What size of MIC (kVa) for new build house for EV

2»

Comments

  • Registered Users, Registered Users 2 Posts: 1,508 ✭✭✭Manion


    I'm probably inferring something I shouldn't, all they confirmed was the power supply is 12Kva. I assume that means the Meter fuse is 60A to protect the network. At least now I'm armed with the right questions to ask to electrician when he comes.



  • Moderators, Home & Garden Moderators Posts: 7,015 Mod ✭✭✭✭graememk


    They look, at a glance like 16mm2 tails. and being on a 12kva supply confirms it.

    Did you have a photo of your consumer unit in another thread? I think thats just a switch, not a MCB. (is there another box in your meter box?)



  • Registered Users, Registered Users 2 Posts: 1,508 ✭✭✭Manion


    For those interested, I was onto ESBN today regarding a smart meter and they told me the main fuse is 80amp but the supply is definitely just 12Kva. So that's pretty conclusive that fuse and MIC don't match up one to one.



  • Registered Users, Registered Users 2 Posts: 2,666 ✭✭✭ECO_Mental


    Just for your info I got my new connection over the summer and specced a 16 kVA connection and ESBN put in a 100 Amp fuse. My main isolator on the CU board though is 80A....I dont have any EV's at the moment so not going near it, but planning to over the coming years. I have prewired for 2 charging points and I have a heat pump etc. I probabaly wont have two EV's charging any time soon so I think I have the capacity.

    6.1kWp south facing, South of Cork City



  • Moderators, Home & Garden Moderators Posts: 7,015 Mod ✭✭✭✭graememk


    That tallies with what I'd been told too when I got my supply upgraded, the esbn fuse is 100amp but the mcb on the house is 80amp



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,508 ✭✭✭Manion


    The charger we got installed came with a smart energy monitor on the mains supply. We've an air to water heat pump on a 32 amp breaker. So far we've not gone over 3kw usage at any one time. Feels like there is loads of head room for 7kw charging without the upgrade, though the upgrade is easier now that the main fuse board is in the meter cabinet.



  • Registered Users, Registered Users 2 Posts: 1,267 ✭✭✭loopymum


    3kw seems very low. I have a zappi & the hub. I regularly see mine flying up. We don't have any gas though & everything is electric.

    Say oven is on

    The base in our house is 0.6 kw usually.then throw on a few things

    Oven 2.2

    HP 3kw

    Immersion 3kw

    Microwave 2.2

    Ring on the hob 1.3

    Tv & a few computers 1kw +


    I have seen my zappi load manage a good few times even during the night. Washer, dryer & dw & car charging & hp. turn on the kettle & it will drop down. Otherwise I would be paying ESB 1500 to upgrade



  • Registered Users, Registered Users 2 Posts: 1,508 ✭✭✭Manion


    That's fair enough, most of our appliances are A+++ rated (except the dryer). It might be spiking up when we turn on the kettle or the like, but our steady state seems pretty low.



  • Registered Users, Registered Users 2 Posts: 103 ✭✭CHorn


    Been a while but resurrecting as seems closest to my Q, what I worry about is future-proofing for 2EVs and HP with everything going to Electric.

    I’m just doing a sanity check on the electricity supply proposed for a new build- 16kVA Enhanced. Please correct me if I’m wrong but this’ll mean we have a 100A fuse on the ESB side and an 80A fuse on the house side. The idea being the 80A fuse trips first and the customer can figure out why, if the 100A fuse goes the ESB will want to know why (and charge you to correct it).

    That means we’ve got 80A to play with as CONCURRENT power use within the house. If we’re looking to future-proof the house, probably best to look at what’s going to happen down the road with 2 x EVs being charged at night. Worst case scenario is a below zero winter night where the heat pump will be running full blast. That’s 32A (16kW heat pump), and 2x32A with 2x7.4kWh EV chargers running. Now I know the EV chargers can balance the load (i.e. turn down/off if too much total current is being drawn), but that may mean you wake up in a warm house with an EV uncharged.

