 23,911 mickdw
    ✭✭✭✭


    I don't think this will activate the heating with defective climote in the system but I could be wrong.



  • Registered Users, Registered Users 2 Posts: 4,111 joker77
    ✭✭✭




  • Moderators, Home & Garden Moderators Posts: 6,527 Wearb
    Mod ✭✭✭✭




  • Registered Users, Registered Users 2 Posts: 23,911 mickdw
    ✭✭✭✭




  • Registered Users, Registered Users 2 Posts: 2,577 XsApollo
    ✭✭✭


    For future reference or issues, if everything looks like it is working and your boiler isn't turning on or one of the zones doesn’t heat, then do the same thing again opening whichever one doesn’t work and see if the boiler starts heating.

    those things fail, I’ve replaced a couple in my own house over the course of a few years.



  • Registered Users, Registered Users 2 Posts: 217 Tippbhoy1
    ✭✭


    This also makes no sense to me. Why would any change with a valve fire the boiler.



  • Registered Users, Registered Users 2 Posts: 1,710 wiz569
    ✭✭✭


    Normally the Time clock sends a signal to the Motorised valves to open to supply heat or hot water or both, the corresponding valve/s once opened send a signal to the boiler to fire up, in this case the same thing happens once you manually open the valves.



  • Registered Users, Registered Users 2 Posts: 217 Tippbhoy1
    ✭✭




  • Advertisement
  • Registered Users, Registered Users 2 Posts: 845 skydish79
    ✭✭✭


    Our climote unit hub has given up working

    The fact that climote has gone into liquidation is it worth getting a new climote unit or switch to another company like Hive



  • Registered Users, Registered Users 2 Posts: 1,371 youtheman
    ✭✭✭


    Remember that if you manually open the zone valve to turn on your heating you will be bypassing the thermostat. So you won't have the normal heating control that the thermostat offers. So when the room reaches the required temperature (or water) just slive the valve lever back the way it was originally.



  • Registered Users, Registered Users 2 Posts: 565 swededmonkey
    ✭✭✭


    My climote has started showing a "critical fault 7dov" message but the boiler is working. I've restarted the console and it's still there. Should it be anything to be worried about?



  • Registered Users, Registered Users 2 Posts: 1,819 Hannibal
    ✭✭✭


    Is the Climote still switching the boiler on/off?