    Lads

    Am sending in my new connection form to the ESB.

    Now there is 2 options for the standard 12kva - (3.5 kilowatts continuous load, 9 kw switched load, max 2 showers)
    then there is 16kva - (5 kw continuous load, 12kw swithced load, max 4 showers)

    Now 12kva cost 1300 euro and the 16kva cost 1800 euro so if I do not need to spend it then I will not!
    I have yet to confirm which electrician I will be using so would like ur opions.

    We will not have any electic showers, will have a 11.5kw heatpump, then your fridge, tv, washing machine etc, no electric hob.

    Now I cannot figure out should I need the 12kva or the 16kva

    thanks in advance


Comments

  • Moderators Posts: 6,853 ✭✭✭Spocker


    Hey yop,

    If it's any help I recently got my "Welcome to the Electricty Distribution System" letter from ESB Networks for my new house (haven't actually moved in yet - waiting for keys)

    Ours is a 4 bed semi, with 1 electric shower, fridge, washing machine, dryer, electric single oven, dishwasher, gas hob (although electric option was available), gas heating and they've put us on a 12 KVA supply. AFAIK it was the builder who ticked the box on the form so I can only assume that his sparky had some kind of input into the choice.


    Hope this helps


  • Moderators, Home & Garden Moderators, Regional Midwest Moderators, Regional West Moderators Posts: 16,722 Mod ✭✭✭✭yop


    Thanks lad.

    I rang ESB and they could not advise!!


  • Registered Users Posts: 264 ✭✭pajoemccracken


    All you should require is a 12KVA supply. I'm an Electrician and wired my new house recently and have 2 KW showers and 40 sockets , 20 Lights, Shed, Immersion etc and 12KVA is sufficient.
    PaJoe


  • Moderators, Home & Garden Moderators, Regional Midwest Moderators, Regional West Moderators Posts: 16,722 Mod ✭✭✭✭yop


    PaJoe - I would suspect that for a "standard" house but with a 11.5KW heatpump on the ring what do you think?


  • Registered Users Posts: 21,436 ✭✭✭✭Alun


    But, an 11.5kW heat pump doesn't actually consume 11.5kW of electricity, though, does it? With my limited knowledge of these things, I think you're looking at an electrical power consumption of 2-3kW for heat pumps of this capacity.


  • Advertisement
  • Registered Users Posts: 264 ✭✭pajoemccracken


    It would depend on the usage of the heatpump. I suspect it comes on intermittently and mainly at night. If it was running continously during times when you are using everything else in the house then there might be a need to go to a higher KVA supply and your electricity bill would be enormous.

    But since there will be no Electric Shower and most appliances use small amounts of power ( e.g. TVs are around 100w, immersion 2-3kw, then I would think there should be no need for higher KVA.)
    PaJoe


  • Moderators, Home & Garden Moderators, Regional Midwest Moderators, Regional West Moderators Posts: 16,722 Mod ✭✭✭✭yop


    PaJoe- gentleman,

    That makes sense alright, thanks for your help!

    Slán


  • Moderators, Home & Garden Moderators, Regional Midwest Moderators, Regional West Moderators Posts: 16,722 Mod ✭✭✭✭yop


    PaJoe - I put in the app for the new domestic connection, ticked the 12kva standard box, added that we had a HP, no electric showers and standard appliances, no electric hob though.
    I got a call from the ESB on Wed last, asking me the KW input required by the HP and I asked a few different HP suppliers and it came in at about 3.5 - 4 KW so I told her 3.7kw at most.

    Got the quote yesterday and they have me quoted for a 16kva (1800 euro) connection, personally I think they have this wrong, what you think?