    We’d also plan to run the dishwasher, washing machine and tumbler dryer in off-peak hours too (10 each =30A) to take advantage of lower rates. So with heat pump on and ONLY 1 EV charger, we’re still looking at a potential 94A draw, even before adding in lights and minor appliances.

    So max concurrent draw at night to use night rates is potentially 126A (3x10A Appliances, 2x32A EV Chargers, 1x32A Heat Pump). Should we not opt for the (1 Phase) 29kVA with the 160A fuse (and 125A fuse on customer side)? I don’t think there’s a significant difference in cost between the two (16kVA versus 29kVA): https://www.esbnetworks.ie/docs/default-source/publications/esb-networks-dac-statement-of-charges.pdf

    If it turns out we can go lower on the heat pump spec (say 12kW), this may change (down to 20A?). Also I haven’t even considered the power shower in a garden office (30A), a desktop PC (10A) that can use or anything to do with the hot water or rads/underfloor heating in the house (I'm assuming latter is related to heat pump?), just items I can fairly confidently say will all be running at the same time.

    3 Phase not an option. Will 16kVA Enhanced cut it, or should I go to 29kVA? Or am I missing something or doing something desperately wrong with my #s? Thanks.



  • Registered Users, Registered Users 2 Posts: 12,321 ✭✭✭✭KCross


    Or am I missing something or doing something desperately wrong with my #s?

    ^ This

    There is lots wrong in your post and understanding of the HP and EVs and fuses etc.

    The 16kVA connection will suffice. I’ll write you a full explanation tomorrow.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,508 ✭✭✭Manion


    Other than the EV chargers the rest of your appliances will not draw the max current continuously. I wouldn't down grade your Heat pump, it will draw most power at start up and shut down. Ours is rated to 32 amp, typically drawing about 8 amps at start up in the morning and quickly settling down to half that. It might draw 32 amps I guess if it had been off and house temperature was freezing.

    Your office shower doesn't factor in unless you plan to be out there showering in the night, even then in that highly rare instance the load balancer will briefly drop power to the EVs.

    Fuses and breakers work by have a max continuous load threshold and a max instantaneous load.

    As the other poster said, you don't need the 29Kva supply.



  • Registered Users, Registered Users 2 Posts: 7,315 ✭✭✭zg3409


    Another factor in calculations is what is daily commute. I used to do 110km a day which worked out average 20kWh energy needed per car per day, so in less than 3 hours car would be refilled at 6/7kW charging rate. If you have a 9 hour night rate it should be possible to charge 2 cars on typical commute. It would be rare both cars would need a full charge and need to be 100% full the next day. You can set one charger to be priority over the other one to ensure one car can get more. Even just starting charging with priority car first should do that.

    As said dishwashers and washing machine only use high power while heating water which may only be 10 minutes of the wash cycle.


    We may be forced into smart meters with 2 hour low night pricing typical. Will you be forced smart meter on new build?

    You may want to consider solar during planning. You would need massive solar to power heat pump in winter from sun during daytime. However solar is relatively cheap compared to long term bills.

    Do you know the annual cost difference on different supplies?

    Personally I would be worried about cost of heat pump. Electricity is crazy expensive now. I would want my house ideally passive rated (using sun through windows to warm house) and have house a+++ rated.



  • Registered Users, Registered Users 2 Posts: 12,990 ✭✭✭✭the_amazing_raisin


    I can assure you that 16kVA will be enough because I'm in almost the exact situation you describe for the past year and have never had an issue with the cars not being charged

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 2,666 ✭✭✭ECO_Mental


    HI I'm the OP of this tread and I am a year into my house now and I got a 16 kVA connection and it is more than enough, I would highly recommend getting the 16 kVA connection and it does give you the wiggle room. I am all electricity and I have one EV at the moment.

    See below here a day last week where I had the Car charging, I had the dishwasher timed to go on at 2am and the Heat pump when through its once a week legionella heating routine.. I nearly tipped 13 kW import during the night so the 12 kVA might have struggled

    Regarding EV charging I agree if you charge about 2 hrs every night that should keep you topped up in the car for the average mileage (I do about 40- 60km a day in the EV) so if you had two you could easily schedule the charges not to overlap. Even then I am sure two charging at the same time with a 16 kVA connection you would be alight. 80 Amps is about 19kW so there is plenty of room (if my math's is right..)

