what part is this leaking next to circulation pump

  • 02-05-2025 10:19AM
    #1
    Registered Users, Registered Users 2 Posts: 725 ✭✭✭


    Hi,

    There is one of these brass connections on either side of the ciruclation pump, is the bit I'm pointing at a valve of some sort?

    Reason I ask, is that it is leaking nice drip in to a bucket, what has failed and is it an easy fix?

    what tool is used if this is a valve?

    Pump.JPG


Comments

  • Registered Users, Registered Users 2 Posts: 9,031 ✭✭✭10-10-20




  • Registered Users, Registered Users 2 Posts: 9,031 ✭✭✭10-10-20


    Just need a plumber's wrench and maybe a bit of ptfe tape to replace the whole valve.



  • Registered Users, Registered Users 2 Posts: 725 ✭✭✭P_Cash


    Thanks, what tool is used to turn the valve even, I assume its just a ball valve inside. If i could turn it off on the other side it may help with changing it.



  • Registered Users, Registered Users 2 Posts: 753 ✭✭✭Escapees


    Just a large flat head screwdriver!



  • Moderators, Home & Garden Moderators Posts: 6,537 Mod ✭✭✭✭Wearb


    Changing the valve can be tricky enough if you haven't done it before.

    The wheel head valves are much better, but not the exact same length.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 853 ✭✭✭stephenmarr


    the heating system needs to be drained down first.



  • Registered Users, Registered Users 2 Posts: 9,031 ✭✭✭10-10-20


    That's the difficult part to sell, that's why I left it out of my response. 😝 I reckon it can be done without fully draining about 50% of the time.



  • Registered Users, Registered Users 2 Posts: 853 ✭✭✭stephenmarr




  • Registered Users, Registered Users 2 Posts: 1,611 ✭✭✭monseiur


    Hire (or borrow) a pipe freezing kit for a day, freeze both pipes at the same time. Be sure to have all the required fittings & tools etc. to hand. Don't forget to isolate power to pump at consumer unit/fuse board to be on the same side.



  • Registered Users, Registered Users 2 Posts: 1,611 ✭✭✭monseiur


    o

    oops…typo error - Last two words should read '' safe side''



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 725 ✭✭✭P_Cash


    Thanks all, managed to buy the same fitting on the day, replaced it, managed to turn off the other side only to see it leaking away after I turned it back on again so ended up changing both valves on either side of the pump. What I dont understand that while i turned all other valves off, from live feed, compression tank etc, after I switched all back on I assumed I would have to bleed any air out. so far I am seeing no signs of an airlock.

    obviously this time of year I havent all the rads on, but perhaps Ill need to bleed it somewhere



  • Registered Users, Registered Users 2 Posts: 753 ✭✭✭Escapees


    If it's two story, try bleeding some of the heaters upstairs with the pump/system not running.