Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Dual Earth or Clean Earth?

  • 21-07-2005 10:03am
    #1
    Registered Users, Registered Users 2 Posts: 3,420 ✭✭✭


    I am ordering sockets for a rewiring job and I'd like to know if I need dual earth or clean earth? (Yes, I know I should be asking the electrician, he's on holidays!)

    Can either be used? The reason I ask is that illuminated switched sockets, in the range that I want, are only available in dual earth form and I have a sneaking suspicion that we use clean earth here.

    Thanks.

    D.


Advertisement