    FYI...ESB Fuse is 100amp

    image.png


    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 1,508 ✭✭✭Manion


    I'd guess it's the convenience of not having to think about actively managing what you put on when. Though I don't thing there is any issue anyway.

    Regarding concerns about heatpumps, it's not really a subjective thing. It's a new build and you have to heat it somehow. A heat pump should provide you an efficiency of 300% in a new build. Gas cost have increase as well. Taking gas prices at 12.617c per kWh if you can get your average electricity for less than 50 cents, you're winning. Keep in mind that you also have a Gas standing order, are you even allowed put a gas/oil boiler into new builds?

    People are often shocked when they get a heat pump because their electricity builds are much larger but forget they aren't getting a gas bill at all.



  • Registered Users, Registered Users 2 Posts: 12,321 ✭✭✭✭KCross


    You need to look up "electrical diversity".

    All of your post is calculating based on everything being on and drawing max power at the same time. In reality it wont happen. Thats not to say you dont need to take some precautions (load balancing etc) but the point is you dont calculate your MIC based on everything being on at the same time.

    16kVA Enhanced. Please correct me if I’m wrong but this’ll mean we have a 100A fuse on the ESB side and an 80A fuse on the house side

    The ESB fuse could be 100A. It could also be 80A but I think they are installing 100A now. It gives you access to 80A at your consumer unit either way. Note also that the ESB fuse wont just pop at 80A. They are designed to last beyond 80A to account for load spikes when things like HP's turn on and very short bursts.

    That’s 32A (16kW heat pump)

    Thats a rather large heat pump for a new build. Unless its a massive house (400m²+) it looks like overkill to me. Somewhere between 6-12kW would be more normal, particularly for a modern A rated build.

    2x32A with 2x7.4kWh EV chargers running. Now I know the EV chargers can balance the load (i.e. turn down/off if too much total current is being drawn), but that may mean you wake up in a warm house with an EV uncharged.

    Its unlikely you would wake up to an uncharged car unless you are doing huge mileage every day in both cars. In reality you will be charging them a couple of times a week and on random days. On the rare occasion where both need a big topup on the one night let the load balancing do its thing and you will still get 100kWh+ into the 2 cars over the 9hr night rate. e.g. You have an 80A fuse, 60A used by the 2 cars for 9hrs, so that's 124kWh. Thats two long range cars charged from 0-100% and you still had 20A to spare for the HP so the cars might ramp down by a few amps to just keep you under 80A. It wont change the end result much and its unlikely you would be going from 0-100% on both anyway.

    We’d also plan to run the dishwasher, washing machine and tumbler dryer in off-peak hours too (10 each =30A)

    Those appliances are pulling 10A for a tiny portion of their full 1-2hr cycle. Im not sure they would even pull 10A. When they are rinsing, spinning etc they use very small amount of power. When they are heating the water for a few minutes they peak, but that's only minutes, not hours (i.e. electrical diversity). So, those appliances wont materially affect your ability to have a charged car in the morning.

    So with heat pump on and ONLY 1 EV charger, we’re still looking at a potential 94A draw

    I'd say closer to 50A in reality.

    Should we not opt for the (1 Phase) 29kVA with the 160A fuse (and 125A fuse on customer side)? I don’t think there’s a significant difference in cost between the two (16kVA versus 29kVA

    The costs are likely to be much higher for the 29kVA but very much dependent on your local grid supply. The key thing in the ESB charges document is where it says "+ MV Network Charges". Those MV charges could be many thousands if they have to run extra supply specifically for you. The only way you would know is by asking them to give you a quote for it and they would visit your site and match that to the grid. I'd be willing to bet it will be thousands, particularly if you are in a rural setting with not much grid around you.


    If it turns out we can go lower on the heat pump spec (say 12kW), this may change (down to 20A?)

