removed zone showing tamper on aritech cs350

  • 01-07-2020 01:16PM
    #1
    Registered Users, Registered Users 2 Posts: 71 ✭✭


    Hello, recently joined up two rooms into in one and removed one PIR from room. Disconnected cables at panel and changed zone to unused. Keypad is now showing a temper on this zone when I try to arm. Its a long time since I installed this alarm and trying to remember is the only way to fix this to put a 4K7 resistor across the removed zone terminals. Thanks Michael.


Comments

  • Registered Users, Registered Users 2 Posts: 12,016 ✭✭✭✭altor


    mick111112 wrote: »
    Hello, recently joined up two rooms into in one and removed one PIR from room. Disconnected cables at panel and changed zone to unused. Keypad is now showing a temper on this zone when I try to arm. Its a long time since I installed this alarm and trying to remember is the only way to fix this to put a 4K7 resistor across the removed zone terminals. Thanks Michael.

    If you set the zone as unused it should close the zone off so the panel is not looking at it.


  • Registered Users, Registered Users 2 Posts: 71 ✭✭mick111112


    Thanks for that, I tried that and it still showed a tamper on that zone. I put in a 4k7 across that zone terminals back at the panel and the alarm is working now. Thanks for your help.