    Yes, you should definitely be looking at that. My 12kW HP is rated for 20A but some are variable rather than a set rate whenever its running so its not drawing 20A all the time and it will also be cycling on/off as required.


    Also I haven’t even considered the power shower in a garden office (30A), a desktop PC (10A) that can use or anything to do with the hot water or rads/underfloor heating in the house (I'm assuming latter is related to heat pump?), just items I can fairly confidently say will all be running at the same time.

    Again, diversity... will the shower be running while the cars are charging? And a shower will only be running for minutes anyway so again, not a big deal. The cars will rate down while the shower is running if it happens to coincide..... rating down for 5,10,20mins over a 9hr period is just background noise.

    I doubt your PC is taking anything close to 10A. Unless you are crypto mining with it or something! Again, diversity will be at play here, the PC wont be doing much at night, presumably.

    Will 16kVA Enhanced cut it, or should I go to 29kVA?

    16kVA will cut it.

    I have all of what you have described above. It works fine on 16kVA. I do occasionally hit the limit and the charge points rate down as required. Plenty to spare over the 9hr night rate.


    If you are still a bit unsure and want to future proof what you could do is wire the house to take the next step up (20kVA) but only get 16kVA from the ESB. If you find you have issues you can then relatively easily upgrade the ESB side without having to upgrade the house "tails" and consumer unit etc. Thats a discussion you'd need to have with your electrician.



  • Registered Users, Registered Users 2 Posts: 1,508 ✭✭✭Manion


    Fair point, you should right size your heat pump, too big and you'll have it knocking on and off frequently.



  • Registered Users, Registered Users 2 Posts: 103 ✭✭CHorn


    Thanks so much to all for the answers, HUGELY helpful. And @ECO_Mental if a picture is worth a 1000 words, that graph of yours surely is. If I can ask how did you generate it and what are you (and anyone else who cares to comment) using to monitor your consumption like this?



  • Registered Users, Registered Users 2 Posts: 2,666 ✭✭✭ECO_Mental


    I use Home Assistant on a Raspberry

    I use Home Assistant (HA) on a Raspberry Pi4b . I use 3 ShellyEM's to log 6 circuits on my main consumer board. The data from the ShellyEMs is pulled into HA and those graphs are generated using Grafana on HA...

    If you are not measuring you are not managing!

    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 1,508 ✭✭✭Manion


    Hey @ECO_Mental did you have any issues with installing multiple ShellyEM units on the one home network?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,666 ✭✭✭ECO_Mental


    No problem at all they have been rock solid all year. The only issue is if you can get 2.4ghz wifi signal in your consumer board and fitting them in your board physically. They are small so you should fit them no probs as well.

    Now I do have a fancy enough home network Unifi UDM Pro but any router would take them without any issues.

    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 1,508 ✭✭✭Manion


    Well based on that I've bought 3 of them in prep for solar installation. I've the EV coming off the meter, so going to bang on out there on the sub board and the other two for monitoring solar, the heat pump and the cylinder. Last I'll use for the kitchen maybe or the utility.

    I saw they support up to WiFi 4 and the main consumer unit sits above the router.



  • Registered Users, Registered Users 2 Posts: 12,990 ✭✭✭✭the_amazing_raisin


    Is there a 20kVA option available from ESB? I've noticed some people have 100A fuses which should be good up to 23kVA.

    So I'm wondering if ESB have, or are planning on having higher powered grid connections in houses


    The jump from 16kVA single phase to 29kVA three phase is a bit extreme IMO

    At some point in the future I'll probably be getting an extension and putting in a bigger heat pump. Plus some solar batteries which I'll be charging from the night rate in winter

    Between those and 2 EVs, I could see myself hitting the grid limit a fair bit on 16kVA in winter. So if upgrading to 20kVA is fairly simple then the extra juice would be nice


    EDIT: Just looked at the price list and there's a 20kVA connection option but requires connection to the MV network, and isn't cheap (€4k + vat and MV cabling)

    Not really worth the expense for the small added luxury. It'd be nice if there was an upgrade option from 16kVA, but we'll probably have to wait and see on that option